<DIV>Interesting. We recently decided not to "take credit" for substantial cascade/transfer air in a restaurant EAc1 app (i.e. the transfer air from dining to kitchen/hood&nbsp;was included in the baseline model).&nbsp;Our experience&nbsp;is that this mode&nbsp;has been extremely common&nbsp;for many, many years in commercial and school kitchens.&nbsp;(And it's very&nbsp;inexpensive, sometimes decreasing construction costs.)&nbsp;&nbsp;We felt&nbsp;taking credit for it&nbsp;did not meet the spirit of the PRM. Maybe if one needed to build all kinds of transfer ducting in a hotel, then it might seem like an improvement worthy of recognition...<BR></DIV>
<DIV>I could go on with a rant about the opacity of the&nbsp;credit review process, loopholes, "consensus" standards,&nbsp;etc. But actual work beckons.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Fred</DIV>
<DIV><BR>&gt;&gt;&gt; "Andrew Craig" &lt;AndrewC@InterfaceEng.Com&gt; 11/7/2008 3:42 PM &gt;&gt;&gt;<BR><FONT size=2>We have successfully taken credit for reduced OSA rates in a number of applications where a "cascading" make-up air system has been designed.&nbsp; In a kitchen hood application for instance, the traditional design might bring in 100% OSA to offset the hood exhaust from a separate intake or unit.&nbsp; In certain projects (schools come to mind), this make-up air can be transferred into the space via adjacent spaces with high OSA requirements (i.e. commons), thus saving all or a portion of the mechanical energy to heat/cool this air.&nbsp; We have always taken the path of the exceptional calculation for LEED purposes because this is definitely a grey area as far as Appendix G is concerned.<BR><BR><BR>-----Original Message-----<BR>From: bldg-sim-bounces@lists.onebuilding.org on behalf of Mitchell Dec<BR>Sent: Fri 11/7/2008 1:50 PM<BR>To: Paul Riemer; Brandon Nichols; Michael Tillou<BR>Cc: bldg-sim@lists.onebuilding.org<BR>Subject: Re: [Bldg-sim] Exhaust, outside air and infiltration for LEED<BR><BR>Bill, Paul, Mike, et al -<BR><BR><BR><BR>We also have not mentioned another item relative to Appendix G, which<BR>requires sizing the flow rate based on a 20-degree delta T. If the<BR>system is a 100% OSA unit, and the baseline is sized for a 20-degree<BR>space-to-coil temperature differential, what happens if the makeup air<BR>unit&nbsp; is not designed with a 20-degree delta-T? Then it is possible the<BR>peak CFM rates could potentially vary. So right there, we could<BR>potentially have a contradiction between 2 lines in Appendix G - (1) OSA<BR>ventilation rates are to be identical, and (2) The baseline AHU flow<BR>rate is specified by a 20-degree delta T - now, which statement in<BR>Appendix G "over rules" the other?<BR><BR><BR><BR>This seems like this should fall under the Exceptional Calculation<BR>methodology to explicitly document where the savings come from, and<BR>whether the savings are justified...<BR><BR><BR><BR>Also regarding an earlier item from this thread, that one cannot take<BR>credit for UFAD and displacement ventilation systems with reduced CFM<BR>rates - as long as the OSA CFM rates are identical, then credit can be<BR>taken from the UFAD/DV system design. You'll be providing the same OSA,<BR>but different Total CFM rates could be calculated based on the different<BR>mixed air temperatures and designed coil leaving temperatures. This can<BR>be either a positive or negative, which truly depends on the climate and<BR>the ability to maximize the economizer hours...<BR><BR><BR><BR><BR><BR>Mitch Dec<BR>Senior Energy Analyst, EIT<BR><BR>LEED(r) Accredited Professional<BR><BR><BR><BR><BR>&nbsp; &lt;<A href="http://www.glumac.com/">http://www.glumac.com/</A>&gt;<BR><BR>________________________________<BR><BR>320 SW Washington, Suite 200<BR>Portland, OR 97204-2640<BR>T.&nbsp; 503.227.5280&nbsp; F. 503.274.7674<BR><BR>Thinking. Inside the building.<BR>www.glumac.com &lt;<A href="http://www.glumac.com/">http://www.glumac.com/</A>&gt;&nbsp;<BR>&nbsp; &lt;<A href="http://www.glumac.com/">http://www.glumac.com/</A>&gt;<BR><BR><BR><BR><BR><BR>From: bldg-sim-bounces@lists.onebuilding.org<BR>[<A href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</A>] On Behalf Of Paul Riemer<BR>Sent: Friday, November 07, 2008 1:37 PM<BR>To: 'Brandon Nichols'; Michael Tillou<BR>Cc: bldg-sim@lists.onebuilding.org<BR>Subject: Re: [Bldg-sim] Exhaust, outside air and infiltration for LEED<BR><BR><BR><BR>Bill,<BR><BR>This is a fascinating convergence of issues.&nbsp;<BR><BR><BR><BR>Appendix G's requirement for the same minimum ventilation rate in the<BR>baseline as the proposed is true but also a bit incomplete when<BR>considering a design of a 100% OA VAV systems serving fume hoods.<BR><BR><BR><BR>We have a similar scenario of a small building with likely VAV hoods,<BR>possibly lower flow, likely served by a 100% outside air system BUT with<BR>my favorite added complexity of district heating and cooling.&nbsp;<BR><BR><BR><BR>Alas, while I was scratching my head, the client abandoned their LEED<BR>goal.<BR><BR><BR><BR>So I have not fully solved it for myself and cannot solve for it your<BR>project but I do suggest the following actions:<BR><BR>1) Read the 90.1-2004 prescriptive requirements for certain systems<BR>serving fume hoods to be VAV or have heat recovery.&nbsp;<BR><BR>2) Read the 90.1-2004 Appendix G base system selection section<BR><BR>3) Now read those same sections in 90.1-2007 and ponder which changes<BR>represent revisions and which ones represent clarifications of original<BR>intent<BR><BR>4) And maybe read the User's Manuals too<BR><BR>5) Consider the exceptional calculation method as the venue to claim<BR>energy savings, that you consider real but are not explicitly allowed or<BR>defined by the document, for consideration by the LEED reviewer<BR><BR>6) Research the existing CIR's<BR><BR>7) Before spending numerous hours on an approach that may or may not be<BR>accepted, buy a CIR and propose your tact to the USGBC itself. If they<BR>reject yours they almost certainly will dictate a new tact that their<BR>reviewer would be obligated to accept for your project.<BR><BR><BR><BR>And lastly, do not wade too much further through this on a Friday<BR>afternoon unless you have to do so. For me, tasks like this should be<BR>tackled early in the day and early in the week.<BR><BR><BR><BR>Good luck,<BR><BR><BR><BR>Paul<BR><BR><BR><BR><BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>________________________________<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; From: bldg-sim-bounces@lists.onebuilding.org<BR>[<A href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</A>] On Behalf Of Brandon<BR>Nichols<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Sent: Friday, November 07, 2008 2:47 PM<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; To: Michael Tillou<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Cc: bldg-sim@lists.onebuilding.org<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Subject: Re: [Bldg-sim] Exhaust, outside air and infiltration<BR>for LEED<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; My two cents...<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; The same OSA for baseline vs as-designed makes sense for<BR>occupant-required OSA, such that there is no reward for compromising<BR>occupant health to gain LEED points.<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; However, that fraction of the fumehood OSA over and above<BR>occupancy-required is process OSA, an opportunity where LEED should be<BR>encouraging savings.&nbsp; Now I'm not saying they do, just that they<BR>should...<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; And after rereading the requirements it shakes out that LEED<BR>really doesn't give credit for reducing process outside air loads, keep<BR>the parametric run in your model -- the local utility may see things<BR>differently, and 'recognize you' with a big fat rebate check.<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Cheers<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Brandon Nichols<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; BW Nichols PE<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Seattle WA<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 206-228-8707<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; On Fri, Nov 7, 2008 at 11:53 AM, Michael Tillou &lt;<BR>michael.tillou@gmail.com&gt; wrote:<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; You are correct that Appendix G requires outside air to be the<BR>same for both as-designed and baseline models.&nbsp; You would not be able to<BR>claim savings for reduced ventilation airflow from a more efficient fume<BR>hood.&nbsp;&nbsp; Similarly you cannot claim credit for reduced ventilation<BR>airflow on displacement ventilation and UFAD systems.<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; However I see no reason why you wouldn't be able to claim the<BR>fan energy savings associated with a more efficient fume hood.<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Mike<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Michael Tillou, PE, LEED<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Tillou Engineering, LLC<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Williamstown, MA 01267<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; P: 413-458-9870 C: 413-652-1087<BR><BR>________________________________<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; From: bldg-sim-bounces@lists.onebuilding.org [mailto:<BR>bldg-sim-bounces@lists.onebuilding.org] On Behalf Of Bishop, Bill<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Sent: Friday, November 07, 2008 9:04 AM<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; To: bldg-sim@lists.onebuilding.org<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Subject: [Bldg-sim] Exhaust, outside air and infiltration for<BR>LEED<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; The mechanical engineer for a campus laboratory building with<BR>100% OA wants to claim energy savings for reduced exhaust from more<BR>efficient fume hoods. (Established design practice uses hoods with 100<BR>fpm flow - they are installing 70 fpm hoods. This reduces peak exhaust<BR>from 700 to 490 CFM per hood.) My approach has always been to keep<BR>outside air, exhaust and infiltration flows identical between the<BR>proposed and baseline models (except for DCV). (This was not easy for<BR>this model with proposed VAV and baseline constant volume packaged<BR>rooftops.)<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Has anybody successfully claimed OA/exhaust/infiltration savings<BR>for a LEED project?<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Thanks,<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Bill<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Mechanical Engineer<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; 3300 Monroe Ave., Suite 306<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Rochester, NY&nbsp; 14618<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; TEL (585) 218-0730 Ext. 114<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; FAX (585) 218-0737<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; bbishop@pathfinderengineers.com<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; www.pathfinderengineers.com<BR>&lt;http://console.mxlogic.com/redir/?2OVtNCZSjqrXXRTDD3o09rpATpgg-fM8Ox_NF<BR>OVKVKVIwuwhbQAGn8lrxrW0E-l9QWIf8dOfgB0zM04SyUMehdEFFKnd7dTAn3ry9I5-Aq83i<BR>ScDE4iZ9aCBQQg3gujRKAM3d45mVQAxVEwSkjh1I43h1a3IzVNSsGMd43JoCy0azgQ76V-7P<BR>No_pgdECQPqrXXRTDDzpsZzREJzkq2t&gt;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; P Please consider the environment before printing this email<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; _______________________________________________<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Bldg-sim mailing list<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>&lt;http://console.mxlogic.com/redir/?5BOXzdXICQTTTHLfe6M0pYGjFRougrAuxa17w<BR>0e7OFek7qY0C43Q29uABiZougrAuxa17w09KVKVIwuwhbQAGn8lrxrW0E-l9QWIf8dOfgB0z<BR>M04SyUMehdEFFKnd7dTAn3ry9I5-Aq83iScDE4iZ9aCBQQg3gujRKAM3d45mVQAxVEwSkjh1<BR>I43h1a3IzVNSsGMd43JoCy0azgQ76V-7PNo_pgdFCQPqrXXRTDDzpsZzREJzkq2t&gt;<BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; To unsubscribe from this mailing list send&nbsp; a blank message to<BR>BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR><BR>&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;<BR><BR><BR></FONT></DIV></BODY></HTML>