JRR wrote;<br>
<br>
    I won an ASME regional design contest prize with my Solar House
design, a graduating<br>
    semester design project. It was later fully detailed and built in
1986. We moved in Jan<br>
   1987. It is basically a LEED Platinum building, one story with
finished basement, 2x6<br>
    studs 24 OC upstairs with 1" XPS sheathing, brick vernier 100%, etc.<br>
<br>
    The main surprises vis a vis air infiltration  were / are<br>
<br>
    1) The porosity of the above grade basement CMUs allowing air
infiltration.<br>
    2) The top or finish course of CMUs was not always sealed from an
air infiltration<br>
       point of view and many of these CMU cores were hidden behind
finish dry wall<br>
       for years.<br>
    3)The air return duct through the attic even though sealed with
metal tape and covered<br>
       with R-25 batts was not sealed to the attic penetration / wood
surround for years.<br>
    4) One bathroom had an outside wall stud space with no insulation
at all - it contained<br>
       the plumbing  vent stack. The framing crew and insulation crews
thought we were <br>
       'over insulated' and just didn't need it.<br>
    5) None of the plumbing stacks were sealed at the attic penetration
on the outside<br>
       by the work crews.<br>
    6) The Active Solar plumbing penetrations were not sealed at the
attic penetration<br>
       by the work crews.<br>
    7) Rodentia bent the clothes dryer outside vent flap so severely
that it would not close<br>
       completely on its own, but we never had mice enter the house via
this access.<br>
    8) Conventional plumbing stack boots, black rubber, were utterly
destroyed by the<br>
       heat from the Active Solar pipes. We made silicon rubber
fittings to replace them.<br>
       We run an oversquare ( more sq ft collector than gal of tankage
) system with 6/12<br>
       slope 20 degrees W of S at  ~ 38:45 N. We use the active system
for more than<br>
       domestic hot water. Since we sabotaged the evil tempering valve <span
 class="moz-smiley-s8"><span> =-O  </span></span><br>
       we have all metal bodied valves through out the house and a
stainless steel tub on the<br>
       dishwasher.<br>
    9) None of these problems was detected by a military grade IR video
shot from outside<br>
       the house in freezing cold weather.  IR shot inside the attic
was extremely revealing.<br>
    10) Leak testing has to be done during windy weather -- the leaks
act in concert., and<br>
       CFD considerations show that differing pressures exist at
specific locations.<br>
<br>
Our all electric bill for 4500 sq ft this last December was  $72.00<br>
<br>
We are developing a new version of this house with architectural as
well as energy improvements.<br>
<br>
John R Ross III PE<br>
Westwind Corporation<br>
Vienna, VA  22182-1958<br>
<a class="moz-txt-link-abbreviated" href="mailto:energy.wwind@cox.net">energy.wwind@cox.net</a><br>
<br>
<br>
Andy hoover wrote:
<blockquote cite="mid:F075D88711C84BB6842445AA1D7A6339@DEN" type="cite">
  <meta http-equiv="Content-Type" content="text/html; ">
  <meta name="Generator" content="Microsoft Word 11 (filtered medium)">
<!--[if !mso]>
<style>
v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style>
<![endif]--><o:SmartTagType
 namespaceuri="urn:schemas-microsoft-com:office:smarttags"
 name="PostalCode">
  <o:SmartTagType
 namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="State"><o:SmartTagType
 namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="City">
  <o:SmartTagType
 namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="place"><o:SmartTagType
 namespaceuri="urn:schemas-microsoft-com:office:smarttags" name="Street">
  <o:SmartTagType
 namespaceuri="urn:schemas-microsoft-com:office:smarttags"
 name="address"><!--[if !mso]>
<style>
st1\:*{behavior:url(#default#ieooui) }
</style>
<![endif]-->
  <style>
<!--a:link
        {mso-style-priority:99;}
span.MSOHYPERLINK
        {mso-style-priority:99;}
a:visited
        {mso-style-priority:99;}
span.MSOHYPERLINKFOLLOWED
        {mso-style-priority:99;}

 /* Font Definitions */
 @font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Papyrus;
        panose-1:3 7 5 2 6 5 2 3 2 5;}
@font-face
        {font-family:"Arial Black";
        panose-1:2 11 10 4 2 1 2 2 2 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:Calibri;}
a:link, span.MsoHyperlink
        {color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;
        text-decoration:underline;}
p
        {mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman";}
span.EmailStyle17
        {mso-style-type:personal;
        font-family:Calibri;
        color:windowtext;}
span.EmailStyle18
        {mso-style-type:personal-reply;
        font-family:Arial;
        color:navy;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
  </style><!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
  </o:SmartTagType></o:SmartTagType></o:SmartTagType></o:SmartTagType></o:SmartTagType></o:SmartTagType>
  <div class="Section1">
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">Hi all:<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">We do
building envelope consulting and are
very curious as to what folks do and what rates they use whatever
approach. 
When looking at buildings we find that most  infiltrate much more in
the
real world than designers estimate and that the fluctuations are far
greater
than predicted.  We would also love it if anyone has any experiences
which
can be shared.<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">Thanks,<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">Andy <o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;"><o:p> </o:p></span></font></p>
  <div>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">Andy Hoover</span></font><font
 color="navy"><span style="color: navy;"><o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">Principal<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">The BEST
Consultant, Inc.<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">Office:
678-200-7648<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">Fax:678-827-0574<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;">Cell:
678-793-1159<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: navy;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Calibri" size="2"><span
 style="font-size: 11pt; color: navy;"><a moz-do-not-send="true"
 href="http://www.thebestconsultant.com">www.thebestconsultant.com</a></span></font><font
 color="navy" face="Times New Roman" size="3"><span
 style="font-size: 12pt; font-family: "Times New Roman"; color: navy;"><o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Calibri" size="2"><span
 style="font-size: 11pt; color: navy;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font color="navy" face="Calibri" size="2"><span
 style="font-size: 11pt; color: navy;"><o:p> </o:p></span></font></p>
  <div class="MsoNormal" style="text-align: center;" align="center"><font
 color="navy" face="Calibri" size="2"><span
 style="font-size: 10pt; color: navy;">
  <hr align="center" size="3" width="100%"></span></font></div>
  <p><font color="gray" face="Arial" size="1"><span
 style="font-size: 7.5pt; font-family: Arial; color: gray;">This
message may contain confidential and/or privileged
information. If you are not the addressee or authorized to receive this
information for the addressee, you must not use, copy, disclose, or
take any
action based on this message or information herein. If you have
received this
message in error, please advise the sender immediately by reply e-mail
and
delete this message. Thank you for your cooperation.</span></font><font
 size="2"><span style="font-size: 10pt;"><o:p></o:p></span></font></p>
  </div>
  <div>
  <div class="MsoNormal" style="text-align: center;" align="center"><font
 face="Times New Roman" size="3"><span
 style="font-size: 12pt; font-family: "Times New Roman";">
  <hr tabindex="-1" align="center" size="3" width="100%"></span></font></div>
  <p class="MsoNormal"><b><font face="Tahoma" size="2"><span
 style="font-size: 10pt; font-family: Tahoma; font-weight: bold;">From:</span></font></b><font
 face="Tahoma" size="2"><span
 style="font-size: 10pt; font-family: Tahoma;">
<a class="moz-txt-link-abbreviated" href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</a>] <b><span
 style="font-weight: bold;">On Behalf Of </span></b>Talbert, Joshua<br>
  <b><span style="font-weight: bold;">Sent:</span></b> Friday, February
06, 2009
10:30 AM<br>
  <b><span style="font-weight: bold;">To:</span></b>
<a class="moz-txt-link-abbreviated" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
  <b><span style="font-weight: bold;">Subject:</span></b> [Bldg-sim]
Infiltration
Schedule</span></font><font face="Times New Roman" size="3"><span
 style="font-size: 12pt; font-family: "Times New Roman";"><o:p></o:p></span></font></p>
  </div>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;">Howdy
Bldg Sim peers!<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;">While
working on LEED Equest simulations I find that in an effort to simplify
I end
up deleting the P-Inf and C-Inf Infiltration Schedules all of the time
and end
just use "<i><span style="font-style: italic;">undefined"</span></i> to
simulate a constant infiltration rate.  I was curious to know if anyone
uses the actual Infiltrations schedules, to emulate winds and or
building
pressurization, and if so do you typically achieve more energy savings,
and do
you find it worth the extra effort?<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;">Thanks
all and be well.<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;">Josh<o:p></o:p></span></font></p>
  <div>
  <p class="MsoNormal"><font color="#003366" face="Papyrus" size="3"><span
 style="font-size: 12pt; font-family: Papyrus; color: rgb(0, 51, 102);">Joshua
W. Talbert </span></font><font color="#003366" face="Times New Roman"
 size="2"><span
 style="font-size: 10pt; font-family: "Times New Roman"; color: rgb(0, 51, 102);">P.E.,
LEED-AP</span></font><font color="#003366" face="Papyrus" size="3"><span
 style="font-size: 12pt; font-family: Papyrus; color: rgb(0, 51, 102);"><o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="#003366" face="Papyrus" size="3"><span
 style="font-size: 12pt; font-family: Papyrus; color: rgb(0, 51, 102);">Mechanical
Engineer<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="#003366" face="Arial" size="5"><span
 style="font-size: 16pt; font-family: Arial; color: rgb(0, 51, 102);">Hallam</span></font><b><font
 color="#cc3300" face="Arial Black" size="5"><span
 style="font-size: 16pt; font-family: "Arial Black"; color: rgb(204, 51, 0); position: relative; top: -1pt; font-weight: bold;">///</span></font></b><font
 color="#003366" face="Arial" size="5"><span
 style="font-size: 16pt; font-family: Arial; color: rgb(0, 51, 102);">ICS<o:p></o:p></span></font></p>
  <p class="MsoNormal"><st1:Street w:st="on"><st1:address w:st="on"><font
 color="#003366" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: rgb(0, 51, 102);">38
Eastwood Dr. Suite 200</span></font></st1:address></st1:Street><font
 color="#003366" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: rgb(0, 51, 102);"><o:p></o:p></span></font></p>
  <p class="MsoNormal"><st1:place w:st="on"><st1:City w:st="on"><font
 color="#003366" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: rgb(0, 51, 102);">S.
Burlington</span></font></st1:City><font color="#003366" face="Arial"
 size="2"><span
 style="font-size: 10pt; font-family: Arial; color: rgb(0, 51, 102);">,
  <st1:State w:st="on">VT</st1:State> <st1:PostalCode w:st="on">05403</st1:PostalCode></span></font></st1:place><font
 color="#003366" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: rgb(0, 51, 102);"><o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="#003366" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: rgb(0, 51, 102);">P:
(802) 658-4891<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="#003366" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: rgb(0, 51, 102);">F:
(802) 658-1457<o:p></o:p></span></font></p>
  <p class="MsoNormal"><font color="#003366" face="Arial" size="2"><span
 style="font-size: 10pt; font-family: Arial; color: rgb(0, 51, 102);"><o:p> </o:p></span></font></p>
  </div>
  <p class="MsoNormal"><font face="Calibri" size="2"><span
 style="font-size: 11pt;"><o:p> </o:p></span></font></p>
  <p class="MsoNormal"><font face="Times New Roman" size="3"><span
 style="font-size: 12pt; font-family: "Times New Roman";"><o:p> </o:p></span></font></p>
  <div class="MsoNormal" style="text-align: center;" align="center"><font
 face="Times New Roman" size="3"><span
 style="font-size: 12pt; font-family: "Times New Roman";">
  <hr align="center" size="3" width="100%"></span></font></div>
  <p class="MsoNormal"><font color="gray" face="Arial" size="1"><span
 style="font-size: 7.5pt; font-family: Arial; color: gray;"><br>
CONFIDENTIALITY NOTICE:<br>
The information contained in this transmission, as well as any
accompanying
documents, constitutes confidential and/or legally privileged
information which
is the property of Hallam-ICS. The information is intended solely for
the
individual entity named on this transmittal sheet. If you are not the
designated
recipient, you are hereby notified that any disclosure, copying,
distribution
or taking any action in reliance on this information is strictly
prohibited. If
you received this in error, please contact the sender and delete the
material
from any computer. Opinions, conclusions and the information in this
message
that do not relate to the official business of my firm shall be
understood as
neither given nor endorsed by it.</span></font><font
 face="Times New Roman" size="3"><span
 style="font-size: 12pt; font-family: "Times New Roman";"><o:p></o:p></span></font></p>
  </div>
  <pre wrap="">
<hr size="4" width="90%">
_______________________________________________
Bldg-sim mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a>
  </pre>
</blockquote>
</body>
</html>