<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman,new york,times,serif;font-size:12pt"><br>Hi All,<br><br>I am modeling a residential building with RESYS as a system, and using auto sizing for system sizing.<br><br>The space temperature (space design temperature) for load calculation is set at 75 oF while the Design-Cool-T is set at 78 oF.&nbsp; I believe that this has the effect of decreasing the system cooling capacity. There is no set-back or set-up applied.&nbsp;&nbsp;&nbsp; No ventilation outdoor air is specified.&nbsp; Infiltration, which is already captured in the building load calculation, is part of the building load.&nbsp; <br><br>How does the system cooling capacity increases by more than 50% (in the case of Minneapolis and Duluth, Minnesota) compared to the building peak load in the absence of any out door air load for ventilation?&nbsp;
 <br><br>Thanks,<br>&nbsp;<br>Bereket<br><div><br></div><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><br><div style="font-family: times new roman,new york,times,serif; font-size: 12pt;"><font size="2" face="Tahoma"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> Joe Huang &lt;joe@drawbdl.com&gt;<br><b><span style="font-weight: bold;">To:</span></b> Ellen Franconi &lt;EFranconi@archenergy.com&gt;; bldg-sim@lists.onebuilding.org; Jeff Haberl &lt;jeffhaberl@tees.tamus.edu&gt;; Bereket Nigusse &lt;nigusse_ba@yahoo.com&gt;<br><b><span style="font-weight: bold;">Sent:</span></b> Tuesday, February 3, 2009 2:16:32 AM<br><b><span style="font-weight: bold;">Subject:</span></b> Re: [Bldg-sim] Residential System Sizing<br></font><br>       <style></style>  <div><font face="Arial">Ellen, </font></div> <div><font face="Arial"></font>&nbsp;</div> <div><font face="Arial">Not exactly. What you wrote is definitely
 true&nbsp;during  the SYSTEMS simulation and peak loads reported in SS-F (?), but Bereket was  referring to the SV-A, which is the systems sizing report. Assuming that he's  doing "auto-sizing",&nbsp; the DOE-2 sizing routine will take the peak loads  from LOADS and compute the design cooling capacity at the  COOLING-DESIGN-TEMPERATURE. (I may have the keyword wrong, since I don't have a  DOE-2 manual handy).&nbsp; Thus, the termperature discrepancy between the single  LOADS temperature and the COOLING-DESIGN-TEMPERATURE&nbsp;does exist, as you've  mentioned, but transient loads due to tempeature set-up or set-back  or&nbsp;interzone heat flows&nbsp;are not reflected. That's why an autosized  SYSTEM will often still result in a few undercooled or underheated  hours.</font></div> <div><font face="Arial"></font>&nbsp;</div> <div><font face="Arial">My suggestion to Bereket in making sense of the numbers is  to&nbsp;compare the TEMPERATURE under
 SPACE-CONDITIONS for the LOADS reference  temperature,&nbsp;to the COOLING-DESIGN-TEMPERATURE (I may have this keyword  wrong) is ZONE-CONDITIONS in SYSTEMS. What kind of HVAC are you modeling?&nbsp;  It sounds like a residential system (RESYS), but that system doesn't have any  OUTSIDE-AIR, does it ? </font></div> <div><font face="Arial"></font>&nbsp;</div> <div><font face="Arial">Joe Huang</font></div> <div><font face="Arial">White Box Technologies, Inc.</font></div> <div><font face="Arial"></font>&nbsp;</div> <blockquote style="border-left: 2px solid rgb(0, 0, 0); padding-right: 0px; padding-left: 5px; margin-left: 5px; margin-right: 0px;">   <div style="font-family: arial; font-style: normal; font-variant: normal; font-weight: normal; font-size: 10pt; line-height: normal; font-size-adjust: none; font-stretch: normal;">----- Original Message ----- </div>   <div style="background: rgb(228, 228, 228) none repeat scroll 0% 0%; -moz-background-clip:
 -moz-initial; -moz-background-origin: -moz-initial; -moz-background-inline-policy: -moz-initial; font-family: arial; font-style: normal; font-variant: normal; font-weight: normal; font-size: 10pt; line-height: normal; font-size-adjust: none; font-stretch: normal;"><b>From:</b>    <a rel="nofollow" title="EFranconi@archenergy.com" ymailto="mailto:EFranconi@archenergy.com" target="_blank" href="mailto:EFranconi@archenergy.com">Ellen    Franconi</a> </div>   <div style="font-family: arial; font-style: normal; font-variant: normal; font-weight: normal; font-size: 10pt; line-height: normal; font-size-adjust: none; font-stretch: normal;"><b>To:</b> <a rel="nofollow" title="bldg-sim@lists.onebuilding.org" ymailto="mailto:bldg-sim@lists.onebuilding.org" target="_blank" href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>    ; <a rel="nofollow" title="jeffhaberl@tees.tamus.edu" ymailto="mailto:jeffhaberl@tees.tamus.edu" target="_blank"
 href="mailto:jeffhaberl@tees.tamus.edu">Jeff Haberl</a> ; <a rel="nofollow" title="nigusse_ba@yahoo.com" ymailto="mailto:nigusse_ba@yahoo.com" target="_blank" href="mailto:nigusse_ba@yahoo.com">Bereket    Nigusse</a> </div>   <div style="font-family: arial; font-style: normal; font-variant: normal; font-weight: normal; font-size: 10pt; line-height: normal; font-size-adjust: none; font-stretch: normal;"><b>Sent:</b> Monday, February 02, 2009 7:50    PM</div>   <div style="font-family: arial; font-style: normal; font-variant: normal; font-weight: normal; font-size: 10pt; line-height: normal; font-size-adjust: none; font-stretch: normal;"><b>Subject:</b> Re: [Bldg-sim] Residential    System Sizing</div>   <div><br></div>   <div>Another reason that the results are different is that the space    temperature may be different in the "loads" part of the DOE-2 program than in    the&nbsp;"systems" part of the program. In "loads",&nbsp;the space    temperatures
 are&nbsp;set equal to the space design temperate. In "systems",    the space temperature&nbsp;is based on the zone setpoint schedule and whatever    temperature is actually achieved in the space. Thus, if you have a set up or a    setback&nbsp;from the design space temperature, it will be different. </div>   <div>Ellen</div>   <div>&nbsp;</div>   <div>   <div>Ellen Franconi, Ph.D., LEED AP</div>   <div>Energy Analysis Group Manager</div>   <div>Architectural Energy Corporation</div>   <div>2540 Frontier Avenue</div>   <div>Boulder, CO 80301</div>   <div>tel. 303-444-4149</div>   <div>fax 303-444-4303</div>   <div><a rel="nofollow" ymailto="mailto:efranconi@archenergy.com" target="_blank" href="mailto:efranconi@archenergy.com">efranconi@archenergy.com</a></div>   <div><a rel="nofollow" target="_blank" href="http://www.archenergy.com/">http://www.archenergy.com/</a></div><br><br>&gt;&gt;&gt;    Jeff Haberl &lt;jeffhaberl@tees.tamus.edu&gt; 2/2/2009 8:40
 PM    &gt;&gt;&gt;<br>Bereket:<br><br>I would not expect the values in SV-A and LS-B    to agree for most buildings. There are many reasons for this.<br><br>First,    peak loads from LOADS do not include ventilation loads as would be the case in    SYSTEMS, only infiltration. <br>Second, you may be looking at different days    on the weather file between LOADS and SYSTEMS, so this would <br>need to be    checked. <br><br>In addition, DOE-2 sizes for the absolute peak, whereas other    methods, such as Manual J, have some undersizing<br>built into the procedures,    hence you'll almost always get a much larger system size in DOE-2.    <br><br>Both the SV-A and LS-B lists you show seem reasonable, with the    exception of the MN #s, which I suspect that you<br>may have a fair bit of 24    hour infiltration in your input file...(i.e., low night time temps in MN?)    <br>However, without looking at the file I can only guess. <br><br>There are    100s of
 reasons for the funny little differences you show.&nbsp; You're    probabloy better off running a Manual J <br>calculation on the house if it is    residential. DOE-2 is known for doing a very bad job of sizing for    residential.<br><br>Jeff<br><br>8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) :=') 8=) 8=)    8=?<br>Jeff S. Haberl, Ph.D.,    P.E.............................jhaberl@esl.tamu.edu<br>Professor......................................................Office    Ph: 979-845-6507<br>Department of Architecture.......................Lab Ph:    979-845-6065 <br>Energy Systems Laboratory.......................FAX:    979-862-2457 <br>Texas A&amp;M    University..............................77843-3581<br>College Station, Texas,    USA.......................URL: <a target="_blank" href="http://www-esl.tamu.edu">www-esl.tamu.edu</a><br>8=/ 8=) :=) 8=) ;=) 8=)    8=() 8=) 8=? 8=) 8=) 8=) <br><br>________________________________<br><br>From:   
 bldg-sim-bounces@lists.onebuilding.org on behalf of Bereket Nigusse<br>Sent:    Mon 2/2/2009 5:59 PM<br>To: bldg-sim@lists.onebuilding.org<br>Subject:    [Bldg-sim] Residential System Sizing<br><br><br><br>Hello All,<br><br>I have a    problem with DOE2.1E cooling system sizing.&nbsp; The cooling capacity    reported by DOE2.1e in SV-A and LS-B reports are quite different and shows    different sensitivity trends depending locations.&nbsp; <br><br>Question    1<br>For the case with out door air flow ratio input set to zero DOE2.1E    calculated cooling capacity and the peak coolig load are shown    below.&nbsp;&nbsp; I assume that the out door air contribution to the system    load is zero for zero out door air fraction and with this assumption the    system cooling capacity will be different from the peak cooling load only due    to difference in ARI and the peak cooling load hour weather conditions.&nbsp;    What else could cause the cooling capacity
 to be different from the peak load    for zero out door air flow rate case?&nbsp; I have looked into to DOE2.1E    manual but wasn't able connect the steps from the peak cooling load to the    system capacity?&nbsp; <br><br>Question 2<br>Does the change from the peak    cooling load to the&nbsp; system cooling capacity seem a reasonable for the    different loacations given below? <br>The building is 2100 sqft conditioned    floor area, two story, single family house.&nbsp; Each floor is modeled as a    single zone.<br><br><br>&nbsp; Report AV-A Report LS-B&nbsp; &nbsp;    <br>Locations Supply Flow, CFM Cooling Capacity, kBtu/hr Peak Cooling Load,    kBtu/hr Outdoor DB Temp at Peak Load, oF Outdoor WB Temp at Peak Load,    oF<br>Baltimore, MD 850.0 25.7 22.1 93 73<br>Houston, TX 813.0 27.0 20.2 93    78<br>Chicago, IL 1054.0 29.3 20.3 89 72<br>Minneapolis, MN 1226.0 33.5 20.3    89 79<br>Duluth, MN 1258.0 34.8 18.1 87 72<br>Phoenix, AZ 1281.0 37.4 31.6
 114    71<br><br><br>Thank you in advance for the    help,<br><br><br>Bereket<br><br>_______________________________________________<br>Bldg-sim    mailing list<br><a rel="nofollow" target="_blank" href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</a>-sim-onebuilding.org<br>To    unsubscribe from this mailing list send&nbsp; a blank message to    BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<br></div>   <p>   </p><hr>    <p></p>_______________________________________________<br>Bldg-sim mailing    list<br><a target="_blank" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>To    unsubscribe from this mailing list send&nbsp; a blank message to    BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<br></blockquote></div></div></div><br>