<div>Nuno,</div>
<div>&nbsp;</div>
<div>I have used the IndoorPoolCalc.xls spreadsheet tool for analyzing indoor pool heating and dehumidification energy.</div>
<div>&nbsp;</div>
<div>It is&nbsp;available here:</div>
<div><a href="http://www.energyideas.org/documents/spreadsheets/IndoorPoolCalc.xls">http://www.energyideas.org/documents/spreadsheets/IndoorPoolCalc.xls</a></div>
<div>&nbsp;</div>
<div>It can be used to find energy savings resulting from using a pool cover, changing air/water temperature and humidity setpoints, new boiler, new dehumidifier and so on.&nbsp;&nbsp;It is based on the Shah Method--see &quot;Calculating Evaporation from Indoor Water Pools&quot;, HPAC Engineering, March 2004.</div>

<div>&nbsp;</div>
<div>I hope this helps,</div>
<div>&nbsp;</div>
<div>Eric Wilson</div>University of Colorado<br>Dept. of Civil, Env., and Architectural Engineering<br>Building Systems Program 
<div><br>&nbsp;</div>
<div class="gmail_quote">On Tue, Nov 4, 2008 at 1:01 PM, <span dir="ltr">&lt;<a href="mailto:bldg-sim-request@lists.onebuilding.org">bldg-sim-request@lists.onebuilding.org</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="PADDING-LEFT: 1ex; MARGIN: 0px 0px 0px 0.8ex; BORDER-LEFT: #ccc 1px solid">Send Bldg-sim mailing list submissions to<br>&nbsp; &nbsp; &nbsp; &nbsp;<a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>
<br>To subscribe or unsubscribe via the World Wide Web, visit<br>&nbsp; &nbsp; &nbsp; &nbsp;<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
or, via email, send a message with subject or body &#39;help&#39; to<br>&nbsp; &nbsp; &nbsp; &nbsp;<a href="mailto:bldg-sim-request@lists.onebuilding.org">bldg-sim-request@lists.onebuilding.org</a><br><br>You can reach the person managing the list at<br>
&nbsp; &nbsp; &nbsp; &nbsp;<a href="mailto:bldg-sim-owner@lists.onebuilding.org">bldg-sim-owner@lists.onebuilding.org</a><br><br>When replying, please edit your Subject line so it is more specific<br>than &quot;Re: Contents of Bldg-sim digest...&quot;<br>
<br><br>Today&#39;s Topics:<br><br>&nbsp; 1. New Blog: Tools for Better and more Sustainable Building<br>&nbsp; &nbsp; &nbsp;Design (Jason Glazer)<br>&nbsp; 2. Swimming Pool Modelling (Nuno Brandao)<br>&nbsp; 3. Performance Modeling Opening (Mathew Higgins)<br>
&nbsp; 4. Radiance: Determining Specularity Values - Spandrel &nbsp; &nbsp; &nbsp; Panels:<br>&nbsp; &nbsp; &nbsp;Marble vs Fritted Glass (Pearson, Nastassja)<br>&nbsp; 5. Re: Swimming Pool Modelling (Yuvaraj Saravanan)<br>&nbsp; 6. IBE Consulting Engineers - Building Simulation Engineer<br>
&nbsp; &nbsp; &nbsp;Position (Patrick Wilkinson)<br><br><br>----------------------------------------------------------------------<br><br>Message: 1<br>Date: Mon, 03 Nov 2008 14:21:30 -0600<br>From: Jason Glazer &lt;<a href="mailto:jglazer@gard.com">jglazer@gard.com</a>&gt;<br>
Subject: [Bldg-sim] New Blog: Tools for Better and more Sustainable<br>&nbsp; &nbsp; &nbsp; &nbsp;Building &nbsp; &nbsp; &nbsp; &nbsp;Design<br>To: <a href="mailto:bldg-sim@onebuilding.org">bldg-sim@onebuilding.org</a><br>Message-ID: &lt;<a href="mailto:490F5D4A.4040504@gard.com">490F5D4A.4040504@gard.com</a>&gt;<br>
Content-Type: text/plain; charset=ISO-8859-1; format=flowed<br><br>Here is a new blog that might be of interest.<br><br><a href="http://bldgsim.wordpress.com/" target="_blank">http://bldgsim.wordpress.com/</a><br><br>This blog is not related to the BLDG-SIM mailing list even<br>
though the name is very close.<br><br>Jason<br><br>--<br>Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair<br>Admin for <a href="http://onebuilding.org/" target="_blank">onebuilding.org</a> building performance mailing lists<br>
<br><br>------------------------------<br><br>Message: 2<br>Date: Tue, 4 Nov 2008 12:30:24 +0000<br>From: &quot;Nuno Brandao&quot; &lt;<a href="mailto:ncostab@gmail.com">ncostab@gmail.com</a>&gt;<br>Subject: [Bldg-sim] Swimming Pool Modelling<br>
To: <a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>Message-ID:<br>&nbsp; &nbsp; &nbsp; &nbsp;&lt;<a href="mailto:79c8d8d0811040430tba761f9k95d43997aa5363b6@mail.gmail.com">79c8d8d0811040430tba761f9k95d43997aa5363b6@mail.gmail.com</a>&gt;<br>
Content-Type: text/plain; charset=&quot;iso-8859-1&quot;<br><br>Dear bldg members,<br><br>I?m trying to execute a simulation approach on a swimming pool simulation<br>using EnergyPlus. I decided to write &nbsp;hoping you could give me some guidance<br>
help on this kind of simulation approach since Energyplus does not have a<br>model for it.<br><br>The objective would be to simulate the pool environment, accounting for all<br>the heat transfer phenomenons, heat losses, etc., but more important the<br>
evaporation losses which must be treated with dehumidification equipment.<br>The space must be heated and dehumidified using a standard dehumidifier<br>equipment.<br><br>Defining the space and boundary conditions is not difficult using the<br>
current geometry interfaces. At the end I would like to obtain the energy<br>consumption of HVAC equipment on treating the space loads (mainly<br>dehumidification and heating).<br><br>Can you give me some guidance help on what have you done in your approach on<br>
EnergyPlus? Is there any other software or application which is capable of<br>simulating this kind of model?<br><br>Thanks in advance,<br>Nuno<br>-------------- next part --------------<br>An HTML attachment was scrubbed...<br>
URL: &lt;<a href="http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/5dd4efa9/attachment.html" target="_blank">http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/5dd4efa9/attachment.html</a>&gt;<br>
<br>------------------------------<br><br>Message: 3<br>Date: Tue, 04 Nov 2008 08:15:50 -0700<br>From: Mathew Higgins &lt;<a href="mailto:higgins@edi-arch.com">higgins@edi-arch.com</a>&gt;<br>Subject: [Bldg-sim] Performance Modeling Opening<br>
To: <a href="mailto:bldg-sim@onebuilding.org">bldg-sim@onebuilding.org</a><br>Message-ID: &lt;<a href="mailto:49106726.2050206@edi-arch.com">49106726.2050206@edi-arch.com</a>&gt;<br>Content-Type: text/plain; charset=ISO-8859-1; format=flowed<br>
<br>A consulting firm with offices in New Mexico and Florida is seeking to<br>hire a performance modeling specialist with 2 to 5 years experience in<br>building energy and daylight modeling. &nbsp;Professional qualifications in<br>
architecture, engineering and the LEED rating system is preferred.<br>Interested parties should send a letter highlighting their<br>qualifications, listing experience with performance modeling programs,<br>to <a href="mailto:kris@edi-arch.com">kris@edi-arch.com</a>.<br>
<br>--<br>Matthew Higgins, LEED AP<br>Technical Specialist<br>Environmental Dynamics, Inc.<br>Architecture and Sustainability Consulting Services<br>505.242.2851<br><br>Any data provided by the Consultant, verbal or written, are to be considered opinions of building energy and/or daylight performance. The Client understands that the Consultant has no control of occupant habits, equipment or material performance or characteristics, site or climate conditions or the Contractor&#39;s method of assembly, and that the Consultant&#39;s opinions regarding building energy/daylight performance are made on the basis of the Consultant&#39;s professional judgment and experience. The Consultant makes no warranty, express or implied, that the energy/daylight performance of the building will not vary from the Consultant&#39;s opinion of building energy/daylight performance.<br>
<br><br><br>------------------------------<br><br>Message: 4<br>Date: Tue, 4 Nov 2008 12:09:54 -0500<br>From: &quot;Pearson, Nastassja&quot; &lt;<a href="mailto:npearson@halsall.com">npearson@halsall.com</a>&gt;<br>Subject: [Bldg-sim] Radiance: Determining Specularity Values -<br>
&nbsp; &nbsp; &nbsp; &nbsp;Spandrel &nbsp; &nbsp; &nbsp; &nbsp;Panels: Marble vs Fritted Glass<br>To: &lt;<a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>&gt;<br>Message-ID:<br>&nbsp; &nbsp; &nbsp; &nbsp;&lt;<a href="mailto:3EC944427F87D84793DBBC4137A2B5AD4CD833@to1exc02wp.halsall.com">3EC944427F87D84793DBBC4137A2B5AD4CD833@to1exc02wp.halsall.com</a>&gt;<br>
Content-Type: text/plain; charset=&quot;us-ascii&quot;<br><br>Hello All,<br><br><br><br>I am trying to compare the difference in glare given off a building<br>after a cladding retrofit (from the perspective of occupants in<br>
neighboring buildings). The original curtain wall cladding is a<br>white/grey marble and glass spandrel panels with a white patterned frit<br>are proposed for the retrofit. I am using Radiance in IES&#39; Virtual<br>Environment program; this is my first time using the simulation<br>
software.<br><br><br><br>I have some questions about determining/selecting material properties,<br>specifically deciding what material type (plastic/metal) and secularity<br>to use for the two cladding options.<br><br><br>
<br>Specifically how do I choose a realistic secularity value for the<br>material I am using? Is there a definitive way to select a value or is<br>it dependant on multiple iterations comparing how the images produced<br>look? I&#39;m trying to use the program to show me how much glare I could<br>
expect to see, if the results are based on constantly tweaking the<br>parameters so the image &quot;looks&quot; right for me I don&#39;t see how the results<br>can be accurate.<br><br><br><br>Is a more extensive database of materials and their properties (beyond<br>
what is provided with the program) available? For the materials<br>described below what specularity values would you recommend - and what<br>is the basis behind choosing those values?<br><br><br><br><br><br>My assumptions:<br>
<br><br><br>Marble - Originally white, but panels have become grey with dirt over<br>time, not polished, dull finish<br><br>Type: &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp;Plastic<br><br>Colour: &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; (0.91, 0.91, 0.83)<br><br>Specularity: &nbsp; &nbsp; &nbsp; ?????? (I think this may be low because it is not<br>
polished marble)<br><br>Roughness: &nbsp; &nbsp; &nbsp;0.05 (???)<br><br><br><br><br><br><br><br>Glass Frit - Composed of: Clear glass, 60% coverage white frit, clear<br>glass, 100% coverage white frit. From Window 6, I estimate the solar<br>
reflectance of the system to be around 25-35%.<br><br><br><br>Typle: &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; Metal ??? (Does the frit have specular and diffuse<br>reflection of light?)<br><br>Colour: &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; &nbsp; (1.0,1.0, 1.0)<br><br>Specularity: &nbsp; &nbsp; &nbsp; ????? (Clean polished glass)<br>
<br>Roughness: &nbsp; &nbsp; &nbsp;0.00<br><br><br><br><br><br>If anyone has information from doing a similar simulation or has any<br>suggestion on what specularity values I should use to model these<br>materials it would be very much appreciated.<br>
<br><br><br><br><br>Thanks,<br><br><br><br>Nastassja<br><br>-------------- next part --------------<br>An HTML attachment was scrubbed...<br>URL: &lt;<a href="http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/927dc8f9/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/927dc8f9/attachment-0001.htm</a>&gt;<br>
<br>------------------------------<br><br>Message: 5<br>Date: Tue, 4 Nov 2008 10:00:07 -0800<br>From: &quot;Yuvaraj Saravanan&quot; &lt;<a href="mailto:Yuvaraj.Saravanan@arup.com">Yuvaraj.Saravanan@arup.com</a>&gt;<br>Subject: Re: [Bldg-sim] Swimming Pool Modelling<br>
To: &quot;Nuno Brandao&quot; &lt;<a href="mailto:ncostab@gmail.com">ncostab@gmail.com</a>&gt;<br>Cc: <a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>Message-ID:<br>&nbsp; &nbsp; &nbsp; &nbsp;&lt;<a href="mailto:141D50E6B1F9E247BD450DA0BB288FE103814D81@l-aexc01.global.arup.com">141D50E6B1F9E247BD450DA0BB288FE103814D81@l-aexc01.global.arup.com</a>&gt;<br>
Content-Type: text/plain; charset=&quot;iso-8859-1&quot;<br><br>Hi Nuno,<br>I have not used Energyplus before. But I guess you would have to do a hand calculation to determine the evaporation rate and model it as a latent load. You could input that latent load as a plug load or even add to people latent load. I know that there is some ASHRAE journal/article which talks about how to calculate the evaporation rate in swimming pools. But unfortunately, I am not able to point you were to download that article. I am sure you can find it if you do some Google search. Hope this helps!<br>
If you end up modeling in a different way, please let me know. I would be interested to know.<br>Regards,<br>Yuvaraj<br><br>________________________________<br><br>From: <a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</a>] On Behalf Of Nuno Brandao<br>
Sent: Tuesday, November 04, 2008 4:30 AM<br>To: <a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a><br>Subject: [Bldg-sim] Swimming Pool Modelling<br><br><br>Dear bldg members,<br><br>I?m trying to execute a simulation approach on a swimming pool simulation using EnergyPlus. I decided to write &nbsp;hoping you could give me some guidance help on this kind of simulation approach since Energyplus does not have a model for it.<br>
<br>The objective would be to simulate the pool environment, accounting for all the heat transfer phenomenons, heat losses, etc., but more important the evaporation losses which must be treated with dehumidification equipment. The space must be heated and dehumidified using a standard dehumidifier equipment.<br>
<br>Defining the space and boundary conditions is not difficult using the current geometry interfaces. At the end I would like to obtain the energy consumption of HVAC equipment on treating the space loads (mainly dehumidification and heating).<br>
<br>Can you give me some guidance help on what have you done in your approach on EnergyPlus? Is there any other software or application which is capable of simulating this kind of model?<br><br>Thanks in advance,<br>Nuno<br>
<br>____________________________________________________________<br>Electronic mail messages entering and leaving Arup &nbsp;business<br>systems are scanned for acceptability of content and viruses<br>-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>URL: &lt;<a href="http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/a4f2eb34/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/a4f2eb34/attachment-0001.htm</a>&gt;<br>
<br>------------------------------<br><br>Message: 6<br>Date: Tue, 4 Nov 2008 10:04:43 -0800<br>From: &quot;Patrick Wilkinson&quot; &lt;<a href="mailto:patrick.wilkinson@ibece.net">patrick.wilkinson@ibece.net</a>&gt;<br>Subject: [Bldg-sim] IBE Consulting Engineers - Building Simulation<br>
&nbsp; &nbsp; &nbsp; &nbsp;Engineer &nbsp; &nbsp; &nbsp; &nbsp;Position<br>To: &lt;<a href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</a>&gt;<br>Message-ID:<br>&nbsp; &nbsp; &nbsp; &nbsp;&lt;B9A3AA6F98276B4EB15DECA51DB7F851011DDE5B@smain07.IBECE07.local&gt;<br>
Content-Type: text/plain; charset=&quot;us-ascii&quot;<br><br>IBE Consulting Engineers (IBE) is an established architectural<br>engineering firm specializing in providing innovative mechanical,<br>electrical, plumbing engineering and fire protection services. IBE<br>
provides sustainable, cost effective engineering designs that integrate<br>the engineering components with the building design and architecture.<br>Our approach to building design involves understanding the building<br>site, architecture and program to produce a design that enhances and<br>
contributes to creating a sustainable built environment. IBE has a<br>varied workload including high profile museums, laboratories,<br>commercial, and academic facilities located throughout the United States<br>and in Paris, France with several projects internationally. In recent<br>
years, IBE&#39;s has won several awards for its work on sustainable building<br>systems.<br><br><br><br>A building simulation engineer in the Advanced Technology Group (ATG)<br>must have demonstrated practical experience, competence, and proven<br>
expertise in evaluating state-of-the-art building energy-efficiency<br>technologies and managing sustainable design assistance projects. He or<br>she must be experienced with hourly simulation software programs and<br>industry-accepted engineering methods for evaluating energy performance<br>
and should be fully capable of performing all aspects of whole-building<br>energy analysis associated with completing sustainable design projects.<br>In addition, s/he must be able to provide quality assurance review of<br>
analysis methods, simulation results, and project deliverables. The<br>candidate must be a team player willing to contribute to and build<br>energy analysis group methods, knowledge, and capabilities. S/he should<br>have a strong background in the design and operation of mechanical<br>
heating, ventilation, and air-conditioning (HVAC) systems and knowledge<br>of the specialized HVAC requirements of highly technical facilities.<br>Candidates should have experience working within the architectural<br>design process and understand design team members&#39; roles, perspectives,<br>
and analysis needs. A holistic understanding of whole building and<br>mechanical systems and a strong commitment to state-of-the-art design<br>innovations are essential.<br><br><br><br>Essential Responsibilities:<br><br>The building simulation engineer will be a member of Advanced Technology<br>
Group (ATG) within IBE Consulting Engineers Typical duties may include<br>(but are not limited to) the following:<br><br>o &nbsp; &nbsp; &nbsp; &nbsp;Support the ATG in delivering and documenting green building<br>technologies and strategies for their projects with focus on analysis of<br>
energy, day lighting and/or air flow modeling of building and master<br>planning projects.<br><br>o &nbsp; &nbsp; &nbsp; &nbsp;Perform detailed energy modeling, evaluation of complicated<br>building systems, and life-cycle-cost analysis;<br>
<br>o &nbsp; &nbsp; &nbsp; &nbsp;Provide clear and well-written memorandums, and reports to<br>various clients (building owners, architects, engineers) regarding<br>project specific energy performance and modeling results;<br><br>o &nbsp; &nbsp; &nbsp; &nbsp;Conduct quality assurance reviews to ensure engineering quality<br>
and accurate technical content of project-related documents;<br><br>o &nbsp; &nbsp; &nbsp; &nbsp;Meet / contact clients as appropriate to discuss energy<br>analysis methods, results and recommendations;<br><br>o &nbsp; &nbsp; &nbsp; &nbsp;Prepare analyses, calculations and reports to support<br>
energy-related LEED components;<br><br>o &nbsp; &nbsp; &nbsp; &nbsp;The building simulation engineer will be expected to become a<br>LEED Accredited Professional if not already, and to remain current on<br>issues related to sustainable and green building design, US Green<br>
Building activities, and the various versions of the LEED Green Building<br>Rating System.<br><br>o &nbsp; &nbsp; &nbsp; &nbsp;The building simulation engineer will also be expected to<br>assist in the development and implementation of an internal<br>
sustainability and green building training curriculum for the firm as a<br>whole.<br><br><br><br>Qualifications:<br><br><br><br>* &nbsp; &nbsp; &nbsp;Must have a Bachelor&#39;s or Master&#39;s Degree in Architecture/<br>Engineering.<br>
<br>* &nbsp; &nbsp;Expertise in complex building mechanical systems and<br>state-of-the-art energy efficiency technologies/ applications;<br><br>* &nbsp; &nbsp;2-5 yrs energy modeling experience with DOE-2(eQUEST), IES Virtual<br>Environment, TRNSYS, E-Plus or other detailed hourly simulation;<br>
<br>* &nbsp; &nbsp; &nbsp; Demonstrated experience with additional simulation software<br>programs such as Ecotect, Radiance and/or computational fluid dynamic<br>software. BIM experience preferable (Revit Digital Projects or 3D<br>modeling programs)<br>
* &nbsp; &nbsp; &nbsp; Demonstrated knowledge of sustainable and green building design<br>and/or construction. Experience in designing/evaluating state-of-the-art<br>sustainable design technologies for commercial new construction that<br>
might include: natural ventilation, mixed-mode ventilation, solar<br>cooling, etc.<br>* &nbsp; &nbsp; &nbsp; Preferred to be a licensed architect or professional engineer or<br>approaching end of licensing process.<br>* &nbsp; &nbsp; &nbsp; 2 or more years of increasing responsibility in all phases of<br>
design and technical architecture and/or engineering.<br>* &nbsp; &nbsp; &nbsp; Demonstrated knowledge and use of the USGBC&#39;s LEED Green<br>Building Rating System (NC, EB, CI, etc) and/or other green building<br>rating systems. Preferred to be LEED Accredited.<br>
* &nbsp; &nbsp; &nbsp; Demonstrated ability to perform independent research on<br>environmentally preferred alternative materials and strategies for<br>building design, construction and operation.<br>* &nbsp; &nbsp; &nbsp; Excellent written and verbal communication skills and commitment<br>
to work within the integrated design team structure.<br><br><br><br><br><br>Please fax or e-mail resume/coverletter in MS Word or Adobe pdf format<br>to:<br><br><br><br>Patrick Wilkinson, B.Sc. ENG, LEED(r) AP<br>Advanced Technology Group<br>
<br><br>14130 Riverside Drive Suite 201<br>Sherman Oaks, CA 91423<br>p: &nbsp; (818) 377-8220 ext. 240<br>f: &nbsp; &nbsp;(818) 377-8230<br><br><br><br><br><br><br><br><br><br><br><br><br><br>This e-mail message, including any attachments, is for the sole use of<br>
the intended recipient(s) and may contain confidential and privileged<br>information. Any unauthorized review, use, disclosure, or distribution<br>is prohibited. If you are not the intended recipient, please contact the<br>
sender by reply e-mail and destroy all copies of the original message<br><br><br><br>&nbsp;.<br><br><br><br>-------------- next part --------------<br>An HTML attachment was scrubbed...<br>URL: &lt;<a href="http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/19383890/attachment-0001.htm" target="_blank">http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/19383890/attachment-0001.htm</a>&gt;<br>
-------------- next part --------------<br>A non-text attachment was scrubbed...<br>Name: not available<br>Type: image/jpeg<br>Size: 1400 bytes<br>Desc: image001.jpg<br>URL: &lt;<a href="http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/19383890/attachment-0002.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/19383890/attachment-0002.jpeg</a>&gt;<br>
-------------- next part --------------<br>A non-text attachment was scrubbed...<br>Name: not available<br>Type: image/jpeg<br>Size: 1658 bytes<br>Desc: image002.jpg<br>URL: &lt;<a href="http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/19383890/attachment-0003.jpeg" target="_blank">http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081104/19383890/attachment-0003.jpeg</a>&gt;<br>
<br>------------------------------<br><br>_______________________________________________<br>Bldg-sim mailing list<br><a href="mailto:Bldg-sim@lists.onebuilding.org">Bldg-sim@lists.onebuilding.org</a><br><a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
<br><br>End of Bldg-sim Digest, Vol 12, Issue 5<br>***************************************<br></blockquote></div><br>