size=2>Shaojie,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial size=2>I
believe you should be concerned with the wetbulb temp of the mixed air entering
the coil (unless you are 100% OA). If I remember correctly, I
went through the same analysis once. It becomes a little difficult because
I don't believe the mixed air wetbulb is a variable that you'll find available
in the hourly reports. But if you do the manual calculation things should start
to come together.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><FONT face=Arial
size=2>Good luck,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><B><SPAN
style="FONT-FAMILY: 'GillSans Light'"><SPAN
style="mso-spacerun: yes"></SPAN></SPAN></B></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=689404818-13022009><B><SPAN
style="FONT-FAMILY: 'GillSans Light'"><SPAN style="mso-spacerun: yes">
</SPAN></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt">Jonathan
M. Curtin, EIT, LEED</SPAN></B><SUP><SPAN
style="FONT-FAMILY: 'GillSans Light'">®</SPAN></SUP><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt">
AP</SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'"><BR></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 10.0pt"><SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></B><B><SPAN
style="COLOR: #4d4d4d; FONT-FAMILY: 'GillSans Light'">Mechanical
Engineer</SPAN></B><STRONG><SPAN
style="FONT-FAMILY: 'GillSans Light'"><?xml:namespace prefix = o ns =
"urn:schemas-microsoft-com:office:office" /><o:p></o:p></SPAN></STRONG></DIV>
<DIV dir=ltr align=left>
<DIV class=Section1>
<P class=MsoNormal><STRONG><SPAN style="FONT-FAMILY: 'GillSans Light'"><SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></STRONG><B><SPAN
style="FONT-FAMILY: 'GillSans Light'"><IMG height=159
src="cid:689404818@13022009-2207" width=240
v:shapes="_x0000_i1025"><STRONG><o:p></o:p></STRONG></SPAN></B></P></DIV></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>eric
wang<BR><B>Sent:</B> Friday, February 13, 2009 12:48 PM<BR><B>To:</B>
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] DX Cooling EIR
Ratio Curve<BR></FONT><BR></DIV>
<DIV></DIV>
<TABLE cellSpacing=0 cellPadding=0 border=0>
<TBODY>
<TR>
<TD vAlign=top>
<DIV>Hi,</DIV>
<DIV> </DIV>
<DIV>I used the default DX Cooling EIR Ratio Curve
(DX-Cool-Cap-fEWB&OAT) in eQUEST. The variables are t
entering wetbulb and t enter condenser. I assume these refer to
outside air wet and dry bulb temperatures. After exporting outside
air wet and dry bulb temperatures in hourly report, the value of
"Temp correction to COOLING-EIR" I calculated is different to the one in
the hourly report by using the curve coefficients. Can anyone point out if
my understanding is correct?</DIV>
<DIV> </DIV>
<DIV>Thanks a lot for your help</DIV>
<DIV> </DIV>
<DIV>Shaojie</DIV></TD></TR></TBODY></TABLE><BR>
<!--qsdbegin-->
<DIV><SPAN class=469015015-07012009><FONT face=Arial
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=469015015-07012009>
<DIV class=MsoNormal style="MARGIN: 0in 0in 0pt; TEXT-ALIGN: center"
align=center>
<HR align=center width="100%" SIZE=2>
</DIV><FONT color=#000000><U><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">Legal
Disclaimer:</SPAN></U><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">
</SPAN><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">The
information contained in this communication is confidential and is
</SPAN></STRONG><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">covered
by the Electronic Communications Privacy Act, 18 U.S.C. §§ 2510-2521; it
</SPAN><STRONG><SPAN
style="FONT-WEIGHT: normal; FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">may
be privileged and is intended for the exclusive use of the above named
addressee(s). If you are not the intended recipient(s), you are expressly
prohibited from copying, distributing, disseminating, or in any other way using
any of the information contained within this communication. If you have received
this communication in error, please contact the sender by telephone at
(713) 781-2526 or by response via email and permanently delete the original
email (including attachments) and any copies. </SPAN></STRONG><SPAN
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial; mso-bidi-font-size: 12.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA">
<BR><BR><SPAN
style="FONT-SIZE: 6.5pt; COLOR: #007213; FONT-FAMILY: Arial">Please consider the
environment before printing this email.</SPAN></I></SPAN></FONT></SPAN><B><SPAN
style="FONT-SIZE: 11pt; FONT-FAMILY: 'GillSans Light'; mso-bidi-font-size: 12.0pt"> <SPAN
style="mso-spacerun: yes"> </SPAN></SPAN></B><B><SPAN
<!--qsdend-->
<br></BODY></HTML>