size=2>Hi Ding,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=724252606-03062009><FONT face=Verdana 
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=724252606-03062009><FONT face=Verdana 
size=2>With regards to importing the boundary conditions from the dynamic 
(thermal) simulation, how do you take building mass into account. Some of the 
external conditions i absorbed by the floors and walls. Can you get the CFD 
calculations to take this factor into account when using CFD? I haven't heard of 
this before. </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=724252606-03062009><FONT face=Verdana 
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=724252606-03062009><FONT face=Verdana 
size=2>Also the CFD results are only a predicted airflow and are extremely 
sensitive to input parameters, and the flow is more or less steady state. 
Therefore the CFD can only be used to illustrate what could possibly happen, and 
to get an idea of the stratefication. However as you mention with regards to 
stratefication, I need a dynamic simulation which can calculate stratefication 
relatively simple so that the stratefication would vary over time. E+ sounds 
like a possibility, but if it only can calculate stratefication when using 
displacement ventilation, then it becomes less attractive to use. Do you know of 
any other software which can calculate stratefication? The Danish program BSim 
has a fixed parameter for stratification so this program can not be used for 
calculation over a whole year unless the calculation is divided up into smaller 
parts, and the stratefication is changed manually, based on CFD 
calculations.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=724252606-03062009><FONT face=Verdana 
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=724252606-03062009><FONT face=Verdana 
size=2>I agree with you that it is important to include radiation! However it 
takes longer to obtain convergance with this module "on". How do you manage to 
calculate large rooms with many surfaces, and still including radiation? 
Clustering of (many) computers?</FONT></SPAN></DIV>
<DIV><FONT face=Verdana size=2></FONT> </DIV>
<DIV class=Section1>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA"><?xml:namespace prefix = o ns = 
"urn:schemas-microsoft-com:office:office" /><o:p> </o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">Med venlig hilsen<o:p></o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 9pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">Frederik V. Winther<o:p></o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA"><o:p> </o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">Civilingeniør, Indeklima og 
Energi<o:p></o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">Ingeniør<o:p></o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">Indeklima og Miljø<o:p></o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA"><o:p> </o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">D +45 4598 6254<o:p></o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #009ee3; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA"><A title=FRW@RAMBOLL.DK 
href="mailto:frw@ramboll.dk"><SPAN 
style="COLOR: #009ee3; TEXT-DECORATION: none; text-underline: none">frw@ramboll.dk</SPAN></A><o:p></o:p></SPAN></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; FONT-FAMILY: Times New Roman; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">________________________________________<o:p></o:p></SPAN></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA"><o:p> </o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">Rambøll<o:p></o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">Teknikerbyen 31<o:p></o:p></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA">DK-2830 Virum</SPAN><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; FONT-FAMILY: Times New Roman; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA"><o:p></o:p></SPAN></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #009ee3; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="mso-ansi-language: DA"><A title=WWW.RAMBOLL.DK 
href="http://www.ramboll.dk/"><SPAN 
style="COLOR: #009ee3; TEXT-DECORATION: none; text-underline: none">www.ramboll.dk</SPAN></A><o:p></o:p></SPAN></SPAN></DIV>
<DIV 
class=MsoNormal><o:p> </o:p></DIV></DIV></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> Ding Li [mailto:dingli@ucla.edu] 
<BR><B>Sent:</B> 3. juni 2009 02:41<BR><B>To:</B> Frederik Vildbrad Winther 
(FRW); Paul Carey; bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> Re: 
[Bldg-sim] Links between CFD or MZ and thermal simulations for simulating air 
and temperature distributions in atria<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: tahoma, new york, times, serif">
<DIV>I put my comments in blue below.</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>
<DIV>Ding Li, PhD, PE<BR></DIV>
<DIV 
style="FONT-SIZE: 10pt; FONT-FAMILY: tahoma, new york, times, serif">Capital 
Engineering Consultants Inc.<BR><SPAN class=yshortcuts id=lw_1243988966_1 
style="BACKGROUND: none transparent scroll repeat 0% 0%; CURSOR: hand; BORDER-BOTTOM: #0066cc 1px dashed">11020 
Sun Center Drive, Suite 100<BR>Rancho Cordova, CA  95670</SPAN></DIV>
<DIV 
style="FONT-SIZE: 10pt; FONT-FAMILY: tahoma, new york, times, serif">Tel:  
<SPAN class=yshortcuts id=lw_1243988966_2 
style="BACKGROUND: none transparent scroll repeat 0% 0%; CURSOR: hand; BORDER-BOTTOM: #0066cc 1px dashed">916-851-3579</SPAN><BR>Fax: 
<SPAN class=yshortcuts id=lw_1243988966_3 
style="BACKGROUND: none transparent scroll repeat 0% 0%; CURSOR: hand; BORDER-BOTTOM: #0066cc 1px dashed">916-631-4424</SPAN><BR></DIV></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: tahoma, new york, times, serif"><BR>
<DIV 
style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif"><FONT 
face=Tahoma size=2>
<HR SIZE=1>
<B><SPAN style="FONT-WEIGHT: bold">From:</SPAN></B> Frederik Vildbrad Winther 
(FRW) <FRW@ramboll.dk><BR><B><SPAN 
style="FONT-WEIGHT: bold">To:</SPAN></B> Paul Carey <paul@zed-uk.com>; 
bldg-sim@lists.onebuilding.org<BR><B><SPAN 
style="FONT-WEIGHT: bold">Sent:</SPAN></B> Tuesday, June 2, 2009 6:35:38 
AM<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> Re: [Bldg-sim] 
Links between CFD or MZ and thermal simulations for simulating air and 
temperature distributions in atria<BR></FONT><BR>
<STYLE>UNKNOWN {
        FONT-FAMILY: Cambria Math
}
UNKNOWN {
        FONT-FAMILY: Calibri
}
UNKNOWN {
        FONT-FAMILY: Tahoma
}
UNKNOWN {
        FONT-FAMILY: Verdana
}
UNKNOWN {
        FONT-FAMILY: MS Reference Sans Serif
}
UNKNOWN {
        MARGIN: 72pt
}
P.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman", "serif"
}
LI.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman", "serif"
}
DIV.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Times New Roman", "serif"
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline
}
P {
        FONT-SIZE: 12pt; MARGIN-LEFT: 0cm; MARGIN-RIGHT: 0cm; FONT-FAMILY: "Times New Roman", "serif"
}
P.MsoAcetate {
        FONT-SIZE: 8pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Tahoma", "sans-serif"
}
LI.MsoAcetate {
        FONT-SIZE: 8pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Tahoma", "sans-serif"
}
DIV.MsoAcetate {
        FONT-SIZE: 8pt; MARGIN: 0cm 0cm 0pt; FONT-FAMILY: "Tahoma", "sans-serif"
}
SPAN.EmailStyle18 {
        COLOR: #1f497d; FONT-FAMILY: "Calibri", "sans-serif"
}
SPAN.BalloonTextChar {
        FONT-FAMILY: "Tahoma", "sans-serif"
}
.MsoChpDefault {
        FONT-SIZE: 10pt
}
DIV.Section1 {
        
}
</STYLE>

<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2>Hi Paul,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2>Thanks for your reply. I haven't heard about DesignBuilder CFD before and 
I have only heard and peaked to EnergyPlus. EnergyPlus seems OK for simulating 
multizones and thermal simulations. Do you know how it handles stratification? I 
am thinking of using thermal simulations, with a good link to a multizone 
program so that the 2 programs can predict the air movement as well as the 
stratification in the room. I am then thinking of doing 4 CFD studies and these 
simulations should have input from the thermal simulation. The output from the 
CFD simulations should then be compared to the results from the thermal 
simulation. The two calculations should therefor be reasonably comparable (in 
the end).</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2></FONT></SPAN><FONT color=#0000ff></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff>DesignBuilder just released v2. I'm 
not quite familiar with its CFD module, but I believe DB was mainly used with 
E+. If you want to achieve stratification, you have to use some CFD package. E+ 
has a DV module which may have stratification feature, but that's only for DV. 
</FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff></FONT> </DIV>
<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2>I think that the use LES turbulence model for indoor climate analysis is 
rather hazardous because this turbulence model is mostly used for fire and smoke 
simulations. I have obtained good results for indoor climate using ke-turbulence 
model. Is my thought "out of date" on this point? Does ke-turbulence model also 
work for larger rooms? When can/should LES-turbulence model be used, apart from 
smoke/fire simulations? The problem is also getting a thermal simulation 
program, which can import the results from a CFD calculation. 
</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2>Using the transient calculations could prove very useful in showing the 
uncertainty in the CFD calculations. However, can I, when importing the boundary 
conditions from the thermal simulation to the CFD simulation, import the 
temperature stratefication as a start condition for the simulation? What is your 
experience on coupling thermal/multizone simulations with CFD calculations? Does 
it work? It could be very useful if the CFD calculation starts with the same 
boundary conditions and results from the thermal simulation, rather than 
starting from scratch every time a CFD analysis has to be 
performed.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff>I'm not sure the exact meaning of 
your "thermal simulation". If you refer to the mechanical load calculation 
software, eg. Trane trace or other heating/cooling software, the answer is yes. 
You can calculate the heat flux at the exterior wall/roof/floor and then import 
them into your CFD model. But you need to verify the CFD result carefully since 
the setpoint may be different from the result of your CFD modeling. This could 
cause some inaccurate result.</FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff></FONT> </DIV>
<DIV dir=ltr align=left><SPAN class=683285912-02062009><FONT face=Verdana 
size=2>Do you know of any papers dealing with modeling of solar gain in CFD 
tools?</FONT></SPAN></DIV>
<DIV> </DIV>
<DIV><FONT color=#0000ff></FONT> </DIV>
<DIV> </DIV>
<DIV class=Section1>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN></SPAN> </DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>Med 
venlig hilsen</SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 9pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>Frederik 
V. Winther</SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN></SPAN> </DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>Civilingeniør, 
Indeklima og Energi</SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>Ingeniør</SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>Indeklima 
og Miljø</SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN></SPAN> </DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>D 
+45 4598 6254</SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #009ee3; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN><A 
title=FRW@RAMBOLL.DK href="mailto:frw@ramboll.dk" target=_blank rel=nofollow 
ymailto="mailto:frw@ramboll.dk"><SPAN 
style="COLOR: #009ee3; TEXT-DECORATION: none">frw@ramboll.dk</SPAN></A></SPAN></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; FONT-FAMILY: Times New Roman; TEXT-DECORATION: none"><SPAN>________________________________________</SPAN></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN></SPAN> </DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>Rambøll</SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>Teknikerbyen 
31</SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN>DK-2830 
Virum</SPAN><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; FONT-FAMILY: Times New Roman; TEXT-DECORATION: none"><SPAN></SPAN></SPAN></DIV>
<DIV><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #000000; LINE-HEIGHT: 11pt; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 8pt; COLOR: #009ee3; FONT-FAMILY: Verdana; TEXT-DECORATION: none"><SPAN><A 
title=WWW.RAMBOLL.DK href="http://www.ramboll.dk/" target=_blank 
rel=nofollow><SPAN 
style="COLOR: #009ee3; TEXT-DECORATION: none">www.ramboll.dk</SPAN></A></SPAN></SPAN></DIV>
<DIV 
class=MsoNormal> </DIV></DIV></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN></SPAN>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> Paul Carey [mailto:paul@zed-uk.com] 
<BR><B>Sent:</B> 29. maj 2009 16:49<BR><B>To:</B> Frederik Vildbrad Winther 
(FRW); bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> RE: [Bldg-sim] Links 
between CFD or MZ and thermal simulations for simulating air and temperature 
distributions in atria<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV class=Section1>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Hi 
Frederik,</SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">DesignBuilder 
CFD would allow you to come up with an EnergyPlus multizone air flow linked 
thermal simulation coupled with a steady state CFD solution.  This has 
recently been released and is a cost-effective way of linking the 2.  If 
you used DesignBuilder to develop the energy model/Steady State CFD solution 
carried out and then use their model export options to give you the model upon 
which to then import it into a more complex transient CFD tool should it be 
necessary.  To some extent you could argue whether or not you need the 
transient analysis as the dynamic simulations should give you the temporal 
solution for the airflow and then you could look at what happens for say peak or 
mean flow conditions perhaps.  But I’d suggest that it might well be worth 
it from what you are describing as even a well set up thermal multizone model 
would do most of what you describe, but the thermal stratification issues are 
going to be a sticking point for most simulation tools, both Dynamic or CFD to 
some extent.</SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">If 
you really wanted to see the time effects of the Solar Gain on airflows, etc, 
there are many CFD tools available that would be able to do this, obviously all 
the major CFD engines would do this comfortably (Airpak from Ansys Fluent most 
easily I suspect with its integrated solar gain modelling tool) but they are 
going to be quite expensive and there is quite a learning curve to some of 
them.</SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Alternatively, 
you could use something like PyroSim, which is a good front end for NIST that 
would probably be suitable.  NIST does transient analysis and is used 
commonly for smoke/fire analysis.  It uses LES turbulence models from 
memory and so would be likely to be more accurate for the sort of stratified 
flows you’d get in an Atria as well.  You could then set transient 
boundaries based on files of data exported by the dynamic engine.  Might 
take a bit of work, but it should work.</SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Regards</SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Paul</SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<TABLE class=MsoTableGrid 
style="BORDER-RIGHT: medium none; BORDER-TOP: medium none; BORDER-LEFT: medium none; BORDER-BOTTOM: medium none; BORDER-COLLAPSE: collapse" 
cellSpacing=0 cellPadding=0 border=0>
  <TBODY>
  <TR>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 162.3pt; PADDING-TOP: 0cm" 
    vAlign=top width=216 rowSpan=2>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"><IMG 
      id=Picture_x0020_1 height=154 width=142></SPAN></P></TD>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 158.55pt; PADDING-TOP: 0cm" 
    vAlign=top width=211>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Dr 
      Paul Carey</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Director</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Low 
      Carbon Energy Assessor</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P></TD>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 157.95pt; PADDING-TOP: 0cm" 
    vAlign=top width=211>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Zero 
      Energy Design Ltd</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">10A 
      Portland Place</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">2-22 
      Mottram Road</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Stalybridge</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">SK15 
      3AD</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P></TD></TR>
  <TR>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 158.55pt; PADDING-TOP: 0cm" 
    vAlign=top width=211>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">T:  
      0161 3386200</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">F:  
      0161 3031281</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">M: 
      0789 4098012</SPAN></P></TD>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 157.95pt; PADDING-TOP: 0cm" 
    vAlign=top width=211>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">E:  
      paul@zed-uk.com</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">W:  
      <A href="http://www.zed-uk.com/" 
      target=_blank>www.zed-uk.com</A></SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P></TD></TR>
  <TR>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 162.3pt; PADDING-TOP: 0cm" 
    vAlign=top width=216>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"><IMG 
      id=Picture_x0020_2 height=81 width=200></SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P></TD>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 158.55pt; PADDING-TOP: 0cm" 
    vAlign=top width=211>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P></TD>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 157.95pt; PADDING-TOP: 0cm" 
    vAlign=top width=211>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P></TD></TR>
  <TR>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 162.3pt; PADDING-TOP: 0cm" 
    vAlign=top width=216>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"><IMG 
      id=Picture_x0020_3 height=88 width=110></SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 8pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Certificate 
      No: GB16647</SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P></TD>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 158.55pt; PADDING-TOP: 0cm" 
    vAlign=top width=211>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"><IMG 
      id=Picture_x0020_4 height=88 width=110></SPAN></P>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 8pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'">Certificate 
      No: GB16646</SPAN><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN></P></TD>
    <TD 
    style="PADDING-RIGHT: 5.4pt; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; WIDTH: 157.95pt; PADDING-TOP: 0cm" 
    vAlign=top width=211>
      <P class=MsoNormal><SPAN 
      style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P></TD></TR></TBODY></TABLE>
<P class=MsoNormal><SPAN lang=EN-US 
style="FONT-SIZE: 9pt; COLOR: green; FONT-FAMILY: 'MS Reference Sans Serif', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN lang=EN-US 
style="FONT-SIZE: 9pt; COLOR: green; FONT-FAMILY: 'MS Reference Sans Serif', 'sans-serif'">Please 
carefully consider the environment before you print this email.</SPAN></P>
<P class=MsoNormal><SPAN lang=EN-US 
style="FONT-SIZE: 9pt; COLOR: green; FONT-FAMILY: 'MS Reference Sans Serif', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN lang=EN-US 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Verdana', 'sans-serif'">Company 
Registered in England & Wales.  Registration No. 5815068</SPAN></P>
<P class=MsoNormal><SPAN lang=EN-US 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Verdana', 'sans-serif'">Registered 
Address: 10A Portland Place, 2-22 Mottram Road, Stalybridge, SK15 3AD, 
UK.</SPAN><SPAN lang=EN-US style="COLOR: #1f497d"></SPAN></P>
<P class=MsoNormal><SPAN lang=EN-US 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN><SPAN 
lang=EN-US 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><U><SPAN lang=EN-US 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Verdana', 'sans-serif'">Privilege 
and Confidentiality Notice:</SPAN></U><U><SPAN lang=EN-US 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN></U></P>
<P class=MsoNormal style="MARGIN-RIGHT: 486pt"><SPAN lang=EN-US 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Verdana', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN lang=EN-US 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Verdana', 'sans-serif'">This 
email and any attachments to it are intended only for the party to whom they are 
addressed.  They may contain privileged and/or 
confidential information.  If you have received this transmission in 
error, please notify the sender immediately and delete any digital copies and 
destroy any paper copies.  Thank you.</SPAN><SPAN lang=EN-US 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri', 'sans-serif'"></SPAN> </P>
<DIV>
<DIV 
style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0cm; BORDER-TOP: #b5c4df 1pt solid; PADDING-LEFT: 0cm; PADDING-BOTTOM: 0cm; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
<P class=MsoNormal><B><SPAN lang=EN-US 
style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma', 'sans-serif'">From:</SPAN></B><SPAN 
lang=EN-US style="FONT-SIZE: 10pt; FONT-FAMILY: 'Tahoma', 'sans-serif'"> 
bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Frederik 
Vildbrad Winther (FRW)<BR><B>Sent:</B> 29 May 2009 13:17<BR><B>To:</B> 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] Links between CFD 
or MZ and thermal simulations for simulating air and temperature distributions 
in atria</SPAN></P></DIV></DIV>
<P class=MsoNormal> </P>
<P><SPAN lang=DA 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Verdana', 'sans-serif'">Hi,</SPAN><SPAN 
lang=DA> </SPAN></P>
<P><SPAN lang=DA 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Verdana', 'sans-serif'">I am 
currently starting up on simulating a relatively large atrium in Denmark (app. 
55°N) with a glazed roof (sloped towards the sun - clever), open balconies with 
working areas connected to the atrium, as well as a smaller atrium with smaller 
openings connecting the two atria together with each other.<B> The main focus in 
the simulation is first of all the air velocity and temperature distribution in 
the occupied zone and on the balconies - describing the thermal comfort as well 
as draft rate.</B> The next focus is on integrating the smaller atria as a heat 
exchanger in winter time as well as analyzing if this can be used for cooling in 
summer time, transporting the air from outside to the biggest atrium, via the 
smaller atrium with little heating of the air. The calculations I want to 
perform in CFD also regards simulations of the solar gain in the biggest atrium. 
However simulating radiation in CFD simulations require more computing power for 
bigger rooms with a lot of surfaces. Any advice on simulating solar gain in CFD? 
How can this dynamic gain be simulated in CFD? Another cool thing in this atrium 
would be the heat recovery of the extracted air in the top part of the 
atrium.</SPAN></P>
<P><SPAN lang=DA 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Verdana', 'sans-serif'">Simulating 
this in a thermal simulation software requires a lot of luck to obtain the 
correct (and true) result in the first couple of simulations. However I am 
thinking of integrating the results from a CFD calculation into the thermal 
simulation. I am thinking of doing this as an iterative process, integrating the 
results from CFD when needed in the thermal simulations. This will probably 
result in at least 4 different simulations over a whole year, giving detailed 
results (temperature gradient, flow between zones, convective heat-transfer 
coefficients etc.) which can be used in the thermal simulation for these 4 
periods over a year. As mentioned above simulating radiation in CFD is tough, I 
am thinking of leaving this calculation in the thermal simulation.</SPAN></P>
<P><SPAN lang=DA 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Verdana', 'sans-serif'">Another 
simpler setup would be the integration of a multi-zone calculation in the 
thermal simulation giving a more coarse result of the main flow route in the 
atrium and mixing between balconies and the atrium. However these results could 
potentially give the same detailed results I am looking for.</SPAN></P>
<P><SPAN lang=DA 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Verdana', 'sans-serif'">Finally 
has any one worked on an uncertainty analysis of these coupling methods 
illustrating first of all the uncertainty in the results as well as the 
sensitivity in the input parameters?</SPAN></P>
<P><SPAN lang=DA 
style="FONT-SIZE: 10pt; COLOR: black; FONT-FAMILY: 'Verdana', 'sans-serif'">Has 
anyone done something like this before and what tools were used? I have been 
given free hands with regards to choice of software so any feedback on this 
subject will be useful. I'm really looking forward to hear from you 
:-)</SPAN></P>
<P><B><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">Kind 
regards</SPAN></B><SPAN lang=DA> </SPAN></P>
<P class=MsoNormal> </P>
<P><B><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">Frederik Vildbrad 
Winther (FRW)</SPAN></B><SPAN lang=DA><BR></SPAN><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">M.Sc., Indoor 
Environments</SPAN> <BR><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">Indoor Climate 
and HVAC</SPAN> <BR><BR><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">Rambøll Danmark 
A/S</SPAN> <BR><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">Teknikerbyen 
31</SPAN> <BR><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">DK-2830 
Virum</SPAN> <BR><A href="http://www.ramboll.dk/" target=_blank 
rel=nofollow><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">http://www.ramboll.dk</SPAN></A><SPAN 
lang=DA><BR><BR></SPAN><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">Direct 4598 
6254<BR></SPAN><A href="mailto:frw@ramboll.dk" target=_blank rel=nofollow 
ymailto="mailto:frw@ramboll.dk"><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">mailto:frw@ramboll.dk</SPAN></A><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'"> </SPAN><BR><SPAN 
lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">__________________________________________________ 
</SPAN><BR><SPAN lang=DA 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: 'Verdana', 'sans-serif'">Knowledge taking 
people further---</SPAN><SPAN lang=DA> 