You are right. The Unmet hours of the proposed design can be less than base case unmet hours and the difference can be more than 50 hours (or upto 300 hours as shown by you). <br><br>However, the ASHRAE 90.1 2004 user manual on page G37states:<br>
<br>"If the number of hours that loads are unmet by either the systems or plant of either the baseline or the proposed model exceeds 300 hours of the 8760 hours simulated, or <b>differs by more than 50 hours between the two models</b>, these simulation results will not be accepted as valid." I think this is incorrect. <br>
<br>According to ASHRAE 90.1 2004 - "unmet load hours for the proposed design <b>shall not exceed</b> the number of unmet load hours for the baseline building design by more than 50." Reverse is not required. <br>
<br>So, the unmet load hours for the proposed design can be less than the number of unmet load hours for the baseline building design by more than 50. <br><br>Vishal<br clear="all">Head, Center for IT in Building Science | IIIT-H | Research University | Gachibowli | Hyderabad 500 032 <br>
Website: <a href="http://cbs.iiit.ac.in">cbs.iiit.ac.in</a> | Tel#+91 40 6653 1125| Fax: #+91 40 6653 1413| Mobile # +919949990900| Email: <a href="mailto:vishal@iiit.ac.in">vishal@iiit.ac.in</a><br>
<br><br><div class="gmail_quote">On Tue, Oct 27, 2009 at 11:57 PM, Crockett, Jim <span dir="ltr"><<a href="mailto:Jcrockett@nexant.com">Jcrockett@nexant.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div bgcolor="white" link="blue" vlink="purple" lang="EN-US">
<div>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;">It’s splitting hairs, but one item in
the email from Ashu is not quite correct.  The following sentence is from
his email, and the incorrect line is in bold:</span></font></p><div class="im">
<ul style="margin-top: 0in;" type="disc">
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">As
     per ASHRAE 90.1-2004, the unmet hours of the total building should be less
     than or equal to 300 hours and <b><i><span style="font-weight: bold; font-style: italic;">the difference in the base case and proposed case
     should be less than or equal to 50 hours.</span></i></b></span></font></li>
</ul>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
</div><p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;">What Ashrae actually says is, “. .
.unmet load hours for the <i><span style="font-style: italic;">proposed</span></i>
design shall not exceed the number of load hours for the <i><span style="font-style: italic;">baseline building design</span></i> by more than 50.” 
</span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;">If you have a building where the baseline
has 300 unmet hours, and the proposed has 0 unmet hours, no correction is
needed.  A correction is only needed if the unmet hours in the <i><span style="font-style: italic;">proposed</span></i> exceeds those in the <i><span style="font-style: italic;">baseline </span></i>by more than 50.  (or if
either exceeds 300).  Worded differently, if the baseline has 300 unmet
hours, and the proposed system has 0 unmet hours, you do not need to make the
baseline more stringent.  </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<div>
<div class="MsoNormal" style="text-align: center;" align="center"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt; color: windowtext;">
<hr align="center" size="2" width="100%">
</span></font></div>
<p class="MsoNormal"><b><font color="black" size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma; color: windowtext; font-weight: bold;">From:</span></font></b><font color="black" size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma; color: windowtext;"> Scott Criswell [mailto:<a href="mailto:scott.criswell@doe2.com" target="_blank">scott.criswell@doe2.com</a>] <br>
<b><span style="font-weight: bold;">Sent:</span></b> Tuesday, October 27, 2009
10:09 AM<br>
<b><span style="font-weight: bold;">To:</span></b> Rosenberg, Michael I<br>
<b><span style="font-weight: bold;">Cc:</span></b> ashu gupta; Nick Caton; Crockett,
Jim; Kendra Tupper; <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><div><div></div><div class="h5"><br>
<b><span style="font-weight: bold;">Subject:</span></b> Re: [Bldg-sim] Ashrae
90.1 - Unmet hours</div></div></span></font><font color="black"><span style="color: windowtext;"></span></font></p>
</div><div><div></div><div class="h5">
<p class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">I can confirm Mike's understanding of the DOE-2/eQUEST
results.  To get the correct number of hours of unmet loads, people should
MULTIPLY the Percent hours outside throttling range from BEPS or BEPU by the
total annual "hours fans on" listed in report SS-E.<br>
<br>
One other comment re: Ashu's write-up - I believe that (for DOE-2/eQUEST) a
zone temperature has to be more than one degree outside the throttling range
for that hour to be counted as an hour outside throttling range.  So for a
zone with a heating thermostat setpoint of 72 and a 2 degree throttling range
(=> 71-73 degree "throttling range"), the zone temperature would
have to be LESS THAN 70 in order for that hour to be counted.<br>
<br>
related info -<br>
We are contemplating a change to the Air-Side HVAC Summary view in the eQUEST
interface to report this total number of hours as opposed to just the percent
in the totals section at the bottom of the report.<br>
We have also just in the past several days (thanks to the efforts of Steve
Gates) added precision to the percent hours outside throttling range reported
on BEPS & BEPU and ALSO added separate reporting of hours any zone is
either under cooled or under heated, intended for reporting to LEED submission
templates.  Assuming no further changes (which is certainly not out of the
question), future releases of DOE-2/eQUEST will report the following in the
BEPS & BEPU reports:<br>
</span></font><tt><font size="2" face="Courier New"><span style="font-size: 10pt;">        
PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING RANGE =  4.45</span></font></tt><font size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";"><br>
<tt><font face="Courier New">        
PERCENT OF HOURS ANY PLANT LOAD NOT
SATISFIED               
=  0.00</font></tt><br>
<tt><font face="Courier New">        
HOURS ANY ZONE ABOVE COOLING THROTTLING
RANGE               
=    98</font></tt><br>
<tt><font face="Courier New">        
HOURS ANY ZONE BELOW HEATING THROTTLING
RANGE               
=    25</font></tt><br>
</span></font><br>
- Scott<br>
<br>
<br>
Rosenberg, Michael I wrote: </p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Ashu,</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">I am in agreement with everything you stated except
possibly this;</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p class="MsoNormal" style="margin-left: 0.25in; text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">“When
percentage of unmet is specified, than this is the percentage of total number
of hours (1 year- 8760 hours) for which the simulation is performed (not just
the occupied hours)”</span></font></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">My understanding is that
some simulation programs (DOE2 and eQuest in particular) report this as a
percentage of hours that the fan is running. I could be wrong, and I am sure
some of you DOE2 experts can comment on what is reported in the DOE2 BEPS
report.</span></font></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Mike</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<div>
<p class="MsoNormal"><b><font color="#d47500" size="3" face="Verdana"><span style="font-size: 12pt; font-family: Verdana; color: rgb(212, 117, 0); font-weight: bold;">__________________________</span></font></b>
</p>
<p class="MsoNormal"><b><font color="black" size="3" face="Verdana"><span style="font-size: 12pt; font-family: Verdana; font-weight: bold;">Michael Rosenberg</span></font></b>
<br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Senior
Commercial Buildings Energy Analyst</span></font> <br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">ENERGY
& ENVIRONMENT DIRECTORATE </span></font></p>
</div>
<p class="MsoNormal"><font color="black" size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Pacific Northwest National
Laboratory </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">2032 Todd Street</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"> </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Eugene</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">, OR 97405</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"> </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">(541)
844-1960 </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"><a href="mailto:michael.rosenberg@pnl.gov" target="_blank">michael.rosenberg@pnl.gov</a> </span></font><br>
<font color="#d47500" size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana; color: rgb(212, 117, 0);"><a href="http://www.pnl.gov" target="_blank">www.pnl.gov</a></span></font>
</p>
<div>
<div style="border-style: solid none none; border-color: -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><font color="black" size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma; font-weight: bold;">From:</span></font></b><font size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma;"> ashu
gupta [<a href="mailto:kce2@kamalcogentenergy.com" target="_blank">mailto:kce2@kamalcogentenergy.com</a>]
<br>
<b><span style="font-weight: bold;">Sent:</span></b> Monday, October 26, 2009
10:17 PM<br>
<b><span style="font-weight: bold;">To:</span></b> Rosenberg, Michael I; 'Nick
Caton'; 'Crockett, Jim'; 'Kendra Tupper'<br>
<b><span style="font-weight: bold;">Cc:</span></b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b><span style="font-weight: bold;">Subject:</span></b> RE: [Bldg-sim] Ashrae
90.1 - Unmet hours</span></font></p>
</div>
</div>
<p class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;">Dear All,</span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;">Explanation of Unmet Hours is as follows:</span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<p class="MsoNormal" style="text-align: justify;"><b><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt; font-weight: bold;">Unmet
Hours:</span></font></b></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Unmet hours of a building
are the summation of the number of hours when the heating or the cooling set
point temperature of a zone is not met either by the HVAC system or by the
plant.</span></font></p>
<p><b><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt; font-weight: bold;">Understanding/Interpreting/Calculating the number of
unmet hours:</span></font></b></p>
<ul style="margin-top: 0in;" type="disc">
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Unmet
     hour is for a particular zone when the zone indoor temperature is higher
     than the heating or cooling set point specified in that hour.</span></font></li>
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">The
     number or the percentage of unmet hours in a building is usually given as
     one of the outputs of the simulation.</span></font></li>
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Zone
     wise unmet can also be read from the various output files provided by the
     software used for simulation.</span></font></li>
</ul>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">(Example:  </span></font></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Visual DOE: “SS-J
System Peak Heating and Cooling Days” report &</span></font></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Energy Plus: Output
Variable, “Time Cooling Set point Not met”)</span></font></p>
<ul style="margin-top: 0in;" type="disc">
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">When
     two zones are unmet at the same hour, this will count to one unmet hour
     for the building.</span></font></li>
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">When
     two zones have unmet hours during different non overlapping times of a
     day, the total number of unmet hours in that day is the summation of these
     unmet hours of each zone. This total for the year should be considered as
     the total unmet hours of the building.</span></font></li>
</ul>
<p class="MsoNormal" style="text-align: justify; text-indent: 0.25in;"><i><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt; font-style: italic;">Example: </span></font></i></p>
<p class="MsoNormal" style="text-align: justify; text-indent: 0.25in;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">When each
zone is unmet in the specified hours as beside,</span></font></p>
<p class="MsoNormal" style="text-align: justify; text-indent: 0.25in;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal" style="text-align: justify; text-indent: 0.25in;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Zone 1 unmet
during:                       
6         
8         
14        16</span></font></p>
<p class="MsoNormal" style="text-align: justify; text-indent: 0.25in;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Zone 2 unmet
during:                       
6         
8         
12        16</span></font></p>
<p class="MsoNormal" style="text-align: justify; text-indent: 0.25in;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Zone 3 unmet
during:                       
7         
8         
12        13</span></font></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">           
</span></font></p>
<p class="MsoNormal" style="text-align: justify; text-indent: 0.5in;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">Total number of
unmet hours of the building: <b><span style="font-weight: bold;">7 hrs</span></b>
and not 12hrs.</span></font></p>
<p class="MsoNormal" style="text-align: justify; text-indent: 0.5in;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">6         
7         
8         
12       
13       
14        16</span></font></p>
<p class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<ul style="margin-top: 0in;" type="disc">
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">When
     percentage of unmet is specified, than this is the percentage of total
     number of hours (1 year- 8760 hours) for which the simulation is performed
     (not just the occupied hours)</span></font></li>
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">As
     per ASHRAE 90.1-2004, the unmet hours of the total building should be less
     than or equal to 300 hours and the difference in the base case and
     proposed case should be less than or equal to 50 hours.</span></font></li>
 <li class="MsoNormal" style="text-align: justify;"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">If
     unmet load hours in the proposed building exceed the unmet load hours in
     the baseline building by more than 50, then the size of equipment in the
     baseline building shall be reduced incrementally, until the condition is
     satisfied.</span></font></li>
</ul>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;"> </span></font></p>
<p class="MsoNormal"><font color="navy" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; color: navy;">Thanks</span></font></p>
<div>
<p style="margin-bottom: 12pt;"><font color="#004080" size="2" face="Times New Roman"><span style="font-size: 10pt; color: rgb(0, 64, 128);">Ashu Gupta,<br>
Project Engineer,<br>
Kamal Cogent Energy,<br>
Kamal Ratan Chanbers 1st Floor,<br>
Opp. GPO, M.I. Road,<br>
Jaipur 302001<br>
Ph 141 2373185(W)<br>
Ph 9251665008(M)<br>
</span></font><font color="#004080" face="Book Antiqua"><span style="font-family: "Book Antiqua"; color: rgb(0, 64, 128);"><a href="mailto:kce2@kamalcogentenergy.com" target="_blank"><font size="2" face="Times New Roman"><span style="font-size: 10pt; font-family: "Times New Roman";">kce2@kamalcogentenergy.com</span></font></a><br>
<a href="http://www.kamalcogentenergy.com" target="_blank"><font size="2" face="Times New Roman"><span style="font-size: 10pt; font-family: "Times New Roman";">www.kamalcogentenergy.com</span></font></a></span></font></p>
</div>
<div>
<div class="MsoNormal" style="text-align: center;" align="center"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;">
<hr align="center" size="2" width="100%">
</span></font></div>
<p class="MsoNormal"><b><font color="black" size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma; font-weight: bold;">From:</span></font></b><font size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma;"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">mailto:bldg-sim-bounces@lists.onebuilding.org</a>]
<b><span style="font-weight: bold;">On Behalf Of </span></b>Rosenberg, Michael I<br>
<b><span style="font-weight: bold;">Sent:</span></b> Tuesday, October 27, 2009
9:07 AM<br>
<b><span style="font-weight: bold;">To:</span></b> Nick Caton; Crockett, Jim;
Kendra Tupper<br>
<b><span style="font-weight: bold;">Cc:</span></b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b><span style="font-weight: bold;">Subject:</span></b> Re: [Bldg-sim] Ashrae
90.1 - Unmet hours</span></font></p>
</div>
<p class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">I think eQuest and any DOE2 based software does
report the hours of loads not being met as required by Appendix G. In the BEPS
report it gives “PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING
RANGE”. My understanding of this number is that it is a percentage of
scheduled fan run-time hours, so some calculation may be necessary.</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<div>
<p class="MsoNormal"><b><font color="#d47500" size="3" face="Verdana"><span style="font-size: 12pt; font-family: Verdana; color: rgb(212, 117, 0); font-weight: bold;">__________________________</span></font></b>
</p>
<p class="MsoNormal"><b><font color="black" size="3" face="Verdana"><span style="font-size: 12pt; font-family: Verdana; font-weight: bold;">Michael Rosenberg</span></font></b>
<br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Senior
Commercial Buildings Energy Analyst</span></font> <br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">ENERGY
& ENVIRONMENT DIRECTORATE </span></font></p>
</div>
<p class="MsoNormal"><font color="black" size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Pacific Northwest National
Laboratory </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">2032 Todd Street</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"> </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Eugene</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">, OR 97405</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"> </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">(541)
844-1960 </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"><a href="mailto:michael.rosenberg@pnl.gov" target="_blank">michael.rosenberg@pnl.gov</a> </span></font><br>
<font color="#d47500" size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana; color: rgb(212, 117, 0);"><a href="http://www.pnl.gov" target="_blank">www.pnl.gov</a></span></font>
</p>
<div>
<div style="border-style: solid none none; border-color: -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><font color="black" size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma; font-weight: bold;">From:</span></font></b><font size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma;"> Nick
Caton [<a href="mailto:ncaton@smithboucher.com" target="_blank">mailto:ncaton@smithboucher.com</a>]
<br>
<b><span style="font-weight: bold;">Sent:</span></b> Monday, October 26, 2009
8:20 PM<br>
<b><span style="font-weight: bold;">To:</span></b> Rosenberg, Michael I;
Crockett, Jim; Kendra Tupper<br>
<b><span style="font-weight: bold;">Cc:</span></b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b><span style="font-weight: bold;">Subject:</span></b> RE: [Bldg-sim] Ashrae
90.1 - Unmet hours</span></font></p>
</div>
</div>
<p class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">Mike,</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">I appreciate you
bringing this up.  This definition drives straight to the heart of
defining the issue-at-hand…  Since I kinda presented both sides of
the issue at once – I’d like to clarify where I stand regarding
what the correct interpretation <u>should be</u>.  </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">The logic is as
follows:  If a modeled year has 8,760 hours, can there be 10,000 unmet
load hours?  By strict reading of the standard’s definition below, I
would put my foot down stating there can <u>only</u> be 8,760, at most.  </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">By common practice
however, it appears a majority (myself included) sum unmet cooling/heating
hours between the zones, even if they should fall on the same modeled hour,
against the intent of the standard.  </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">My pure speculation
(for what it’s worth, as a young EIT) is this practice developed because
eQuest BDL reports don’t present the crunched numbers in a way that makes
the sum of unmet load hours, as intended by 90.1, easy to determine.  I
wouldn’t be shocked to learn other energy modeling software packages generate
LEED compliance summaries featuring unmet load hour totals in sync with the
real intent of ASHRAE 90.1.</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">If there’s
anything I’ve learned from going out on a limb, it’s that I’m
sure to learn something whether I fall or not!</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">~Nick</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<div>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"><img src="" alt="cid:489575314@22072009-0ABB" border="0" height="37" width="119"></span></font></p>
<p class="MsoNormal"><b><font color="#2d4d5e" size="2" face="Stylus BT"><span style="font-size: 11pt; font-family: "Stylus BT"; color: rgb(45, 77, 94); font-weight: bold;"> </span></font></b></p>
<p class="MsoNormal"><b><font color="#2d4d5e" size="2" face="Stylus BT"><span style="font-size: 11pt; font-family: "Stylus BT"; color: rgb(45, 77, 94); font-weight: bold;">NICK
CATON, E.I.T.</span></font></b></p>
<p class="MsoNormal"><font color="#cc9900" size="1" face="Calibri"><span style="font-size: 7.5pt; font-family: Calibri; color: rgb(204, 153, 0);">PROJECT ENGINEER</span></font></p>
<p class="MsoNormal"><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);">25501 west valley
parkway</span></font></p>
<p class="MsoNormal"><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);">olathe</span></font><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);"> ks 66061</span></font></p>
<p class="MsoNormal"><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);">direct 913 344.0036</span></font></p>
<p class="MsoNormal"><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);">fax 913 345.0617</span></font></p>
<p class="MsoNormal"><i><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94); font-style: italic;">Check
out our new web-site @ </span></font></i><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><font size="2"><span style="font-size: 10pt;">www.smithboucher.com</span></font></a></span></font><u><font color="blue" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: blue;"> </span></font></u></p>
</div>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<div>
<div style="border-style: solid none none; border-color: -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><font color="black" size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma; font-weight: bold;">From:</span></font></b><font size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma;">
Rosenberg, Michael I [<a href="mailto:michael.rosenberg@pnl.gov" target="_blank">mailto:michael.rosenberg@pnl.gov</a>]
<br>
<b><span style="font-weight: bold;">Sent:</span></b> Monday, October 26, 2009
7:39 PM<br>
<b><span style="font-weight: bold;">To:</span></b> Nick Caton; Crockett, Jim; <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b><span style="font-weight: bold;">Subject:</span></b> RE: [Bldg-sim] Ashrae
90.1 - Unmet hours</span></font></p>
</div>
</div>
<p class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Nick,</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Your interpretation is the correct one. According to
the definitions in Standard 90.1.</span></font></p>
<p><b><i><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial; font-weight: bold; font-style: italic;">unmet
load hour:</span></font></i></b><font face="Arial"><span style="font-family: Arial;">
an hour in which one or more zones is outside of the thermostat setpoint range.</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Mike</span></font></p>
<div>
<p class="MsoNormal"><b><font color="#d47500" size="3" face="Verdana"><span style="font-size: 12pt; font-family: Verdana; color: rgb(212, 117, 0); font-weight: bold;">__________________________</span></font></b>
</p>
<p class="MsoNormal"><b><font color="black" size="3" face="Verdana"><span style="font-size: 12pt; font-family: Verdana; font-weight: bold;">Michael Rosenberg</span></font></b>
<br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Senior
Commercial Buildings Energy Analyst</span></font> <br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">ENERGY
& ENVIRONMENT DIRECTORATE </span></font></p>
</div>
<p class="MsoNormal"><font color="black" size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Pacific Northwest National
Laboratory </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">2032 Todd Street</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"> </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">Eugene</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">, OR 97405</span></font><font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"> </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;">(541)
844-1960 </span></font><br>
<font size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana;"><a href="mailto:michael.rosenberg@pnl.gov" target="_blank">michael.rosenberg@pnl.gov</a> </span></font><br>
<font color="#d47500" size="2" face="Verdana"><span style="font-size: 10pt; font-family: Verdana; color: rgb(212, 117, 0);"><a href="http://www.pnl.gov" target="_blank">www.pnl.gov</a></span></font>
</p>
<div>
<div style="border-style: solid none none; border-color: -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><font color="black" size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma; font-weight: bold;">From:</span></font></b><font size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma;"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">mailto:bldg-sim-bounces@lists.onebuilding.org</a>]
<b><span style="font-weight: bold;">On Behalf Of </span></b>Nick Caton<br>
<b><span style="font-weight: bold;">Sent:</span></b> Monday, October 26, 2009
5:33 PM<br>
<b><span style="font-weight: bold;">To:</span></b> Crockett, Jim; <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b><span style="font-weight: bold;">Subject:</span></b> Re: [Bldg-sim] Ashrae
90.1 - Unmet hours</span></font></p>
</div>
</div>
<p class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">Jim,</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">That’s
actually a really good question that I was afraid to ask when I first
encountered it – kudos to you!  I’ve currently resolved to
follow what others seemed to be doing within and outside of my office: 
Sum up all unmet hours for cooling and heating between the zones just as you
describe.   In your example, I’d agree that the unmet hours of
your 301 zone building total 301.</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">I do agree that this
doesn’t seem intuitively to be the intent of the standard, however
between what is suggested within 90.1, the LEED handbook, and the LEED credit
templates – I honestly can’t see any clear indication either way on
which is the appropriate interpretation.  </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">I think the
appropriate metric for ensuring appropriately sized systems should be something
like: “hours of the modeled year in which at least one zone has an unmet
cooling/heating load,”  but I think that was avoided by all
concerned parties because it’s too wordy!</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">My acting
interpretation, again referencing your example, is that all systems of your 301
zone example affecting the zones with unmet cooling/heating hours should have
their heating/cooling/overall sizing capacity ratios increased incrementally
until the design hours fall below 300 (and/or within 50 of the sum from the
other model, depending on your situation).</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);">Afraid I’m
only really adding to the discussion here without providing a solid
answer.  Would like to echo the desire to see anyone’s experiences
that would help us know the “right” way to interpret this (in my
case, specifically in the context of a LEED submittal).</span></font></p>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<div>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"><img src="" alt="cid:489575314@22072009-0ABB" border="0" height="37" width="119"></span></font></p>
<p class="MsoNormal"><b><font color="#2d4d5e" size="2" face="Stylus BT"><span style="font-size: 11pt; font-family: "Stylus BT"; color: rgb(45, 77, 94); font-weight: bold;"> </span></font></b></p>
<p class="MsoNormal"><b><font color="#2d4d5e" size="2" face="Stylus BT"><span style="font-size: 11pt; font-family: "Stylus BT"; color: rgb(45, 77, 94); font-weight: bold;">NICK
CATON, E.I.T.</span></font></b></p>
<p class="MsoNormal"><font color="#cc9900" size="1" face="Calibri"><span style="font-size: 7.5pt; font-family: Calibri; color: rgb(204, 153, 0);">PROJECT ENGINEER</span></font></p>
<p class="MsoNormal"><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);">25501 west valley
parkway</span></font></p>
<p class="MsoNormal"><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);">olathe</span></font><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);"> ks 66061</span></font></p>
<p class="MsoNormal"><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);">direct 913 344.0036</span></font></p>
<p class="MsoNormal"><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94);">fax 913 345.0617</span></font></p>
<p class="MsoNormal"><i><font color="#2d4d5e" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: rgb(45, 77, 94); font-style: italic;">Check
out our new web-site @ </span></font></i><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"><a href="http://www.smithboucher.com" title="blocked::www.smithboucher.com" target="_blank"><font size="2"><span style="font-size: 10pt;">www.smithboucher.com</span></font></a></span></font><u><font color="blue" size="2" face="Calibri"><span style="font-size: 10pt; font-family: Calibri; color: blue;"> </span></font></u></p>
</div>
<p class="MsoNormal"><font color="#1f497d" size="2" face="Calibri"><span style="font-size: 11pt; font-family: Calibri; color: rgb(31, 73, 125);"> </span></font></p>
<div>
<div style="border-style: solid none none; border-color: -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">
<p class="MsoNormal"><b><font color="black" size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma; font-weight: bold;">From:</span></font></b><font size="2" face="Tahoma"><span style="font-size: 10pt; font-family: Tahoma;"> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">mailto:bldg-sim-bounces@lists.onebuilding.org</a>]
<b><span style="font-weight: bold;">On Behalf Of </span></b>Crockett, Jim<br>
<b><span style="font-weight: bold;">Sent:</span></b> Monday, October 26, 2009
4:27 PM<br>
<b><span style="font-weight: bold;">To:</span></b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b><span style="font-weight: bold;">Subject:</span></b> [Bldg-sim] Ashrae 90.1 -
Unmet hours</span></font></p>
</div>
</div>
<p class="MsoNormal"><font color="black" size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">Ashrae 90.1 (2004) Appendix
G3.1.2.2 requires a baseline building to have less than 300 unmet hours.
 What exactly does this mean?</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">To illustrate my question:
 assume you have a building with 301 zones, and each zone has 1 unmet hour
per year.  This gives you a total of 301 unmet hours, and requires you to
increase your baseline equipment capacity.  But you could argue that, on
average, the building has only 1 unmet hour per year.</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">Have any of you run into
this?  Is it addressed in an addendum somewhere, etc?</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">Any help is
appreciated.  Thanks,</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">Jim Crockett, P.E.</span></font></p>
<p class="MsoNormal"><font color="black" size="3" face="Courier New"><span style="font-size: 12pt; font-family: "Courier New";"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">Senior Project Engineer</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">Energy & Carbon
Management</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">Nexant, Inc.</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">4021 S. 700 E., Suite 250</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">Salt Lake City</span></font><font size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">, Utah 84107</span></font></p>
<p class="MsoNormal"><font color="black" size="3" face="Courier New"><span style="font-size: 12pt; font-family: "Courier New";"> </span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">(801) 639-5603 - phone</span></font></p>
<p class="MsoNormal"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt; font-family: "Courier New";">(801) 266-4786 - fax</span></font></p>
<p class="MsoNormal"><font color="black" size="3" face="Courier New"><span style="font-size: 12pt; font-family: "Courier New";"> </span></font></p>
<pre><font color="black" size="2" face="Courier New"><span style="font-size: 10pt;"> </span></font></pre><pre style="text-align: center;"><font color="black" size="2" face="Courier New"><span style="font-size: 10pt;">
<hr align="center" size="4" width="90%">
</span></font></pre><pre><font color="black" size="2" face="Courier New"><span style="font-size: 10pt;"> </span></font></pre><pre><font color="black" size="2" face="Courier New"><span style="font-size: 10pt;">_______________________________________________</span></font></pre>
<pre><font color="black" size="2" face="Courier New"><span style="font-size: 10pt;">Bldg-sim mailing list</span></font></pre><pre><font color="black" size="2" face="Courier New"><span style="font-size: 10pt;"><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a></span></font></pre>
<pre><font color="black" size="2" face="Courier New"><span style="font-size: 10pt;">To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a></span></font></pre>
<pre><font color="black" size="2" face="Courier New"><span style="font-size: 10pt;">  </span></font></pre></div></div></div>
</div>
<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>