color=#0000ff size=2>I can attest first hand to having witnessed ERV systems 
operating in a "FLOAT" mode that were using chilled water for cooling on a 
50-degree day because heat recovery increased SAT to ~67F and they then 
proceeded to cool SA back down to 55F.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=640503816-28102008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=640503816-28102008><FONT face=Arial 
color=#0000ff size=2>I believe equest folks made the ERV default "FLOAT" so that 
people would at least stop and think about the fact that an improperly 
designed ERV system will actually increase energy use.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=640503816-28102008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=640503816-28102008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=640503816-28102008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=640503816-28102008><FONT face=Arial 
color=#0000ff size=2>Mike</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=640503816-28102008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=640503816-28102008>
<DIV align=left><FONT face="Arial Black" size=2>Michael Tillou, PE, 
LEED</FONT></DIV>
<DIV align=left><FONT face="Arial Black" size=2>Tillou Engineering, 
LLC</FONT></DIV>
<DIV align=left><FONT face="Arial Black" 
size=1></FONT> </DIV></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Brian 
Fountain<BR><B>Sent:</B> Tuesday, October 28, 2008 11:29 AM<BR><B>To:</B> 
Xiaobing Liu; bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> Re: [Bldg-sim] 
ERV with increasing cooling load<BR></FONT><BR></DIV>
<DIV></DIV>The eQUEST default for temperature control is FLOAT whereby the heat 
recovery device aims to maximize heat recovery for all ambient conditions.  
This leads to heat recovery when economizer free cooling would be 
preferable.<BR><BR>With "Mixed Air Reset", the device is modulated, either by 
bypassing air or by modulating the heat exchanger (slowing the wheel), to 
maintain the mixed air temperature at the mixed air temperature setpoint -- 
which is typically the supply air temperature setpoint less a couple of degrees 
for fan pick-up.  This is definitely a common building automation system 
strategy.<BR><BR>Xiaobing Liu wrote: 
<BLOCKQUOTE 
cite=mid:4356BBD2A1FD7547B10BB742FFAD4B20074C24D4@lsbsrvr04.lsb-okc.com 
type="cite">
  <META content="MSHTML 6.00.2900.3354" name=GENERATOR>
  <DIV><SPAN class=543091215-28102008><FONT face=Arial color=#0000ff size=2>I'm 
  wondering whether the Mixed Air Reset will really be implemented in the 
  real system? How big difference the air temperature control strategy will 
  make?</FONT></SPAN></DIV>
  <DIV><SPAN class=543091215-28102008></SPAN> </DIV>
  <DIV><SPAN class=543091215-28102008><FONT face=Arial color=#0000ff 
  size=2>Xiaobing</FONT></SPAN></DIV>
  <BLOCKQUOTE>
    <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
    size=2>-----Original Message-----<BR><B>From:</B> <A 
    class=moz-txt-link-abbreviated 
    href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</A> 
    [<A class=moz-txt-link-freetext 
    href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</A>]<B>On 
    Behalf Of </B>eric wang<BR><B>Sent:</B> Tuesday, October 28, 2008 10:06 
    AM<BR><B>To:</B> <A class=moz-txt-link-abbreviated 
    href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</A>; 
    Kingsley, Michael L.<BR><B>Subject:</B> Re: [Bldg-sim] ERV with increasing 
    cooling load<BR><BR></FONT></DIV>
    <TABLE cellSpacing=0 cellPadding=0 border=0>
      <TBODY>
      <TR>
        <TD vAlign=top>
          <DIV id=yiv1804779766>
          <DIV>Hi,</DIV>
          <DIV> </DIV>
          <DIV>Thanks a lot for all your replies. I changed the following 
          settings and solved the problem.</DIV>
          <DIV> </DIV>
          <DIV>Control Sequences Operation: when minimum OA </DIV>
          <DIV>Make air temperature cotrol: Mixed Air Reset</DIV>
          <DIV> </DIV>
          <DIV>Best,</DIV>
          <DIV> </DIV>
          <DIV>Shaojie<BR><BR>--- On <B>Tue, 10/28/08, Kingsley, Michael L. 
          <I><A class=moz-txt-link-rfc2396E 
          href="mailto:MICHAEL.L.KINGSLEY@saic.com"><MICHAEL.L.KINGSLEY@saic.com></A></I></B> 
          wrote:<BR></DIV>
          <BLOCKQUOTE 
          style="PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: rgb(16,16,255) 2px solid">From: 
            Kingsley, Michael L. <A class=moz-txt-link-rfc2396E 
            href="mailto:MICHAEL.L.KINGSLEY@saic.com"><MICHAEL.L.KINGSLEY@saic.com></A><BR>Subject: 
            RE: [Bldg-sim] ERV with increasing cooling load<BR>To: <A 
            class=moz-txt-link-abbreviated 
            href="mailto:shaojieworld2006@yahoo.com">shaojieworld2006@yahoo.com</A>, 
            <A class=moz-txt-link-abbreviated 
            href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</A><BR>Date: 
            Tuesday, October 28, 2008, 8:09 AM<BR><BR><PRE>Shaojie,

Check to make sure that you are not recovering heat during hours that
you can be using the economizer.  Choose the Control Sequences:
Operation: "When Minimum OA" so that the heat recovery device will
only
operate when you cannot benefit from free cooling.

Mike

Michael L. Kingsley, PhD, PE, LEED AP
Senior Engineer/ Project Manager
SAIC
6390 Fly Road
East Syracuse, New York 13057
Phone:  (315) 437-1869  x205
Cell:     (315) 373-4081
Fax:     (315) 437-1866
Email:  <A class=moz-txt-link-abbreviated href="mailto:kingsleym@saic.com">kingsleym@saic.com</A>

-----Original Message-----
From: <A class=moz-txt-link-abbreviated href="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</A>
[<A class=moz-txt-link-freetext href="mailto:bldg-sim-bounces@lists.onebuilding.org">mailto:bldg-sim-bounces@lists.onebuilding.org</A>] On Behalf Of eric wang
Sent: Monday, October 27, 2008 11:32 PM
To: <A class=moz-txt-link-abbreviated href="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</A>
Subject: [Bldg-sim] ERV with increasing cooling load

Hi,
 
I model a PSZ system with exhaust air heat recovery. I set the static
pressures of supply/exhaust fans as zero in ERV tab. Therefore, the fan
energy is the same with or without ERV. However, there is an increasing
cooling load in the cooling model. I changed the hourly report and
didn't find the reason. Any suggestions are highly appreciated.
 
Thanks
 
Shaojie 

            </PRE></BLOCKQUOTE></DIV></TD></TR></TBODY></TABLE><BR></BLOCKQUOTE><PRE wrap=""><HR width="90%" SIZE=4>
_______________________________________________
Bldg-sim mailing list
<A class=moz-txt-link-freetext href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A>
To unsubscribe from this mailing list send  a blank message to <A class=moz-txt-link-abbreviated href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A>
  </PRE><PRE wrap=""><HR width="90%" SIZE=4>
No virus found in this incoming message.
Checked by AVG. 
Version: 7.5.549 / Virus Database: 270.8.4/1752 - Release Date: 10/28/2008 10:04 AM
  </PRE></BLOCKQUOTE><BR></BODY></HTML>