Vikram, of course those two people even things out!!  Umm, but really, this is why I&#39;m looking for a MRT calculator.  This way I can test a few locations in a given room quickly (much easier than doing hand calcs).  I think that <a href="http://www.meanradianttemperature.com">www.meanradianttemperature.com</a> used to have one online, but the site seems to be down.  Does anyone have any information?  Is this site down permanently, or is this a temporary issue?<br>
<br>I will probably end up with the ASHRAE calculator as it seems easiest to use.<br><br>Thanks for all the input.<br><br>--<br>Karen<br><br><div class="gmail_quote">On Tue, Apr 21, 2009 at 3:02 PM, Vikram Sami <span dir="ltr">&lt;<a href="mailto:VSami@lasarchitect.com">VSami@lasarchitect.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">









<div link="blue" vlink="purple" lang="EN-US">

<div>

<p><span style="font-size: 11pt; color: rgb(0, 37, 196);">It’s an interesting conundrum that the times that MRT
becomes a significant player in the comfort calculation is when there is an
uneven radiant field (hot or cold window; fireplace; thermal mass wall). In
such a situation, is it fair to average out the MRT for an entire room? Don’t
your view factors change drastically depending on your position in the room? </span></p>

<p><span style="font-size: 11pt; color: rgb(0, 37, 196);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(0, 37, 196);">Does one person too hot near the window and another person too
cold on the inside equal thermal comfort?  </span></p>

<p><span style="font-size: 11pt; color: rgb(0, 37, 196);"> </span></p>

<div>

<p><b><span style="font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: black;">Vikram Sami,</span></b><span style="color: rgb(0, 37, 196);"> </span><span style="font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: black;">LEED AP</span><span style="color: rgb(0, 37, 196);"> <br>

</span><span style="font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: black;">Direct Phone
404-253-1466 | Direct Fax 404-253-1366</span><span style="color: rgb(0, 37, 196);"> </span></p>

<p><b><span style="font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">L</span></b><b><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">ORD</span></b><b><span style="font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">, A</span></b><b><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">ECK</span></b><b><span style="font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;"> &amp; S</span></b><b><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">ARGENT</span></b><b><span style="font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;"> A</span></b><b><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: maroon;">RCHITECTURE</span></b><b><span style="color: rgb(0, 37, 196);"><br>

</span></b><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: rgb(0, 37, 196);">1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361</span><span style="color: rgb(0, 37, 196);"> <br>

</span><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: rgb(0, 37, 196);">Responsive
Design</span><span style="color: rgb(0, 37, 196);"> </span><span style="font-size: 7.5pt; font-family: Symbol; color: rgb(0, 37, 196);">·</span><span style="color: rgb(0, 37, 196);"> </span><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: rgb(0, 37, 196);">Technological
Expertise</span><span style="color: rgb(0, 37, 196);"> </span><span style="font-size: 7.5pt; font-family: Symbol; color: rgb(0, 37, 196);">·</span><span style="color: rgb(0, 37, 196);">
</span><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: rgb(0, 37, 196);">Exceptional
Service</span><span style="color: rgb(0, 37, 196);"> <br>
</span><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: rgb(0, 127, 0);">Please
visit our new website</span><span style="color: rgb(0, 37, 196);"> </span><span style="font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: black;">|</span><span style="color: rgb(0, 37, 196);"> <a><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;;">www.lordaecksargent.com</span></a></span></p>


<p><span style="font-size: 24pt; font-family: Webdings; color: rgb(0, 127, 0);">P </span><span style="font-size: 10pt; font-family: &quot;Garamond&quot;,&quot;serif&quot;; color: rgb(0, 127, 0);">Think GREEN
before you print.</span><span style="color: rgb(0, 37, 196);"></span></p>

<p><span style="color: rgb(0, 37, 196);"> </span></p>

</div>

<p><span style="font-size: 11pt; color: rgb(0, 37, 196);"> </span></p>

<div>

<div style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">

<p><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Peter
Simmonds<br>
<b>Sent:</b> Tuesday, April 21, 2009 1:36 PM<br>
<b>To:</b> Timothy Moore; Karen Walkerman; <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><div><div></div><div class="h5"><br>
<b>Subject:</b> Re: [Bldg-sim] MRT Tool</div></div></span></p>

</div>

</div><div><div></div><div class="h5">

<p> </p>

<p><span style="font-size: 10pt; color: navy;">I do not think the thermal comfort tool calculates the MRT it is a
user input.</span></p>

<p><span style="font-size: 10pt; color: navy;"> </span></p>

<div>

<p style="margin-bottom: 12pt;"><span style="font-size: 10pt; color: black;">Peter
Simmonds. Ph.D.</span><span style="font-size: 7.5pt; color: gray;"><br>
Senior Associate, Advanced Technology Group<br>
<br>
</span><span style="color: gray;">IBE Consulting
Engineers</span><span style="color: gray;"><br>
</span><span style="font-size: 7.5pt; color: gray;">14130 Riverside Drive Suite 201</span><span style="font-size: 7.5pt; color: navy;"><br>
</span><span style="font-size: 7.5pt; color: gray;">Sherman Oaks, CA 91423<br>
p:   (818) 377-8220 ext. 246<br>
f:    (818) 377-8230<br>
m:  (818) 219-1284</span></p>

<p><span style="font-size: 7.5pt; color: gray;">This e-mail
message, including any attachments, is for the sole use of the intended
recipient(s) and may contain confidential and privileged information. Any
unauthorized review, use, disclosure, or distribution is prohibited. If you are
not the intended recipient, please contact the sender by reply e-mail and
destroy all copies of the original message</span></p>

</div>

<p><span style="font-size: 10pt; color: navy;"> </span></p>

<div>

<div style="text-align: center;" align="center">

<hr align="center" size="2" width="100%">

</div>

<p><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;"> Timothy Moore
[mailto:<a href="mailto:timothy.moore@iesve.com" target="_blank">timothy.moore@iesve.com</a>] <br>
<b>Sent:</b> Tuesday, April 21, 2009 10:00 AM<br>
<b>To:</b> Karen Walkerman; <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Bldg-sim] MRT Tool</span></p>

</div>

<p> </p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Karen,</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">The ASHRAE-55 Thermal Comfort Tool created by the UC Berkeley
Center for the Built Environment and available from ASHRAE publications (if I
recall correctly) includes a very easy-to-use MRT calculator for rectangular
rooms. It allows for MRT at a particular position in that room, separate
surface temperatures and dimensions for surfaces, and also the inclusion of a
“panel” or other area within one of the walls (such as a cold/hot
window, heating panel, etc.) that has a distinct temperature. This is part of a
very handy tool for determining PPD, etc. based upon the typical range of human
thermal comfort variables (clo value, activity level, air temp, MRT, humidity,
air movement).</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Cheers,</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);">Timothy</span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<table style="width: 331.5pt; border-collapse: collapse; margin-bottom: 3.25pt;" align="left" border="0" cellpadding="0" cellspacing="0" width="442">
 <tbody><tr>
  <td style="padding: 0.7pt; width: 49.5pt;" valign="top" width="66">
  <p style="line-height: 115%;"><span style="width: 60px; height: 58px;"><img src="cid:image003.jpg@01C9C291.F7225A80" alt="IES logo CMYK" width="60" height="58"></span><br clear="all">
  <b><span style="color: rgb(31, 73, 125);"></span></b></p>
  </td>
  <td style="padding: 0.7pt; width: 112.5pt;" valign="top" width="150">
  <p><b><span style="font-size: 13pt; color: navy;">Timothy Moore <br>
  </span></b><b><span style="font-size: 10pt; color: navy;">Senior Consultant<br>
  Special Projects </span></b></p>
  </td>
  <td style="padding: 0.7pt; width: 169.5pt;" valign="top" width="226">
  <p style="margin-top: 3pt;"><span style="font-size: 8pt; color: navy;">Mobile:
  415 810 2495 <br>
  Office: 415 983-0603<br>
  <u><a href="mailto:timothy.moore@iesve.com" target="_blank"><span style="color: navy;">timothy.moore@iesve.com</span></a></u><br>
  </span><span style="color: rgb(31, 73, 125);"><a href="http://www.iesve.com/" target="_blank"><span style="font-size: 8pt; color: navy;">www.iesve.com
  </span></a></span><span style="font-size: 8pt; color: navy;"></span></p>
  </td>
 </tr>
 <tr>
  <td colspan="3" style="padding: 0.7pt; width: 331.5pt;" valign="top" width="442">
  <p style="line-height: 115%;"><span style="font-size: 8pt; line-height: 115%; color: navy;">**Design, Simulate +
  Innovate with the &lt;Virtual Environment&gt;**</span><span style="color: rgb(31, 73, 125);"></span></p>
  </td>
 </tr>
 <tr>
  <td colspan="3" style="padding: 0.7pt; width: 331.5pt;" valign="top" width="442">
  <p style="line-height: 115%;"><span style="color: rgb(31, 73, 125);"><a href="http://www.iesve.com/disclaimer.html" target="_blank"><span style="font-size: 8pt; line-height: 115%; color: navy;">Email Disclaimer</span></a></span></p>

  </td>
 </tr>
</tbody></table>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<p><span style="font-size: 11pt; color: rgb(31, 73, 125);"> </span></p>

<div style="border-style: solid none none; border-color: rgb(181, 196, 223) -moz-use-text-color -moz-use-text-color; border-width: 1pt medium medium; padding: 3pt 0in 0in;">

<p><b><span style="font-size: 10pt;">From:</span></b><span style="font-size: 10pt;">
<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Karen
Walkerman<br>
<b>Sent:</b> Tuesday, April 21, 2009 9:50 AM<br>
<b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
<b>Subject:</b> [Bldg-sim] MRT Tool</span></p>

</div>

<p> </p>

<p>Hello,<br>
<br>
Is anyone aware of a simple Mean Radiant Temperature calculation tool? 
I&#39;m looking for something that will calculate MRT for a basic rectangular room.<br>
<br>
Thanks!<br>
<br>
--<br>
Karen</p>

</div></div></div>

</div>


</blockquote></div><br>