<html><body bgcolor="#FFFFFF"><div>And the whole thing gets even more complicated if you want to pursue this credit in combination with the credit for Outdoor Air Delivery Monitoring.</div><div><span class="Apple-style-span" style="-webkit-composition-fill-color: rgba(175, 192, 227, 0.231373); -webkit-composition-frame-color: rgba(77, 128, 180, 0.231373);"><br></span></div><div><span class="Apple-style-span" style="-webkit-composition-fill-color: rgba(175, 192, 227, 0.231373); -webkit-composition-frame-color: rgba(77, 128, 180, 0.231373); ">Not to mention the conflict of whether you do or do not have to claim the added energy cost in credit EA-1 associated with 30% increase in ventilation. </span><br></div><div><br>Michael Tillou, PE LEED A<span class="Apple-style-span" style="-webkit-composition-fill-color: rgba(175, 192, 227, 0.231373); -webkit-composition-frame-color: rgba(77, 128, 180, 0.231373); ">P</span><div><div>Tillou Engineering, LLC</div><div><br></div><div><br></div><div>Sent from my iPhone</div></div></div><div><br>On May 18, 2009, at 12:58 PM, "James Hansen" <<a href="mailto:JHANSEN@ghtltd.com">JHANSEN@ghtltd.com</a>> wrote:<br><br></div><div></div><blockquote type="cite"><div>

<div class="Section1">

<p class="MsoNormal">I’m having a tough time deciphering how the USGBC
wants you to prove a 30% increase in OA (versus ASHRAE 62) for multi-zone
systems, and how this impacts the energy model for the proposed building.<o:p></o:p></p>

<p class="MsoNormal"><o:p> </o:p></p>

<p class="MsoNormal">There is a very specific way to determine the volume of outside
air for a multi-zone system (VPR using the 62MZCalc spreadsheet).  This
takes into account, among other things, room area, population, supply volume,
minimum primary air volume, efficiency of transfer air, system efficiency,
etc.  Once you understand all of the variables, it’s fairly
straightforward to prove compliance with EQp1, and obtain the minimum OA intake
volume.<o:p></o:p></p>

<p class="MsoNormal"><o:p> </o:p></p>

<p class="MsoNormal">However, EQc2 requires a 30% increase in outside air volume
for EACH zone “above the minimum rates required by ASHRAE Standard 62.1-2004
as determined by EQ Prerequisite 1”.  Although I’ve received
USGBC comments before claiming that I have to prove that EACH zone has 30% more
OA than required by the VPR, can anyone <b><u>confirm for sure</u></b> if this
is the case for multi-zone systems?<o:p></o:p></p>

<p class="MsoNormal"><o:p> </o:p></p>

<p class="MsoNormal">To give you an example:<o:p></o:p></p>

<p class="MsoNormal"><o:p> </o:p></p>

<p class="MsoNormal">I’ve got a 33,000 square foot floor served by an
AHU.  Standard office space with 3 or 4 conference rooms.  I’ve
used the 62MZCalc spreadsheet, and determined that my AHU needs 3,800 CFM
OA.  I’ve *<b>designed</b>* the system to provide 7,000 CFM. 
Almost twice the amount of outside air as needed (I have DCV in place). 
However, the critical conference room doesn’t get even the minimum
required OA.  It doesn’t need to – that’s the whole
point of the Multizone calc, and a good reason to use series fan-powered
terminals.<o:p></o:p></p>

<p class="MsoNormal"><o:p> </o:p></p>

<p class="MsoNormal">Per the NCv2.2 Reference Guide, we are supposed to include
the actual OA volumes in the energy model, so I guess it’s important to get
this right, especially for those clients that request a 30% increase.<o:p></o:p></p>

<p class="MsoNormal"><o:p> </o:p></p>

<p class="MsoNormal">Thanks in advance,<o:p></o:p></p>

<p class="MsoNormal"><o:p> </o:p></p>

<p class="MsoNormal"><b><span style="font-size:12.0pt;font-family:"Arial","sans-serif";
color:teal">GHT Limited<br>
</span></b><b><span style="font-family:"Arial","sans-serif""><ns0:personname><span style="color:black">James Hansen</span></ns0:personname></span></b><b><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:black">,
PE, LEED AP<o:p></o:p></span></b></p>

<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif";
color:black">Senior Associate</span></b><b><span style="font-size:12.0pt;
font-family:"Times New Roman","serif";color:black"><o:p></o:p></span></b></p>

<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif""><ns0:street><ns0:address><span style="color:black">1010 N. Glebe Rd, Suite 200</span></ns0:address></ns0:street></span><span style="font-size:12.0pt;font-family:"Times New Roman","serif""><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif""><ns0:place><ns0:city><span style="color:black">Arlington</span></ns0:city><span style="color:black">, </span><ns0:state><span style="color:black">VA</span></ns0:state><span style="color:black">  </span><ns0:postalcode><span style="color:black">22201-4749</span></ns0:postalcode></ns0:place></span><span style="font-size:12.0pt;font-family:"Times New Roman","serif";color:black"><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif";
color:black">703-338-5754 (Cell)</span><span style="font-size:12.0pt;
font-family:"Times New Roman","serif";color:black"><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif";
color:black">703-243-1200 (Office)</span><span style="font-size:12.0pt;
font-family:"Times New Roman","serif";color:black"><o:p></o:p></span></p>

<p class="MsoNormal"><span style="font-size:7.5pt;font-family:"Arial","sans-serif";
color:black">703-276-1376 (Fax)</span><span style="font-size:12.0pt;font-family:
"Times New Roman","serif";color:black"><o:p></o:p></span></p>

<p class="MsoNormal"><a href="http://www.ghtltd.com/"><span style="font-size:
10.0pt;font-family:"Arial","sans-serif";color:blue">www.ghtltd.com</span></a><o:p></o:p></p>

</div>



<!--[object_id=#ghtltd.com#]--><p align="left"><font size="2"><font face="Tahoma"><font color="#0000ff">
<hr>
</font></font><font color="#0000ff"><font color="#000000"><font face="Arial">The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee.  It is the property of GHT Limited.  Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful.  If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to </font><a href="mailto:ght@ghtltd.com"><font face="Arial">ght@ghtltd.com</font></a><font face="Arial">, and destroy this communication and all copies thereof, including all attachments.  Thank you.</font></font><font face="Tahoma" color="#000000"></font></font></font></p><font size="2"><font color="#0000ff"></font></font>
</div></blockquote><blockquote type="cite"><div><span>_______________________________________________</span><br><span>Bldg-sim mailing list</span><br><span><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a></span><br><span>To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG"><a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a></a></span><br></div></blockquote></body></html>