color=#0000ff size=2>Bill,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>This is a fascinating convergence of issues.  
</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2><SPAN class=889141221-07112008>Appendix G's requirement for 
the same minimum ventilation rate in the baseline as the proposed 
is true but also a bit incomplete when considering a design of a 100% OA 
VAV systems serving fume hoods.</SPAN></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT><FONT 
face=Arial><FONT color=#0000ff><FONT size=2>We have a similar scenario of a 
small building with likely VAV hoods, possibly lower flow, likely served by a 
100% <SPAN class=889141221-07112008>outside </SPAN>air system <SPAN 
class=889141221-07112008>BUT</SPAN> with <SPAN class=889141221-07112008>my 
favorite </SPAN>added complexity of district heating and cooling.<SPAN 
class=889141221-07112008>  </SPAN></FONT></FONT></FONT></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT><FONT 
face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=889141221-07112008></SPAN></FONT></FONT></FONT></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT><SPAN 
class=889141221-07112008></SPAN><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>Alas<SPAN class=889141221-07112008>,</SPAN> <SPAN 
class=889141221-07112008>while I was scratching my head, </SPAN>the client 
abandoned their LEED goal. </FONT></SPAN></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2> </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>So I have not fully solved it for myself and cannot solve 
for it your project but </FONT></SPAN><SPAN 
class=546303120-07112008><FONT face=Arial color=#0000ff size=2>I do suggest 
the following actions:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>1) Read the 90.1-2004 prescriptive requirements for 
certain systems serving <SPAN class=889141221-07112008>fume </SPAN>hoods to 
be VAV or have heat recovery.  </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>2) Read the 90.1-2004 Appendix G base system 
selection section</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>3) Now read those same sections 
in 90.1-2007 and p</FONT></SPAN><SPAN 
class=546303120-07112008><FONT face=Arial color=#0000ff size=2>onder which 
changes represent revisions and which ones represent clarifications of original 
intent</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><SPAN 
class=889141221-07112008><FONT face=Arial color=#0000ff size=2>4) And maybe 
read the User's Manuals too</FONT></SPAN></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial><FONT 
color=#0000ff><FONT size=2><SPAN class=889141221-07112008>5</SPAN>) Consider the 
exceptional calculation method as the venue to claim energy 
savings, that <SPAN class=889141221-07112008>you 
consider</SPAN> real but are not explicitly allowed<SPAN 
class=889141221-07112008> or defined</SPAN> by the document, 
for consideration by the LEED reviewer</FONT></FONT></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial><FONT 
color=#0000ff><FONT size=2><SPAN 
class=889141221-07112008>6</SPAN>) Research the existing 
CIR's</FONT></FONT></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial><FONT 
color=#0000ff><FONT size=2><SPAN class=889141221-07112008>7</SPAN>) Before 
spending numerous hours on an approach that may or may not be 
accepted, buy a CIR and propose your tact <SPAN 
class=889141221-07112008>to </SPAN>the USGBC itself. If they reject yours 
they almost <SPAN class=889141221-07112008>certainly will </SPAN><SPAN 
class=889141221-07112008>dictate </SPAN>a new tact that <SPAN 
class=889141221-07112008>their </SPAN>reviewer would be obligated to 
accept<SPAN class=889141221-07112008> for your 
project.</SPAN></FONT></FONT></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>And lastly, do not wade too much further through this on a 
Friday afternoon unless you have to do so. For me, tasks like this should be 
tackled early in the day and early in the week.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>Good luck,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2>Paul</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=546303120-07112008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV></DIV><BR>
<BLOCKQUOTE style="MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
  <HR tabIndex=-1>
  <FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
  [mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Brandon 
  Nichols<BR><B>Sent:</B> Friday, November 07, 2008 2:47 PM<BR><B>To:</B> 
  Michael Tillou<BR><B>Cc:</B> bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> 
  Re: [Bldg-sim] Exhaust, outside air and infiltration for 
  LEED<BR></FONT><BR></DIV>
  <DIV></DIV>My two cents...<BR><BR>The same OSA for baseline vs as-designed 
  makes sense for occupant-required OSA, such that there is no reward for 
  compromising occupant health to gain LEED points.<BR><BR>However, that 
  fraction of the fumehood OSA over and above occupancy-required is 
  <B><I>process</I></B> OSA, an opportunity where LEED <I><B>should </B></I>be 
  encouraging savings.  Now I'm not saying they do, just that they 
  <I><B>should...</B></I><BR><BR>And after rereading the requirements it shakes 
  out that LEED really doesn't give credit for reducing process outside air 
  loads, keep the parametric run in your model -- the local utility may see 
  things differently, and 'recognize you' with a big fat rebate 
  check.<BR><BR>Cheers<BR><BR>Brandon Nichols<BR>BW Nichols PE<BR>Seattle 
  WA<BR>206-228-8707<BR><BR>
  <DIV class=gmail_quote>On Fri, Nov 7, 2008 at 11:53 AM, Michael Tillou <SPAN 
  dir=ltr><<A 
  href="mailto:michael.tillou@gmail.com">michael.tillou@gmail.com</A>></SPAN> 
  wrote:<BR>
  <BLOCKQUOTE class=gmail_quote 
  style="PADDING-LEFT: 1ex; MARGIN: 0pt 0pt 0pt 0.8ex; BORDER-LEFT: rgb(204,204,204) 1px solid">
    <DIV lang=EN-US link="blue" vlink="purple">
    <DIV dir=ltr align=left><SPAN><FONT face=Arial color=#0000ff size=2>You are 
    correct that Appendix G requires outside air to be the same for both 
    as-designed and baseline models.  You would not be able to claim 
    savings for reduced ventilation airflow from a more efficient fume 
    hood.   Similarly you cannot claim credit for reduced 
    ventilation airflow on displacement ventilation and UFAD 
    systems. </FONT></SPAN></DIV>
    <DIV dir=ltr align=left><SPAN><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV>
    <DIV dir=ltr align=left><SPAN><FONT face=Arial color=#0000ff size=2>However 
    I see no reason why you wouldn't be able to claim the fan energy 
    savings associated with a more efficient fume hood.</FONT></SPAN></DIV>
    <DIV dir=ltr align=left><SPAN><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV>
    <DIV dir=ltr align=left><SPAN><FONT face=Arial color=#0000ff 
    size=2>Mike</FONT></SPAN></DIV>
    <DIV dir=ltr align=left><SPAN><FONT face=Arial color=#0000ff 
    size=2></FONT></SPAN> </DIV>
    <DIV dir=ltr align=left><SPAN>
    <DIV align=left><FONT face="Arial Black" size=2>Michael Tillou, PE, 
    LEED</FONT></DIV>
    <DIV align=left><FONT face="Arial Black" size=2>Tillou Engineering, 
    LLC</FONT></DIV>
    <DIV align=left><FONT face="Arial Black" size=1>Williamstown, MA 
    01267</FONT></DIV>
    <DIV align=left><FONT face="Arial Black" size=1>P: 
    413-458-9870</FONT> <FONT face="Arial Black" size=1>C: 
    413-652-1087</FONT></DIV></SPAN></DIV>
    <DIV lang=en-us dir=ltr align=left>
    <HR>
    <FONT face=Tahoma size=2><B>From:</B> <A 
    href="mailto:bldg-sim-bounces@lists.onebuilding.org" 
    target=_blank>bldg-sim-bounces@lists.onebuilding.org</A> [mailto:<A 
    href="mailto:bldg-sim-bounces@lists.onebuilding.org" 
    target=_blank>bldg-sim-bounces@lists.onebuilding.org</A>] <B>On Behalf Of 
    </B>Bishop, Bill<BR><B>Sent:</B> Friday, November 07, 2008 9:04 
    AM<BR><B>To:</B> <A href="mailto:bldg-sim@lists.onebuilding.org" 
    target=_blank>bldg-sim@lists.onebuilding.org</A><BR><B>Subject:</B> 
    [Bldg-sim] Exhaust, outside air and infiltration for 
    LEED<BR></FONT><BR></DIV>
    <DIV>
    <DIV></DIV>
    <DIV class=Wj3C7c>
    <DIV></DIV>
    <DIV>
    <P><FONT face=Arial size=2><SPAN 
    style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">The mechanical engineer for a 
    campus laboratory building with 100% OA wants to claim energy savings for 
    reduced exhaust from more efficient fume hoods. (Established design practice 
    uses hoods with 100 fpm flow – they are installing 70 fpm hoods. This 
    reduces peak exhaust from 700 to 490 CFM per hood.) My approach has always 
    been to keep outside air, exhaust and infiltration flows identical between 
    the proposed and baseline models (except for DCV). (This was not easy for 
    this model with proposed VAV and baseline constant volume packaged 
    rooftops.)</SPAN></FONT></P>
    <P><FONT face=Arial size=2><SPAN 
    style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"></SPAN></FONT> </P>
    <P><FONT face=Arial size=2><SPAN 
    style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Has anybody successfully claimed 
    OA/exhaust/infiltration savings for a LEED project?</SPAN></FONT></P>
    <P><FONT face=Arial size=2><SPAN 
    style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"></SPAN></FONT> </P>
    <P><FONT face=Arial size=2><SPAN 
    style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Thanks,</SPAN></FONT></P>
    <P><FONT face=Arial size=2><SPAN 
    style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Bill</SPAN></FONT></P>
    <P><FONT face=Arial size=2><SPAN 
    style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"></SPAN></FONT> </P>
    <P><B><FONT face="Franklin Gothic Medium" color=black size=2><SPAN 
    style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: black">William 
    Bishop</SPAN></FONT></B><B><FONT face="Franklin Gothic Medium Cond" 
    color=black size=2><SPAN 
    style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: black">, EIT, 
    LEED<SUP>®</SUP> AP</SPAN></FONT></B><B><FONT 
    face="Franklin Gothic Medium Cond" color=#003300 size=2><SPAN 
    style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: rgb(0,51,0)"> 
    </SPAN></FONT></B><B><FONT face="Franklin Gothic Medium Cond" color=green 
    size=2><SPAN 
    style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: green">|</SPAN></FONT></B><B><FONT 
    face="Franklin Gothic Medium Cond" color=#003300 size=2><SPAN 
    style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: rgb(0,51,0)"> 
    </SPAN></FONT></B><B><FONT face="Franklin Gothic Medium Cond" color=black 
    size=2><SPAN 
    style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; COLOR: black">Pathfinder 
    Engineers LLP</SPAN></FONT></B></P>
    <P><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 9pt; COLOR: black; FONT-FAMILY: Arial">Mechanical 
    Engineer</SPAN></FONT></P>
    <P><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 3pt; COLOR: black; FONT-FAMILY: Arial"></SPAN></FONT> </P>
    <P><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 9pt; COLOR: black; FONT-FAMILY: Arial">3300 Monroe Ave., 
    Suite 306</SPAN></FONT><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 9pt; COLOR: black; FONT-FAMILY: Arial"> <BR>Rochester, 
    NY  14618</SPAN></FONT><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 9pt; COLOR: black; FONT-FAMILY: Arial"></SPAN></FONT></P>
    <P><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 9pt; COLOR: black; FONT-FAMILY: Arial">TEL (585) 
    218-0730 Ext. 114<BR>FAX (585) 218-0737 </SPAN></FONT></P>
    <P><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 9pt; COLOR: black; FONT-FAMILY: Arial"><A 
    href="mailto:bbishop@pathfinderengineers.com" 
    target=_blank>bbishop@pathfinderengineers.com</A></SPAN></FONT></P>
    <P><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 3pt; COLOR: black; FONT-FAMILY: Arial"></SPAN></FONT> </P>
    <P><FONT face=Arial color=black size=1><SPAN 
    style="FONT-SIZE: 9pt; COLOR: black; FONT-FAMILY: Arial"><A 
    href="http://console.mxlogic.com/redir/?2OVtNCZSjqrXXRTDD3o09rpATpgg-fM8Ox_NFOVKVKVIwuwhbQAGn8lrxrW0E-l9QWIf8dOfgB0zM04SyUMehdEFFKnd7dTAn3ry9I5-Aq83iScDE4iZ9aCBQQg3gujRKAM3d45mVQAxVEwSkjh1I43h1a3IzVNSsGMd43JoCy0azgQ76V-7PNo_pgdECQPqrXXRTDDzpsZzREJzkq2t" 
    target=_blank>www.pathfinderengineers.com</A></SPAN></FONT></P>
    <P><FONT face=Webdings color=green size=5><SPAN 
    style="FONT-SIZE: 18pt; COLOR: green; FONT-FAMILY: Webdings">P</SPAN></FONT><FONT 
    color=green><SPAN style="COLOR: green"> </SPAN></FONT><FONT color=green 
    size=1><SPAN style="FONT-SIZE: 7.5pt; COLOR: green">Please consider the 
    environment before printing this email</SPAN></FONT><FONT color=green><SPAN 
    style="COLOR: green"></SPAN></FONT></P>
    <P><FONT face="Times New Roman" size=3><SPAN 
    style="FONT-SIZE: 12pt"></SPAN></FONT> </P></DIV></DIV></DIV></DIV><BR>_______________________________________________<BR>Bldg-sim 
    mailing list<BR><A 
    href="http://console.mxlogic.com/redir/?5BOXzdXICQTTTHLfe6M0pYGjFRougrAuxa17w0e7OFek7qY0C43Q29uABiZougrAuxa17w09KVKVIwuwhbQAGn8lrxrW0E-l9QWIf8dOfgB0zM04SyUMehdEFFKnd7dTAn3ry9I5-Aq83iScDE4iZ9aCBQQg3gujRKAM3d45mVQAxVEwSkjh1I43h1a3IzVNSsGMd43JoCy0azgQ76V-7PNo_pgdFCQPqrXXRTDDzpsZzREJzkq2t" 
    target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To 
    unsubscribe from this mailing list send  a blank message to <A 
    href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR><BR></BLOCKQUOTE></DIV><BR></BLOCKQUOTE></BODY></HTML>