Dear Mr. James V. Dirkes II:<br><br>Could you please clarify what you mean by "The definition depends only indirectly on "U" values and wall areas?" I am not designing the mechanical system, I am only reviewing it. Therefore I can't chose which spaces to condition. The building has many rooms that don't have any cooling coils, nor do they have any cold air entering the rooms. These must surely be indirectly conditioned spaces?<br>
<br>For these indirectly conditioned spaces, I am wondering if I need to perform the U-factor and surface area calculations and comparisons? The spaces in question surely are not ventilated with 3 ACH from conditioned spaces. As there are quite a few of these spaces, I just wanted to know if it is really common practice to perform these calculations?<br>
<br>Thank you for a quick reply.<br><br>Sincerely yours,<br><br><br><b>Ulrik Welle-Strand Horn </b><br>Sustainability Engineer<br><div><br><b>Silpa Inc.</b><br><font size="1"><b>s</b> i m p l e  .  <b>s</b> c i e n t i f i c  .  <b>s</b> u s t a i n a b l e<br>
</font></div>
<font size="1"><div>AMERICAS | MIDDLE EAST | ASIA<br>




<a href="http://www.silpainc.com/" target="_blank">www.silpainc.com</a><br></div><font size="2"><br></font></font><font size="2">India: +91.90080.96083</font><br><br><div class="gmail_quote">On Mon, Jan 12, 2009 at 9:06 PM, James V. Dirkes II  P.E. <span dir="ltr"><<a href="mailto:jvd2pe@tds.net">jvd2pe@tds.net</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">



<div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Dear Ulrik,</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Regarding "conditioned space":</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">"Conditioned space" seems pretty straightforward to 
me.  If, for example, the cooling system for a 10,000 sq.ft. space 
has 10 tons cooling capacity, then the capacity is 12Btu/hr/ft2 (10tons x 
12,000 Btu/hr/ton / 10,000 ft2)  This exceeds the ASHRAE threshold of 5 
Btu/h/ft2, so it's "conditioned".  If the cooling system was only 4 tons, 
it would not be "conditioned" (only 4.8 Btu/hr/ft2).</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">The definition depends only indirectly on "U" values and 
wall areas.  For any given construction, you choose to provide an air 
conditioning system or not.  You can also choose to cool a lot or a 
little.  Each choice affects whether you end up with an air conditioning 
system greater than 5 Btu/hr/ft2 or not.</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Heating works the same way, except the threshold varies by 
climate zone.</font></span></div>
<div> </div>
<div>
<p style="text-align: center;" align="center"><b><font size="4">The Building Performance 
Team<br></font></b><b>James V. Dirkes II, 
P.E., LEED AP<br></b>1631 Acacia Drive NW<br>Grand Rapids, MI 49504<br>616 
450 8653</p>
<p> </p></div>
<div> </div><br>
<div dir="ltr" align="left" lang="en-us">
<hr>
<font size="2" face="Tahoma"><b>From:</b> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a> 
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Ulrik 
Welle-Strand Horn<br><b>Sent:</b> Saturday, January 10, 2009 9:47 
AM<br><b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br><b>Subject:</b> [Bldg-sim] 
ASHRAE 90.1 Definition of "Conditioned" - The PRM Reportfor LEED EAc1 and 
Appendix G Energy Model<br></font><br></div><div><div></div><div class="Wj3C7c">
<div></div>Dear All,<br><br>I would like to know if and how you consider 
ASHRAE's definition of conditioned space on page 13 of the 2004 
version.<br><br>Specifically, I am interested to know if you abide by this 
definition when listing the conditioned vs unconditioned area? The definition 
seems really specific to me, explaining how the system serving a conditioned 
area must have a certain capacity per square foot of building area served. It 
even goes on to explain how for some spaces one must consider the sum of the 
products of various U-factors and wall areas. To me, it does not seem like one 
can eyeball all these comparisons and definitions and therefore one has to go 
ahead and measure the capacities of systems and compare them with the area they 
serve, as well as do computations for rooms that might be indirectly 
conditioned.<br><br>The PRM report for LEED requires you to list unconditioned 
and conditioned areas separately. Do any of you actually go through the 
calculations to find out if each single space in your project complies with the 
definitions put forward in the 90.1 document? It seems to me like more effort 
than what it's worth. I don't recall ever using this classification of 
unconditioned vs conditioned anywhere else in the LEED certification process. 
Especially, I don't recall ever having to use this definition to do the PRM 
model itself under Appendix G. Has anyone come across another place than the PRM 
report where the efforts of classifying their spaces accoring to the 90.1 
definition above has been rewarded? Please also let me know if any one of you 
have ever experienced trouble getting your project LEED certified because of 
lack of compliance with this definition.<br><br>Lastly, the definition 
explicitly states that "Crawlspaces, attics, and parking garages with natural or 
mechanical ventilation are not considered enclosed spaces." Do most of you 
usually leave out car parks from the PRM area report? I am working on a building 
where about 60% of the floor area is parking space, meaning the sum total in my 
Space Summary will be much less than stated otherwise in the documents submitted 
to USGBC. I know that they are looking for all the total areas to be pretty 
consistent, and that some people experience problems when thes total areas don't 
match up. Has anyone ever dealt with this issue? If so, how did you deal with 
it?<br><br>I appreciate any response you may have to any or all of my 
questions.<br><br>Sincerely yours,<br><br><br><b>Ulrik Welle-Strand Horn 
</b><br>Sustainability Engineer<br>
<div><br><b>Silpa Inc.</b><br><font size="1"><b>s</b> i m p l e  . 
 <b>s</b> c i e n t i f i c  .  <b>s</b> u s t a i n a b l 
e<br></font></div><font size="1">
<div>AMERICAS | MIDDLE EAST | ASIA<br><a href="http://www.silpainc.com/" target="_blank">www.silpainc.com</a><br></div><font size="2"><br></font></font><font size="2">India: +91.90080.96083</font><br></div></div></div>
</blockquote></div><br>