color=#0000ff size=2>I may be a bit late in responding and haven't gone through 
all the e-mails about it.  That being said,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=578253519-02072009><FONT face=Arial 
color=#0000ff size=2>I think it makes a difference as to how it's divided 
up.  The difference isn't in fan consumption, but where the fan heat is 
dumped.  That will effect the cooling and heating loads.  For example, 
if all the energy were in the supply fan, that would increase supply 
temperature of require the temperature off the coil to be lowered.  If 
it was all in the return fan, that fan energy would just end 
up increasing the return temperature.  I'm thinking more how that 
difference affects the economizer cycle and ventilation air. I'd proportion 
it out based on the relative HP's of your supply, return and exhaust fans.  
Someone had a 70-20-10 split, which seems to be a good stab at 
it..</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=578253519-02072009></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=578253519-02072009><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=578253519-02072009><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=578253519-02072009>
<DIV align=left>
<P class=MsoNormal><B><FONT face=Arial color=#0069aa size=1><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 8pt; COLOR: #0069aa; FONT-FAMILY: Arial">Michael 
Williamson</SPAN></FONT></B><FONT face=Arial color=#939598 size=1><SPAN 
style="FONT-SIZE: 8pt; COLOR: #939598; FONT-FAMILY: Arial"> |</SPAN></FONT> <B><SPAN 
style="FONT-WEIGHT: bold"><BR></SPAN></B><FONT face=Arial color=#939598 
size=1><SPAN 
style="FONT-SIZE: 8pt; COLOR: #939598; FONT-FAMILY: Arial">Phone: 617-494-9090 
| Fax: 617-494-9292</SPAN></FONT><?xml:namespace prefix = o ns = 
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></P><FONT face=Arial 
color=#939598 size=1><SPAN 
style="FONT-SIZE: 8pt; COLOR: #939598; FONT-FAMILY: Arial">
<P class=MsoNormal><BR></SPAN></FONT><FONT face=Arial size=1><SPAN 
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial"><A 
title=mailto:tdooleyl@cosentini-ma.com 
href="mailto:mwilliamson@cosentini-ma.com">mwilliamson@cosentini-ma.com</A></SPAN></FONT><FONT 
face=Arial size=1><SPAN 
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial"><BR><BR><B><FONT color=#939598><SPAN 
style="FONT-WEIGHT: bold; COLOR: #939598">Cosentini Associates - A Tetra Tech 
Company<BR></SPAN></FONT></B><FONT color=#939598><SPAN 
style="COLOR: #939598">One Broadway - Tenth Floor - <?xml:namespace prefix = st1 
ns = "urn:schemas-microsoft-com:office:smarttags" /><st1:place 
w:st="on"><st1:City w:st="on">Cambridge</st1:City>, <st1:State 
w:st="on">MA</st1:State> <st1:PostalCode 
w:st="on">02142</st1:PostalCode></st1:place><BR><A 
title=http://www.cosentini.com/ 
href="http://www.cosentini.com/">www.cosentini.com</A><BR><BR></P><o:p></o:p></SPAN></FONT></SPAN></FONT>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"><o:p> </o:p></SPAN></FONT></P></DIV></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> James Hess [mailto:JHess@tmecorp.com] 
<BR><B>Sent:</B> Thursday, July 02, 2009 10:28 AM<BR><B>To:</B> 
Bldg-Sim<BR><B>Subject:</B> Re: [Bldg-sim] Appendix G Fan 
Power<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>
<DIV>We got a review comment on a recent LEED project asking us to break down 
the baseline HVAC power into components even though there is no direction, or 
requirement, from 90.1-2004 to do so.</DIV>
<DIV><BR></DIV>
<DIV>Can someone please help me understand why this would be 
necessary? </DIV>
<DIV><BR></DIV>
<DIV>LEED guidelines say we have to model per Appendix G, but Appendix G doesn't 
say we have to do this.</DIV>
<DIV><BR></DIV>
<DIV>I do not think it is necessary to do this as the baseline total fan energy 
consumption numbers would still be the same.</DIV>
<DIV><BR></DIV>
<DIV>The equation in Appendix G is meant to give a total allowance (for each 
system) for supply, return, and exhaust fans. It doesn't matter if we break the 
allowance down into components or not as the total fan energy consumption 
remains the same. Therefore, there is no value in doing this.</DIV>
<DIV><BR></DIV>
<DIV>If we did break the fan energy numbers into components, how would we do 
that given that there is no direction from ASHRAE or LEED on how to do 
this?</DIV>
<DIV><BR></DIV>
<DIV>Thoughts?</DIV>
<DIV><BR></DIV>
<DIV>Regards,</DIV>
<DIV><BR>
<DIV>James A. Hess, PE, CEM</DIV>
<DIV>Energy Engineer</DIV>
<DIV>TME, Inc.</DIV></DIV>
<DIV><BR>On Jul 2, 2009, at 8:41 AM, "Jeremy Poling" <<A 
href="mailto:jpoling@epsteinglobal.com"><A 
href="mailto:jpoling@epsteinglobal.com">jpoling@epsteinglobal.com</A></A>> 
wrote:<BR><BR></DIV>
<DIV></DIV>
<BLOCKQUOTE type="cite">
  <DIV><O:SMARTTAGTYPE name="PostalCode" 
  namespaceuri="urn:schemas-microsoft-com:office:smarttags"><O:SMARTTAGTYPE 
  name="State" 
  namespaceuri="urn:schemas-microsoft-com:office:smarttags"><O:SMARTTAGTYPE 
  name="City" 
  namespaceuri="urn:schemas-microsoft-com:office:smarttags"><O:SMARTTAGTYPE 
  name="place" 
  namespaceuri="urn:schemas-microsoft-com:office:smarttags"><O:SMARTTAGTYPE 
  name="Street" 
  namespaceuri="urn:schemas-microsoft-com:office:smarttags"><O:SMARTTAGTYPE 
  name="address" namespaceuri="urn:schemas-microsoft-com:office:smarttags"><!--[if !mso]>
  <STYLE>st1\:* {
        BEHAVIOR: url(#default#ieooui)
}
</STYLE>
<![endif]-->
  <STYLE>@font-face {
        font-family: Tahoma;
}
@font-face {
        font-family: Calibri;
}
@font-face {
        font-family: Verdana;
}
@font-face {
        font-family: Webdings;
}
@font-face {
        font-family: Garamond;
}
@page Section1 {size: 8.5in 11.0in; margin: 1.0in 1.0in 1.0in 1.0in; }
A:link {
        mso-style-priority: 99
}
SPAN.MSOHYPERLINK {
        mso-style-priority: 99
}
A:visited {
        mso-style-priority: 99
}
SPAN.MSOHYPERLINKFOLLOWED {
        mso-style-priority: 99
}
P.MsoNormal {
        FONT-SIZE: 11pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: Calibri; mso-believe-normal-left: yes
}
LI.MsoNormal {
        FONT-SIZE: 11pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: Calibri; mso-believe-normal-left: yes
}
DIV.MsoNormal {
        FONT-SIZE: 11pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: Calibri; mso-believe-normal-left: yes
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline
}
SPAN.EmailStyle17 {
        COLOR: windowtext; FONT-FAMILY: Calibri; mso-style-type: personal
}
SPAN.EmailStyle18 {
        FONT-WEIGHT: normal; COLOR: windowtext; FONT-STYLE: normal; FONT-FAMILY: Arial; TEXT-DECORATION: none; mso-style-type: personal
}
SPAN.EmailStyle19 {
        COLOR: navy; FONT-FAMILY: Arial; mso-style-type: personal-reply
}
DIV.Section1 {
        page: Section1
}
</STYLE>

  <STYLE>P.MsoNormal {
        MARGIN-LEFT: 3pt
}
</STYLE>
<!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
  <DIV class=Section1>
  <P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">This issue will start 
  to become a problem for anyone running energy models for LEED projects – 
  reviewers on the new review teams are asking to see the total fan power for 
  the baseline broken into individual components and reported as such in the 
  template for Energy and Atmosphere Credit 1.  The 90.1-2004 User’s Manual 
  is also silent on the issue; however it raises another issue.  In the 
  example (Example G-J on page G-28) the calculations use total building supply 
  CFM for an 80,000SF medical office building.  Since the baseline is 
  System 5 in that example and there would be multiple zones for the baseline, 
  it appears that the equation should be used for the whole building only and 
  not individual systems.  Is this how you are applying the formulas?  
  The user’s manual notes that fan powered VAV boxes are NOT included in the 
  total fan power number as calculated from 
  G3.1.2.9.<O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><O:P></O:P></SPAN></FONT></P>
  <DIV>
  <P class=MsoNormal><STRONG><B><FONT face=Arial color=navy size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">Jeremy R. Poling, 
  LEED AP</SPAN></FONT></B></STRONG><FONT face=Arial color=navy size=1><SPAN 
  style="FONT-SIZE: 9pt; COLOR: navy; FONT-FAMILY: Arial"><BR></SPAN></FONT><FONT 
  face=Arial color=navy size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">Senior Sustainability 
  Analyst<BR>Strategic Services</SPAN></FONT><FONT color=navy><SPAN 
  style="COLOR: navy"><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><I><FONT face=Arial color=navy size=1><SPAN 
  style="FONT-SIZE: 8pt; COLOR: navy; FONT-STYLE: italic; FONT-FAMILY: Arial">Site 
  Solutions | Operations | Sustainability</SPAN></FONT></I><FONT 
  face=Arial color=navy size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><BR><BR></SPAN></FONT><STRONG><B><FONT 
  face=Arial color=#c75b12 size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: #c75b12; FONT-FAMILY: Arial">EPSTEIN</SPAN></FONT></B></STRONG><FONT 
  face=Arial color=navy size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><BR></SPAN></FONT><FONT 
  face=Arial color=navy size=1><SPAN 
  style="FONT-SIZE: 8pt; COLOR: navy; FONT-FAMILY: Arial">Architecture<BR>Interiors<BR>Engineering<BR>Construction</SPAN></FONT><FONT 
  face=Arial color=navy size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><BR><BR></SPAN></FONT><STRONG><B><FONT 
  face=Arial color=green size=1><SPAN 
  style="FONT-SIZE: 9pt; COLOR: green; FONT-FAMILY: Arial">Epstein is a firm 
  believer in sustainability. We ask that you please consider the environment 
  before printing this e-mail.</SPAN></FONT></B></STRONG><O:P></O:P></P></DIV>
  <DIV>
  <DIV class=MsoNormal style="TEXT-ALIGN: center" align=center><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'">
  <HR tabIndex=-1 align=center width="100%" SIZE=2>
  </SPAN></FONT></DIV>
  <P class=MsoNormal><B><FONT face=Tahoma size=2><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">From:</SPAN></FONT></B><FONT 
  face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma"> <A 
  href="mailto:bldg-sim-bounces@lists.onebuilding.org"><A 
  href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</A></A> 
  [mailto:bldg-sim-bounces@lists.onebuilding.org] <B><SPAN 
  style="FONT-WEIGHT: bold">On Behalf Of </SPAN></B>Ellen Franconi<BR><B><SPAN 
  style="FONT-WEIGHT: bold">Sent:</SPAN></B> Thursday, July 02, 2009 7:37 
  AM<BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> Vikram Sami; Bldg-Sim; 
  Michael I Rosenberg<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> 
  Re: [Bldg-sim] Appendix G Fan Power</SPAN></FONT><FONT face="Times New Roman" 
  size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><O:P></O:P></SPAN></FONT></P></DIV>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN 
  style="FONT-SIZE: 11pt"><O:P></O:P></SPAN></FONT></P>
  <DIV>
  <P class=MsoNormal><FONT face=Tahoma size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">At my firm, we proportion the 
  baseline total fan power determined as an aggregated W/CFM based 
  on  the hp assigned to the fan motors (supply, return, 
  exhaust) in the design documents. Of course this assumes that your 
  baseline and your proposed design have a one-to-one fan 
  correspondence.  <O:P></O:P></SPAN></FONT></P></DIV>
  <DIV>
  <P class=MsoNormal><FONT face=Tahoma size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">Ellen<O:P></O:P></SPAN></FONT></P></DIV>
  <DIV>
  <P class=MsoNormal><FONT face=Tahoma size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma"><O:P></O:P></SPAN></FONT></P></DIV>
  <DIV>
  <P class=MsoNormal><FONT face=Tahoma size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma"><O:P></O:P></SPAN></FONT></P></DIV>
  <DIV>
  <P class=MsoNormal><FONT face=Tahoma size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">Ellen Franconi, Ph.D., LEED 
  AP<BR>Senior Energy Analyst<BR>Architectural Energy Corporation<BR><ST1:STREET 
  w:st="on"><ST1:ADDRESS w:st="on">2540 Frontier 
  Avenue</ST1:ADDRESS></ST1:STREET><BR><ST1:PLACE w:st="on"><ST1:CITY 
  w:st="on">Boulder</ST1:CITY>, <ST1:STATE w:st="on">CO</ST1:STATE> 
  <ST1:POSTALCODE w:st="on">80301</ST1:POSTALCODE></ST1:PLACE><BR>tel. 
  303-444-4149<BR>fax 303-444-4303<BR><A 
  href="mailto:efranconi@archenergy.com"></A><A 
  href="mailto:efranconi@archenergy.com"><A 
  href="mailto:efranconi@archenergy.com">efranconi@archenergy.com</A></A><BR><A 
  href="http://www.archenergy.com/"></A><A href="http://www.archenergy.com/"><A 
  href="http://www.archenergy.com/">http://www.archenergy.com/</A></A><BR><BR><BR>>>> 
  "Rosenberg, Michael I" <<A href="mailto:michael.rosenberg@pnl.gov"><A 
  href="mailto:michael.rosenberg@pnl.gov">michael.rosenberg@pnl.gov</A></A>> 
  7/1/2009 4:48 PM >>><O:P></O:P></SPAN></FONT></P></DIV>
  <P class=MsoNormal><FONT face=Arial size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">You have calculated the kW/cfm 
  correctly according to the 2004 version of Appendix G. The allowance actually 
  goes up a little in 2007, for your case. As for the second part of your 
  question, no you do not apply the same kW/cfm to the exhaust fan. The 
  calculated allowed fan power the total allowed power for all fans that are 
  part of the system, including the exhaust fan. The cfm component is based on 
  the supply fan cfm only. Unfortunately, Appendix G gives no direction on how 
  to divide the allowed fan power up among the various fans in the system. 
  <O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Arial size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Arial size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Mike<O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Arial size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><O:P></O:P></SPAN></FONT></P>
  <DIV>
  <P class=MsoNormal 
  style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><B><FONT 
  face=Verdana color=#d47500 size=3><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; COLOR: #d47500; FONT-FAMILY: Verdana">__________________________</SPAN></FONT></B><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> 
  <O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal 
  style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><B><FONT 
  face=Verdana size=3><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; FONT-FAMILY: Verdana">Michael 
  Rosenberg</SPAN></FONT></B><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> 
  <BR></SPAN></FONT><FONT face=Verdana size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana">Senior Commercial Buildings 
  Energy Analyst</SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> 
  <BR></SPAN></FONT><FONT face=Verdana size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana">ENERGY & ENVIRONMENT 
  DIRECTORATE </SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><O:P></O:P></SPAN></FONT></P></DIV>
  <P class=MsoNormal><FONT face=Verdana size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana">Pacific Northwest National 
  Laboratory </SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><BR></SPAN></FONT><ST1:ADDRESS 
  w:st="on"><ST1:STREET w:st="on"><FONT face=Verdana size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana">2032 Todd 
  Street</SPAN></FONT></ST1:STREET><FONT face=Verdana size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana"> </SPAN></FONT><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><BR></SPAN></FONT><ST1:CITY 
  w:st="on"><FONT face=Verdana size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana">Eugene</SPAN></FONT></ST1:CITY><FONT 
  face=Verdana size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana">, 
  <ST1:STATE w:st="on">OR</ST1:STATE> <ST1:POSTALCODE 
  w:st="on">97405</ST1:POSTALCODE></SPAN></FONT></ST1:ADDRESS><FONT face=Verdana 
  size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana"> 
  </SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><BR></SPAN></FONT><FONT 
  face=Verdana size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana">(541) 
  844-1960 </SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><BR></SPAN></FONT><FONT 
  face=Verdana size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Verdana"><A 
  href="mailto:michael.rosenberg@pnl.gov"><A 
  href="mailto:michael.rosenberg@pnl.gov">michael.rosenberg@pnl.gov</A></A> 
  </SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><BR></SPAN></FONT><FONT 
  face=Verdana color=#d47500 size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: #d47500; FONT-FAMILY: Verdana"><A 
  href="http://www.pnl.gov"><A 
  href="http://www.pnl.gov">www.pnl.gov</A></A></SPAN></FONT><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> </SPAN></FONT><FONT 
  face=Arial size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><O:P></O:P></SPAN></FONT></P>
  <DIV>
  <DIV 
  style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
  <P class=MsoNormal><B><FONT face=Tahoma size=2><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">From:</SPAN></FONT></B><FONT 
  face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma"> <A 
  href="mailto:bldg-sim-bounces@lists.onebuilding.org"><A 
  href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</A></A> 
  [mailto:bldg-sim-bounces@lists.onebuilding.org] <B><SPAN 
  style="FONT-WEIGHT: bold">On Behalf Of </SPAN></B>Vikram Sami<BR><B><SPAN 
  style="FONT-WEIGHT: bold">Sent:</SPAN></B> Wednesday, July 01, 2009 3:03 
  PM<BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> Bldg-Sim<BR><B><SPAN 
  style="FONT-WEIGHT: bold">Subject:</SPAN></B> [Bldg-sim] Appendix G Fan 
  Power<O:P></O:P></SPAN></FONT></P></DIV></DIV>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN 
  style="FONT-SIZE: 11pt"><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN 
  style="FONT-SIZE: 11pt">G3.1.2.9 Gives you a formula for calculating system 
  fan electrical power for supply, return, exhaust and relief. Lets sat I have a 
  zone with a PSZ-HP that has a supply volume of 1500 cfm. Using this formula 
  along with table G3.1.2.9 I get a fan horse power of 1.29 and kW of 1.17. This 
  equates to 0.00078 kW/cfm – which seems really high. 
  <O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN 
  style="FONT-SIZE: 11pt"><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN style="FONT-SIZE: 11pt">The 
  second part to my question is assuming I have 500cfm of exhaust in this zone, 
  do I apply the same kW/cfm to the exhaust fans as well as the return fans? It 
  seems that the lower the fan volume the more inefficient the Appendix G values 
  get from these tables. <O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN 
  style="FONT-SIZE: 11pt"><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN style="FONT-SIZE: 11pt">Any 
  guidance would be much appreciated. <O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN 
  style="FONT-SIZE: 11pt"><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal 
  style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><B><FONT 
  face=Garamond color=black size=3><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: Garamond">Vikram 
  Sami,</SPAN></FONT></B><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> </SPAN></FONT><FONT 
  face=Garamond color=black size=3><SPAN 
  style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: Garamond">LEED 
  AP</SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> 
  <BR></SPAN></FONT><FONT face=Garamond color=black size=3><SPAN 
  style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: Garamond">Direct Phone 
  404-253-1466 | Direct Fax 404-253-1366</SPAN></FONT><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> 
  <O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal 
  style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><B><FONT 
  face=Garamond color=maroon size=3><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; COLOR: maroon; FONT-FAMILY: Garamond">L</SPAN></FONT></B><B><FONT 
  face=Garamond color=maroon size=2><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: maroon; FONT-FAMILY: Garamond">ORD</SPAN></FONT></B><B><FONT 
  face=Garamond color=maroon size=3><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; COLOR: maroon; FONT-FAMILY: Garamond">, 
  A</SPAN></FONT></B><B><FONT face=Garamond color=maroon size=2><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: maroon; FONT-FAMILY: Garamond">ECK</SPAN></FONT></B><B><FONT 
  face=Garamond color=maroon size=3><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; COLOR: maroon; FONT-FAMILY: Garamond"> 
  & S</SPAN></FONT></B><B><FONT face=Garamond color=maroon size=2><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: maroon; FONT-FAMILY: Garamond">ARGENT</SPAN></FONT></B><B><FONT 
  face=Garamond color=maroon size=3><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; COLOR: maroon; FONT-FAMILY: Garamond"> 
  A</SPAN></FONT></B><B><FONT face=Garamond color=maroon size=2><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: maroon; FONT-FAMILY: Garamond">RCHITECTURE</SPAN></FONT></B><B><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><BR></SPAN></FONT></B><FONT 
  face=Garamond size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Garamond">1201 
  Peachtree Street NE, Suite 300, Atlanta, GA 30361</SPAN></FONT><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> 
  <BR></SPAN></FONT><FONT face=Garamond size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Garamond">Responsive 
  Design</SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> </SPAN></FONT><FONT 
  face=Symbol size=1><SPAN 
  style="FONT-SIZE: 7.5pt; FONT-FAMILY: Symbol">·</SPAN></FONT><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> </SPAN></FONT><FONT 
  face=Garamond size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Garamond">Technological 
  Expertise</SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> </SPAN></FONT><FONT 
  face=Symbol size=1><SPAN 
  style="FONT-SIZE: 7.5pt; FONT-FAMILY: Symbol">·</SPAN></FONT><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> </SPAN></FONT><FONT 
  face=Garamond size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Garamond">Exceptional 
  Service</SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> 
  <BR></SPAN></FONT><FONT face=Garamond color=#007f00 size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: #007f00; FONT-FAMILY: Garamond">Please visit 
  our new website</SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> </SPAN></FONT><FONT 
  face=Garamond color=black size=3><SPAN 
  style="FONT-SIZE: 12pt; COLOR: black; FONT-FAMILY: Garamond">|</SPAN></FONT><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"> <A 
  href="file:///\\www.lordaecksargent.com\"><FONT face=Garamond size=2><SPAN 
  style="FONT-SIZE: 10pt; FONT-FAMILY: Garamond">www.lordaecksargent.com</SPAN></FONT></A><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal 
  style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><FONT 
  face=Webdings color=#007f00 size=6><SPAN 
  style="FONT-SIZE: 24pt; COLOR: #007f00; FONT-FAMILY: Webdings">P 
  </SPAN></FONT><FONT face=Garamond color=#007f00 size=2><SPAN 
  style="FONT-SIZE: 10pt; COLOR: #007f00; FONT-FAMILY: Garamond">Think GREEN 
  before you print.</SPAN></FONT><FONT face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal 
  style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><FONT 
  face="Times New Roman" size=3><SPAN 
  style="FONT-SIZE: 12pt; FONT-FAMILY: 'Times New Roman'"><O:P></O:P></SPAN></FONT></P>
  <P class=MsoNormal><FONT face=Calibri size=2><SPAN 
  style="FONT-SIZE: 11pt"><O:P></O:P></SPAN></FONT></P></DIV></O:SMARTTAGTYPE></O:SMARTTAGTYPE></O:SMARTTAGTYPE></O:SMARTTAGTYPE></O:SMARTTAGTYPE></O:SMARTTAGTYPE></DIV></BLOCKQUOTE>
<BLOCKQUOTE type="cite">
  <DIV><SPAN>_______________________________________________</SPAN><BR><SPAN>Bldg-sim 
  mailing list</SPAN><BR><SPAN><A 
  href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"><A 
  href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A></A></SPAN><BR><SPAN>To 
  unsubscribe from this mailing list send  a blank message to <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"></A><A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"><A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A></A></SPAN><BR></DIV></BLOCKQUOTE></DIV>
<DIV></DIV><br clear=all> NOTICE OF CONFIDENTIALITY

This E-mail message and its attachments (if any) are intended solely for the use of the addressees hereof.  In addition, this message and the attachments (if any) may contain information that is confidential, privileged and exempt from disclosure under applicable law.  If you are not the intended recipient of this message, you are prohibited from reading, disclosing, reproducing, distributing, disseminating or otherwise using this transmission.  Delivery of this message to any person other than the intended recipient is not intended to waive any right or privilege.  If you have received this message in error, please promptly notify the sender by reply E-mail and immediately delete this message from your system.
</BODY></HTML>