color=#0000ff size=2>I believe a cycling type of fan shuts off when the space 
temperature falls below the Throttling Range you assign for the particular mode 
(Heating or Cooling) you are in. For example, a cooling thermostat of 72°F and a 
throttling range of 4°F yields a high limit of 74°F and a low limit of 
70°F.  When you fall within this range, I believe the fan should shut off 
(if you choose the Fan Intermittent mode).There should be no 
airflow.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2>But now I am unsure if ALL SYSTEMS allow fan cycling..I 
believe you can with a fan coil.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2>The other responder is correct in that eQuest deals in 
hourly chunks, and a fan may only be on part of an hour, thus a lower CFM, but 
in reality, the same CFM for only part of the hour.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008>
<DIV align=left>
<DIV align=left><FONT color=#0000ff>John R. Aulbach, PE, CEM</FONT></DIV>
<DIV align=left><FONT face=Arial size=2><EM>Project Manager</EM></FONT></DIV>
<DIV align=left><FONT face=Arial size=2><FONT color=#0000ff>Nexant, 
Inc</FONT>.</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>701 West Kimberly Ave., Suite 
245</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Placentia, CA 92870-6342 
USA</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Phone: 714-524-4402</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>Fax: 714-524-4407</FONT></DIV>
<DIV align=left><FONT face=Arial size=2>email: <A 
title=mailto:jaulbach@nexant.com 
href="mailto:jaulbach@nexant.com">jaulbach@nexant.com</A></FONT></DIV>
<DIV> </DIV></DIV></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=580561218-24092008><FONT face=Arial 
color=#0000ff size=2> </FONT></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Yuvaraj 
Saravanan<BR><B>Sent:</B> Wednesday, September 24, 2008 10:57 AM<BR><B>To:</B> 
equest-users-bounces@lists.onebuilding.org; 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] eQuest - FCU - how 
to make it cycle<BR></FONT><BR></DIV>
<DIV></DIV><!-- Converted from text/rtf format -->
<P><FONT face=Arial size=2>Hi All,</FONT> <BR><FONT face=Arial size=2>Does 
anyone know how to make a FCU cycle ON/OFF based on the zone thermostat setting? 
I tried choosing the "Fan on mode" to be intermittent in the Fan->Flow 
parameters tab. When I make the fan to be intermittent, fan is cycling but the 
supply CFM is no more a constant volume. It is varying the supply CFM. I 
observed this in the hourly report.</FONT></P>
<P><FONT face=Arial size=2>ASHRAE standard 90.1 requires the fan to cycle to 
meet the loads during unoccupied hours. How everybody model this in eQuest when 
you have a FCU system?</FONT></P>
<P><FONT face=Arial size=2>Any suggestions is greatly appreciated.</FONT> </P>
<P><FONT face=Arial size=2>Regards,</FONT> <BR><FONT face=Arial 
size=2>Yuvaraj</FONT> <BR><FONT face=Arial size=2>_</FONT><FONT face=Arial 
color=#000000 size=2>_____________________________________________</FONT> 
<BR><FONT face=Arial color=#000000 size=2>Yuvaraj Saravanan, PE</FONT> <BR><FONT 
face=Arial color=#000000 size=2>Engineer</FONT> </P>
<P><FONT face=Arial color=#000000 size=2>Arup </FONT><BR><FONT face=Arial 
color=#000000 size=2>12777 West Jefferson Boulevard Suite 200</FONT> <BR><FONT 
face=Arial color=#000000 size=2>Los Angeles CA 90066</FONT> <BR><FONT face=Arial 
color=#000000 size=1>tel:    1 310 578 4400</FONT> <BR><FONT 
face=Arial color=#000000 size=1>dir:    1 310 578 4521</FONT> 
<BR><FONT face=Arial color=#000000 size=1>fax:    1 310 577 
7011</FONT> <BR><FONT face=Arial color=#000000 size=1>internal freecall: 
x20521</FONT> <BR><FONT face=Arial color=#000000 
size=1>yuvaraj.saravanan@arup.com</FONT><BR><A 
href="file://www.arup.com"><U></U><U><FONT face=Arial color=#0000ff 
size=2>www.arup.com</FONT></U></A> </P><BR><PRE>____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
</PRE></BODY></HTML>