<div>I don't know what section of 90.1 requires garage ventilation control either.  Nathen's assumption that CO controlled garage ventilation fans rarely run is correct.  We did a fair amount of M&V for a utility that rebated CO control retrofits.  Significant savings were achieved.  Most systems ran 24/7 and CO systems rarely operated.</div>

<div> </div>
<div>I think if you clearly make the case for the baseline and take a conservative estimate of the proposed, it will get accepted.  I was preparing to submit a project in this manner when it went bankrupt and came to a halt!<br>
<br></div>
<div class="gmail_quote">On Thu, Nov 12, 2009 at 9:13 AM, Nathan Miller <span dir="ltr"><<a href="mailto:nathanm@rushingco.com">nathanm@rushingco.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><span style="COLOR: #1f497d">I know this is a contentious issue on bldg-sim regarding whether this should be a allowable measure or not. </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d"> </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">I can tell you that on a recent office building project (LEED-NC v2.2) we submitted for energy savings from garage CO sensors. The only comment we got from the reviewer was that “ASHRAE mandates some sort of timed control or CO control as part of the mandatory measures,” so we couldn’t compare against a 24/7 constant volume system. I wish they had quoted a specific section of 90.1 for clarity. </span></p>

<p class="MsoNormal"><span style="COLOR: #1f497d"> </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">We switched the baseline system to be off for ~6 hours during the night (not in agreement with the IMC requirement for continuous air movement), and they accepted our energy savings.</span></p>

<p class="MsoNormal"><span style="COLOR: #1f497d"> </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">Our proposed case simply had the fans on a VFD and we created a custom schedule, which we presented to the reviewer, to reflect that the fans typically were at their lowest setting, and only ramped up for peak commuting hours (small peaks for morning and lunch, big peak at end of the day when all the cold engines start up and really put out the CO). </span></p>

<p class="MsoNormal"><span style="COLOR: #1f497d"> </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d">It is unclear to me if you are modeling a residential garage, where there may genuinely be 24/7 use, if you get to compare to a 24/7 constant volume system. </span></p>
<p class="MsoNormal"><span style="COLOR: #1f497d"> </span></p>
<div>
<p class="MsoNormal"><span style="FONT-SIZE: 12pt; COLOR: #1f497d">Nathan Miller</span><span style="FONT-SIZE: 12pt; COLOR: #1f497d; FONT-FAMILY: 'Times New Roman','serif'"></span></p>
<p class="MsoNormal"><i><span style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Times New Roman','serif'">Senior Energy Engineer/Mechanical Engineer</span></i></p>
<p class="MsoNormal"><span style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Times New Roman','serif'">direct: 206.788.4577</span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Times New Roman','serif'">fax: 206.285.7111 </span><span style="COLOR: #1f497d"></span></p></div>
<p class="MsoNormal"><span style="COLOR: #1f497d"> </span></p>
<div>
<div style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt">From:</span></b><span style="FONT-SIZE: 10pt"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>James Hansen<br>
<b>Sent:</b> Thursday, November 12, 2009 8:09 AM<br><b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br><b>Subject:</b> [Bldg-sim] GBCI approval of carbon monoxide control of garage fans?</span></p>
</div></div>
<div>
<div></div>
<div class="h5">
<p class="MsoNormal"> </p>
<p class="MsoNormal">Does anyone know if the GBCI reviewers are currently accepting ECMs based off of garage carbon monoxide sensors to index garage fans?  Or if this can actually be included in the model with appropriate explanation?</p>

<p class="MsoNormal"> </p>
<p class="MsoNormal">IMC requires constant ventilation for enclosed garages, but allows CO-based systems to activate the fans.  This equates to a substantial energy savings since most systems like this only operate a few hours in the morning, evening, and at lunch (other than the minimum 0.05 cfm / sq ft continuous ventilation required by the IMC).</p>

<p class="MsoNormal"> </p>
<p class="MsoNormal">If we explain the system, and explain our assumptions for the use schedules that dictate the proposed building fan schedules for the garage, is this acceptable?</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal">Do they require any backup support/studies for exactly how often the CO levels will rise above acceptable limits, or is it sufficient to make a conservative assumption that the garage fans will operate from 7-9am, 11-1pm, and 4-6pm at full load?  In my engineering experience, CO-based systems rarely run, and the circulation fans throughout the garage (which approximate the continuous 0.05 cfm / sq ft requirements of the IMC CO-based systems) are what really prevent isolated CO buildup.</p>

<p class="MsoNormal"> </p>
<p class="MsoNormal">Thanks in advance,</p>
<p class="MsoNormal"> </p>
<p class="MsoNormal"><b><span style="FONT-SIZE: 12pt; COLOR: teal">GHT Limited<br></span></b><b><span><span style="COLOR: black">James Hansen</span></span></b><b><span style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: 'Times New Roman','serif'">, PE, LEED AP</span></b></p>

<p class="MsoNormal"><b><span style="FONT-SIZE: 10pt; COLOR: black">Senior Associate</span></b><b><span style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: 'Times New Roman','serif'"></span></b></p>
<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt"><span style="COLOR: black">1010 N. Glebe Rd, Suite 200</span></span><span style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman','serif'"></span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt"><span style="COLOR: black">Arlington</span><span style="COLOR: black">, </span><span style="COLOR: black">VA</span><span style="COLOR: black">  </span><span style="COLOR: black">22201-4749</span></span><span style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: 'Times New Roman','serif'"></span></p>

<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt; COLOR: black">703-338-5754 (Cell)</span><span style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: 'Times New Roman','serif'"></span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt; COLOR: black">703-243-1200 (Office)</span><span style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: 'Times New Roman','serif'"></span></p>
<p class="MsoNormal"><span style="FONT-SIZE: 7.5pt; COLOR: black">703-276-1376 (Fax)</span><span style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: 'Times New Roman','serif'"></span></p>
<p class="MsoNormal"><span style="COLOR: teal"><a href="http://www.ghtltd.com/" target="_blank"><span style="FONT-SIZE: 10pt">www.ghtltd.com</span></a></span></p>
<div class="MsoNormal" style="TEXT-ALIGN: center" align="center"><span style="FONT-SIZE: 10pt; COLOR: blue">
<hr align="center" width="100%" size="2">
</span></div>
<p class="MsoNormal"><span style="FONT-SIZE: 10pt; COLOR: black">The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to </span><span style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Times New Roman','serif'"><a href="mailto:ght@ghtltd.com" target="_blank"><span>ght@ghtltd.com</span></a></span><span style="FONT-SIZE: 10pt; COLOR: black">, and destroy this communication and all copies thereof, including all attachments.  Thank you.</span><span style="FONT-SIZE: 10pt; COLOR: blue; FONT-FAMILY: 'Times New Roman','serif'"></span></p>
</div></div></div></div><br>_______________________________________________<br>Bldg-sim mailing list<br><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br><br></blockquote></div><br>