I have submitted two projects for LEED C&S.  In both cases the
budget case was assigned the PSZ-AC system.  I used one system per
zone regardless of how the proposed model systems were assigned
zones.  The proposed designs both had multiple zone systems. 
The LEED reviewer agreed with how I modelled the baseline case.<br><br>
At 17:32 2008-09-04, Eric Youngson wrote:<br>
<blockquote type=cite class=cite cite="">Content-class:
urn:content-classes:message<br>
Content-Type: multipart/related;
type="multipart/alternative";<br>
<x-tab>        </x-tab>
boundary="----_=_NextPart_001_01C90ED5.C6E195CC"<br><br>
Sim List,<br>
               
ASHRAE system 3 is, Packaged Single Zone Air Conditioner (PSZ-AC). The
description of PSZ-AC says, “Packaged rooftop air conditioner”. I assume
that this means a single unit serving multiple zones. This doesn’t seem
to make sense since the name contains the phrase ‘single zone’.<br>
               
I have a building with baseline system 3, PSZ-AC and I’m not sure how to
apply this system. The proposed building has a variety of systems. Should
I have a system per zone or a single unit for the building?<br>
 <br>
Thanks<br>
 <br>
<a href="http://www.pae-engineers.com/">
<img src="cid:7.1.0.9.2.20080908111603.034dd1e0@cr-jay.ca.2" width=62 height=62 alt="http://www.pae-engineers.com/images/PAElogobug.gif">
</a><br>
<b>Eric Youngson <br>
PAE Consulting Engineers, Inc.</b> <br>
503.226.2921 Main<br>
503.542.0567 Direct<br>
503.226.2930 Fax<br>
ericy@pae-engineers.com <br>
Mechanical <br>
808 SW Third Avenue - Suite 300<br>
Portland, OR 97204-2426<br>
<a href="http://www.pae-engineers.com/" eudora="autourl">
www.pae-engineers.com</a> <br>
<div align="center">inspire  interpret  integrate <br>
</div>
<br><br>
<br><br>
<br><br>
<br>
_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to
BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<br><br>
<br><br>
__________ Information from ESET NOD32 Antivirus, version of virus
signature database 3416 (20080904) __________<br><br>
The message was checked by ESET NOD32 Antivirus.<br><br>
<a href="http://www.eset.com/" eudora="autourl">http://www.eset.com</a>
</blockquote>
<x-sigsep><p></x-sigsep>
<br>
Chris Jones, P.Eng.<br>
14 Oneida Avenue<br>
Toronto, ON M5J2E3<br>
Tel. 416 203-7465<br>
Fax. 416 946-1005</body>
</html>