<html><body>
<p><tt><font size="2">Robby - the fans must cycle with occupancy, and then when the space is not occupied the must cycle with load. They can not cycle with load only. For Mike Kennedy's system he would need to model the baseline with VAV heating and cooling. And also model the same system in the proposed, however you could set the heating coil capacities to zero, not create a heating plant, or not assign any systems to the heating plant for the VAV system. (This is if you are using Trace 700).</font></tt><br>
<br>
<tt><font size="2">Good luck.</font></tt><br>
<br>
<br>
<font size="2">-Shariq Ali<br>
</font><img src="cid:10__=0ABBFF4DDFF945608f9e8a93df93@urscorp.com" width="360" height="240" alt=""><br>
<font size="2"><br>
</font>
<table border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="610" valign="middle"><font size="1" color="#4F4F4F">This e-mail and any attachments contain URS Corporation confidential information that may be proprietary or privileged. If you receive this message in error or are not the intended recipient, you should not retain, distribute, disclose or use any of this information and you should destroy the e-mail and any attachments or copies.</font></td></tr>