>From table G3.1:<br><br>"The HVAC system(s) in the baseline building design shall be of the type and<br>description specified in G3.1.1, shall meet the general HVAC system<br>requirements specified in G3.1.2, and shall meet any system-specific<br>
requirements in G3.1.3 that are applicable to the baseline HVAC system<br>type(s)."<br><br>the only time the existing building properties are used are for the building envelope.<br><br>--<br>Karen<br><br><div class="gmail_quote">
On Fri, Sep 4, 2009 at 9:50 AM, James Hansen <span dir="ltr"><<a href="mailto:JHANSEN@ghtltd.com">JHANSEN@ghtltd.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">










<div link="blue" vlink="purple" lang="EN-US">

<div>

<p><span style="color: rgb(31, 73, 125);">Thanks for the response
Seth.  The entire building is undergoing a renovation (new windows,
insulation, lighting)…and I’m going to keep the existing HVAC
system in the EXISTING portion of the building for my baseline model.  I
just don’t know how to treat the NEW portion of my building in the
baseline model.  The plant is interconnected, so Item No 2 in Table G3.1
doesn’t apply.  I want to include the existing building in the model
(and I have to).</span></p>

<p><span style="color: rgb(31, 73, 125);"> </span></p>

<p><span style="color: rgb(31, 73, 125);">Any other advice on how to properly
set up the baseline HVAC system for a new portion of an existing building if
the proposed chilled water plant is being expanded to accommodate new load but
the existing airside systems in the existing building are NOT being touched?</span></p>

<p><span style="color: rgb(31, 73, 125);"> </span></p>

<p><span style="color: rgb(31, 73, 125);">Common sense would say that my
baseline building also has a new App G chiller to accommodate new load and the
new airside systems are shutoff boxes….but if there is a chance that the
new portion of the building is treated as a standalone 15,000 square foot
addition, packaged RTUs may make the proposed system even more efficient.</span></p>

<p><span style="color: rgb(31, 73, 125);"> </span></p>

<p><span style="color: rgb(31, 73, 125);">Paul, thanks for the email…I’m
going to look thru CIRs and see what I can find.  Can’t wait for
LEED v3.0 where this convenient Option goes away.</span></p>

<p><span style="color: rgb(31, 73, 125);"> </span></p>

<p><span style="color: rgb(31, 73, 125);">Thanks again,</span></p><div class="im">

<p><span style="color: rgb(31, 73, 125);"> </span></p>

<div>

<p><b><span style="font-size: 12pt; color: teal;">GHT Limited<br>
</span></b><b><span><span style="color: black;">James Hansen</span></span></b><b><span style="font-size: 12pt; font-family: "Times New Roman","serif"; color: black;">,
PE, LEED AP</span></b></p>

<p><b><span style="font-size: 10pt; color: black;">Senior Associate</span></b><b><span style="font-size: 12pt; font-family: "Times New Roman","serif"; color: black;"></span></b></p>

<p><span style="font-size: 7.5pt;"><span style="color: black;">1010 N. Glebe Rd, Suite 200</span></span><span style="font-size: 12pt; font-family: "Times New Roman","serif"; color: rgb(31, 73, 125);"></span></p>


<p><span style="font-size: 7.5pt;"><span style="color: black;">Arlington</span><span style="color: black;">, </span><span style="color: black;">VA</span><span style="color: black;">  </span><span style="color: black;">22201-4749</span></span><span style="font-size: 12pt; font-family: "Times New Roman","serif"; color: black;"></span></p>


<p><span style="font-size: 7.5pt; color: black;">703-338-5754 (Cell)</span><span style="font-size: 12pt; font-family: "Times New Roman","serif"; color: black;"></span></p>

<p><span style="font-size: 7.5pt; color: black;">703-243-1200 (Office)</span><span style="font-size: 12pt; font-family: "Times New Roman","serif"; color: black;"></span></p>

<p><span style="font-size: 7.5pt; color: black;">703-276-1376 (Fax)</span><span style="font-size: 12pt; font-family: "Times New Roman","serif"; color: black;"></span></p>

</div>

<p><span style="color: teal;"><a href="http://www.ghtltd.com/" target="_blank"><span style="font-size: 10pt;">www.ghtltd.com</span></a></span><span style="color: rgb(31, 73, 125);"></span></p>

</div><div>

<div style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">

<p><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> Seth P. Spangler
[mailto:<a href="mailto:sspangle@rmf.com" target="_blank">sspangle@rmf.com</a>] <br><div class="im">
<b>Sent:</b> Friday, September 04, 2009 9:23 AM<br>
</div><b>To:</b> James Hansen; <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> RE: [Bldg-sim] Existing building HVAC modeling</span></p>

</div>

</div><div><div></div><div class="h5">

<p> </p>

<p><span style="font-size: 10pt; color: blue;">James,</span></p>

<p><span style="font-size: 10pt; color: blue;"> </span></p>

<p><span style="font-size: 10pt; color: blue;">If you are only adding an additional floor – and are not
renovating any portion of the existing 1<sup>st</sup>-4<sup>th</sup> floors
then I would model the 5<sup>th</sup> floor as if it was a new building by itself
according to App. G guidelines. See Table G 3.1 item no. 2 in 90.1-2004</span></p>

<p><span style="font-size: 10pt; color: blue;"> </span></p>

<p><span style="font-size: 10pt; color: blue;"> </span></p>

<p><span style="font-size: 10pt; color: blue;">If the entire building is undergoing a renovation but the existing
HVAC systems are existing to remain then the building would be modeled to
reflect the existing system types and capacities. Refer to the LEED manual for
these guidelines.</span></p>

<p><span style="font-size: 10pt; color: blue;"> </span></p>

<p><span style="font-size: 10pt; color: blue;">Hope this helps.</span></p>

<p><span style="font-size: 10pt; color: blue;"> </span></p>

<div>

<p><span style="font-size: 10pt; font-family: "Georgia","serif"; color: blue;">Seth Spangler, LEED® AP </span></p>

<p><span style="font-size: 10pt; font-family: "Georgia","serif"; color: blue;">Project Engineer</span></p>

<p><span style="font-size: 12pt; font-family: "Georgia","serif"; color: blue;"> </span></p>

<p><span style="font-size: 10pt; font-family: "Georgia","serif"; color: blue;">RMF Engineering, Inc </span></p>

<p><span style="font-size: 10pt; font-family: "Georgia","serif"; color: blue;">Ph: (843) 971-9639 ext:1497</span></p>

<p><span style="font-size: 10pt; font-family: "Georgia","serif"; color: blue;">Fax: (843) 971-9641 </span></p>

</div>

<p><span style="font-size: 10pt; font-family: "Georgia","serif"; color: blue;"><a href="mailto:sspangle@rmf.com" target="_blank">sspangle@rmf.com</a></span></p>

<div>

<div style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">

<p><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>James
Hansen<br>
<b>Sent:</b> Friday, September 04, 2009 9:07 AM<br>
<b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> [Bldg-sim] Existing building HVAC modeling</span></p>

</div>

</div>

<p> </p>

<p>I’m modeling a building for LEED EAc1 compliance, and
was wondering how you are supposed to model existing building HVAC systems if
you are adding square footage to the building.</p>

<p> </p>

<p>Let’s assume you have a 4-story building with a
2-chiller HVAC plant and dual temp boxes.  If you were to add a 5<sup>th</sup>
floor to the building, what would your baseline model look like?  I know
that the 1<sup>st</sup> four floors would use the existing HVAC system, but
would your new 5<sup>th</sup> floor be treated as a new 15,000 square foot area
with packaged RTUs, or would you add a new chiller to the existing HVAC chilled
water plant, and have that chiller meet all the requirements of App G, and have
shutoff VAV boxes for the 5<sup>th</sup> floor in lieu of dual temp boxes? </p>

<p> </p>

<p>For reference, under our proposed design, we are doing just
that:  adding a frictionless chiller to the plant to make up the extra
load.</p>

<p> </p>

<p><b><span style="font-size: 12pt; color: teal;">GHT Limited<br>
</span></b><b><span style="color: black;">James
Hansen</span></b><b><span style="font-size: 12pt; font-family: "Times New Roman","serif"; color: black;">, PE, LEED AP</span></b></p>

<p><b><span style="font-size: 10pt; color: black;">Senior Associate</span></b></p>

<p><span style="font-size: 7.5pt; color: black;">1010 N. Glebe Rd, Suite 200</span></p>

<p><span style="font-size: 7.5pt; color: black;">Arlington, VA  22201-4749</span></p>

<p><span style="font-size: 7.5pt; color: black;">703-338-5754 (Cell)</span></p>

<p><span style="font-size: 7.5pt; color: black;">703-243-1200 (Office)</span></p>

<p><span style="font-size: 7.5pt; color: black;">703-276-1376 (Fax)</span></p>

<p><span style="color: teal;"><a href="http://www.ghtltd.com/" target="_blank"><span style="font-size: 10pt;">www.ghtltd.com</span></a></span></p>

<div style="text-align: center;" align="center"><span style="font-size: 10pt; color: blue;">

<hr size="2" width="100%" align="center">

</span></div>

<p><span style="font-size: 10pt; color: black;">The information contained in this communication is confidential,
may be privileged, and is intended only for the use of the addressee.  It
is the property of GHT Limited.  Unauthorized use, disclosure or copying
of this communication or any part thereof is strictly prohibited and may be
unlawful.  If you have received this communication in error, please notify
me immediately by return e-mail or by e-mail to </span><span style="font-size: 10pt; font-family: "Times New Roman","serif"; color: black;"><a href="mailto:ght@ghtltd.com" target="_blank"><span>ght@ghtltd.com</span></a></span><span style="font-size: 10pt; color: black;">, and
destroy this communication and all copies thereof, including all
attachments.  Thank you.</span></p>

</div></div></div>

</div><div><div></div><div class="h5">

<p align="left"><font size="2"><font face="Tahoma"><font color="#0000ff">
<hr>
</font></font><font color="#0000ff"><font color="#000000"><font face="Arial">The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to </font><a href="mailto:ght@ghtltd.com" target="_blank"><font face="Arial">ght@ghtltd.com</font></a><font face="Arial">, and destroy this communication and all copies thereof, including all attachments.  Thank you.</font></font><font color="#000000" face="Tahoma"></font></font></font></p>

</div></div><br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>