<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META HTTP-EQUIV="Content-Type" CONTENT="text/html; charset=iso-8859-1">


<META content="MSHTML 6.00.2900.3354" name=GENERATOR></HEAD>
<BODY>
<DIV><SPAN class=543091215-28102008><FONT face=Arial color=#0000ff size=2>I'm 
wondering whether the Mixed Air Reset will really be implemented in the 
real system? How big difference the air temperature control strategy will 
make?</FONT></SPAN></DIV>
<DIV><SPAN class=543091215-28102008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=543091215-28102008><FONT face=Arial color=#0000ff 
size=2>Xiaobing</FONT></SPAN></DIV>
<BLOCKQUOTE>
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> 
  bldg-sim-bounces@lists.onebuilding.org 
  [mailto:bldg-sim-bounces@lists.onebuilding.org]<B>On Behalf Of </B>eric 
  wang<BR><B>Sent:</B> Tuesday, October 28, 2008 10:06 AM<BR><B>To:</B> 
  bldg-sim@lists.onebuilding.org; Kingsley, Michael L.<BR><B>Subject:</B> Re: 
  [Bldg-sim] ERV with increasing cooling load<BR><BR></FONT></DIV>
  <TABLE cellSpacing=0 cellPadding=0 border=0>
    <TBODY>
    <TR>
      <TD vAlign=top>
        <DIV id=yiv1804779766>
        <DIV>Hi,</DIV>
        <DIV> </DIV>
        <DIV>Thanks a lot for all your replies. I changed the following settings 
        and solved the problem.</DIV>
        <DIV> </DIV>
        <DIV>Control Sequences Operation: when minimum OA </DIV>
        <DIV>Make air temperature cotrol: Mixed Air Reset</DIV>
        <DIV> </DIV>
        <DIV>Best,</DIV>
        <DIV> </DIV>
        <DIV>Shaojie<BR><BR>--- On <B>Tue, 10/28/08, Kingsley, Michael L. 
        <I><MICHAEL.L.KINGSLEY@saic.com></I></B> wrote:<BR></DIV>
        <BLOCKQUOTE 
        style="PADDING-LEFT: 5px; MARGIN-LEFT: 5px; BORDER-LEFT: rgb(16,16,255) 2px solid">From: 
          Kingsley, Michael L. <MICHAEL.L.KINGSLEY@saic.com><BR>Subject: 
          RE: [Bldg-sim] ERV with increasing cooling load<BR>To: 
          shaojieworld2006@yahoo.com, bldg-sim@lists.onebuilding.org<BR>Date: 
          Tuesday, October 28, 2008, 8:09 AM<BR><BR><PRE>Shaojie,

Check to make sure that you are not recovering heat during hours that
you can be using the economizer.  Choose the Control Sequences:
Operation: "When Minimum OA" so that the heat recovery device will
only
operate when you cannot benefit from free cooling.

Mike

Michael L. Kingsley, PhD, PE, LEED AP
Senior Engineer/ Project Manager
SAIC
6390 Fly Road
East Syracuse, New York 13057
Phone:  (315) 437-1869  x205
Cell:     (315) 373-4081
Fax:     (315) 437-1866
Email:  kingsleym@saic.com

-----Original Message-----
From: bldg-sim-bounces@lists.onebuilding.org
[mailto:bldg-sim-bounces@lists.onebuilding.org] On Behalf Of eric wang
Sent: Monday, October 27, 2008 11:32 PM
To: bldg-sim@lists.onebuilding.org
Subject: [Bldg-sim] ERV with increasing cooling load

Hi,
 
I model a PSZ system with exhaust air heat recovery. I set the static
pressures of supply/exhaust fans as zero in ERV tab. Therefore, the fan
energy is the same with or without ERV. However, there is an increasing
cooling load in the cooling model. I changed the hourly report and
didn't find the reason. Any suggestions are highly appreciated.
 
Thanks
 
Shaojie 

</PRE></BLOCKQUOTE></DIV></TD></TR></TBODY></TABLE><BR></BLOCKQUOTE></BODY></HTML>