<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META http-equiv=Content-Type content="text/html; charset=iso-8859-1">
<META content="MSHTML 6.00.2900.2963" name=GENERATOR>
<STYLE></STYLE>
</HEAD>
<BODY bgColor=#ffffff>
<DIV dir=ltr align=left><SPAN class=489145420-05112008><FONT face=Arial 
color=#0000ff size=2>Rich:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=489145420-05112008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=489145420-05112008><FONT face=Arial 
color=#0000ff size=2>What is your Cooling Control range set at? Try a 6°F 
range.</FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Routh 
Consulting Engineers<BR><B>Sent:</B> Wednesday, November 05, 2008 12:46 
PM<BR><B>To:</B> bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] 
PVVT System Modeling<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><FONT face=Arial size=2>I am modeling a building with packaged gas/electric 
rooftop units with Carrier System 3 (previously Parker) zone dampers and bypass. 
I am getting a huge number of hours with loads not met and I'm thinking it's due 
to the model using just the one control zone to determine the operating mode of 
the unit, instead of the combination of "majority rules" and "zone of greatest 
demand" logic the actual system uses. Does anyone have a method of better 
simulating the actual equipment operation which accounts for the system's 
ability to reverse modes if some zones, in my case other than the specified 
control zone, are calling for the opposite? Is the ceiling bypass VAV model more 
similar to this actual system? I'm thinking maybe not as it resets leaving air 
temperature only on zone of greatest cooling demand. I'm confident&nbsp;the 
system design will maintain comfort conditions in the various zones even if the 
unit has to reverse modes occasionally, but the modeling is for LEED which 
restricts how many unmet load hours you can have. All thoughts and experience on 
this subject would be appreciated, and thanks for your replies to my other 
recent messages.</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT>&nbsp;</DIV>
<DIV><FONT face=Arial size=2>Rick Routh</FONT></DIV>
<DIV><FONT face=Arial size=2></FONT>&nbsp;</DIV></BODY></HTML>