<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman, new york, times, serif;font-size:10pt"><DIV>I have noted that the number of hours as per the % shown in the BEPS report is always slightly high than the actual. In a situation where you are close to 300 hours or 50 hours as applicable, it is best to check the SS-F reports and calculate the highest number of hours under-cooled or under-heated in any zone&nbsp;for each month.&nbsp;Adding the highest number for undercooled&nbsp;in each month for each&nbsp;zone and the highest number for underheated in each month for each zone will give the total number of unmet hours.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Consider only the highest number. Do not add all hours. That&nbsp;could be even higher than 8760.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Thanks,</DIV>
<DIV>Ruju Rathod.</DIV>
<DIV>Kirksey</DIV>
<DIV><A href="http://www.kirkseygreen.com">www.kirkseygreen.com</A>&nbsp;<BR></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: times new roman, new york, times, serif"><BR>
<DIV style="FONT-SIZE: 13px; FONT-FAMILY: arial, helvetica, sans-serif">----- Original Message ----<BR>From: Jay Keazer &lt;JKeazer@tmecorp.com&gt;<BR>To: Dan Russell &lt;danr@engineeringinc.com&gt;; Brandon Nichols &lt;BrandonN@Hargis.biz&gt;; bldg-sim@lists.onebuilding.org<BR>Sent: Thursday, August 21, 2008 4:15:30 PM<BR>Subject: Re: [Bldg-sim] Spam:Re: LEED NC Submittal Template, Heating/Cooling Hours Loads Not Met<BR><BR>I am not certain, but I think the unmet load hours on the BEPS report is<BR>consistent with the definition in Addendum a.&nbsp; The BEPS report says "Percent<BR>of hours any system zone outside of throttling range."&nbsp; To me this is the<BR>same as "one or more zones" being out of range for a particular hour.&nbsp; <BR><BR>Adding up the unmet load hours of every zone would count a lot of coincident<BR>unmet hours and could get large with a lot of systems (note this is what SS-R<BR>does for multiple zone systems).&nbsp; It could be
 greater than 8760, and I don't<BR>think this is what appendix G is looking for.&nbsp; If a lot of zones are out of<BR>range during an hour (say an exceptionally cold night) that should only count<BR>as 1 hour.<BR><BR>I don't think that the number on the BEPS is for the "worst case zone."&nbsp; I<BR>just checked a SIM file I had open and the BEPS report listed 3.3% unmet load<BR>hours, so 289 hours (actually anywhere from 285-293).&nbsp; Looking through SS-R<BR>for each zone, the worst case had 177 hours under heated + 24 hours under<BR>cooled, so 201 total unmet hours.<BR><BR>I have always gone by the BEPS (i.e. 3.4% or less is good), but have never<BR>known how to find more detailed output regarding how many are cooling vs. how<BR>many are heating.&nbsp; Theoretically I think you could do this with an hourly<BR>report for every zone and some postprocessing, but I don't really want to go<BR>there.&nbsp; Anybody have a more practical
 approach?<BR><BR><BR>Jay Keazer,&nbsp; EI<BR>Energy Engineer<BR>TME, Inc.<BR>2039 N Green Acres Road<BR>Fayetteville, AR&nbsp; 72703<BR>&nbsp;<BR>ph&nbsp;&nbsp; 479.521.8634<BR>fax&nbsp; 479.521.1014<BR><A href="mailto:jkeazer@tmecorp.com" ymailto="mailto:jkeazer@tmecorp.com">jkeazer@tmecorp.com</A><BR><A href="http://www.tmecorp.com/" target=_blank>www.tmecorp.com</A><BR><BR><BR><BR>-----Original Message-----<BR>From: <A href="mailto:bldg-sim-bounces@lists.onebuilding.org" ymailto="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</A><BR>[mailto:<A href="mailto:bldg-sim-bounces@lists.onebuilding.org" ymailto="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</A>] On Behalf Of Dan Russell<BR>Sent: Thursday, August 21, 2008 1:12 PM<BR>To: Brandon Nichols; <A href="mailto:bldg-sim@lists.onebuilding.org"
 ymailto="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</A><BR>Subject: Spam:Re: [Bldg-sim] LEED NC Submittal Template,Heating/Cooling Hours<BR>Loads Not Met<BR><BR>Brandon, I have been on the same page regarding this issue, and have<BR>submitted for successful LEED certifications using those assumptions ...<BR>until I read Addendum a to 90.1-2004, which adds the definition of<BR>"unmet load hour" to Section 3.2.&nbsp; The definition is:<BR><BR>unmet load hour: an hour in which one or more zones is outside of the<BR>thermostat setpoint range.<BR><BR>Unfortunately this seems to clearly indicate the unmet load hour value<BR>asked for refers to all zones at once.&nbsp; <BR><BR>My previous assumptions to only consider the worst-case zone were based<BR>on the example set forth by the USGBC's document titled "Example LEED-NC<BR>v2.1 Energy &amp; Atmosphere Credit 1 Submittal", which I referenced back<BR>when I did my first LEED
 submittal in 2005.&nbsp; This document is still<BR>available from their server at the following address:<BR><BR><A href="http://www.usgbc.org/ShowFile.aspx?DocumentID=2423" target=_blank>http://www.usgbc.org/ShowFile.aspx?DocumentID=2423</A><BR><BR>This document uses the following paragraph to demonstrate compliance<BR>with the unmet load hour requirement:<BR><BR>"The worst-case zone in the budget case is a North classroom. This zone<BR>is under-heated 40 hours out of the year in the Energy Cost Budget case<BR>and 0 hours per year in the Design Energy Cost case. This is within the<BR>50 hour per year limit required by ASHRAE 90.1-1999."<BR><BR>Now, if Addendum a were not used in any part as basis for LEED submittal<BR>one could possibly argue using the quoted precedent above.&nbsp; Granted, the<BR>above precedent applied to the 1999 version of 90.1 and the 2.1 version<BR>of LEED, but it seems to reasonable that the implications made there<BR>should
 carry over until otherwise directed (as in Addendum a).<BR>Furthermore, it is my opinion that 90.1-2004 (not including addendums)<BR>does not clearly resolve the issue.&nbsp; The ASHRAE technical committee must<BR>have agreed, hence the inclusion of the new definition for "unmet load<BR>hour" in Addendum a.<BR><BR>So, if Addendum a is not used, there may be a possibility to consider<BR>unmet load hour only on a worst-zone basis.&nbsp; However, if Addendum a is<BR>used it seems clear that the unmet load hour applies to all zones at<BR>once.<BR><BR>Certainly larger project simulations with multiple zones will suffer<BR>from this added definition.<BR><BR>Thanks,<BR><BR>Dan Russell, EIT <BR><BR><BR><BR><BR>-----Original Message-----<BR>From: <A href="mailto:bldg-sim-bounces@lists.onebuilding.org" ymailto="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</A><BR>[mailto:<A
 href="mailto:bldg-sim-bounces@lists.onebuilding.org" ymailto="mailto:bldg-sim-bounces@lists.onebuilding.org">bldg-sim-bounces@lists.onebuilding.org</A>] On Behalf Of Brandon<BR>Nichols<BR>Sent: Thursday, August 21, 2008 11:22 AM<BR>To: <A href="mailto:bldg-sim@lists.onebuilding.org" ymailto="mailto:bldg-sim@lists.onebuilding.org">bldg-sim@lists.onebuilding.org</A><BR>Subject: [Bldg-sim] LEED NC Submittal Template,Heating/Cooling Hours<BR>Loads Not Met<BR><BR><BR>All,<BR><BR>"Table 1.3 -- Advisory Messages" of the LEED NC Submittal Template<BR>requests "number of hours heating loads not met" and "number of hours<BR>cooling loads not met".&nbsp; We've taken a vote here in the office, and its<BR>2-0 in favor of reporting the worst case zone as shown on the BEPS<BR>report.<BR><BR>But we have some lingering doubts... can anyone say definitively what<BR>numbers are being asked to for here?&nbsp; our runner-up in the voting was<BR>the total of all zone hours
 out of throttling range -- however this<BR>could easily exceed the limit of 300 hours on a large project with many<BR>zones.&nbsp; <BR><BR>As 300 hours is less than 5% (3.4% actually) of 8760, we think that the<BR>300 hours is "per zone", not a total limit for the entire project.&nbsp; <BR><BR>Comments appreciated....<BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To unsubscribe from this mailing list send&nbsp; a blank message to<BR><A href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" ymailto="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org"
 target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To unsubscribe from this mailing list send&nbsp; a blank message to<BR><A href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" ymailto="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To unsubscribe from this mailing list send&nbsp; a blank message to <A href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" ymailto="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR></DIV></DIV></div><br>