<div dir="ltr">I have noticed this too.&nbsp; The constant volume exhaust fan merely means that the fan runs constantly, but may not draw air through the space (read the help file on this, it&#39;s more eloquent than I am).<br>
<br>What I have done to remedy this issue using other system types is specify that the system fan operates as a variable volume fan, with the fan curve being linear.&nbsp; This will allow the fan to modulate down to the required exhaust airflow.&nbsp; If you look at the help files for &quot;SUPPLY-KW/FLOW&quot; it shows the fan curves for variable speed fans, cycling fans, discharge, etc.&nbsp; So this is the way that the program models cycling fans already, and you can use it to your advantage with the exhaust airflow piece.<br>
<br>Hope this works!<br><br>--<br>Karen<br><br><br><div class="gmail_quote">On Tue, Sep 23, 2008 at 12:11 PM, Yuvaraj Saravanan <span dir="ltr">&lt;<a href="mailto:Yuvaraj.Saravanan@arup.com">Yuvaraj.Saravanan@arup.com</a>&gt;</span> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">






<div>


<p><font size="2" face="Courier New">Hi All,</font>

<br><font size="2" face="Courier New">I am trying to model a residential unit served by a Fan coil unit (FCU). It has a separate outside air fan and exhaust fan operating 24/7. The fan coil unit is available to operate for all hours but should operate intermittently depending on the room load.</font></p>


<p><font size="2" face="Courier New">I tried modeling this by selecting a 4-pipe FCU and specified the exhaust and outside air at the thermal zone level. I made the FCU to operate intermittently by making the "Fan on mode" to be intermittent. By doing this, what I observed in the hourly report was:</font></p>


<p><font size="2" face="Courier New">1. FCU unit cycles intermittently as intended.</font>

<br><font size="2" face="Courier New">2. Exhaust fan operates continuously (24/7) (with the specified cfm) as intended.</font>

<br><font size="2" face="Courier New">3. However, the outside air cycles per the FCU. </font>

<br><font size="2" face="Courier New">•If the FCU is off, then OA cfm is zero</font>

<br><font size="2" face="Courier New">•If FCU supply air cfm &lt; the OSA cfm specified at the zone level, then hourly OSA cfm matches the FCU supply air cfm •If FCU supply air cfm &gt; the OSA cfm specified at the zone level, then hourly OSA cfm matches the cfm specified at the zone level.</font></p>


<p><font size="2" face="Courier New">As mentioned before, I want my outside air to operate continuously with constant flow-rate. Can anyone suggest me a way to model this system?</font></p>

<p><font size="2" face="Courier New">Thanks in advance for your help!</font>

<br><font size="2" face="Courier New">Regards,</font>

<br><font size="2" face="Courier New">Yuvaraj</font>
</p>
<br>

<p><font size="2" face="Arial">_</font><font size="2" color="#000000" face="Arial">_____________________________________________</font>

<br><font size="2" color="#000000" face="Arial">Yuvaraj Saravanan, PE</font>

<br><font size="2" color="#000000" face="Arial">Engineer</font>
</p>

<p><font size="2" color="#000000" face="Arial">Arup </font>

<br><font size="2" color="#000000" face="Arial">12777 West Jefferson Boulevard Suite 200</font>

<br><font size="2" color="#000000" face="Arial">Los Angeles CA 90066</font>

<br><font size="1" color="#000000" face="Arial">tel:&nbsp;&nbsp;&nbsp; 1 310 578 4400</font>

<br><font size="1" color="#000000" face="Arial">dir:&nbsp;&nbsp;&nbsp; 1 310 578 4521</font>

<br><font size="1" color="#000000" face="Arial">fax:&nbsp;&nbsp;&nbsp; 1 310 577 7011</font>

<br><font size="1" color="#000000" face="Arial">internal freecall: x20521</font>

<br><font size="1" color="#000000" face="Arial"><a href="mailto:yuvaraj.saravanan@arup.com" target="_blank">yuvaraj.saravanan@arup.com</a></font><br>
<a><u></u><u><font size="2" color="#0000ff" face="Arial">www.arup.com</font></u></a>
</p>
<br>

<pre>____________________________________________________________
Electronic mail messages entering and leaving Arup  business
systems are scanned for acceptability of content and viruses
</pre></div>
<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send &nbsp;a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br>
</div>