<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial 
size=2>Shaojie,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial size=2>I 
believe you should be concerned with the wetbulb temp of the mixed air entering 
the coil (unless you are 100% OA). If I remember correctly, I 
went through the same analysis once. It becomes a little difficult because 
I don't believe the mixed air wetbulb is a variable that you'll find available 
in the hourly reports. But if you do the manual calculation things should start 
to come together.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial 
size=2>Good luck,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><B><SPAN 
style="FONT-FAMILY: 'GillSans Light'"><SPAN 
style="mso-spacerun: yes"></SPAN></SPAN></B></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><B><SPAN 
style="FONT-FAMILY: 'GillSans Light'"><SPAN style="mso-spacerun: yes">  
</SPAN></SPAN></B><B><SPAN 
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt">Jonathan 
M. Curtin, EIT, LEED</SPAN></B><SUP><SPAN 
style="FONT-FAMILY: 'GillSans Light'">®</SPAN></SUP><B><SPAN 
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt"> 
AP</SPAN></B><B><SPAN 
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'"><BR></SPAN></B><B><SPAN 
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt"><SPAN 
style="mso-spacerun: yes">  </SPAN></SPAN></B><B><SPAN 
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'">Mechanical 
Engineer</SPAN></B><STRONG><SPAN 
style="FONT-FAMILY: 'GillSans Light'"><?xml:namespace prefix = o ns = 
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></SPAN></STRONG></DIV>
<DIV dir=ltr align=left>
<DIV class=Section1>
<P class=MsoNormal><STRONG><SPAN style="FONT-FAMILY: 'GillSans Light'"><SPAN 
style="mso-spacerun: yes"> </SPAN></SPAN></STRONG><B><SPAN 
style="FONT-FAMILY: 'GillSans Light'"><IMG height=159 
src="cid:689404818@13022009-2207" width=240 
v:shapes="_x0000_i1025"><STRONG><o:p></o:p></STRONG></SPAN></B></P></DIV></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>eric 
wang<BR><B>Sent:</B> Friday, February 13, 2009 12:48 PM<BR><B>To:</B> 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] DX Cooling EIR 
Ratio Curve<BR></FONT><BR></DIV>
<DIV></DIV>
<TABLE cellSpacing=0 cellPadding=0 border=0>
  <TBODY>
  <TR>
    <TD vAlign=top>
      <DIV>Hi,</DIV>
      <DIV> </DIV>
      <DIV>I used the default DX Cooling EIR Ratio Curve 
      (DX-Cool-Cap-fEWB&OAT) in eQUEST. The variables are t 
      entering wetbulb and t enter condenser. I assume these refer to 
      outside air wet and dry bulb temperatures. After exporting outside 
      air wet and dry bulb temperatures in hourly report, the value of 
      "Temp correction to COOLING-EIR" I calculated is different to the one in 
      the hourly report by using the curve coefficients. Can anyone point out if 
      my understanding is correct?</DIV>
      <DIV> </DIV>
      <DIV>Thanks a lot for your help</DIV>
      <DIV> </DIV>
      <DIV>Shaojie</DIV></TD></TR></TBODY></TABLE><BR>
<!--qsdbegin-->

<DIV><SPAN class=469015015-07012009><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=469015015-07012009>
<DIV class=MsoNormal style="MARGIN: 0in 0in 0pt; TEXT-ALIGN: center" 
align=center>
<HR align=center width="100%" SIZE=2>
</DIV><FONT color=#000000><U><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">Legal 
Disclaimer:</SPAN></U><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"> 
</SPAN><STRONG><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">The 
information contained in this communication is confidential and is 
</SPAN></STRONG><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">covered 
by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it 
</SPAN><STRONG><SPAN 
style="FONT-WEIGHT: normal; FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">may 
be privileged and is intended for the exclusive use of the above named 
addressee(s). If you are not the intended recipient(s), you are expressly 
prohibited from copying, distributing, disseminating, or in any other way using 
any of the information contained within this communication. If you have received 
this communication in error, please contact the sender by telephone at 
(713) 781-2526 or by response via email and permanently delete the original 
email (including attachments) and any copies. </SPAN></STRONG><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"> 
<BR><BR><SPAN 
style="FONT-SIZE: 6.5pt; COLOR: #007213; FONT-FAMILY: Arial">Please consider the 
environment before printing this email.</SPAN></I></SPAN></FONT></SPAN><B><SPAN 
style="FONT-SIZE: 11pt; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 12.0pt"> <SPAN 
style="mso-spacerun: yes">   </SPAN></SPAN></B><B><SPAN 
<!--qsdend-->
<br></BODY></HTML>