<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML xmlns="http://www.w3.org/TR/REC-html40" xmlns:v = 
"urn:schemas-microsoft-com:vml" xmlns:o = 
"urn:schemas-microsoft-com:office:office" xmlns:w = 
"urn:schemas-microsoft-com:office:word" xmlns:x = 
"urn:schemas-microsoft-com:office:excel" xmlns:p = 
"urn:schemas-microsoft-com:office:powerpoint" xmlns:a = 
"urn:schemas-microsoft-com:office:access" xmlns:dt = 
"uuid:C2F41010-65B3-11d1-A29F-00AA00C14882" xmlns:s = 
"uuid:BDC6E3F0-6DA3-11d1-A2A3-00AA00C14882" xmlns:rs = 
"urn:schemas-microsoft-com:rowset" xmlns:z = "#RowsetSchema" xmlns:b = 
"urn:schemas-microsoft-com:office:publisher" xmlns:ss = 
"urn:schemas-microsoft-com:office:spreadsheet" xmlns:c = 
"urn:schemas-microsoft-com:office:component:spreadsheet" xmlns:oa = 
"urn:schemas-microsoft-com:office:activation" xmlns:html = 
"http://www.w3.org/TR/REC-html40" xmlns:q = 
"http://schemas.xmlsoap.org/soap/envelope/" XMLNS:D = "DAV:" xmlns:x2 = 
"http://schemas.microsoft.com/office/excel/2003/xml" xmlns:ois = 
"http://schemas.microsoft.com/sharepoint/soap/ois/" xmlns:dir = 
"http://schemas.microsoft.com/sharepoint/soap/directory/" xmlns:ds = 
"http://www.w3.org/2000/09/xmldsig#" xmlns:dsp = 
"http://schemas.microsoft.com/sharepoint/dsp" xmlns:udc = 
"http://schemas.microsoft.com/data/udc" xmlns:xsd = 
"http://www.w3.org/2001/XMLSchema" xmlns:sub = 
"http://schemas.microsoft.com/sharepoint/soap/2002/1/alerts/" xmlns:ec = 
"http://www.w3.org/2001/04/xmlenc#" xmlns:sp = 
"http://schemas.microsoft.com/sharepoint/" xmlns:sps = 
"http://schemas.microsoft.com/sharepoint/soap/" xmlns:xsi = 
"http://www.w3.org/2001/XMLSchema-instance" xmlns:udcxf = 
"http://schemas.microsoft.com/data/udc/xmlfile" xmlns:wf = 
"http://schemas.microsoft.com/sharepoint/soap/workflow/" xmlns:mver = 
"http://schemas.openxmlformats.org/markup-compatibility/2006" xmlns:m = 
"http://schemas.microsoft.com/office/2004/12/omml" xmlns:mrels = 
"http://schemas.openxmlformats.org/package/2006/relationships" xmlns:ex12t = 
"http://schemas.microsoft.com/exchange/services/2006/types" xmlns:ex12m = 
"http://schemas.microsoft.com/exchange/services/2006/messages" XMLNS:Z = 
"urn:schemas-microsoft-com:" xmlns:st = ""><HEAD>
<META http-equiv=Content-Type content="text/html; charset=us-ascii">
<META content="MSHTML 6.00.6000.16705" name=GENERATOR>
<STYLE>@font-face {
        font-family: Cambria Math;
}
@font-face {
        font-family: Calibri;
}
@font-face {
        font-family: Garamond;
}
@font-face {
        font-family: Webdings;
}
@page Section1 {size: 8.5in 11.0in; margin: 1.0in 1.0in 1.0in 1.0in; }
P.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"
}
LI.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"
}
DIV.MsoNormal {
        FONT-SIZE: 12pt; MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.EmailStyle17 {
        FONT-WEIGHT: normal; COLOR: #1f497d; FONT-STYLE: normal; FONT-FAMILY: "Arial","sans-serif"; mso-style-type: personal
}
SPAN.EmailStyle19 {
        COLOR: #1f497d; FONT-FAMILY: "Calibri","sans-serif"; mso-style-type: personal-reply
}
.MsoChpDefault {
        FONT-SIZE: 10pt; mso-style-type: export-only
}
DIV.Section1 {
        page: Section1
}
</STYLE>
<!--[if gte mso 9]><xml>
 <o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
 <o:shapelayout v:ext="edit">
  <o:idmap v:ext="edit" data="1" />
 </o:shapelayout></xml><![endif]--></HEAD>
<BODY lang=EN-US vLink=purple link=blue>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2>Dear Vikram,</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2>Although I know nothing about GC equipment, physics 
mandates that all energy which goes into almost all&nbsp;mechanical / electrical 
devices becomes heat.&nbsp; Your job is to a) figure out whether the heat ends 
up in the conditioned space or elsewhere and b) figure out what the effective 
load diversity is for your particular piece of equipment. (almost nothing 
operates 100% of the time at 100% of its maximum energy.)</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2>Forgive me if I'm too elementary here with a 
couple&nbsp;simple examples:</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2>1)&nbsp;An exhaust fan motor imparts a certain amount of 
energy (its work energy) to the exhaust air.&nbsp; If the air ends up outdoors, 
that energy does not affect the AC load.&nbsp; In addition, the motor itself may 
be in the exhaust airstream or outside it.&nbsp; If it's in the airstream, the 
~10% motor inefficiency also ends up in the exhaust airstream.&nbsp; If the 
motor is outside the exhaust airstream, the ~10% ends up wherever the motor is 
located.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2>2) Similarly, an air handler fan motor imparts its work 
energy to the airstream and therefore always&nbsp;becomes part of the AC 
load.&nbsp; The motor inefficiency, depending on the motor placement, may become 
part of the AC load (or not).</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2>A fine point in this consideration is that belt-driven 
motors always lose ~6-7% via the transmission (belt) system.&nbsp; Most people 
forget about this.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008></SPAN><SPAN 
class=125391817-18082008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN>&nbsp;</DIV>
<DIV dir=ltr align=left><SPAN class=125391817-18082008><FONT face=Arial 
color=#0000ff size=2>I suspect that your GC equipment will dissipate all of its 
energy into the space it occupies unless, for example, it is water-cooled, in 
which case the water cooling system will remove some of the heat from the space 
in which it is located.</FONT></SPAN></DIV>
<DIV>&nbsp;</DIV>
<DIV class=Section1>
<P class=MsoNormal style="TEXT-ALIGN: center" align=center><B 
style="mso-bidi-font-weight: normal"><FONT size=4>The Building Performance 
Team<BR></FONT></B><B style="mso-bidi-font-weight: normal">James V. Dirkes II, 
P.E., LEED AP<BR></B>1631 Acacia Drive&nbsp;NW<BR>Grand Rapids, MI 49504<BR>616 
450 8653<o:p></o:p></P>
<P class=MsoNormal><o:p>&nbsp;</o:p></P></DIV>
<DIV>&nbsp;</DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Vikram 
Sami<BR><B>Sent:</B> Monday, August 18, 2008 1:04 PM<BR><B>To:</B> 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] CFD modeling for 
lab buildings<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV class=Section1>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'">I&#8217;m 
curious if there are any published papers on CFD modeling of lab equipment. I&#8217;m 
particularly interested in gas chromatographers. We are working on a lab 
building with GCs and I would like to see what portion of their considerable 
heat output is actually seen by the chillers. <o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-SIZE: 11pt; COLOR: #1f497d; FONT-FAMILY: 'Calibri','sans-serif'"><o:p>&nbsp;</o:p></SPAN></P>
<DIV>
<P class=MsoNormal 
style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><B><SPAN 
style="COLOR: black; FONT-FAMILY: 'Garamond','serif'">Vikram 
Sami,</SPAN></B><SPAN style="COLOR: #1f497d"> </SPAN><SPAN 
style="COLOR: black; FONT-FAMILY: 'Garamond','serif'">LEED AP</SPAN><SPAN 
style="COLOR: #1f497d"> <BR></SPAN><SPAN 
style="COLOR: black; FONT-FAMILY: 'Garamond','serif'">Direct Phone 404-253-1466 
| Direct Fax 404-253-1366</SPAN><SPAN style="COLOR: #1f497d"> 
<o:p></o:p></SPAN></P>
<P class=MsoNormal 
style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><B><SPAN 
style="COLOR: maroon; FONT-FAMILY: 'Garamond','serif'">L</SPAN></B><B><SPAN 
style="FONT-SIZE: 10pt; COLOR: maroon; FONT-FAMILY: 'Garamond','serif'">ORD</SPAN></B><B><SPAN 
style="COLOR: maroon; FONT-FAMILY: 'Garamond','serif'">, A</SPAN></B><B><SPAN 
style="FONT-SIZE: 10pt; COLOR: maroon; FONT-FAMILY: 'Garamond','serif'">ECK</SPAN></B><B><SPAN 
style="COLOR: maroon; FONT-FAMILY: 'Garamond','serif'"> &amp; 
S</SPAN></B><B><SPAN 
style="FONT-SIZE: 10pt; COLOR: maroon; FONT-FAMILY: 'Garamond','serif'">ARGENT</SPAN></B><B><SPAN 
style="COLOR: maroon; FONT-FAMILY: 'Garamond','serif'"> A</SPAN></B><B><SPAN 
style="FONT-SIZE: 10pt; COLOR: maroon; FONT-FAMILY: 'Garamond','serif'">RCHITECTURE</SPAN></B><B><SPAN 
style="COLOR: #1f497d"><BR></SPAN></B><SPAN 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Garamond','serif'">1201 
Peachtree Street NE, Suite 300, Atlanta, GA 30361</SPAN><SPAN 
style="COLOR: #1f497d"> <BR></SPAN><SPAN 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Garamond','serif'">Responsive 
Design</SPAN><SPAN style="COLOR: #1f497d"> </SPAN><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: #1f497d; FONT-FAMILY: Symbol">&middot;</SPAN><SPAN 
style="COLOR: #1f497d"> </SPAN><SPAN 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Garamond','serif'">Technological 
Expertise</SPAN><SPAN style="COLOR: #1f497d"> </SPAN><SPAN 
style="FONT-SIZE: 7.5pt; COLOR: #1f497d; FONT-FAMILY: Symbol">&middot;</SPAN><SPAN 
style="COLOR: #1f497d"> </SPAN><SPAN 
style="FONT-SIZE: 10pt; COLOR: #1f497d; FONT-FAMILY: 'Garamond','serif'">Exceptional 
Service</SPAN><SPAN style="COLOR: #1f497d"> <BR></SPAN><SPAN 
style="FONT-SIZE: 10pt; COLOR: #007f00; FONT-FAMILY: 'Garamond','serif'">Please 
visit our new website</SPAN><SPAN style="COLOR: #1f497d"> </SPAN><SPAN 
style="COLOR: black; FONT-FAMILY: 'Garamond','serif'">|</SPAN><SPAN 
style="COLOR: #1f497d"> <A href="file:///\\www.lordaecksargent.com\"><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: 'Garamond','serif'">www.lordaecksargent.com</SPAN></A><o:p></o:p></SPAN></P>
<P class=MsoNormal 
style="mso-margin-top-alt: auto; mso-margin-bottom-alt: auto"><SPAN 
style="FONT-SIZE: 24pt; COLOR: #007f00; FONT-FAMILY: Webdings">P </SPAN><SPAN 
style="FONT-SIZE: 10pt; COLOR: #007f00; FONT-FAMILY: 'Garamond','serif'">Think 
GREEN before you print.</SPAN><SPAN 
style="COLOR: #1f497d"><o:p></o:p></SPAN></P></DIV>
<DIV>
<DIV>
<P class=MsoNormal><o:p>&nbsp;</o:p></P></DIV></DIV></DIV></BODY></HTML>