Dear All:<br><br>I know a related topic has been discussed here on the list serve before. However, after reviewing all the correspondence on this topic, and the 90.1 standard itself, I still have a few uncertainties I hope at least one of you are able to clarify. If not I sincerely value as many of your thoughts as you can offer so I can understand what the common interpretation is. This question pertains to the 2004 edition. I don&#39;t even understand if using addendum A can solve this problem for me, so please also inform me if it does?<br>
<br>In table G3.1.5 it is stated:<br><br>&quot;Vertical fenestration areas for new buildings and additions shall equal that in the proposed design or 40% of gross abovegrade wall area, whichever is smaller, and shall be distributed uniformly in horizontal bands across the four orientations.&quot;<br>
<br>Addendum A states:<br><br>&quot;Vertical fenestration areas for new buildings and additions shall equal that in the proposed design or 40% of gross above-grade wall area, whichever is smaller, and shall be distributed uniformly in horizontal bands across the four orientations and shall be distributed on each face of the building in the same proportion as on the Proposed Design.&quot;<br>
<br>Let us assume there is a building with mostly above grade parking garage and a few offices that are conditioned. The parking garage has a wall to the outside, but no windows and is not conditioned. If I am following the prescriptions above, what do I do of the following two options, or is there a third option, when following Appendix G?<br>
<br>1 - I take the area of windows in the proposed building and apply them equally (or not for Addendum A) on all facades in the baseline building, for all floors in horizontal bands. This way even the parking garage gets windows in the baseline building, and the offices in the baseline building has very little window area compared to the proposed (because so much of the fenestration<br>
&nbsp;are is on the parking garage in the baseline), so little that this model significantly penalizes the project for not putting windows in the parking garage! I here apply the windows to whatever surface I would bump into if I approached the building by foot (and I can be as tall as the building itself, so it&#39;s not just the lower floors&#39; walls).<br>
<br>2 - I take the area of the windows and only apply them to walls that separate conditioned space and the outside. This way the parking garage in the baseline building does not receive any windows. In this instance I can get savings from placing the glazing strategically within the offices. The sum of the area in all offices are the same for the baseline and proposed (since there are only two types of spaces: parking and office).<br>
<br>I have seen in previous correspondence that only below-grade walls to conditioned spaces are included (I did not understand why only conditioned but at least I know it&#39;s common practice), but is it the case that only walls between the conditioned spaces and the outside conditions get windows for above-grade walls too? In the above quotes from the standard and the addendum, the problem arises with the use of &nbsp;&quot;orientations&quot; and &quot;face&quot;. The statement that fenestration is supposed to be distributed on the &quot;orientation&quot; or &quot;face&quot; of the building does not explain much, since neither of these terms seems to be defined in 3.2 or elsewhere in the standard. If the texts had used the term &quot;exterior building envelope&quot;, I would have been quite confident in using option 2 above. Since the quotes does not mention that only parts of the baseline building will receive glazing, I am inclined to follow option 1 above, although it seems to go against the intention of standard 90.1and Appendix G.<br>
<br>The terms &quot;orientations&quot; and &quot;face&quot; is substituted by the term &quot;exterior wall&quot; in the User&#39;s Manual on page G-15. This is yet another undefined term. Initially I was inclined to think that exterior wall is the same as &quot;Nonresidential Exterior&quot; and/or &quot;Residential Exterior&quot; wall on page G-35 of the User&#39;s Manual which I think might be the same as exterior building envelope, but this link is not established anywhere. Moreover, on this very same page, the term &quot;exterior wall&quot; is used to describe an &quot;Unconditioned Exterior&quot; wall, so clearly the term &quot;exterior wall&quot; is not unique to only walls separating conditioned spaces from outdoor conditions. In fact, this use of exterior wall leads me to again consider option 1, above, and apply windows in the baseline building to the parking garage in the hypothetical building above.<br>
<br>Closely linked to the discourse above, I do not see why windows in unconditioned spaces in the proposed building must be included in either option 1 or 2 above. Let&#39;s examine another hypothetical building. This building is half storage, half office. The offices are conditioned and have windows. The storage space is unconditioned, and well ventilated so that the walls between the offices and the storage rooms are treated as exterior building envelope. However, there are many windows in the storage spaces too. Disregarding the discourse above of allocating the fenestration area in the baseline building, I am seeing difficulties in what the fenestration area is in the first place. If I consult section 3.2 of 90.1 I find:<br>
<br>&quot;fenestration area: total area of the fenestration measured using the rough opening and including the glazing, sash, and frame. For doors where the glazed vision area is less than 50% of the door area, the fenestration area is the glazed vision area. For all other doors, the fenestration area is the door area. (See door area.)&quot;<br>
<br>Where fenestration is defined as:<br><br>&quot;fenestration: all areas (including the frames) in the building envelope that let in light, including windows, plastic panels, clerestories, skylights, glass doors that are more than one-half glass, and glass block walls. (See building envelope and door.) (a) skylight: a fenestration surface having a slope of less than 60 degrees from the horizontal plane. Other fenestration, even if mounted on the roof of a building, is considered vertical fenestration. 8 ANSI/ASHRAE/IESNA STANDARD 90.1-2004 (b) vertical fenestration: all fenestration other than skylights. Trombe wall assemblies, where glazing is installed within 12 in. of a mass wall, are considered walls, not fenestration.&quot;<br>
<br>Is the fenestration area all the fenestration in the building, both for the conditioned and for the unconditioned spaces? Or is it only the fenestration for the conditioned spaces? When I look at option 2 above, if I take all the fenestration in the proposed building and apply it to only to the conditioned spaces for the baseline, we can get huge energy savings just from the type of building, not from the way this type of building was designed. We can even get more windows than there are walls in the conditioned offices which in my instance (Trace 700) can cause problems running the simulation. Even if the software ran with more windows than walls, the output could potentially be of little value for analysis. It seems like I am supposed to take the entire fenestration area, both in conditioned and unconditioned spaces, of a building and this is another reason I am inclined towards option 1 above. However, option 1 still remains very unfair when I consider a building with more above grade car park than offices, as explained above.<br>
<br>Thank you for reading through this. Please post your answers or opinions, if any. Also remember to reference any section of the 90.1 Standard, its addenda or its User&#39;s Manual if you have any clarifications regarding my uncertainties pertaining to the various definitions discussed in this email.<br>
<br>Faithfully yours,<br><br><br><b>Ulrik Welle-Strand Horn </b><br>Sustainability Engineer<br><div><br><b>Silpa Inc.</b><br><font size="1"><b>s</b> i m p l e &nbsp;. &nbsp;<b>s</b> c i e n t i f i c&nbsp; .&nbsp; <b>s</b> u s t a i n a b l e<br>