<p><font size="2">Vikram,</font><br>
<br>
<font size="2">If you look at LEED NC CIR ruling date 2/20/2009 you'll find a similar situation in a hospital, that was told to use PTACs. This is a situation I looked up a while ago. I modeled my special pressurization requirement rooms with PTACs quickly and saw the baseline used less energy than my proposed design with the chiller / boiler. I didn't go back to look into it in much, I've got that on my list to do. I can only think it was because the PTACs fan and coils cycle as needed and don't need to keep running like the chiller and boiler in the hospital. Anyone have any other insight into this?</font><br>
<br>
<font size="2">Good luck Vikram.<br>
</font><img src="cid:20__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" width="360" height="240" alt=""><br>
<font size="2"><br>
</font>
<table border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="610" valign="middle"><font size="1" color="#4F4F4F">This e-mail and any attachments contain URS Corporation confidential information that may be proprietary or privileged. If you receive this message in error or are not the intended recipient, you should not retain, distribute, disclose or use any of this information and you should destroy the e-mail and any attachments or copies.</font></td></tr>
</table>
<font size="2"><br>
<br>
</font><br>
<img src="cid:30__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" width="16" height="16" alt="Inactive hide details for bldg-sim-request@lists.onebuilding.org"><font size="2">bldg-sim-request@lists.onebuilding.org</font><br>
<br>
<br>

<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td style="background-image:url(cid:40__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com); background-repeat: no-repeat; " width="49%">
<ul>
<ul>
<ul>
<ul><b><font size="2">bldg-sim-request@lists.onebuilding.org</font></b><font size="2"> </font><br>
<font size="2">Sent by: bldg-sim-bounces@lists.onebuilding.org</font>
<p><font size="2">06/18/2009 03:00 PM</font>
<table border="1">
<tr valign="top"><td width="168" bgcolor="#FFFFFF"><div align="center"><font size="2">Please respond to<br>
bldg-sim@lists.onebuilding.org</font></div></td></tr>
</table>
</ul>
</ul>
</ul>
</ul>
</td><td width="51%">
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="1%"><img src="cid:50__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" border="0" height="1" width="58" alt=""><br>
<div align="right"><font size="2">To</font></div></td><td width="100%"><img src="cid:50__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" border="0" height="1" width="1" alt=""><br>
<font size="2">bldg-sim@lists.onebuilding.org</font></td></tr>

<tr valign="top"><td width="1%"><img src="cid:50__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" border="0" height="1" width="58" alt=""><br>
<div align="right"><font size="2">cc</font></div></td><td width="100%"><img src="cid:50__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" border="0" height="1" width="1" alt=""><br>
</td></tr>

<tr valign="top"><td width="1%"><img src="cid:50__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" border="0" height="1" width="58" alt=""><br>
<div align="right"><font size="2">Subject</font></div></td><td width="100%"><img src="cid:50__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" border="0" height="1" width="1" alt=""><br>
<font size="2">Bldg-sim Digest, Vol 19, Issue 15</font></td></tr>
</table>

<table border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="58"><img src="cid:50__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" border="0" height="1" width="1" alt=""></td><td width="336"><img src="cid:50__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" border="0" height="1" width="1" alt=""></td></tr>
</table>
</td></tr>
</table>
<br>
<tt><font size="2">Send Bldg-sim mailing list submissions to<br>
                 bldg-sim@lists.onebuilding.org<br>
<br>
To subscribe or unsubscribe via the World Wide Web, visit<br>
                 </font></tt><tt><font size="2"><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a></font></tt><tt><font size="2"><br>
or, via email, send a message with subject or body 'help' to<br>
                 bldg-sim-request@lists.onebuilding.org<br>
<br>
You can reach the person managing the list at<br>
                 bldg-sim-owner@lists.onebuilding.org<br>
<br>
When replying, please edit your Subject line so it is more specific<br>
than &quot;Re: Contents of Bldg-sim digest...&quot;<br>
Today's Topics:<br>
<br>
 &nbsp; 1. Appendix G Zoning (Vikram Sami)<br>
 &nbsp; 2. Re: Appendix G Zoning (David S Eldridge)<br>
 &nbsp; 3. Re: Appendix G Zoning (David Reddy)<br>
 &nbsp; 4. BESTTEST Certification (Harding, Ross)<br>
 &nbsp; 5. Re: BESTTEST Certification (Linda Lawrie)<br>
 &nbsp; 6. Re: BESTTEST Certification (Michael Donn)<br>
 &nbsp; 7. conversion factors electricity primary energy (leen peeters)<br>
 &nbsp; 8. VRV / VRF systems (Allison Coley)<br>
 &nbsp; 9. Re: VRV / VRF systems (Marcus Sheffer)<br>
 &nbsp;10. Re: VRV / VRF systems (Julia Beabout)<br>
 &nbsp;11. Re: conversion factors electricity primary energy<br>
 &nbsp; &nbsp; &nbsp;(Cramer Silkworth)<br>
 &nbsp;12. Chilled Water Meter and Utility Rate (eric wang)<br>
</font></tt><font size="2" color="#800080"><br>
----- Message from Vikram Sami &lt;VSami@lasarchitect.com&gt; on Wed, 17 Jun 2009 17:22:42 -0400 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="17%" valign="middle"><div align="right"><b>To:</b></div></td><td width="83%" valign="middle">&quot;Bldg-Sim&quot; &lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="17%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="83%" valign="middle">[Bldg-sim] Appendix G Zoning</td></tr>
</table>
<b><font face="Arial">Exceptions to G3.1.1:</font></b>
<p> <font face="Arial">(c) If the baseline HVAC system type is 5, 6, 7, or 8, use separate</font>
<p><font face="Arial">single-zone systems conforming with the requirements</font>
<p><font face="Arial">of System 3 or System 4 (depending on building</font>
<p><font face="Arial">heat source) for any zones having special pressurization</font>
<p><font face="Arial">relationships, cross-contamination requirements, or code</font> <font face="Arial">required</font>
<p><font face="Arial">minimum circulation rates.</font>
<p><font face="Arial">I’m modeling a building that has baseline system 7.</font> <font face="Arial">If I read this correctly then all lab spaces will</font> <font face="Arial">have their own system and that system will conform to</font> <font face="Arial">system 3  from table g3.1.1A. Is that correct? If so</font> <font face="Arial">–</font> <font face="Arial">are all of my lab spaces going to be packaged single zone units? That doesn’t seem right</font> <font face="Arial">–</font> <font face="Arial">especially since lab spaces are more than 50% of the building area in this case. </font>
<p><font face="Arial">I’d appreciate anyone’s help with this.</font>
<p><font face="Arial">Thanks</font>
<p><b><font face="Garamond">Vikram Sami,</font></b> <font face="Garamond">LEED AP<br>
Direct Phone 404-253-1466 | Direct Fax 404-253-1366</font><font face="Times New Roman"> </font>
<p><b><font color="#800000" face="Garamond">L</font></b><b><font size="2" color="#800000" face="Garamond">ORD</font></b><b><font color="#800000" face="Garamond">, A</font></b><b><font size="2" color="#800000" face="Garamond">ECK</font></b><b><font color="#800000" face="Garamond"> &amp; S</font></b><b><font size="2" color="#800000" face="Garamond">ARGENT</font></b><b><font color="#800000" face="Garamond"> A</font></b><b><font size="2" color="#800000" face="Garamond">RCHITECTURE</font></b><font size="2" face="Garamond"><br>
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361<br>
Responsive Design</font> <font size="1" face="Symbol">·</font> <font size="2" face="Garamond">Technological Expertise</font> <font size="1" face="Symbol">·</font> <font size="2" face="Garamond">Exceptional Service</font><font size="2" color="#007F00" face="Garamond"><br>
Please visit our new website</font> <font face="Garamond">|</font> <a href="file://www.lordaecksargent.com/"><u><font size="2" color="#0000FF" face="Garamond">www.lordaecksargent.com</font></u></a>
<p><font size="6" color="#007F00" face="Webdings">P </font><font size="2" color="#007F00" face="Garamond">Think GREEN before you print.</font><font size="2" color="#800080"><br>
----- Message from David S Eldridge &lt;DSE@grummanbutkus.com&gt; on Wed, 17 Jun 2009 17:33:09 -0500 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="18%" valign="middle"><div align="right"><b>To:</b></div></td><td width="82%" valign="middle">Bldg-Sim &lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="18%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="82%" valign="middle">Re: [Bldg-sim] Appendix G Zoning</td></tr>
</table>
<font face="Times New Roman">Vikram, you should follow the exception (c) if you have a few zones in a larger building that have special requirements, different from the bulk of the System 7.  This I think would be intended for cold rooms, server rooms, etc.</font><br>
<font face="Times New Roman"> </font><br>
<font face="Times New Roman">For your case with roughly 50% labs and 50% other, you may instead want to use the exception (a) to add a second system type in order to account for differences in space requirements between labs and other spaces.</font><br>
<font face="Times New Roman"> </font><br>
<font face="Times New Roman">The design building is probably a good guide – if you are accomplishing your proposed design with one system, then you might find some way to use one system 7.  If you have separate lab/office AHUs in the proposed design, then two systems under exception (a) may be called for.</font><br>
<font face="Times New Roman"> </font><br>
<font face="Times New Roman">Depending on the size of the lab, you may end up with several System type 3 or 4 in the baseline, but for larger labs I think the intention would be to make two System 7’s.</font><br>
<font face="Times New Roman"> </font><br>
<font face="Times New Roman">You may also want to look for the Labs21 guide to Appendix G which includes some other unrelated suggestions.</font><br>
<font face="Times New Roman"> </font><br>
<font face="Times New Roman">David</font><br>
<font face="Times New Roman"> </font><br>
<font face="Tahoma">____________________________________________________________________________________________________________________</font><br>
<font face="Calibri"> </font><br>
<font size="2" color="#808080" face="Tahoma">David Eldridge, PE</font><br>
<font size="2" color="#808080" face="Tahoma">LEED® AP, HBDP</font><br>
<b><font size="2" color="#365F91" face="Tahoma"><br>
Grumman/Butkus Associates</font></b><font size="2" color="#808080" face="Tahoma"> | </font><font size="2" color="#8DB3E2" face="Tahoma">820 Davis Street, STE 300 | Evanston, IL 60201 | Ph: (847) 328-3555, ext 224 | Fax: (847) 328-4550</font><br>
<font size="2" color="#808080" face="Tahoma"> </font><br>
<font size="2" color="#808080" face="Tahoma">Energy Consultants and Design Engineers</font><font face="Tahoma"><br>
____________________________________________________________________________________________________________________</font><br>
<font face="Times New Roman"> </font><br>
<font face="Times New Roman"> </font><br>
<font face="Times New Roman"> </font><br>
<font face="Times New Roman"> </font><br>
<b><font size="2" face="Tahoma">From:</font></b><font size="2" face="Tahoma"> bldg-sim-bounces@lists.onebuilding.org [<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] </font><b><font size="2" face="Tahoma">On Behalf Of </font></b><font size="2" face="Tahoma">Vikram Sami</font><b><font size="2" face="Tahoma"><br>
Sent:</font></b><font size="2" face="Tahoma"> Wednesday, June 17, 2009 4:23 PM</font><b><font size="2" face="Tahoma"><br>
To:</font></b><font size="2" face="Tahoma"> Bldg-Sim</font><b><font size="2" face="Tahoma"><br>
Subject:</font></b><font size="2" face="Tahoma"> [Bldg-sim] Appendix G Zoning</font><br>
<font face="Times New Roman"> </font>
<p><b><font face="Arial">Exceptions to G3.1.1:</font></b>
<p><font face="Times New Roman"> </font><font face="Arial">(c) If the baseline HVAC system type is 5, 6, 7, or 8, use separate</font>
<p><font face="Arial">single-zone systems conforming with the requirements</font>
<p><font face="Arial">of System 3 or System 4 (depending on building</font>
<p><font face="Arial">heat source) for any zones having special pressurization</font>
<p><font face="Arial">relationships, cross-contamination requirements, or code</font><font face="Times New Roman"> </font><font face="Arial">required</font>
<p><font face="Arial">minimum circulation rates.</font>
<p><font face="Arial">I’m modeling a building that has baseline system 7.</font><font face="Times New Roman"> </font><font face="Arial">If I read this correctly then all lab spaces will</font><font face="Times New Roman"> </font><font face="Arial">have their own system and that system will conform to</font><font face="Times New Roman"> </font><font face="Arial">system 3  from table g3.1.1A. Is that correct? If so</font><font face="Times New Roman"> </font><font face="Arial">–</font><font face="Times New Roman"> </font><font face="Arial">are all of my lab spaces going to be packaged single zone units? That doesn’t seem right</font><font face="Times New Roman"> </font><font face="Arial">–</font><font face="Times New Roman"> </font><font face="Arial">especially since lab spaces are more than 50% of the building area in this case. </font>
<p><font face="Arial">I’d appreciate anyone’s help with this.</font>
<p><font face="Times New Roman"> </font><i>(See attached file: Labs21 - Appendix G for Laboratories.pdf)</i><font size="2" color="#800080"><br>
----- Message from &quot;David Reddy&quot; &lt;davidr@madisonengineeringps.com&gt; on Wed, 17 Jun 2009 18:27:10 -0700 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="9%" valign="middle"><div align="right"><b>To:</b></div></td><td width="91%" valign="middle">&quot;'Vikram Sami'&quot; &lt;VSami@lasarchitect.com&gt;, &quot;'Bldg-Sim'&quot; &lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="9%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="91%" valign="middle">Re: [Bldg-sim] Appendix G Zoning</td></tr>
</table>
<font color="#1F497D" face="Calibri">USGBC also has provided some guidance on the appropriate baseline system for large laboratories via a few CIRs.  Specifically LEED-NC CIR rulings dated on:</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri">2/27/2007 </font><br>
<font color="#1F497D" face="Calibri">&amp;</font><br>
<font color="#1F497D" face="Calibri">8/13/2007</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<b><font color="#1F497D" face="Tahoma">David Reddy</font></b><br>
<font color="#1F497D" face="Tahoma">Madison Engineering, PS</font><br>
<font color="#1F497D" face="Tahoma">444 NE Ravenna Blvd, Suite 406</font><br>
<font color="#1F497D" face="Tahoma">Seattle, WA 98115</font><br>
<font color="#1F497D" face="Tahoma">office: 206-834-0002</font><br>
<font color="#1F497D" face="Tahoma">direct: 206-829-8622</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<b><font size="2" face="Tahoma">From:</font></b><font size="2" face="Tahoma"> bldg-sim-bounces@lists.onebuilding.org [<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] </font><b><font size="2" face="Tahoma">On Behalf Of </font></b><font size="2" face="Tahoma">Vikram Sami</font><b><font size="2" face="Tahoma"><br>
Sent:</font></b><font size="2" face="Tahoma"> Wednesday, June 17, 2009 2:23 PM</font><b><font size="2" face="Tahoma"><br>
To:</font></b><font size="2" face="Tahoma"> Bldg-Sim</font><b><font size="2" face="Tahoma"><br>
Subject:</font></b><font size="2" face="Tahoma"> [Bldg-sim] Appendix G Zoning</font><br>
<font face="Times New Roman"> </font>
<p><b><font face="Arial">Exceptions to G3.1.1:</font></b>
<p><font face="Times New Roman"> </font><font face="Arial">(c) If the baseline HVAC system type is 5, 6, 7, or 8, use separate</font>
<p><font face="Arial">single-zone systems conforming with the requirements</font>
<p><font face="Arial">of System 3 or System 4 (depending on building</font>
<p><font face="Arial">heat source) for any zones having special pressurization</font>
<p><font face="Arial">relationships, cross-contamination requirements, or code</font><font face="Times New Roman"> </font><font face="Arial">required</font>
<p><font face="Arial">minimum circulation rates.</font>
<p><font face="Arial">I’m modeling a building that has baseline system 7.</font><font face="Times New Roman"> </font><font face="Arial">If I read this correctly then all lab spaces will</font><font face="Times New Roman"> </font><font face="Arial">have their own system and that system will conform to</font><font face="Times New Roman"> </font><font face="Arial">system 3  from table g3.1.1A. Is that correct? If so</font><font face="Times New Roman"> </font><font face="Arial">–</font><font face="Times New Roman"> </font><font face="Arial">are all of my lab spaces going to be packaged single zone units? That doesn’t seem right</font><font face="Times New Roman"> </font><font face="Arial">–</font><font face="Times New Roman"> </font><font face="Arial">especially since lab spaces are more than 50% of the building area in this case. </font>
<p><font face="Arial">I’d appreciate anyone’s help with this.</font>
<p><font face="Arial">Thanks</font>
<p><b><font face="Garamond">Vikram Sami,</font></b><font face="Times New Roman"> </font><font face="Garamond">LEED AP<br>
Direct Phone 404-253-1466 | Direct Fax 404-253-1366</font><font face="Times New Roman"> </font>
<p><b><font color="#800000" face="Garamond">L</font></b><b><font size="2" color="#800000" face="Garamond">ORD</font></b><b><font color="#800000" face="Garamond">, A</font></b><b><font size="2" color="#800000" face="Garamond">ECK</font></b><b><font color="#800000" face="Garamond"> &amp; S</font></b><b><font size="2" color="#800000" face="Garamond">ARGENT</font></b><b><font color="#800000" face="Garamond"> A</font></b><b><font size="2" color="#800000" face="Garamond">RCHITECTURE</font></b><font size="2" face="Garamond"><br>
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361<br>
Responsive Design</font><font face="Times New Roman"> </font><font size="1" face="Symbol">·</font><font face="Times New Roman"> </font><font size="2" face="Garamond">Technological Expertise</font><font face="Times New Roman"> </font><font size="1" face="Symbol">·</font><font face="Times New Roman"> </font><font size="2" face="Garamond">Exceptional Service</font><font size="2" color="#007F00" face="Garamond"><br>
Please visit our new website</font><font face="Times New Roman"> </font><font face="Garamond">|</font><font face="Times New Roman"> </font><a href="file://www.lordaecksargent.com/"><u><font size="2" color="#0000FF" face="Garamond">www.lordaecksargent.com</font></u></a>
<p><font size="6" color="#007F00" face="Webdings">P </font><font size="2" color="#007F00" face="Garamond">Think GREEN before you print.</font><font size="2" color="#800080"><br>
----- Message from &quot;Harding, Ross&quot; &lt;ross.harding@lincolnescott.com&gt; on Thu, 18 Jun 2009 12:09:33 +1000 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="20%" valign="middle"><div align="right"><b>To:</b></div></td><td width="80%" valign="middle">&lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="20%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="80%" valign="middle">[Bldg-sim] BESTTEST Certification</td></tr>
</table>
<font face="Calibri">Hi All,</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">Does anyone know where I can find a list of BESTTEST certified Building Energy Simulation software?</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">I can only find that Energy Plus has done the test, but not that it is BESTTest certified?</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">What about TAS 8.5, does anyone know where the BESTTest certification is?</font><br>
<font face="Calibri"> </font><br>
<font size="2" face="Arial"><br>
Regards<br>
</font><b><font size="2" face="Arial"><br>
Ross Harding</font></b><font size="2" face="Arial"><br>
Environmental Design Consultant<br>
<br>
Phone +61 2 8907 0900<br>
Direct  +61 2 8907 0953</font><u><font size="2" color="#0000FF" face="Arial"><br>
</font></u><a href="mailto:ross.harding@lincolnescott.com"><u><font size="2" color="#0066CC" face="Arial">ross.harding@lincolnescott.com</font></u></a><br>
<font size="2" color="#999999" face="Arial">Please consider the environment before printing this email. </font><br>
<font size="2" color="#999999" face="Arial">This email message is intended only for the addressee(s) and contains information which may be confidential. If you are not the intended recipient please do not read, save, forward, disclose, or copy the contents of this email. If this email has been sent to you in error, please delete this email and any copies or links to this email completely and immediately from your system. Views expressed in this message are those of the individual sender and are not necessarily the views of Lincolne Scott.</font><br>
<font size="2" face="Arial"> </font>
<p>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="48%" bgcolor="#A2C1CD"><img src="cid:60__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" width="216" height="24" alt="http://www.lincolnescott.com/emails/AElogo1.gif"></td><td width="39%" bgcolor="#A2C1CD"><div align="right"><font size="2" face="Arial">Advanced Environmental Pty Ltd<br>
is a specialist service of<br>
Lincolne Scott Pty Ltd<br>
a climate neutral company</font><u><font size="2" color="#0000FF" face="Arial"><br>
</font></u><a href="http://www.lincolnescott.com/"><u><font size="2" color="#0066CC" face="Arial">lincolnescott.com</font></u></a></div></td><td width="13%" bgcolor="#A2C1CD"><div align="right"><img src="cid:70__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" width="56" height="65" alt="http://www.lincolnescott.com/emails/cnlogob.gif"></div></td></tr>
</table>
<font face="Calibri"> </font><br>
<font face="Calibri"> </font><font size="2" color="#800080"><br>
----- Message from Linda Lawrie &lt;linda@fortlawrie.com&gt; on Wed, 17 Jun 2009 20:19:39 -0600 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="15%" valign="middle"><div align="right"><b>To:</b></div></td><td width="85%" valign="middle">&quot;Harding, Ross&quot; &lt;ross.harding@lincolnescott.com&gt;</td></tr>

<tr valign="top"><td width="15%" valign="middle"><div align="right"><b>cc:</b></div></td><td width="85%" valign="middle">bldg-sim@lists.onebuilding.org</td></tr>

<tr valign="top"><td width="15%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="85%" valign="middle">Re: [Bldg-sim] BESTTEST Certification</td></tr>
</table>
<tt><font size="2">All the EnergyPlus testing reports are posted on the EnergyPlus web site: <br>
</font></tt><tt><font size="2"><a href="http://energyplus.gov/testing.cfm">http://energyplus.gov/testing.cfm</a></font></tt><tt><font size="2"><br>
ASHRAE Standard 140-2007 incorporates many of the IEA BESTest methods. &nbsp;IEA<br>
does not certify software--just provides tests.<br>
<br>
Linda<br>
EnergyPlus Development Team<br>
<br>
</font></tt><font size="2" color="#800080"><br>
----- Message from Michael Donn &lt;Michael.Donn@vuw.ac.nz&gt; on Thu, 18 Jun 2009 14:26:20 +1200 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="12%" valign="middle"><div align="right"><b>To:</b></div></td><td width="88%" valign="middle">&quot;Harding, Ross&quot; &lt;ross.harding@lincolnescott.com&gt;</td></tr>

<tr valign="top"><td width="12%" valign="middle"><div align="right"><b>cc:</b></div></td><td width="88%" valign="middle">&quot;bldg-sim@lists.onebuilding.org&quot; &lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="12%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="88%" valign="middle">Re: [Bldg-sim] BESTTEST Certification</td></tr>
</table>
<font color="#1F497D" face="Calibri">Hi Ross</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri">Typically the vendors publish their BESTEST data online. The BESTEST system is one of self-certification, not a central authorising body….. (see </font><a href="http://www.iea-shc.org/task34/index.html"><u><font color="#0000FF" face="Calibri">http://www.iea-shc.org/task34/index.html</font></u></a><font color="#1F497D" face="Calibri"> )</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri">ASHRAE Standard 140 incorporates some of the IEA BESTEST suite and I understand over time will incorporate more. (</font><a href="http://www.nrel.gov/docs/fy06osti/40360.pdf"><u><font color="#0000FF" face="Calibri">http://www.nrel.gov/docs/fy06osti/40360.pdf</font></u></a><font color="#1F497D" face="Calibri"> )</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri">I am not aware that ASHRAE ‘certify’ software in the way you seek.</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri">m</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri">  </font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Times New Roman">Michael Donn                                                       <br>
Director Centre for Building Performance Research<br>
School of Architecture  <br>
Victoria University      +64 4 463 6221  work<br>
PO Box 600              +64 21 611 280  mobile<br>
Wellington                +64 4 463 6204  work fax<br>
New Zealand             +64 21 611 594  mobilefax</font><br>
<font color="#1F497D" face="Times New Roman"> </font><br>
<a href="http://www.vuw.ac.nz/architecture/staff/academics/michael-donn.aspx"><u><font size="2" color="#0000FF" face="Arial">http://www.vuw.ac.nz/architecture/staff/academics/michael-donn.aspx</font></u></a><font size="2" color="#1F497D" face="Arial"> </font><br>
<font size="2" color="#1F497D" face="Arial">------------------------------------------------------------------------------------</font><br>
<b><font size="2" face="Tahoma">From:</font></b><font size="2" face="Tahoma"> bldg-sim-bounces@lists.onebuilding.org [<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] </font><b><font size="2" face="Tahoma">On Behalf Of </font></b><font size="2" face="Tahoma">Harding, Ross</font><b><font size="2" face="Tahoma"><br>
Sent:</font></b><font size="2" face="Tahoma"> Thursday, 18 June 2009 2:10 p.m.</font><b><font size="2" face="Tahoma"><br>
To:</font></b><font size="2" face="Tahoma"> bldg-sim@lists.onebuilding.org</font><b><font size="2" face="Tahoma"><br>
Subject:</font></b><font size="2" face="Tahoma"> [Bldg-sim] BESTTEST Certification</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">Hi All,</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">Does anyone know where I can find a list of BESTTEST certified Building Energy Simulation software?</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">I can only find that Energy Plus has done the test, but not that it is BESTTest certified?</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">What about TAS 8.5, does anyone know where the BESTTest certification is?</font><br>
<font face="Calibri"> </font><br>
<font size="2" face="Arial"><br>
Regards<br>
</font><b><font size="2" face="Arial"><br>
Ross Harding</font></b><font size="2" face="Arial"><br>
Environmental Design Consultant<br>
<br>
Phone +61 2 8907 0900<br>
Direct  +61 2 8907 0953</font><u><font size="2" color="#0000FF" face="Arial"><br>
</font></u><a href="mailto:ross.harding@lincolnescott.com"><u><font size="2" color="#0066CC" face="Arial">ross.harding@lincolnescott.com</font></u></a><br>
<font size="2" color="#999999" face="Arial">Please consider the environment before printing this email. </font><br>
<font size="2" color="#999999" face="Arial">This email message is intended only for the addressee(s) and contains information which may be confidential. If you are not the intended recipient please do not read, save, forward, disclose, or copy the contents of this email. If this email has been sent to you in error, please delete this email and any copies or links to this email completely and immediately from your system. Views expressed in this message are those of the individual sender and are not necessarily the views of Lincolne Scott.</font><br>
<font size="2" face="Arial"> </font>
<p>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="48%" bgcolor="#A2C1CD"><img src="cid:80__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" width="216" height="24" alt="http://www.lincolnescott.com/emails/AElogo1.gif"></td><td width="39%" bgcolor="#A2C1CD"><div align="right"><font size="2" face="Arial">Advanced Environmental Pty Ltd<br>
is a specialist service of<br>
Lincolne Scott Pty Ltd<br>
a climate neutral company</font><u><font size="2" color="#0000FF" face="Arial"><br>
</font></u><a href="http://www.lincolnescott.com/"><u><font size="2" color="#0066CC" face="Arial">lincolnescott.com</font></u></a></div></td><td width="13%" bgcolor="#A2C1CD"><div align="right"><img src="cid:90__=0ABBFF4ADFF9C0318f9e8a93df93@urscorp.com" width="56" height="65" alt="http://www.lincolnescott.com/emails/cnlogob.gif"></div></td></tr>
</table>
<font face="Calibri"> </font><br>
<font face="Calibri"> </font><font size="2" color="#800080"><br>
----- Message from leen peeters &lt;l.f.r.peeters@gmail.com&gt; on Thu, 18 Jun 2009 12:51:02 +0200 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="12%" valign="middle"><div align="right"><b>To:</b></div></td><td width="88%" valign="middle">&quot;bldg-sim@lists.onebuilding.org&quot; &lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="12%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="88%" valign="middle">[Bldg-sim] conversion factors electricity primary energy</td></tr>
</table>
Dear,<br>
 <br>
could anyone help me out with conversion factors primary energy to electricity for Canada and Italy?<br>
 <br>
Thanks!<br>
 <br>
Leen<font size="2" color="#800080"><br>
----- Message from &quot;Allison Coley&quot; &lt;Allison.Coley@cjmw.com&gt; on Thu, 18 Jun 2009 09:10:03 -0400 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="22%" valign="middle"><div align="right"><b>To:</b></div></td><td width="78%" valign="middle">&lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="22%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="78%" valign="middle">[Bldg-sim] VRV / VRF systems</td></tr>
</table>
<font face="Calibri">Hello, </font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">We are in the very early stages of a project and are weighing the pros/cons of a VRV/VRF system vs. geothermal. Any general lessons learned with using VRV/VRF systems, or pros/cons of certain software packages in modeling them for demonstrated energy savings? </font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">Thanks,</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">Allison</font><font size="2" color="#800080"><br>
----- Message from &quot;Marcus Sheffer&quot; &lt;sheffer@energyopportunities.com&gt; on Thu, 18 Jun 2009 09:46:20 -0400 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="10%" valign="middle"><div align="right"><b>To:</b></div></td><td width="90%" valign="middle">&quot;'Allison Coley'&quot; &lt;Allison.Coley@cjmw.com&gt;, &lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="10%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="90%" valign="middle">Re: [Bldg-sim] VRV / VRF systems</td></tr>
</table>
<font color="#1F497D" face="Calibri">I believe EnergyPro can model these systems.</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<font color="#1F497D" face="Calibri">Marcus Sheffer</font><br>
<font color="#1F497D" face="Calibri">7group</font><br>
<font color="#1F497D" face="Calibri"> </font><br>
<b><font size="2" face="Tahoma">From:</font></b><font size="2" face="Tahoma"> bldg-sim-bounces@lists.onebuilding.org [<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] </font><b><font size="2" face="Tahoma">On Behalf Of </font></b><font size="2" face="Tahoma">Allison Coley</font><b><font size="2" face="Tahoma"><br>
Sent:</font></b><font size="2" face="Tahoma"> Thursday, June 18, 2009 9:10 AM</font><b><font size="2" face="Tahoma"><br>
To:</font></b><font size="2" face="Tahoma"> bldg-sim@lists.onebuilding.org</font><b><font size="2" face="Tahoma"><br>
Subject:</font></b><font size="2" face="Tahoma"> [Bldg-sim] VRV / VRF systems</font><br>
<font face="Times New Roman"> </font><br>
<font face="Calibri">Hello, </font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">We are in the very early stages of a project and are weighing the pros/cons of a VRV/VRF system vs. geothermal. Any general lessons learned with using VRV/VRF systems, or pros/cons of certain software packages in modeling them for demonstrated energy savings? </font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">Thanks,</font><br>
<font face="Calibri"> </font><br>
<font face="Calibri">Allison</font><font size="2" color="#800080"><br>
----- Message from Julia Beabout &lt;juliabeabout@yahoo.com&gt; on Thu, 18 Jun 2009 07:41:12 -0700 (PDT) -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="11%" valign="middle"><div align="right"><b>To:</b></div></td><td width="89%" valign="middle">Allison Coley &lt;Allison.Coley@cjmw.com&gt;, bldg-sim@lists.onebuilding.org</td></tr>

<tr valign="top"><td width="11%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="89%" valign="middle">Re: [Bldg-sim] VRV / VRF systems</td></tr>
</table>
<font size="2" face="Arial">Hi Allison</font><br>
<font size="2" face="Arial">Trace 700 can model VRV/VRF systems.</font><br>
<font size="2" face="Arial">I haven't tried in Trace before, but, looks pretty easy.</font><br>
<font size="2" face="Arial"> </font><br>
<font size="2" face="Arial">Julia</font><br>
<br>
<hr width="100%" size="2" align="left"><b><font size="2" face="Tahoma">From:</font></b><font size="2" face="Tahoma"> Allison Coley &lt;Allison.Coley@cjmw.com&gt;</font><b><font size="2" face="Tahoma"><br>
To:</font></b><font size="2" face="Tahoma"> bldg-sim@lists.onebuilding.org</font><b><font size="2" face="Tahoma"><br>
Sent:</font></b><font size="2" face="Tahoma"> Thursday, June 18, 2009 9:10:03 AM</font><b><font size="2" face="Tahoma"><br>
Subject:</font></b><font size="2" face="Tahoma"> [Bldg-sim] VRV / VRF systems</font><font face="Times"><br>
</font><br>
<font face="Calibri">Hello, </font>
<p><font face="Calibri"> </font>
<p><font face="Calibri">We are in the very early stages of a project and are weighing the pros/cons of a VRV/VRF system vs. geothermal. Any general lessons learned with using VRV/VRF systems, or pros/cons of certain software packages in modeling them for demonstrated energy savings? </font>
<p><font face="Calibri"> </font>
<p><font face="Calibri">Thanks,</font>
<p><font face="Calibri"> </font>
<p><font face="Calibri">Allison</font><font size="2" color="#800080"><br>
----- Message from &quot;Cramer Silkworth&quot; &lt;silkworth@transsolar.com&gt; on Thu, 18 Jun 2009 17:07:20 +0200 -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="14%" valign="middle"><div align="right"><b>To:</b></div></td><td width="86%" valign="middle">bldg-sim@lists.onebuilding.org, l.f.r.peeters@gmail.com</td></tr>

<tr valign="top"><td width="14%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="86%" valign="middle">Re: [Bldg-sim] conversion factors electricity primary energy</td></tr>
</table>
<font size="2" color="#0000FF" face="Arial">Awhile ago I found a lot of this type info on Natural Resources Canada's energy webpage: </font><br>
<a href="http://nrcan.gc.ca/eneene/statstat/index-eng.php"><u><font size="2" color="#0000FF" face="Arial">http://nrcan.gc.ca/eneene/statstat/index-eng.php</font></u></a><a href="http://www.nrcan-rncan.gc.ca/com/eneene/index-eng.php"></a> <br>
  <br>
<font size="2" color="#0000FF" face="Arial">it's huge, but maybe some strategic searching will get you to PE factors</font> <br>
  <br>
<font size="2" color="#0000FF" face="Arial">-Cramer</font> <br>
  <br>
<font size="1" face="Arial">J. Cramer Silkworth</font> <br>
<font size="1" face="Arial">Transsolar Inc.</font> <br>
<font size="1" face="Arial">Technical consulting for energy efficiency and user comfort in buildings. Stuttgart - Munich - New York</font> <br>
<font size="1" face="Arial">134 Spring Street Suite 601</font> <br>
<font size="1" face="Arial">New York, NY 10012</font> <br>
<font size="1" face="Arial">212-219-2255</font> <br>
<a href="mailto:silkworth@transsolar.com"><u><font size="1" color="#0000FF" face="Arial">silkworth@transsolar.com</font></u></a> <br>
<br>
<hr width="100%" size="2" align="left">   <b><font size="2" face="Tahoma">From:</font></b><font size="2" face="Tahoma"> leen peeters [<a href="mailto:l.f.r.peeters@gmail.com">mailto:l.f.r.peeters@gmail.com</a>] </font><b><font size="2" face="Tahoma"><br>
Sent:</font></b><font size="2" face="Tahoma"> Thursday, June 18, 2009 6:51 AM</font><b><font size="2" face="Tahoma"><br>
To:</font></b><font size="2" face="Tahoma"> bldg-sim@lists.onebuilding.org</font><b><font size="2" face="Tahoma"><br>
Subject:</font></b><font size="2" face="Tahoma"> [Bldg-sim] conversion factors electricity primary energy</font><br>

<p>Dear, 
<p>  <br>
could anyone help me out with conversion factors primary energy to electricity for Canada and Italy? <br>
  <br>
Thanks! <br>
  <br>
Leen <font size="2" color="#800080"><br>
----- Message from eric wang &lt;shaojieworld2006@yahoo.com&gt; on Thu, 18 Jun 2009 08:53:40 -0700 (PDT) -----</font>
<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="9%" valign="middle"><div align="right"><b>To:</b></div></td><td width="91%" valign="middle">&quot;bldg-sim@lists.onebuilding.org bldg-sim@lists.onebuilding.org&quot; &lt;bldg-sim@lists.onebuilding.org&gt;</td></tr>

<tr valign="top"><td width="9%" valign="middle"><div align="right"><b>Subject:</b></div></td><td width="91%" valign="middle">[Bldg-sim] Chilled Water Meter and Utility Rate</td></tr>
</table>

<table width="100%" border="0" cellspacing="0" cellpadding="0">
<tr valign="top"><td width="100%">Hi,<br>
 <br>
I created a chilled water meter and its utility rate. For the utility rate, all parameters are either left blank or undefined except taxes are set to base. After exporting the DOE2 sim report, I found there is still a charge for chiller water meter. Does anyone know why the charge is not zero for the chilled water meter?<br>
 <br>
Thanks,<br>
 <br>
Shaojie</td></tr>