<font size=2>Shariq Ali,<br><br>
</font>Can you really say you are modeling cooling in the base and
proposed cases if you set the cooling capacity to zero? <br><br>
Mike<br><br>
At 12:31 PM 6/23/2009, Shariq_Ali@URSCorp.com wrote:<br><br>
<blockquote type=cite class=cite cite=""><tt>
<font face="Courier New, Courier" size=2>Robby - the fans must cycle with
occupancy, and then when the space is not occupied the must cycle with
load. They can not cycle with load only. For Mike Kennedy's system he
would need to model the baseline with VAV heating and cooling. And also
model the same system in the proposed, however you could set the heating
coil capacities to zero, not create a heating plant, or not assign any
systems to the heating plant for the VAV system. (This is if you are
using Trace 700).</font></tt><br><br>
<tt><font face="Courier New, Courier" size=2>Good
luck.</font></tt><br><br>
<br>
<font size=2>-Shariq Ali<br>
</font>
<img src="cid:7.1.0.9.0.20090623144445.033da340@madronagrove.com.1" width=360 height=240 alt="[]">
<br>
<font size=2><br>
</font><font size=1 color="#4F4F4F">This e-mail and any attachments
contain URS Corporation confidential information that may be proprietary
or privileged. If you receive this message in error or are not the
intended recipient, you should not retain, distribute, disclose or use
any of this information and you should destroy the e-mail and any
attachments or copies.</font><br>
<font size=2><br><br>
</font><br><br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote></body>
</html>