My two cents...<br><br>The same OSA for baseline vs as-designed makes sense for occupant-required OSA, such that there is no reward for compromising occupant health to gain LEED points.<br><br>However, that fraction of the fumehood OSA over and above occupancy-required is <b><i>process</i></b> OSA, an opportunity where LEED <i><b>should </b></i>be encouraging savings.  Now I'm not saying they do, just that they <i><b>should...</b></i><br>
<br>And after rereading the requirements it shakes out that LEED really doesn't give credit for reducing process outside air loads, keep the parametric run in your model -- the local utility may see things differently, and 'recognize you' with a big fat rebate check.<br>
<br>Cheers<br><br>Brandon Nichols<br>BW Nichols PE<br>Seattle WA<br>206-228-8707<br><br><div class="gmail_quote">On Fri, Nov 7, 2008 at 11:53 AM, Michael Tillou <span dir="ltr"><<a href="mailto:michael.tillou@gmail.com">michael.tillou@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">





<div vlink="purple" link="blue" lang="EN-US">
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">You are correct that Appendix G requires outside air to be 
the same for both as-designed and baseline models.  You would not be able 
to claim savings for reduced ventilation airflow from a more efficient fume 
hood.   Similarly you cannot claim credit for reduced ventilation 
airflow on displacement ventilation and UFAD systems. </font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">However I see no reason why you wouldn't be able to claim 
the fan energy savings associated with a more efficient fume 
hood.</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial">Mike</font></span></div>
<div dir="ltr" align="left"><span><font color="#0000ff" size="2" face="Arial"></font></span> </div>
<div dir="ltr" align="left"><span>
<div align="left"><font size="2" face="Arial Black">Michael Tillou, PE, 
LEED</font></div>
<div align="left"><font size="2" face="Arial Black">Tillou Engineering, 
LLC</font></div>
<div align="left"><font size="1" face="Arial Black">Williamstown, MA 
01267</font></div>
<div align="left"><font size="1" face="Arial Black">P: 
413-458-9870</font> <font size="1" face="Arial Black">C: 
413-652-1087</font></div></span></div>
<div dir="ltr" align="left" lang="en-us">
<hr>
<font size="2" face="Tahoma"><b>From:</b> <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a> 
[mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Bishop, 
Bill<br><b>Sent:</b> Friday, November 07, 2008 9:04 AM<br><b>To:</b> 
<a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br><b>Subject:</b> [Bldg-sim] Exhaust, outside 
air and infiltration for LEED<br></font><br></div><div><div></div><div class="Wj3C7c">
<div></div>
<div>
<p><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">The mechanical engineer for a campus 
laboratory building with 100% OA wants to claim energy savings for reduced 
exhaust from more efficient fume hoods. (Established design practice uses hoods 
with 100 fpm flow – they are installing 70 fpm hoods. This reduces peak exhaust 
from 700 to 490 CFM per hood.) My approach has always been to keep outside air, 
exhaust and infiltration flows identical between the proposed and baseline 
models (except for DCV). (This was not easy for this model with proposed VAV and 
baseline constant volume packaged rooftops.)</span></font></p>
<p><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Has anybody successfully claimed 
OA/exhaust/infiltration savings for a LEED project?</span></font></p>
<p><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Thanks,</span></font></p>
<p><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;">Bill</span></font></p>
<p><font size="2" face="Arial"><span style="font-size: 10pt; font-family: Arial;"> </span></font></p>
<p><b><font color="black" size="2" face="Franklin Gothic Medium"><span style="font-weight: bold; font-size: 10pt; color: black;">William 
Bishop</span></font></b><b><font color="black" size="2" face="Franklin Gothic Medium Cond"><span style="font-weight: bold; font-size: 10pt; color: black;">, 
EIT, LEED<sup>®</sup> AP</span></font></b><b><font color="#003300" size="2" face="Franklin Gothic Medium Cond"><span style="font-weight: bold; font-size: 10pt; color: rgb(0, 51, 0);"> 
</span></font></b><b><font color="green" size="2" face="Franklin Gothic Medium Cond"><span style="font-weight: bold; font-size: 10pt; color: green;">|</span></font></b><b><font color="#003300" size="2" face="Franklin Gothic Medium Cond"><span style="font-weight: bold; font-size: 10pt; color: rgb(0, 51, 0);"> 
</span></font></b><b><font color="black" size="2" face="Franklin Gothic Medium Cond"><span style="font-weight: bold; font-size: 10pt; color: black;">Pathfinder 
Engineers LLP</span></font></b></p>
<p><font color="black" size="1" face="Arial"><span style="font-size: 9pt; color: black; font-family: Arial;">Mechanical 
Engineer</span></font></p>
<p><font color="black" size="1" face="Arial"><span style="font-size: 3pt; color: black; font-family: Arial;"> </span></font></p>
<p><font color="black" size="1" face="Arial"><span style="font-size: 9pt; color: black; font-family: Arial;">3300 Monroe Ave., Suite 
306</span></font><font color="black" size="1" face="Arial"><span style="font-size: 9pt; color: black; font-family: Arial;"> <br>Rochester, NY  
14618</span></font><font color="black" size="1" face="Arial"><span style="font-size: 9pt; color: black; font-family: Arial;"></span></font></p>
<p><font color="black" size="1" face="Arial"><span style="font-size: 9pt; color: black; font-family: Arial;">TEL (585) 218-0730 
Ext. 114<br>FAX (585) 218-0737 </span></font></p>
<p><font color="black" size="1" face="Arial"><span style="font-size: 9pt; color: black; font-family: Arial;"><a href="mailto:bbishop@pathfinderengineers.com" target="_blank">bbishop@pathfinderengineers.com</a></span></font></p>

<p><font color="black" size="1" face="Arial"><span style="font-size: 3pt; color: black; font-family: Arial;"> </span></font></p>
<p><font color="black" size="1" face="Arial"><span style="font-size: 9pt; color: black; font-family: Arial;"><a href="http://www.pathfinderengineers.com" target="_blank">www.pathfinderengineers.com</a></span></font></p>
<p><font color="green" size="5" face="Webdings"><span style="font-size: 18pt; color: green; font-family: Webdings;">P</span></font><font color="green"><span style="color: green;"> </span></font><font color="green" size="1"><span style="font-size: 7.5pt; color: green;">Please consider the 
environment before printing this email</span></font><font color="green"><span style="color: green;"></span></font></p>
<p><font size="3" face="Times New Roman"><span style="font-size: 12pt;"> </span></font></p></div></div></div></div>
<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>