<DIV>A90.1-2007 removed the reference to SHGC_All and refers to the Chapter 5 tables. You should be able to use the SHGC_north in the baseline if you follow 2007.</DIV>
<DIV>Regards,</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>
<DIV><FONT face=Technic>Bill Talbert, PE, <SPAN style="FONT-SIZE: 12pt; LAYOUT-GRID-MODE: line; FONT-FAMILY: Arial; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA"><SPAN style="FONT-SIZE: 12pt; LAYOUT-GRID-MODE: line; FONT-FAMILY: Technic; mso-bidi-font-size: 10.0pt; mso-fareast-font-family: 'Times New Roman'; mso-ansi-language: EN-US; mso-fareast-language: EN-US; mso-bidi-language: AR-SA; mso-bidi-font-family: Arial"><FONT size=2>LEED® AP</FONT></SPAN></SPAN><BR>Mechanical Systems</FONT></DIV>
<DIV><FONT face=Technic>Phone: (608) 441-6677<BR>E-mail: btalbert@aeieng.com<BR><BR>Affiliated Engineers Inc.<BR>5802 Research Park Blvd.<BR>Madison, WI. 53719<BR>Tel. (608) 238-2616<BR>Fax. (608) 238-2614</FONT></DIV><BR><BR>>>> "Ulrik Welle-Strand Horn" <ulrik.horn@silpainc.com> 12/1/2008 8:42 AM >>><BR>Paul, <BR><BR>That's a VERY valid point. Thanks for pointing it out.<BR><BR><BR><B>Ulrik Welle-Strand Horn </B><BR>Sustainability Engineer<BR></DIV>
<DIV><BR><B>Silpa Inc.</B><BR><FONT size=1><B>s</B> i m p l e  .  <B>s</B> c i e n t i f i c  .  <B>s</B> u s t a i n a b l e<BR></FONT></DIV><FONT size=1>
<DIV>AMERICAS | MIDDLE EAST | ASIA<BR><A href="http://www.silpainc.com/" target=_blank>www.silpainc.com</A><BR></DIV><FONT size=2><BR></FONT></FONT><FONT size=2>India: +91.90080.96083</FONT><BR><BR>
<DIV class=gmail_quote>On Mon, Dec 1, 2008 at 7:51 PM, Paul Riemer <SPAN dir=ltr><<A href="mailto:Paul.Riemer@dunhameng.com">Paul.Riemer@dunhameng.com</A>></SPAN> wrote:<BR>
<BLOCKQUOTE class=gmail_quote style="PADDING-LEFT: 1ex; MARGIN: 0pt 0pt 0pt 0.8ex; BORDER-LEFT: rgb(204,204,204) 1px solid">
<DIV lang=EN-US vlink="purple" link="blue">
<DIV>
<P><SPAN style="FONT-SIZE: 11pt; COLOR: rgb(31,73,125)">I read Table G3.1 section 5 sub item (c) under the baseline building performance column to require use of the "SHGC_all" for all vertical glazing.  Have others read that and reached a different conclusion?  Did I miss an addenda? or a CIR?</SPAN></P>
<P><SPAN style="FONT-SIZE: 11pt; COLOR: rgb(31,73,125)"></SPAN> </P>
<DIV>
<DIV style="BORDER-RIGHT: medium none; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; PADDING-LEFT: 0in; PADDING-BOTTOM: 0in; BORDER-LEFT: medium none; PADDING-TOP: 3pt; BORDER-BOTTOM: medium none">
<P style="MARGIN-LEFT: 0.5in"><B><SPAN style="FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-SIZE: 10pt"> <A href="mailto:bldg-sim-bounces@lists.onebuilding.org" target=_blank>bldg-sim-bounces@lists.onebuilding.org</A> [mailto:<A href="mailto:bldg-sim-bounces@lists.onebuilding.org" target=_blank>bldg-sim-bounces@lists.onebuilding.org</A>] <B>On Behalf Of </B>James V. Dirkes II P.E.<BR><B>Sent:</B> Monday, December 01, 2008 8:09 AM<BR><B>To:</B> 'Ulrik Welle-Strand Horn'; <A href="mailto:bldg-sim@lists.onebuilding.org" target=_blank>bldg-sim@lists.onebuilding.org</A><BR><B>Subject:</B> Re: [Bldg-sim] Appendix G - Base Case Orientations and Glazing</SPAN></P></DIV></DIV>
<DIV>
<DIV></DIV>
<DIV class=Wj3C7c>
<P style="MARGIN-LEFT: 0.5in"> </P>
<P style="MARGIN-LEFT: 0.5in"><SPAN style="FONT-SIZE: 10pt; COLOR: blue">Dear Ulrik,</SPAN></P>
<P style="MARGIN-LEFT: 0.5in"> </P>
<P style="MARGIN-LEFT: 0.5in"><SPAN style="FONT-SIZE: 10pt; COLOR: blue">Since the intent of the Standard is to assign the better glazing performance to non-North walls, I always rotate the glazing characteristics with the building. (e.g., I assign the "North" glazing characteristics to the elevation that, after rotating, faces North)</SPAN></P>
<DIV>
<P style="MARGIN-LEFT: 0.5in"> </P></DIV>
<DIV>
<P style="MARGIN-LEFT: 0.5in; TEXT-ALIGN: center" align=center><B><SPAN style="FONT-SIZE: 13.5pt">The Building Performance Team<BR></SPAN>James V. Dirkes II, P.E., LEED AP<BR></B>1631 Acacia Drive NW<BR>Grand Rapids, MI 49504<BR>616 450 8653</P>
<P style="MARGIN-LEFT: 0.5in"> </P></DIV>
<DIV>
<P style="MARGIN-LEFT: 0.5in"> </P></DIV>
<P style="MARGIN-LEFT: 0.5in"> </P>
<DIV style="MARGIN-LEFT: 0.5in; TEXT-ALIGN: center" align=center>
<HR align=center width="100%" SIZE=2>
</DIV>
<P style="MARGIN-BOTTOM: 12pt; MARGIN-LEFT: 0.5in; MARGIN-RIGHT: 0in"><B><SPAN style="FONT-SIZE: 10pt">From:</SPAN></B><SPAN style="FONT-SIZE: 10pt"> <A href="mailto:bldg-sim-bounces@lists.onebuilding.org" target=_blank>bldg-sim-bounces@lists.onebuilding.org</A> [mailto:<A href="mailto:bldg-sim-bounces@lists.onebuilding.org" target=_blank>bldg-sim-bounces@lists.onebuilding.org</A>] <B>On Behalf Of </B>Ulrik Welle-Strand Horn<BR><B>Sent:</B> Monday, December 01, 2008 7:30 AM<BR><B>To:</B> <A href="mailto:bldg-sim@lists.onebuilding.org" target=_blank>bldg-sim@lists.onebuilding.org</A><BR><B>Subject:</B> [Bldg-sim] Appendix G - Base Case Orientations and Glazing</SPAN></P>
<P style="MARGIN-LEFT: 0.5in">Dear all,<BR><BR>When you are rotating the building through 4 different orientations, do you change the glazing so that the glazing with the highest SHGC is always faces north, or do you put the glazing with high SHGC on the original north facade, and then rotate the building so that the high SHGC glazing faces the east, south and west orientations in subsequent simulations?<BR><BR>Yours faithfully,<BR><BR><BR><B>Ulrik Welle-Strand Horn </B><BR>Sustainability Engineer</P>
<DIV>
<P style="MARGIN-LEFT: 0.5in"><BR><B>Silpa Inc.</B><BR><B><SPAN style="FONT-SIZE: 7.5pt">s</SPAN></B><SPAN style="FONT-SIZE: 7.5pt"> i m p l e  .  <B>s</B> c i e n t i f i c  .  <B>s</B> u s t a i n a b l e</SPAN></P></DIV>
<DIV>
<P style="MARGIN-LEFT: 0.5in"><SPAN style="FONT-SIZE: 7.5pt">AMERICAS | MIDDLE EAST | ASIA<BR><A href="http://console.mxlogic.com/redir/?1psKUPuX9JdZZWXPPxI05ihWSOxrBYdTdTdA3Q29uABiV2Hsbvg57OFeDlxV1KhW4E4u00CTHFK6QkQTAmbI3APrypI5-Aq83iScDE4iZ9aCBQQg22OTMgA7Cy096y0Kq81Dquq81bquq80N6nMDIVlxgQgr10Qg18_hik29KvxYY1NJ4SyrjvvuKYYYrV6r6" target=_blank>www.silpainc.com</A></SPAN></P></DIV>
<P style="MARGIN-LEFT: 0.5in"><SPAN style="FONT-SIZE: 10pt"><BR>India: +91.90080.96083</SPAN></P></DIV></DIV></DIV></DIV></BLOCKQUOTE></DIV><BR></BODY></HTML>