<html xmlns:v="urn:schemas-microsoft-com:vml" xmlns:o="urn:schemas-microsoft-com:office:office" xmlns:w="urn:schemas-microsoft-com:office:word" xmlns:x="urn:schemas-microsoft-com:office:excel" xmlns:p="urn:schemas-microsoft-com:office:powerpoint" xmlns:a="urn:schemas-microsoft-com:office:access" xmlns:dt="uuid:C2F41010-65B3-11d1-A29F-00AA00C14882" xmlns:s="uuid:BDC6E3F0-6DA3-11d1-A2A3-00AA00C14882" xmlns:rs="urn:schemas-microsoft-com:rowset" xmlns:z="#RowsetSchema" xmlns:b="urn:schemas-microsoft-com:office:publisher" xmlns:ss="urn:schemas-microsoft-com:office:spreadsheet" xmlns:c="urn:schemas-microsoft-com:office:component:spreadsheet" xmlns:odc="urn:schemas-microsoft-com:office:odc" xmlns:oa="urn:schemas-microsoft-com:office:activation" xmlns:html="http://www.w3.org/TR/REC-html40" xmlns:q="http://schemas.xmlsoap.org/soap/envelope/" xmlns:D="DAV:" xmlns:x2="http://schemas.microsoft.com/office/excel/2003/xml" xmlns:ois="http://schemas.microsoft.com/sharepoint/soap/ois/" xmlns:dir="http://schemas.microsoft.com/sharepoint/soap/directory/" xmlns:ds="http://www.w3.org/2000/09/xmldsig#" xmlns:dsp="http://schemas.microsoft.com/sharepoint/dsp" xmlns:udc="http://schemas.microsoft.com/data/udc" xmlns:xsd="http://www.w3.org/2001/XMLSchema" xmlns:sub="http://schemas.microsoft.com/sharepoint/soap/2002/1/alerts/" xmlns:ec="http://www.w3.org/2001/04/xmlenc#" xmlns:sp="http://schemas.microsoft.com/sharepoint/" xmlns:sps="http://schemas.microsoft.com/sharepoint/soap/" xmlns:xsi="http://www.w3.org/2001/XMLSchema-instance" xmlns:udcxf="http://schemas.microsoft.com/data/udc/xmlfile" xmlns:wf="http://schemas.microsoft.com/sharepoint/soap/workflow/" xmlns:mver="http://schemas.openxmlformats.org/markup-compatibility/2006" xmlns:m="http://schemas.microsoft.com/office/2004/12/omml" xmlns:mrels="http://schemas.openxmlformats.org/package/2006/relationships" xmlns:ex12t="http://schemas.microsoft.com/exchange/services/2006/types" xmlns:ex12m="http://schemas.microsoft.com/exchange/services/2006/messages" xmlns:Z="urn:schemas-microsoft-com:" xmlns:st="&#1;" xmlns="http://www.w3.org/TR/REC-html40">

<head>
<meta http-equiv=Content-Type content="text/html; charset=us-ascii">
<meta name=Generator content="Microsoft Word 12 (filtered medium)">
<!--[if !mso]>
<style>
v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style>
<![endif]-->
<style>
<!--
 /* Font Definitions */
 @font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Cheltenham;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Calibri","sans-serif";
        color:#000099;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";
        color:#000099;}
span.EmailStyle17
        {mso-style-type:personal;
        font-family:"Calibri","sans-serif";
        color:#000099;}
span.EmailStyle18
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";
        color:#000099;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page Section1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.Section1
        {page:Section1;}
-->
</style>
<!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="2050" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]-->
</head>

<body lang=EN-US link=blue vlink=purple>

<div class=Section1>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'>Based on the
fresh air volume in your example (108 l/s), the design air flow would have to
be at least equal to that amount and probably higher unless the primary air
handler is 100% fresh air.&nbsp; The design air flow based on 20F delta T should
always be trumped by the ventilation requirement, if ventilation requirement is
larger than it.&nbsp; <o:p></o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'><o:p>&nbsp;</o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'>In any case, I
would maintain a minimum of 0.4 cfm/sf as a minimum level of ventilation simply
as &#8220;good practice&#8221; to avoid stagnation.&nbsp; This may mean using
additional reheat energy or utilizing a fan-powered terminal unit to provide
additional recirculation air.&nbsp; <o:p></o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'><o:p>&nbsp;</o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'>However, if air
stagnation is not a concern, and design air flow is less than 0.4cfm/sf then I
would say that the minimum setpoint is at the discretion of the designer and any
value less than or equal to 0.4 cfm/sf would not violate the intent of the requirement.&nbsp;
In the same way, if the cooling design load required 1.0 cfm/sf but the heating
load for the space could be handled with less than 0.25 cfm/sf then I don&#8217;t
believe App G would require you to increase your minimum VAV setpoint to 0.4 since
that would be a silly waste of energy.&nbsp; The most extreme example of this
logic is an interior zone, which has zero heating load and zero fresh air load&#8230;Since
there is no reheat required, the 0.4 cfm/sf requirement does not apply and
therefore the VAV damper could be allowed to fully close when the space is
satisfied.&nbsp; Due to Standard 62 this occurrence is highly improbable, but
it helps to illustrate the point.<o:p></o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'><o:p>&nbsp;</o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'>That&#8217;s my
two cents. <o:p></o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'><o:p>&nbsp;</o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'>Thanks,<o:p></o:p></span></p>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'><o:p>&nbsp;</o:p></span></p>

<div>

<p class=MsoNormal><span style='font-size:14.0pt;font-family:Cheltenham;
color:#A0002F'>&nbsp;</span><span style='font-size:18.0pt;font-family:Cheltenham;
color:#A0002F'>Dan Russell, EIT <o:p></o:p></span></p>

<p class=MsoNormal><span style='font-family:Cheltenham;color:#A0002F'><o:p>&nbsp;</o:p></span></p>

<p class=MsoNormal><span style='font-family:Cheltenham;color:#A0002F'><img
width=200 height=174 id="Picture_x0020_1"
src="cid:image001.jpg@01C944DC.7CE499A0"
alt="cid:image001.jpg@01C840A4.E711B250"></span><span style='font-size:11.0pt;
color:#1F497D'><o:p></o:p></span></p>

</div>

<p class=MsoNormal><span style='font-size:11.0pt;color:#1F497D'><o:p>&nbsp;</o:p></span></p>

<div>

<div style='border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in 0in 0in'>

<p class=MsoNormal><b><span style='font-family:"Tahoma","sans-serif";
color:windowtext'>From:</span></b><span style='font-family:"Tahoma","sans-serif";
color:windowtext'> bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] <b>On Behalf Of </b>Anis Ben
Ayed<br>
<b>Sent:</b> Wednesday, November 12, 2008 1:37 PM<br>
<b>To:</b> bldg-sim@lists.onebuilding.org<br>
<b>Subject:</b> [Bldg-sim] System 7 Min VAV setpoint<o:p></o:p></span></p>

</div>

</div>

<p class=MsoNormal><o:p>&nbsp;</o:p></p>

<p class=MsoNormal>Dear all, <o:p></o:p></p>

<p class=MsoNormal><o:p>&nbsp;</o:p></p>

<p class=MsoNormal>The VAV minimum set point for system 7 in Appendix G is
calculated based on (0.4 cfm/ft2). For some spaces this number is bigger than
the calculated design airflow based on 20F delta T. What should the VAV set
points be in this case? <o:p></o:p></p>

<p class=MsoNormal><o:p>&nbsp;</o:p></p>

<p class=MsoNormal>Example:<o:p></o:p></p>

<p class=MsoNormal>Room: &nbsp;&nbsp;&nbsp;<o:p></o:p></p>

<p class=MsoNormal>VAVmin = 131 l/s<o:p></o:p></p>

<p class=MsoNormal>Design Air Flow = 84 l/s <o:p></o:p></p>

<p class=MsoNormal>Fresh Air = 108 l/s<o:p></o:p></p>

<p class=MsoNormal><o:p>&nbsp;</o:p></p>

<p class=MsoNormal>Thank you for your input,<span style='color:black'><o:p></o:p></span></p>

<p class=MsoNormal><span style='font-size:12.0pt;font-family:"Arial","sans-serif";
color:black'><o:p>&nbsp;</o:p></span></p>

<p class=MsoNormal>Anis <o:p></o:p></p>