<DIV><FONT face=Arial color=#000000 size=2>I searched thru the archives but couldn't fiind an answer to this. </FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Why is there a direct conflict in the required Baseline system type between the App G chart in 90.1 and the wording in the 90.1 user manual?</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>I have a 6-story building that is 100,000 sq ft. If I read Table G3.1.1A of 90.1, it says:</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2><STRONG>"Nonresidential & More than 5 floors OR > 150,000 sq ft", that I should use System 8 (VAV with PFP boxes).</STRONG></FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Even Table G-A in the User Manual says the same thing.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>In addition, the requirements for using System 6 say:</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2><STRONG>"Non residential, 4 or 5 floors or less than 75,000 sq ft OR 5 floors or less and 75,000 - 150,000 sq ft".</STRONG></FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Both of these facts would lead me to believe that anything over 5 stories should be System 8. However, the wording in the User Manual goes on to say that:</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2><STRONG>"For intermediate-sized buildings that are 4 or 5 floors and less than 75,000 sq ft or <U>more than 5 floors and between 75,000 and 150,000 sq ft</U>, the baseline building HVAC system for electric heat is packaged VAV system."</STRONG></FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>I've finished modeling the Baseline building with System 8, but now that I've read the User Manual, it would appear that I am supposed to use PVAV. I really hope I don't have to go back and change the baseline system again.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Any thoughts?</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>Thanks</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2>James Hansen</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV>
<DIV><FONT face=Arial size=2></FONT> </DIV></BODY><!--[object_id=#ghtltd.com#]--><P align=left><FONT size=2><FONT face=Tahoma><FONT color=#0000ff>
<HR>
</FONT></FONT><FONT color=#0000ff><FONT color=#000000><FONT face=Arial>The information contained in this communication is confidential, may be privileged, and is intended only for the use of the addressee. It is the property of GHT Limited. Unauthorized use, disclosure or copying of this communication or any part thereof is strictly prohibited and may be unlawful. If you have received this communication in error, please notify me immediately by return e-mail or by e-mail to </FONT><A href="mailto:ght@ghtltd.com"><FONT face=Arial>ght@ghtltd.com</FONT></A><FONT face=Arial>, and destroy this communication and all copies thereof, including all attachments. Thank you.</FONT></FONT><FONT face=Tahoma color=#000000></FONT></P></FONT></FONT></HTML>