<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:arial, helvetica, sans-serif;font-size:10pt"><DIV>Hi Paul,</DIV>
<DIV>Hmmm.&nbsp; Those situations do&nbsp;sound complex and tricky.&nbsp; I've only had to deal "plain vanilla" central plants at this point.&nbsp;</DIV>
<DIV>&nbsp;</DIV>
<DIV>My thought/comment would be that it seems valid to use a simple cost for the chw or hw ($/therm etc.) in the DES step 2 models in lieu of modeling&nbsp;a central plant&nbsp;<U><EM>IF</EM></U>&nbsp;&nbsp;&nbsp;that cost is&nbsp;truly reflective of the central plant's efficiency.</DIV>
<DIV>&nbsp;</DIV>
<DIV>In the cases you describe below, it sounds like there may be a disconnect between cost and efficiency.&nbsp; Sounds like you would need to&nbsp;model a central plant in&nbsp;Step 2 that is reflective of the central plants efficiency.&nbsp; You could&nbsp;ignore any unusual methods (burnt trash&nbsp;etc) in the model.&nbsp;&nbsp;Then&nbsp;you could&nbsp;calc the dollar savings by hand afterward and deduct that&nbsp;via the exceptional calc or renewable energy savings on the EA cr 1 template.&nbsp; This seems like it would meet&nbsp;the requirement to reflect the actual efficiency of&nbsp;your central plant but still give you credit for the dollar savings&nbsp;associated with burnt trash or other energy saving or renewable measures.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Before you go through a lot of work though, it may be worth your time&nbsp;doing a CIR or calling LEED to determine an acceptable approach.</DIV>
<DIV>&nbsp;</DIV>
<DIV>----- Original Message ----<BR>From: Paul Riemer &lt;Paul.Riemer@dunhameng.com&gt;<BR>To: Julia Beabout &lt;juliabeabout@yahoo.com&gt;; "bldg-sim@lists.onebuilding.org" &lt;bldg-sim@lists.onebuilding.org&gt;<BR>Sent: Friday, September 12, 2008 10:51:45 AM<BR>Subject: RE: [Bldg-sim] District Thermal System<BR><BR>
<STYLE type=text/css>DIV { MARGIN:0px;} </STYLE>
</DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif">
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif">
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>Julia,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008></SPAN><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>I have been a bit&nbsp;up in arms about how this document will apply to&nbsp;s</FONT></SPAN><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>ome&nbsp;of the&nbsp;DESs&nbsp;serving our client community who are&nbsp;perhaps&nbsp;a bit unique in doing things like:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>- billing buildings only on&nbsp;peak demand (not&nbsp;consumption)</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>- generating chilled water from waste heat outside of CHP situation</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>- generating heat&nbsp;by burning some rather cheap things including garbage</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>&nbsp;(if they get paid to take it and burn it,&nbsp;probably best to just count it as free and not press the luck on&nbsp;a negative fuel cost) </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN class=632081614-12092008><FONT size=+0><SPAN class=632081614-12092008>I have been assuming that the Step 2 template would have to include the proposed DES energy consumption documented in&nbsp;primary sources like electricity and natural gas and the corresponding costs extended from those specific consumption numbers.&nbsp;</SPAN></FONT></SPAN>T<SPAN class=632081614-12092008>hat could&nbsp;get&nbsp;pretty complicated&nbsp;for some of the above scenarios.</SPAN></FONT></FONT></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN class=632081614-12092008></SPAN></FONT></FONT></FONT>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>Your tact looks considerably simpler and could remain abstracted&nbsp;above my&nbsp;questions about detailed fuel sources and detailed utility rates.</FONT></SPAN></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2></FONT></SPAN></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2>Thank you all for your comments so far and please do share if you&nbsp;have a Step 2 approach reviewed.</FONT></SPAN></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008></SPAN></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008>Paul Riemer</SPAN></FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008></SPAN></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008></SPAN></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008></SPAN></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=632081614-12092008><FONT face=Arial color=#0000ff size=2><SPAN class=632081614-12092008></SPAN></FONT></SPAN>&nbsp;</DIV><BR>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> Julia Beabout [mailto:juliabeabout@yahoo.com] <BR><B>Sent:</B> Wednesday, September 10, 2008 10:57 AM<BR><B>To:</B> Paul Riemer; Karen Walkerman; Eric Youngson<BR><B>Cc:</B> bldg-sim@lists.onebuilding.org; bldg-rate@lists.onebuilding.org<BR><B>Subject:</B> Re: [Bldg-sim] District Thermal System<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif">
<DIV>Let me reiterate, that&nbsp;I have not submitted my model yet to LEED.&nbsp; So, I don't have any feedback from them regarding the&nbsp;validity of my take on things. </DIV>
<DIV>&nbsp;</DIV>
<DIV>In aswer to your question: Yes and no. :)</DIV>
<DIV>&nbsp;</DIV>
<DIV>The way I see things:</DIV>
<DIV>&nbsp;</DIV>
<DIV>For&nbsp;Step 1, the DES document talks about using a "market" rate for the DES utilities.&nbsp; So, my take on that is that if there is a general prevailing rate for these utilities in your area, that should be used in Step 1.&nbsp; Where as the intent for Step 2&nbsp;seems to be to use info (i.e. a rate or other method as discussed below) that reflects your plant's actual efficiency.&nbsp; </DIV>
<DIV>&nbsp;</DIV>
<DIV>In theory, for Step 1, the rate shouldn't matter since&nbsp;it's effect is neutralized by using it in both the proposed and baseline models.&nbsp; However, I'm thinking there may be a situation where if you have a really&nbsp;stellar&nbsp;(i.e. low CHW, steam, HW rate) or poor (i.e. high CHW, steam, or HW rate) performing proposed central plant and you use that rate in Step 1 in both the proposed and baseline models, it may impact your results in Step 1.&nbsp;&nbsp;Although, again, in theory, it shouldn't matter.&nbsp; But, as I do more&nbsp;models,&nbsp;it seems that the&nbsp;relationship between $ saved and the % saved is not&nbsp;linear - i.e.&nbsp;as you demonstrate more and more savings, it seems easier to get to the next LEED increment with smaller amounts of deltas -&nbsp;and vice versa&nbsp;(which to some degree makes sense since dividing by smaller numbers).&nbsp;&nbsp;But, I'm thinking&nbsp;this effect could impact your savings in Step 1
 and thus your ability to even get to Step 2.&nbsp; But, maybe I'm off base here.&nbsp; I'm speculating at this point in that regard.</DIV>
<DIV>&nbsp;</DIV>
<DIV>That being said, it does seem&nbsp;that the rate you used in Step 1 could be the same rate used in Step 2 for your proposed building and thus, the performance shown&nbsp;for the proposed building models on the LEED templates&nbsp;could be the same in both Steps.&nbsp;</DIV>
<DIV>&nbsp;</DIV>
<DIV>Another idea&nbsp;&nbsp;I had was that the&nbsp;DES rate could be used to back calculate the overall COP/efficiency of your plant.&nbsp; And then use those figures in your proposed model for Step 2.&nbsp; It may be easier to adjust those rates for distribution losses etc.&nbsp; All this assumes that your DES rate is based on metered data&nbsp;and actual production costs.&nbsp; It seems LEED&nbsp;may want some demonstration of this.&nbsp;&nbsp;</DIV>
<DIV></DIV>
<DIV>&nbsp;</DIV>
<DIV>----- Original Message ----<BR>From: Paul Riemer &lt;Paul.Riemer@dunhameng.com&gt;<BR>To: Julia Beabout &lt;juliabeabout@yahoo.com&gt;; Karen Walkerman &lt;kwalkerman@gmail.com&gt;; Eric Youngson &lt;ericy@pae-engineers.com&gt;<BR>Cc: "bldg-sim@lists.onebuilding.org" &lt;bldg-sim@lists.onebuilding.org&gt;; "bldg-rate@lists.onebuilding.org" &lt;bldg-rate@lists.onebuilding.org&gt;<BR>Sent: Wednesday, September 10, 2008 11:07:16 AM<BR>Subject: RE: [Bldg-sim] District Thermal System<BR><BR>
<STYLE type=text/css>DIV { MARGIN:0px;} </STYLE>
</DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif">
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif">
<DIV dir=ltr align=left><SPAN class=013135614-10092008><FONT face=Arial color=#0000ff size=2>Julia,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=013135614-10092008><FONT face=Arial color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=013135614-10092008><FONT face=Arial color=#0000ff size=2>Thank you for your comments.&nbsp; Please allow me to ask a bit more.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=013135614-10092008></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=013135614-10092008><FONT face=Arial color=#0000ff size=2>Are you stating that&nbsp;Table 1.8.2(b) at the bottom of your Step 2 EAc1 template&nbsp;will have&nbsp;an energy type line item of "hot water", "steam", or "chilled water"?&nbsp; If so, will the numeric energy use value (e.g. 1,234 MBtu) be exactly the same as in Step 1's EAc1 template?&nbsp; Meaning the only differences between the proposed columns&nbsp;of the two submittal templates will be the&nbsp;dollar costs of the DES energy stream and total costs?</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=013135614-10092008></SPAN><SPAN class=013135614-10092008><FONT face=Arial color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=013135614-10092008></SPAN><SPAN class=013135614-10092008><FONT face=Arial color=#0000ff size=2>Paul Riemer</FONT></SPAN></DIV><BR>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org [mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Julia Beabout<BR><B>Sent:</B> Wednesday, September 10, 2008 9:32 AM<BR><B>To:</B> Karen Walkerman; Eric Youngson<BR><B>Cc:</B> bldg-sim@lists.onebuilding.org; bldg-rate@lists.onebuilding.org<BR><B>Subject:</B> Re: [Bldg-sim] District Thermal System<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif">
<DIV>I just finished my first DES project (not submitted yet, though)&nbsp;and have a couple more in the works.&nbsp;&nbsp;</DIV>
<DIV>&nbsp;</DIV>
<DIV>I agree with the interpretations below especially with respect to Step 2 and the utilization of the DES purchased rates&nbsp;as an acceptable means of reflecting the prposed/actual central plant's efficiency in the proposed energy model.&nbsp;&nbsp;Although, the DES purchased rates should reflect/be adjusted&nbsp;for the&nbsp;items Karen mentions.&nbsp; Additionally,&nbsp;I'd recommend confirming that the&nbsp;DES rate includes all the&nbsp;central plant's bits and pieces.&nbsp;&nbsp;The maintenance costs should also be extracted from the DES rate if possible.&nbsp; (The DES document seems&nbsp;to clarify that the maintenance costs do not need to be included.&nbsp; So, if those can be extracted that will be more of an apples to apples comparison with the baseline model and work in your proposed model's favor).&nbsp; </DIV>
<DIV>&nbsp;</DIV>
<DIV>In my estimation, the above method provides the most expedient, realistic&nbsp;and accurate method of determining the central plant's efficiency.&nbsp; The trick is that that info is not always available - especially in a campus situation.&nbsp; So, in that case you may need to use one of the other methods of modeling the central plant discussed in the DES document: other metering data, modeling of the central plant equipment, etc.&nbsp; However,&nbsp;sometimes even this data can&nbsp;be hard to come by and/or is not within the project's ability or budget to determine or model.&nbsp; So, in that type of situation, the&nbsp;default central plant efficiency values provided in the DES document could be used.&nbsp; </DIV>
<DIV>&nbsp;</DIV>
<DIV>&nbsp;</DIV>
<DIV>&nbsp;</DIV>
<DIV></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif"><BR>
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif">----- Original Message ----<BR>From: Karen Walkerman &lt;kwalkerman@gmail.com&gt;<BR>To: Eric Youngson &lt;ericy@pae-engineers.com&gt;<BR>Cc: bldg-sim@lists.onebuilding.org; bldg-rate@lists.onebuilding.org<BR>Sent: Tuesday, September 9, 2008 3:08:28 PM<BR>Subject: Re: [Bldg-sim] District Thermal System<BR><BR>
<DIV dir=ltr>I am also in the middle of a DES project at the moment.&nbsp; The way that I interpreted Step 1 and 2 is as follows:<BR><BR>Step 1:<BR><BR>Baseline: all downstream (on-site) equipment, envelope components, etc, as in Appendix G.&nbsp; heating and cooling is purchased from a DES system.<BR>Proposed: all downstream (on-site) equipment, envelope components, etc, as designed.&nbsp; Heating and cooling is purchased from a DES system.<BR><BR>Step 2:<BR><BR>Baseline: all equipment is modeled as on-site.&nbsp; Boilers and Chillers are to be modeled as designed in Appendix G.&nbsp; Utility rates are to be local utility rates<BR>Proposed: building is to be modeled as built.&nbsp; Heating and cooling is purchased from a DES system, energy costs must take into account DES production and transmission losses.<BR><BR>In my opinion, the vocabulary in Table 1 is confusing, but the guidelines on pages 5 and 6 seem pretty clear.&nbsp; Am I on the same page as
 everyone else here?<BR><BR>Thanks,<BR><BR>--<BR>Karen<BR><BR></DIV></DIV></DIV></DIV></BLOCKQUOTE></DIV></DIV></DIV></BLOCKQUOTE></DIV></DIV></div></body></html>