Jeff,<br><br>Thank you for responding. I agree that it depends on the climate. <br><br>Design Builder has the option called 'flip' while making the double pane assembly. Hence I was not clear as to which surface is the coating on and what does flip actually mean?<br>
<br><br clear="all">Deepa<br>
<br><br><div class="gmail_quote">On Thu, Aug 27, 2009 at 8:26 PM, Jeff Haberl <span dir="ltr"><<a href="mailto:jhaberl@tamu.edu">jhaberl@tamu.edu</a>></span> wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<p><font color="navy" face="Arial" size="2">
The "surface" depends on the climate. <br><br>Cooling dominated climates benefit from the low-E on the inside surface of the outside pane. <br><br>Heating dominated climates benefit from the low-E on the outside surface of the inside pane. <br>
<br>Such characteristics are normally defined by the applicable codes for a given location. <br><br>Jeff
<br>BB 8=!  8=)  :=)  8=)  ;=)  8=)  8=(  8=)  :=')  8=)  8=)  8=? BB
<br>
<br>Jeff S. Haberl, Ph.D., P.E., <a href="mailto:FASHRAE...................jhaberl@esl.tamu.edu" target="_blank">FASHRAE...................jhaberl@esl.tamu.edu</a>
<br>
<br>Professor......................................................Office Ph: 979-845-6507
<br>
<br>Department of Architecture.......................Lab Ph: 979-845-6065 
<br>
<br>Energy Systems Laboratory.......................FAX: 979-862-2457 
<br>
<br>Texas A&M University..............................77843-3581
<br>
<br>College Station, Texas, USA.......................URL: <a href="http://www-esl.tamu.edu" target="_blank">www-esl.tamu.edu</a>
<br>
<br>BB 8=/  8=)  :=)  8=)  ;=)  8=)  8=()  8=) 8=?  8=)  8=)  8= BB
<br> </font></p>
<p></p><hr width="100%" align="center" size="2">
<font face="Tahoma" size="2">
<b>From</b>: <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a> <<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>>
<br><b>To</b>: Bldg-Sim <<a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a>>
<br><b>Sent</b>: Thu Aug 27 21:58:12 2009<br><b>Subject</b>: [Bldg-sim] Design Builder : Low E coated surface
<br></font><div><div></div><div class="h5">
Hello all,<br><br>I am trying to model several types of Low E glazing in Design Builder to understand the effect on the peak heating and cooling load. <br><br>While choosing different glazing, I could not understand which surface of the glazing has the Low E coating. <br>
<br>I would appreciate any inputs about this aspect.<br><br><br>Thanks,<br clear="all">Deepa Chandrashekaran, LEED AP<br>Master of Building Science 2010<br>University of Southern California<br><br>
</div></div></blockquote></div><br>