<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML xmlns="http://www.w3.org/TR/REC-html40" xmlns:v = 
"urn:schemas-microsoft-com:vml" xmlns:o = 
"urn:schemas-microsoft-com:office:office" xmlns:w = 
"urn:schemas-microsoft-com:office:word" xmlns:st1 = 
"urn:schemas-microsoft-com:office:smarttags"><HEAD>
<META http-equiv=Content-Type content="text/html; charset=us-ascii">
<META content="MSHTML 6.00.2900.3199" name=GENERATOR><!--[if !mso]>
<STYLE>v\:* {
        BEHAVIOR: url(#default#VML)
}
o\:* {
        BEHAVIOR: url(#default#VML)
}
w\:* {
        BEHAVIOR: url(#default#VML)
}
.shape {
        BEHAVIOR: url(#default#VML)
}
</STYLE>
<![endif]--><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="place"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="PostalCode"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="State"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="City"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="Street"></o:SmartTagType><o:SmartTagType 
namespaceuri="urn:schemas-microsoft-com:office:smarttags" 
name="address"></o:SmartTagType><!--[if !mso]>
<STYLE>st1\:* {
        BEHAVIOR: url(#default#ieooui)
}
</STYLE>
<![endif]-->
<STYLE>@font-face {
        font-family: Tahoma;
}
@font-face {
        font-family: Trebuchet MS;
}
@font-face {
        font-family: Franklin Gothic Demi;
}
@font-face {
        font-family: Calibri;
}
@page Section1 {size: 8.5in 11.0in; margin: 1.0in 1.25in 1.0in 1.25in; }
P.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"
}
LI.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"
}
DIV.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman"
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline
}
A:visited {
        COLOR: blue; TEXT-DECORATION: underline
}
SPAN.MsoHyperlinkFollowed {
        COLOR: blue; TEXT-DECORATION: underline
}
P {
        FONT-SIZE: 12pt; MARGIN-LEFT: 0in; MARGIN-RIGHT: 0in; FONT-FAMILY: "Times New Roman"; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto
}
SPAN.EmailStyle18 {
        COLOR: navy; FONT-FAMILY: Arial; mso-style-type: personal
}
SPAN.EmailStyle19 {
        COLOR: navy; FONT-FAMILY: Arial; mso-style-type: personal-reply
}
DIV.Section1 {
        page: Section1
}
</STYLE>
</HEAD>
<BODY lang=EN-US vLink=blue link=blue>
<DIV dir=ltr align=left><SPAN class=643421223-21082008><FONT face=Arial 
color=#0000ff size=2>Here's a nifty user expression to size baseboards based on 
BTU's per unit area -- in this example 30 BTUs per SF:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=643421223-21082008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=643421223-21082008><SPAN 
class=643421223-21082008><FONT face=Arial><FONT color=#0000ff><FONT 
size=2>#LR("SPACE","AREA")*-30<SPAN 
class=940391323-21082008> </SPAN></FONT></FONT></FONT></SPAN></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=643421223-21082008><SPAN 
class=643421223-21082008><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=940391323-21082008></SPAN></FONT></FONT></FONT></SPAN></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=643421223-21082008><SPAN 
class=643421223-21082008><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=940391323-21082008>Plug this into the 'Baseboards / Capacity' field for 
each zone with baseboards (rightclick to get the context menu, select 'Edit/View 
User Expression', etc.)</SPAN></FONT></FONT></FONT></SPAN></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=643421223-21082008><SPAN 
class=643421223-21082008><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=940391323-21082008></SPAN></FONT></FONT></FONT></SPAN></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=643421223-21082008><SPAN 
class=643421223-21082008><FONT face=Arial><FONT color=#0000ff><FONT size=2><SPAN 
class=940391323-21082008>Brando </SPAN></FONT></FONT></FONT></SPAN></SPAN></DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Robby 
Oylear<BR><B>Sent:</B> Thursday, August 21, 2008 8:54 AM<BR><B>To:</B> 'Andrew 
Craig'; 'James Hansen'; bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> Re: 
[Bldg-sim] Baseboard heaters in VAV system<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV class=Section1>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">I was under the 
impression that eQUEST either doesn’t size baseboards correctly or at all. 
 The few times I’ve had to use baseboards I have had to solve the 
underheated hours by manually sizing the baseboard heaters at the zone 
level.  It’s a pretty tedious process.<o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><o:p> </o:p></SPAN></FONT></P>
<DIV>
<P class=MsoNormal><FONT face="Franklin Gothic Demi" color=#004080 size=3><SPAN 
style="FONT-SIZE: 12pt; COLOR: #004080; FONT-FAMILY: 'Franklin Gothic Demi'">Robby 
Oylear</SPAN></FONT><FONT face="Franklin Gothic Demi" color=#004080 size=2><SPAN 
style="FONT-SIZE: 11pt; COLOR: #004080; FONT-FAMILY: 'Franklin Gothic Demi'"><o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal><EM><I><FONT face=Calibri color=#004080 size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: #004080; FONT-FAMILY: Calibri">Mechanical 
Engineer</SPAN></FONT></I></EM><EM><I><FONT face=Calibri color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Calibri"><o:p></o:p></SPAN></FONT></I></EM></P>
<P class=MsoNormal><FONT face="Times New Roman" color=#004080 size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: #004080">direct: 206.788.4571</SPAN></FONT><FONT 
color=navy><SPAN style="COLOR: navy"><o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face="Times New Roman" color=#004080 size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: #004080">cell: 206.354.2721</SPAN></FONT><FONT 
color=navy><SPAN style="COLOR: navy"><o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal style="MARGIN-BOTTOM: 3pt"><U><FONT face=Arial color=blue 
size=1><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: blue; FONT-FAMILY: Arial">www.</SPAN></FONT></U><FONT 
face=Arial color=navy size=1><SPAN 
style="FONT-SIZE: 8pt; COLOR: navy; FONT-FAMILY: Arial"><A 
title=blocked::http://www.rushingco.com/ href="http://www.rushingco.com"><FONT 
size=1><SPAN style="FONT-SIZE: 7.5pt"><SPAN 
title=blocked::http://www.rushingco.com/>rushingco.com</SPAN></SPAN></FONT></A></SPAN></FONT><FONT 
face=Arial size=1><SPAN 
style="FONT-SIZE: 8pt; FONT-FAMILY: Arial"><o:p></o:p></SPAN></FONT></P></DIV>
<DIV>
<DIV class=MsoNormal style="TEXT-ALIGN: center" align=center><FONT 
face="Times New Roman" size=3><SPAN style="FONT-SIZE: 12pt">
<HR tabIndex=-1 align=center width="100%" SIZE=2>
</SPAN></FONT></DIV>
<P class=MsoNormal><B><FONT face=Tahoma size=2><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">From:</SPAN></FONT></B><FONT 
face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma"> 
bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B><SPAN 
style="FONT-WEIGHT: bold">On Behalf Of </SPAN></B>Andrew Craig<BR><B><SPAN 
style="FONT-WEIGHT: bold">Sent:</SPAN></B> Thursday, August 21, 2008 8:41 
AM<BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> James Hansen; 
bldg-sim@lists.onebuilding.org<BR><B><SPAN 
style="FONT-WEIGHT: bold">Subject:</SPAN></B> Re: [Bldg-sim] Baseboard heaters 
in VAV system</SPAN></FONT><o:p></o:p></P></DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"><o:p> </o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">James---<o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><o:p> </o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">In my opinion, 
baseboards act a little funny in eQUEST.  This is how I’ve made the 
scenario you describe work:  <o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><o:p> </o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">Under the Heating tab 
of your unit (Coil Cap/Control), restore the default in the reheat entry so it 
is blank.  Make sure the Hot Water Loop is still enabled as the zone 
heating source though.  Under the Preheat/Baseboard tab, specify Baseboard 
Source as the Hot Water Loop.  You can change the default entries for the 
baseboards (pressure drop, delta T, valve, etc.)  if applicable.  Then 
for each perimeter zone, go into the heating tab and change the Baseboard 
control to Thermostatic if it isn’t already selected.  I’ve had trouble 
getting the Outdoor Reset selection to work and most of our projects have 
baseboards controlled by thermostats anyway.  You can also enter the 
capacity of the baseboards for each zone or let the system self-size.  This 
should work…if not I’d be happy to look at the inp.<o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><o:p> </o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">Regards,<o:p></o:p></SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN 
style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial"><o:p> </o:p></SPAN></FONT></P>
<DIV>
<P><B><FONT face="Trebuchet MS" color=black size=1><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 7.5pt; COLOR: black; FONT-FAMILY: 'Trebuchet MS'">Andrew 
Craig, EIT,LEED AP</SPAN></FONT></B><B><FONT face="Trebuchet MS" color=#663300 
size=1><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 7.5pt; COLOR: #663300; FONT-FAMILY: 'Trebuchet MS'">/</SPAN></FONT></B><FONT 
face="Trebuchet MS" color=black size=1><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: black; FONT-FAMILY: 'Trebuchet MS'"> Mechanical 
Designer</SPAN></FONT><FONT face="Trebuchet MS" color=navy size=1><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: navy; FONT-FAMILY: 'Trebuchet MS'"> <BR></SPAN></FONT><B><FONT 
face="Trebuchet MS" color=#663300 size=1><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 7.5pt; COLOR: #663300; FONT-FAMILY: 'Trebuchet MS'">INTERFACE</SPAN></FONT></B><FONT 
face="Trebuchet MS" color=#663300 size=1><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: #663300; FONT-FAMILY: 'Trebuchet MS'"> 
ENGINEERING</SPAN></FONT><FONT face="Trebuchet MS" color=navy size=1><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: navy; FONT-FAMILY: 'Trebuchet MS'"> 
<BR></SPAN></FONT><B><FONT face="Trebuchet MS" color=black size=1><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 7.5pt; COLOR: black; FONT-FAMILY: 'Trebuchet MS'">direct</SPAN></FONT></B><FONT 
face="Trebuchet MS" color=black size=1><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: black; FONT-FAMILY: 'Trebuchet MS'"> 
503.382.2696</SPAN></FONT><FONT face="Trebuchet MS" color=navy size=1><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: navy; FONT-FAMILY: 'Trebuchet MS'"> 
</SPAN></FONT><o:p></o:p></P></DIV>
<DIV>
<DIV class=MsoNormal style="TEXT-ALIGN: center" align=center><FONT 
face="Times New Roman" size=3><SPAN style="FONT-SIZE: 12pt">
<HR tabIndex=-1 align=center width="100%" SIZE=2>
</SPAN></FONT></DIV>
<P class=MsoNormal><B><FONT face=Tahoma size=2><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">From:</SPAN></FONT></B><FONT 
face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma"> 
bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B><SPAN 
style="FONT-WEIGHT: bold">On Behalf Of </SPAN></B>James Hansen<BR><B><SPAN 
style="FONT-WEIGHT: bold">Sent:</SPAN></B> Thursday, August 21, 2008 8:18 
AM<BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> 
bldg-sim@lists.onebuilding.org<BR><B><SPAN 
style="FONT-WEIGHT: bold">Subject:</SPAN></B> [Bldg-sim] Baseboard heaters in 
VAV system</SPAN></FONT><o:p></o:p></P></DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"><o:p> </o:p></SPAN></FONT></P>
<DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">I've got a building that cools with 
shutoff VAV boxes and heats with perimeter hydronic baseboard 
heaters.</SPAN></FONT><o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"> <o:p></o:p></SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">When I'm setting up my system, do I 
specify hot water baseboard heaters and leave the Zone Heat Source set to "Not 
Installed", or do I specify a hot water loop for the Zone Heat Source, and 
eQuest knows to apply this to the baseboard heaters and NOT the shutoff VAV 
boxes?</SPAN></FONT><o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"> <o:p></o:p></SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">I currently have the Zone Heat 
Source as "Not Installed", but it appears from my SS-R reports that there are 
hundreds of hours of underheating, so something is not working correctly.  
I've had my hot water loop set to snap, demand, and scheduled, so I think the 
loop is running correctly.</SPAN></FONT><o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"> <o:p></o:p></SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal><FONT face=Arial size=2><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Thanks in 
advance!</SPAN></FONT><o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"> <o:p></o:p></SPAN></FONT></P></DIV>
<P class=MsoNormal><B><FONT face=Arial color=teal size=3><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 12pt; COLOR: teal; FONT-FAMILY: Arial">GHT 
Limited<BR></SPAN></FONT></B><B><FONT face=Arial size=2><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 11pt; FONT-FAMILY: Arial"><U1:PERSONNAME>James 
Hansen</U1:PERSONNAME>, </SPAN></FONT></B><B><FONT face=Arial size=2><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; FONT-FAMILY: Arial">PE, LEED 
AP</SPAN></FONT></B><o:p></o:p></P>
<P class=MsoNormal><B><FONT face=Arial size=2><SPAN 
style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; FONT-FAMILY: Arial">Senior 
Associate</SPAN></FONT></B><o:p></o:p></P>
<P class=MsoNormal><st1:Street w:st="on"><st1:address w:st="on"><FONT face=Arial 
size=1><SPAN style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial">1010 N. Glebe Rd, 
Suite 200</SPAN></FONT></st1:address></st1:Street><o:p></o:p></P>
<P class=MsoNormal><st1:place w:st="on"><st1:City w:st="on"><FONT face=Arial 
size=1><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial">Arlington</SPAN></FONT></st1:City><FONT 
face=Arial size=1><SPAN style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial">, 
<st1:State w:st="on">VA</st1:State>  <st1:PostalCode 
w:st="on">22201-4749</st1:PostalCode></SPAN></FONT></st1:place><o:p></o:p></P>
<P class=MsoNormal><FONT face=Arial size=1><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial">703-338-5754 
(Direct)</SPAN></FONT><o:p></o:p></P>
<P class=MsoNormal><FONT face=Arial size=1><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial">703-243-1200 
(Office)</SPAN></FONT><o:p></o:p></P>
<P class=MsoNormal><FONT face=Arial size=1><SPAN 
style="FONT-SIZE: 7.5pt; FONT-FAMILY: Arial">703-276-1376 
(Fax)</SPAN></FONT><o:p></o:p></P>
<P class=MsoNormal><FONT face=Arial size=2><SPAN 
style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><A 
href="http://www.ghtltd.com/"><FONT size=2><SPAN 
style="FONT-SIZE: 10pt">www.ghtltd.com</SPAN></FONT></A></SPAN></FONT><o:p></o:p></P>
<DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN 
style="FONT-SIZE: 12pt"> <o:p></o:p></SPAN></FONT></P></DIV></DIV><!--[object_id=#ghtltd.com#]-->
<P align=left><FONT size=2><FONT face=Tahoma><FONT color=#0000ff>
<HR>
</FONT></FONT><FONT color=#0000ff><FONT color=#000000><FONT face=Arial>The 
information contained in this communication is confidential, may be privileged, 
and is intended only for the use of the addressee.  It is the property of 
GHT Limited.  Unauthorized use, disclosure or copying of this communication 
or any part thereof is strictly prohibited and may be unlawful.  If you 
have received this communication in error, please notify me immediately by 
return e-mail or by e-mail to </FONT><A href="mailto:ght@ghtltd.com"><FONT 
face=Arial>ght@ghtltd.com</FONT></A><FONT face=Arial>, and destroy this 
communication and all copies thereof, including all attachments.  Thank 
you.</FONT></FONT><FONT face=Tahoma color=#000000></FONT> 
<P></P></FONT></FONT></BODY></HTML>