<DIV>Mike and others;</DIV>
<DIV>The concept in the exception&nbsp;is that&nbsp;for a renovation project, the Standard&nbsp;does NOT&nbsp;REQUIRE replacement of&nbsp;existing crappy&nbsp;windows, for example. So&nbsp;the exception (f)&nbsp;gives credit for&nbsp;an improvement to something that&nbsp;could have&nbsp;been left in the same crappy condition and met the Standard. Even though, once you commit to changing them, the Standard&nbsp;indeed requires&nbsp;those new windows to&nbsp;have the&nbsp;minimum performance.&nbsp;Contradiction resolved in my mind. </DIV>
<DIV>&nbsp;</DIV>
<DIV>Fred</DIV>
<DIV><BR>&gt;&gt;&gt; "Michael Tillou" &lt;michael.tillou@gmail.com&gt; 8/21/2008 2:41 PM &gt;&gt;&gt;<BR>I am inclined to agree with Amanda on this issue.&nbsp;&nbsp; <BR><BR>Appendix G is a methodology for demonstrating energy performance beyond the<BR>minimum requirements of ASHRAE 90.1.&nbsp; If you alter a building envelope<BR>element and want to claim energy savings beyond the minimum performance<BR>requirements of ASHRAE 90.1-2004 then the baseline HAS to be ASHRAE<BR>90.1-2004 minimum performance.&nbsp; Otherwise you are no longer making a<BR>comparison to ASHRAE 90.1-2004.&nbsp; <BR><BR>LEED v2.2 EA-1 credits are based on a comparison to an ASHRAE 90.1-2004<BR>baseline.&nbsp; This fact should supersede the apparent contradiction in Appendix<BR>G that is being discussed.&nbsp; <BR><BR>Regards,<BR><BR>Mike<BR><BR>Michael Tillou, PE, LEED<BR>Tillou Engineering, LLC<BR>Williamstown, MA 01267<BR>P: 413-458-9870 C: 413-652-1087<BR><BR><BR><BR>-----Original Message-----<BR>From: bldg-sim-bounces@lists.onebuilding.org<BR>[mailto:bldg-sim-bounces@lists.onebuilding.org] On Behalf Of James V. Dirkes<BR>II P.E.<BR>Sent: Thursday, August 21, 2008 1:53 PM<BR>To: bldg-sim@lists.onebuilding.org<BR>Subject: Re: [Bldg-sim] LEED modeling requirements for existing buildings<BR><BR>Dear All,<BR><BR>I was looking for something else and found this in a LEED-NC EAc1 update<BR>document that I downloaded, but can no longer find on the USGBC site: <BR><BR>"For existing buildings that are being renovated, the building envelope<BR>design parameters for the Baseline Design should be modeled using the<BR>existing (pre-retrofit) building envelope thermal parameters rather than the<BR>ASHRAE Std. 90.1 prescriptive building envelope requirements for the<BR>specified climate. Any proposed changes to the building envelope (such as<BR>replacing windows or increasing roof insulation) should be modeled in the<BR>Proposed Design."<BR><BR><BR><BR>The Building Performance Team<BR>James V. Dirkes II, P.E., LEED AP<BR>1631 Acacia Drive NW<BR>Grand Rapids, MI 49504<BR>616 450 8653<BR><BR><BR>-----Original Message-----<BR>From: bldg-sim-bounces@lists.onebuilding.org<BR>[mailto:bldg-sim-bounces@lists.onebuilding.org] On Behalf Of Jeff Ross-Bain<BR>Sent: Thursday, August 21, 2008 12:29 PM<BR>To: Amanda Bogner; Mark Sorensen; Carol Gardner<BR>Cc: Eric O'Neill; bldg-sim@lists.onebuilding.org<BR>Subject: Re: [Bldg-sim] Spam:Re:LEEDmodelingrequirements<BR>forexistingbuildings<BR><BR>My interpretation is different. Table G3.1 5(f) says for the building<BR>envelope only: <BR><BR>"...the baseline building design shall reflect conditions PRIOR to any<BR>revisions that are part of the scope of work being evaluated."<BR><BR>So, if I read this right, the baseline reflects the as-is conditions and the<BR>design case reflects the new conditions. Now when there are additions, such<BR>as adding an atrium or more space, then the baseline becomes 90.1 because<BR>there was nothing there before.<BR><BR>Regards,<BR><BR>Jeffrey G. Ross-Bain, PE, LEED<BR>Smith Dalia Architects<BR>621 North Ave NE<BR>Suite C-140<BR>Atlanta, GA, 30308<BR>404-892-2443<BR>www.smithdalia.com <BR><BR>P Build Green...Save Time<BR><BR>-----Original Message-----<BR>From: Amanda Bogner [mailto:amanda@bvm-engineering.com]<BR>Sent: Thursday, August 21, 2008 12:12 PM<BR>To: 'Mark Sorensen'; 'Carol Gardner'; Jeff Ross-Bain<BR>Cc: 'Eric O'Neill'; bldg-sim@lists.onebuilding.org<BR>Subject: RE: [Bldg-sim] Spam:Re: LEEDmodelingrequirements<BR>forexistingbuildings<BR><BR>The way I understand it is as follows:<BR><BR>1.&nbsp; All parameters in basecase and as designed case = existing conditions if<BR>not being altered.&nbsp; <BR>2.&nbsp; If improvements will be made to component X in the as designed case, the<BR>basecase component X = 90.1 requirements.<BR><BR>So, for example, if the envelope is not being altered, set it to existing<BR>conditions in both the basecase and as designed models if the information is<BR>available.&nbsp; Otherwise, you can use 90.1 values in both models.&nbsp; If the<BR>glazing is going to be updated as part of the renovation, the basecase =<BR>90.1 requirements, the as designed case = new glazing.&nbsp; <BR><BR>A similar situation applies to system improvements.&nbsp; For example, if a VFD<BR>is going to be added to the cooling tower fan, the basecase will need to be<BR>modeled as a two-speed fan per the requirements of 90.1, regardless of what<BR>is existing.<BR><BR>Essentially, the existing building basecase becomes a moving target as<BR>energy improvements are considered.&nbsp; <BR><BR>If feel this is incorrect, please let me know.<BR><BR>Thanks,<BR>Amanda Bogner<BR>BVM Engineering, Inc.<BR>404.806.2018 x103<BR><BR>-----Original Message-----<BR>From: bldg-sim-bounces@lists.onebuilding.org<BR>[mailto:bldg-sim-bounces@lists.onebuilding.org] On Behalf Of Mark Sorensen<BR>Sent: Thursday, August 21, 2008 10:57 AM<BR>To: 'Carol Gardner'; 'Jeff Ross-Bain'<BR>Cc: 'Eric O'Neill'; bldg-sim@lists.onebuilding.org<BR>Subject: Re: [Bldg-sim] Spam:Re: LEEDmodelingrequirements<BR>forexistingbuildings<BR><BR>Table G3.1 item 5(f) indicates that you would use the U-factors and SHGC<BR>from the existing building envelope prior to any revisions that are part of<BR>the scope of work being evaluated. Someone please straighten me out on this<BR>because I'm having a hard time understanding how it could be interpreted<BR>that you need to use the minimum U-factors and SHGC from the tables in<BR>Section 5 for the baseline building regardless of whether those envelope<BR>components are being altered or not.<BR><BR>Regards,<BR><BR>Mark Sorensen CEM<BR>Diversified Energy Services<BR>5890 E. Pontaluna Rd.<BR>Fruitport, MI 49415<BR><BR><BR>-----Original Message-----<BR>From: bldg-sim-bounces@lists.onebuilding.org<BR>[mailto:bldg-sim-bounces@lists.onebuilding.org] On Behalf Of Carol Gardner<BR>Sent: Thursday, August 21, 2008 11:33 AM<BR>To: Jeff Ross-Bain<BR>Cc: Eric O'Neill; bldg-sim@lists.onebuilding.org<BR>Subject: Re: [Bldg-sim] Spam:Re: LEED modelingrequirements<BR>forexistingbuildings<BR><BR>I thought that the rotation requirement was gone in any case.<BR>Carol<BR><BR>Jeff Ross-Bain wrote:<BR>&gt;<BR>&gt; I asked the USGBC for an interpretation (not an official CIR) on the <BR>&gt; need for rotating an existing building for modeling purposes and the <BR>&gt; response was that the existing building does in fact need to be<BR>rotated.<BR>&gt;<BR>&gt; This is their response (the "specified analysis" refers to building <BR>&gt; rotation of an existing building):<BR>&gt;<BR>&gt; If the existing building being renovated is pursuing LEED-NC rather <BR>&gt; than LEED-EB, then it would indeed be required to undergo the <BR>&gt; specified analysis. This analysis is used to establish the baseline <BR>&gt; for energy performance using the ASHRAE standard. LEED doesn't have <BR>&gt; any specific exemptions for existing buildings in this requirement, <BR>&gt; but if ASHRAE has some kind of exemption, we will honor that.<BR>&gt;<BR>&gt; Regards,<BR>&gt;<BR>&gt; */Jeffrey G. Ross-Bain, PE, LEED/*<BR>&gt; Smith Dalia Architects<BR>&gt; 621 North Ave NE<BR>&gt; Suite C-140<BR>&gt; Atlanta, GA, 30308<BR>&gt; 404-892-2443<BR>&gt; www.smithdalia.com &lt;<A href="http://www.smithdalia.com">http://www.smithdalia.com</A>&gt;<BR>&gt;<BR>&gt; P Build Green...Save Time<BR>&gt;<BR>&gt;<BR>------------------------------------------------------------------------<BR>&gt;<BR>&gt; *From:* bldg-sim-bounces@lists.onebuilding.org<BR>&gt; [mailto:bldg-sim-bounces@lists.onebuilding.org] *On Behalf Of *Michael<BR><BR>&gt; Tillou<BR>&gt; *Sent:* Thursday, August 21, 2008 9:15 AM<BR>&gt; *To:* 'Jay Keazer'<BR>&gt; *Cc:* 'Eric O'Neill'; bldg-sim@lists.onebuilding.org<BR>&gt; *Subject:* Re: [Bldg-sim] Spam:Re: LEED modeling requirements <BR>&gt; forexistingbuildings<BR>&gt;<BR>&gt; Jay,<BR>&gt;<BR>&gt; It is my understanding that that is the correct interpretation.<BR>&gt;<BR>&gt; However, I don't think Eric's interpretation that the baseline <BR>&gt; rotation requirement does not apply to existing buildings is correct.<BR>&gt; Let me explain why I disagree.<BR>&gt;<BR>&gt; Requirement f in Part 5 of Table 3.1 refers specifically to the <BR>&gt; //baseline building design// (note the italics which signify that a <BR>&gt; phrase or word is defined in Section 3 of the Standard) while <BR>&gt; Requirement a in Part 5 of Table 3.1 refers specifically to the <BR>&gt; //baseline building performance// (again in italics). The //baseline <BR>&gt; building design// is not the same as the //baseline building <BR>&gt; performance// and therefore Requirement f. cannot supercede <BR>&gt; Requirement a in any case.<BR>&gt;<BR>&gt; One last comment about the equal window distribution. ASHRAE 90.1-2004<BR><BR>&gt; Addendum a removes the equal distribution requirement for windows in <BR>&gt; the baseline. If you're working on a LEED project I suggest you <BR>&gt; consider adopting Addendum a to avoid this requirement. USGBC has <BR>&gt; allowed the use of ASHRAE 90.1-2004 addenda. If you do decide to adopt<BR><BR>&gt; Addendum a remember that USGBC requires that you incorporate all the <BR>&gt; changes included in the Addenddum. Addendum a has a total of eight <BR>&gt; changes to Appendix G, most important of which are the changes to the <BR>&gt; calculation of the baseline HVAC system types.<BR>&gt;<BR>&gt; regards,<BR>&gt;<BR>&gt; Mike<BR>&gt;<BR>&gt; Michael Tillou, PE, LEED<BR>&gt;<BR>&gt; Tillou Engineering, LLC<BR>&gt;<BR>&gt; Williamstown, MA 01267<BR>&gt;<BR>&gt; P: 413-458-9870 C: 413-652-1087<BR>&gt;<BR>&gt;<BR>------------------------------------------------------------------------<BR>&gt;<BR>&gt; *From:* bldg-sim-bounces@lists.onebuilding.org<BR>&gt; [mailto:bldg-sim-bounces@lists.onebuilding.org] *On Behalf Of *Jay<BR>Keazer<BR>&gt; *Sent:* Tuesday, August 19, 2008 10:42 AM<BR>&gt; *To:* Eric O'Neill; Mark Sorensen; bldg-sim@lists.onebuilding.org<BR>&gt; *Subject:* Re: [Bldg-sim] Spam:Re: LEED modeling requirements for <BR>&gt; existingbuildings<BR>&gt;<BR>&gt; What about the baseline envelope assemblies? As an example I have an <BR>&gt; existing building where the windows are being replaced and insulation <BR>&gt; is being sprayed on the outside of a built up roof.<BR>&gt;<BR>&gt; In the same column of Table G3.1, requirement (b) states that "Opaque <BR>&gt; assemblies used for /alterations/ shall conform with 5.1.3" and <BR>&gt; requirement (c) states that "The fenestration areas for envelope <BR>&gt; /alterations/ shall reflect the limitations on area, U-factor, and <BR>&gt; SHGC as described in 5.1.3."<BR>&gt;<BR>&gt; 5.1.3 states that "Alterations to the building envelope shall comply <BR>&gt; with the requirements of Section 5 for insulation, air leakage, and <BR>&gt; fenestration *applicable to those specific portions of the building <BR>&gt; that are being altered*."<BR>&gt;<BR>&gt; My interpretation is: because the windows and roof are being altered, <BR>&gt; I have to use the appropriate U-factors and SHGC from the tables for <BR>&gt; the baseline windows and roof. However, the walls are not being <BR>&gt; altered, so I can use the existing construction for the baseline<BR>walls.<BR>&gt;<BR>&gt; Does anybody have a different interpretation?<BR>&gt;<BR>&gt; Thanks!<BR>&gt;<BR>&gt; */Jay Keazer, EI/*<BR>&gt;<BR>&gt; Energy Engineer<BR>&gt;<BR>&gt; TME, Inc.<BR>&gt;<BR>&gt; 2039 N Green Acres Road<BR>&gt;<BR>&gt; Fayetteville, AR 72703<BR>&gt;<BR>&gt; ph 479.521.8634<BR>&gt;<BR>&gt; fax 479.521.1014<BR>&gt;<BR>&gt; _jkeazer@tmecorp.com &lt;mailto:email@tmecorp.com&gt;___<BR>&gt;<BR>&gt; _www.tmecorp.com &lt;<A href="http://www.tmecorp.com/">http://www.tmecorp.com/</A>&gt;_<BR>&gt;<BR>&gt; *From:* bldg-sim-bounces@lists.onebuilding.org<BR>&gt; [mailto:bldg-sim-bounces@lists.onebuilding.org] *On Behalf Of *Eric <BR>&gt; O'Neill<BR>&gt; *Sent:* Thursday, August 14, 2008 3:16 PM<BR>&gt; *To:* Mark Sorensen; bldg-sim@lists.onebuilding.org<BR>&gt; *Subject:* Spam:Re: [Bldg-sim] LEED modeling requirements for existing<BR><BR>&gt; buildings<BR>&gt;<BR>&gt; Mark,<BR>&gt; Under ASHRAE 90.1 Appendix G, Table G3.1, Section 5, "Baseline <BR>&gt; Building Performance" column, requirement (f) (take a breath.) it <BR>&gt; states that "For existing building envelopes, the baseline building <BR>&gt; design shall reflect existing conditions prior to any revisions that <BR>&gt; are part of the scope of work being evaluated". So the rotation <BR>&gt; doesn't apply to you. Also, I interpret that to mean the windows don't<BR><BR>&gt; need to be redistributed either. Hope that helps!<BR>&gt;<BR>&gt; */Eric O'Neill/*<BR>&gt; Mechanical Engineer<BR>&gt; Energy Division - Michaels Engineering<BR>&gt;<BR>&gt; 811 Monitor St. Ste 100<BR>&gt; La Crosse, WI 54603<BR>&gt; v: 608-785-1900 x521<BR>&gt; f: 608-784-2270<BR>&gt; elo@michaelsengineering.com<BR>&gt; <A href="http://www.michaelsengineering.com">http://www.michaelsengineering.com</A><BR>&gt;<BR>&gt; *From:* Mark Sorensen [mailto:DEnergyServices@comcast.net]<BR>&gt; *Sent:* Thursday, August 14, 2008 10:40 AM<BR>&gt; *To:* bldg-sim@lists.onebuilding.org<BR>&gt; *Subject:* [Bldg-sim] LEED modeling requirements for existing<BR>buildings<BR>&gt;<BR>&gt; When modeling an existing building, is required to calculate the <BR>&gt; proposed building window to wall ratio and equally redistribute the <BR>&gt; glass area to the baseline building and prepare models for the four <BR>&gt; rotation exposures? My take is that for a proposed existing building, <BR>&gt; there is not an opportunity to position the building to the most <BR>&gt; advantageous exposure and you could end up being penalized if the <BR>&gt; baseline energy use is averaged for all rotations but I have not been <BR>&gt; able to find any reference in LEED or ASHRAE to support this. I'm not <BR>&gt; sure what to think about equal redistribution of the glass areas.<BR>&gt;<BR>&gt; Mark Sorensen<BR>&gt; Diversified Energy Services<BR>&gt; 5890 E. Pontaluna Rd.<BR>&gt; Fruitport, MI 49415<BR>&gt;<BR>&gt;<BR>------------------------------------------------------------------------<BR>&gt;<BR>&gt; _______________________________________________<BR>&gt; Bldg-sim mailing list<BR>&gt; <A href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</A>-sim-onebuilding.org<BR>&gt; To unsubscribe from this mailing list send&nbsp; a blank message to<BR>BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR>&gt;&nbsp;&nbsp; <BR><BR><BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</A>-sim-onebuilding.org<BR>To unsubscribe from this mailing list send&nbsp; a blank message to<BR>BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR><BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</A>-sim-onebuilding.org<BR>To unsubscribe from this mailing list send&nbsp; a blank message to<BR>BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR><BR><BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</A>-sim-onebuilding.org<BR>To unsubscribe from this mailing list send&nbsp; a blank message to<BR>BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR><BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</A>-sim-onebuilding.org<BR>To unsubscribe from this mailing list send&nbsp; a blank message to<BR>BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR><BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg">http://lists.onebuilding.org/listinfo.cgi/bldg</A>-sim-onebuilding.org<BR>To unsubscribe from this mailing list send&nbsp; a blank message to BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG<BR></DIV></BODY></HTML>