<DIV><SPAN class=651085918-04032009><FONT face=Arial size=2>To
All,</FONT></SPAN></DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial size=2>I've got a high
number of hours outside throttling range for a 27-story building in India (40%
of hours). It is a VAV with electric reheat. Upon inputting 40,000
cfm per floor (25,000 sf), I get down to about 3% of hours outside throttling
range. However, Trace only calls for about 20,000 cfm per floor. I
double checked all my load inputs across both programs and it seems like
occupancy, lights and equipment loads match up. </FONT></SPAN></DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial size=2>I noticed that most
of my unmet cooling load hours occur in my internal zones. So I input a
system total supply volume of 25,000 cfm per floor and also allocated 16,000 cfm
to the internal zones. This decreased the number of hours outside throttling
range to about 4%.</FONT></SPAN></DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial size=2>My question is, am I
allowed to "allocate" cfm to the internal zones like that?</FONT></SPAN></DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial size=2>Thanks very much in
advance!</FONT></SPAN></DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial
size=2>Linda</FONT></SPAN></DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=651085918-04032009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV> </DIV>
<DIV align=left><IMG
alt=" Linda Lam, LEED® AP WSP Flack + Kurtz 405 Howard Street, Suite 500 San Francisco, CA 94105 Direct: 415.402.5813 Main Tel: 415.398.3833 Fax: 415.433.5311 website: http://www.wspfk.com vCard: http://vcards.wspfk.com/vcardloader.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.vcf image: "
src="http://vcards.wspfk.com/usercard.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.png"
align=absMiddle useMap=#flackkurtz-linda-lam-wspfk-com-1227040073 border=0
nosend="1">
<STYLE>
a {color: 1D88F6;}
</STYLE>
<MAP name=flackkurtz-linda-lam-wspfk-com-1227040073><AREA shape=RECT
target=_blank coords=401,9,458,31 href="http://www.wspfk.com"><AREA shape=RECT
target=_blank coords=458,9,503,31
href="http://vcards.wspfk.com/vcardloader.php?filename=flackkurtz-linda-lam-wspfk-com-1227040073.vcf"><AREA
shape=RECT target=_blank coords=503,9,536,31
href="http://maps.google.com/maps?f=q&hl=en&geocode=&q=405+Howard+Street,+San+Francisco,+CA+94105&sll=40.754409,-73.988972&sspn=0.019083,0.032616&ie=UTF8&ll=37.79032,-122.395163&spn=0.019908,0.032616&z=15&iwloc=addr"><AREA
shape=RECT target=_blank coords=536,9,578,31
href="mailto:linda.lam@wspfk.com"><AREA shape=RECT target=_blank
coords=0,31,591,161 href="http://www.wspfk.com"></MAP></DIV>
<DIV> </DIV></BODY></HTML>