<DIV><FONT face=Arial>Ellen, </FONT></DIV>
<DIV><FONT face=Arial></FONT>&nbsp;</DIV>
<DIV><FONT face=Arial>Not exactly. What you wrote is definitely true&nbsp;during 
the SYSTEMS simulation and peak loads reported in SS-F (?), but Bereket was 
referring to the SV-A, which is the systems sizing report. Assuming that he's 
doing "auto-sizing",&nbsp; the DOE-2 sizing routine will take the peak loads 
from LOADS and compute the design cooling capacity at the 
COOLING-DESIGN-TEMPERATURE. (I may have the keyword wrong, since I don't have a 
DOE-2 manual handy).&nbsp; Thus, the termperature discrepancy between the single 
LOADS temperature and the COOLING-DESIGN-TEMPERATURE&nbsp;does exist, as you've 
mentioned, but transient loads due to tempeature set-up or set-back 
or&nbsp;interzone heat flows&nbsp;are not reflected. That's why an autosized 
SYSTEM will often still result in a few undercooled or underheated 
hours.</FONT></DIV>
<DIV><FONT face=Arial></FONT>&nbsp;</DIV>
<DIV><FONT face=Arial>My suggestion to Bereket in making sense of the numbers is 
to&nbsp;compare the TEMPERATURE under SPACE-CONDITIONS for the LOADS reference 
temperature,&nbsp;to the COOLING-DESIGN-TEMPERATURE (I may have this keyword 
wrong) is ZONE-CONDITIONS in SYSTEMS. What kind of HVAC are you modeling?&nbsp; 
It sounds like a residential system (RESYS), but that system doesn't have any 
OUTSIDE-AIR, does it ? </FONT></DIV>
<DIV><FONT face=Arial></FONT>&nbsp;</DIV>
<DIV><FONT face=Arial>Joe Huang</FONT></DIV>
<DIV><FONT face=Arial>White Box Technologies, Inc.</FONT></DIV>
<DIV><FONT face=Arial></FONT>&nbsp;</DIV>
<BLOCKQUOTE 
style="PADDING-RIGHT: 0px; PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: #000000 2px solid; MARGIN-RIGHT: 0px">
  <DIV style="FONT: 10pt arial">----- Original Message ----- </DIV>
  <DIV 
  style="BACKGROUND: #e4e4e4; FONT: 10pt arial; font-color: black"><B>From:</B> 
  <A title=EFranconi@archenergy.com href="mailto:EFranconi@archenergy.com">Ellen 
  Franconi</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>To:</B> <A 
  title=bldg-sim@lists.onebuilding.org 
  href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</A> 
  ; <A title=jeffhaberl@tees.tamus.edu 
  href="mailto:jeffhaberl@tees.tamus.edu">Jeff Haberl</A> ; <A 
  title=nigusse_ba@yahoo.com href="mailto:nigusse_ba@yahoo.com">Bereket 
  Nigusse</A> </DIV>
  <DIV style="FONT: 10pt arial"><B>Sent:</B> Monday, February 02, 2009 7:50 
  PM</DIV>
  <DIV style="FONT: 10pt arial"><B>Subject:</B> Re: [Bldg-sim] Residential 
  System Sizing</DIV>
  <DIV><BR></DIV>
  <DIV>Another reason that the results are different is that the space 
  temperature may be different in the "loads" part of the DOE-2 program than in 
  the&nbsp;"systems" part of the program. In "loads",&nbsp;the space 
  temperatures are&nbsp;set equal to the space design temperate. In "systems", 
  the space temperature&nbsp;is based on the zone setpoint schedule and whatever 
  temperature is actually achieved in the space. Thus, if you have a set up or a 
  setback&nbsp;from the design space temperature, it will be different. </DIV>
  <DIV>Ellen</DIV>
  <DIV>&nbsp;</DIV>
  <DIV>
  <DIV>Ellen Franconi, Ph.D., LEED AP</DIV>
  <DIV>Energy Analysis Group Manager</DIV>
  <DIV>Architectural Energy Corporation</DIV>
  <DIV>2540 Frontier Avenue</DIV>
  <DIV>Boulder, CO 80301</DIV>
  <DIV>tel. 303-444-4149</DIV>
  <DIV>fax 303-444-4303</DIV>
  <DIV><A 
  href="mailto:efranconi@archenergy.com">efranconi@archenergy.com</A></DIV>
  <DIV><A 
  href="http://www.archenergy.com/">http://www.archenergy.com/</A></DIV><BR><BR>&gt;&gt;&gt; 
  Jeff Haberl &lt;jeffhaberl@tees.tamus.edu&gt; 2/2/2009 8:40 PM 
  &gt;&gt;&gt;<BR>Bereket:<BR><BR>I would not expect the values in SV-A and LS-B 
  to agree for most buildings. There are many reasons for this.<BR><BR>First, 
  peak loads from LOADS do not include ventilation loads as would be the case in 
  SYSTEMS, only infiltration. <BR>Second, you may be looking at different days 
  on the weather file between LOADS and SYSTEMS, so this would <BR>need to be 
  checked. <BR><BR>In addition, DOE-2 sizes for the absolute peak, whereas other 
  methods, such as Manual J, have some undersizing<BR>built into the procedures, 
  hence you'll almost always get a much larger system size in DOE-2. 
  <BR><BR>Both the SV-A and LS-B lists you show seem reasonable, with the 
  exception of the MN #s, which I suspect that you<BR>may have a fair bit of 24 
  hour infiltration in your input file...(i.e., low night time temps in MN?) 
  <BR>However, without looking at the file I can only guess. <BR><BR>There are 
  100s of reasons for the funny little differences you show.&nbsp; You're 
  probabloy better off running a Manual J <BR>calculation on the house if it is 
  residential. DOE-2 is known for doing a very bad job of sizing for 
  residential.<BR><BR>Jeff<BR><BR>8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) :=') 8=) 8=) 
  8=?<BR>Jeff S. Haberl, Ph.D., 
  P.E.............................jhaberl@esl.tamu.edu<BR>Professor......................................................Office 
  Ph: 979-845-6507<BR>Department of Architecture.......................Lab Ph: 
  979-845-6065 <BR>Energy Systems Laboratory.......................FAX: 
  979-862-2457 <BR>Texas A&amp;M 
  University..............................77843-3581<BR>College Station, Texas, 
  USA.......................URL: www-esl.tamu.edu<BR>8=/ 8=) :=) 8=) ;=) 8=) 
  8=() 8=) 8=? 8=) 8=) 8=) <BR><BR>________________________________<BR><BR>From: 
  bldg-sim-bounces@lists.onebuilding.org on behalf of Bereket Nigusse<BR>Sent: 
  Mon 2/2/2009 5:59 PM<BR>To: bldg-sim@lists.onebuilding.org<BR>Subject: 
  [Bldg-sim] Residential System Sizing<BR><BR><BR><BR>Hello All,<BR><BR>I have a 
  problem with DOE2.1E cooling system sizing.&nbsp; The cooling capacity 
  reported by DOE2.1e in SV-A and LS-B reports are quite different and shows 
  different sensitivity trends depending locations.&nbsp; <BR><BR>Question 
  1<BR>For the case with out door air flow ratio input set to zero DOE2.1E 
  calculated cooling capacity and the peak coolig load are shown 
  below.&nbsp;&nbsp; I assume that the out door air contribution to the system 
  load is zero for zero out door air fraction and with this assumption the 
  system cooling capacity will be different from the peak cooling load only due 
  to difference in ARI and the peak cooling load hour weather conditions.&nbsp; 
  What else could cause the cooling capacity to be different from the peak load 
  for zero out door air flow rate case?&nbsp; I have looked into to DOE2.1E 
  manual but wasn't able connect the steps from the peak cooling load to the 
  system capacity?&nbsp; <BR><BR>Question 2<BR>Does the change from the peak 
  cooling load to the&nbsp; system cooling capacity seem a reasonable for the 
  different loacations given below? <BR>The building is 2100 sqft conditioned 
  floor area, two story, single family house.&nbsp; Each floor is modeled as a 
  single zone.<BR><BR><BR>&nbsp; Report AV-A Report LS-B&nbsp; &nbsp; 
  <BR>Locations Supply Flow, CFM Cooling Capacity, kBtu/hr Peak Cooling Load, 
  kBtu/hr Outdoor DB Temp at Peak Load, oF Outdoor WB Temp at Peak Load, 
  oF<BR>Baltimore, MD 850.0 25.7 22.1 93 73<BR>Houston, TX 813.0 27.0 20.2 93 
  78<BR>Chicago, IL 1054.0 29.3 20.3 89 72<BR>Minneapolis, MN 1226.0 33.5 20.3 
  89 79<BR>Duluth, MN 1258.0 34.8 18.1 87 72<BR>Phoenix, AZ 1281.0 37.4 31.6 114 
  71<BR><BR><BR>Thank you in advance for the 
  help,<BR><BR><BR>Bereket<BR><BR>_______________________________________________<BR>Bldg-sim 
  mailing list<BR><A 
  href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</A>-sim-onebuilding.org<BR>To 
  unsubscribe from this mailing list send&nbsp; a blank message to 
  BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR></DIV>