<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML dir=ltr><HEAD>
<META HTTP-EQUIV="Content-Type" CONTENT="text/html; charset=iso-8859-1">


<META content="MSHTML 6.00.6000.16674" name=GENERATOR></HEAD>
<BODY>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008>All,</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN class=763454321-11082008>There 
is likely some confusion due to two statements in the LEED Reference 
Guide:</SPAN></FONT></DIV>
<UL>
  <LI><FONT face=Arial color=#0000ff size=2><SPAN class=763454321-11082008>On 
  Page 177, under "b. Opague Assemblies" the reference guide states 
  "<EM><U><STRONG>The Performance Rating Method</STRONG></U></EM> specifies the 
  type of assembly required for the Baseline Building wall, roof, and floor 
  construction. <STRONG><EM><U>The ECB method</U></EM></STRONG> varies the 
  construction assembly type modeled in the Building Budget Design based on the 
  actual construction assembly type modeled in the Proposed 
  Design."</SPAN></FONT></LI>
  <LI><FONT face=Arial color=#0000ff size=2><SPAN class=763454321-11082008>On 
  Page 180, under "Building Envelope" the reference guide states 
  "<STRONG><EM><U>The Performance Rating Method</U></EM></STRONG> requires that 
  the Proposed Design be modeled as designed with a few minor exceptions. For 
  the Baseline Design of new buildings, the above-grade walls, roof, and floor 
  assemblies must be modeled using light-weight assembly types (i.e., 
  steel-framed walls, roof with insulation entirely above deck, and steel-joist 
  floors), with ASHRAE Std. 90.1 prescriptive maximum U-factors for the 
  building's climate. <U>Even if the Proposed Design incorporates mass wall 
  construction, the Baseline Design must be modeled using a steel-framed 
  assembly:</U>"</SPAN></FONT></LI></UL>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008>Obviously, the reference to the ECB Method on page 177 
causes some confusion to the reader. However, I read that <U>all 
</U>building baseline constructions should use a light-weight, steel-framed 
construction per the statements on page 180.</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008>Regards</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008>Mitch</SPAN></FONT></DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008></SPAN></FONT> </DIV>
<DIV><FONT face=Arial color=#0000ff size=2><SPAN 
class=763454321-11082008><?xml:namespace prefix = o ns = 
"urn:schemas-microsoft-com:office:office" /><o:p></o:p> </DIV>
<DIV>
<DIV class=Section1>
<P style="MARGIN-BOTTOM: 6pt"><FONT color=#000000><B><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Mitchell J. 
Dec</SPAN></B><BR></FONT><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><FONT 
color=#000000><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Senior Energy 
Analyst</SPAN><BR><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">LEEDŽ 
Accredited Professional</SPAN></FONT></SPAN></P>
<P style="MARGIN-BOTTOM: 6pt"><FONT face=Arial size=2></FONT><A 
href="http://www.glumac.com/"><SPAN 
style="TEXT-DECORATION: none; text-underline: none"><FONT color=#000000><IMG 
height=37 src="cid:763454321@11082008-2c4f" width=339 border=0 
v:shapes="_x0000_i1025"><FONT face=Arial 
size=2></FONT></FONT></P></SPAN></A><o:p></o:p>
<DIV style="MARGIN-BOTTOM: 6pt"><FONT color=#000000>
<HR style="WIDTH: 247.5pt" align=left width=330 color=#9acb33 noShade SIZE=2>
</FONT></DIV>
<P><FONT color=#000000><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">320 SW 
Washington, Suite 200</SPAN><BR><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Portland, OR 
97204-2640</SPAN><BR></FONT><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><FONT color=#000000>T.  
503.227.5280  F. 503.274.7674<BR>Direct: <SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">503.345.6283</SPAN></FONT></SPAN></P>
<P><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"><SPAN 
style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"></SPAN><BR><B><SPAN 
style="COLOR: #333333">Thinking. Inside the 
building.</SPAN></B></SPAN><BR><U><SPAN 
style="FONT-SIZE: 10pt; COLOR: blue; FONT-FAMILY: Arial"><A 
href="http://www.glumac.com/" 
target=_blank>http://www.glumac.com/</A></SPAN></U> 
</P></DIV></SPAN></FONT></DIV>
<BLOCKQUOTE dir=ltr style="MARGIN-RIGHT: 0px">
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> 
  bldg-sim-bounces@lists.onebuilding.org 
  [mailto:bldg-sim-bounces@lists.onebuilding.org]<B>On Behalf Of </B>Aulbach, 
  John<BR><B>Sent:</B> Monday, August 11, 2008 2:29 PM<BR><B>To:</B> Chien Si 
  Harriman; bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> Re: [Bldg-sim] 
  multiple wall constructions for LEED<BR><BR></DIV></FONT>
  <DIV dir=ltr align=left><SPAN class=984422521-11082008><FONT face=Arial 
  color=#0000ff size=2>Hi Chien Si !!</FONT></SPAN></DIV>
  <DIV dir=ltr align=left><SPAN class=984422521-11082008><FONT face=Arial 
  color=#0000ff size=2></FONT></SPAN> </DIV>
  <DIV dir=ltr align=left><SPAN class=984422521-11082008><FONT face=Arial 
  color=#0000ff size=2>I believe you need only put in the one ASHRAE 90.1 
  minimum wall U-value. Exactly what Table 5.5 asks for.</FONT></SPAN></DIV>
  <DIV dir=ltr align=left><SPAN class=984422521-11082008><FONT face=Arial 
  color=#0000ff size=2></FONT></SPAN> </DIV>
  <DIV dir=ltr align=left><SPAN class=984422521-11082008>
  <DIV align=left>
  <DIV align=left><FONT color=#0000ff>John R. Aulbach, PE, CEM</FONT></DIV>
  <DIV align=left><FONT face=Arial size=2><EM>Project Manager</EM></FONT></DIV>
  <DIV align=left><FONT face=Arial size=2><FONT color=#0000ff>Nexant, 
  Inc</FONT>.</FONT></DIV>
  <DIV align=left><FONT face=Arial size=2>701 West Kimberly Ave., Suite 
  245</FONT></DIV>
  <DIV align=left><FONT face=Arial size=2>Placentia, CA 92870-6342 
  USA</FONT></DIV>
  <DIV align=left><FONT face=Arial size=2>Phone: 714-524-4402</FONT></DIV>
  <DIV align=left><FONT face=Arial size=2>Fax: 714-524-4407</FONT></DIV>
  <DIV align=left><FONT face=Arial size=2>email: <A 
  title=mailto:jaulbach@nexant.com 
  href="mailto:jaulbach@nexant.com">jaulbach@nexant.com</A></FONT></DIV>
  <DIV> </DIV></DIV></SPAN></DIV><BR>
  <DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
  <HR tabIndex=-1>
  <FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
  [mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Chien Si 
  Harriman<BR><B>Sent:</B> Monday, August 11, 2008 2:21 PM<BR><B>To:</B> 
  bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] multiple wall 
  constructions for LEED<BR></FONT><BR></DIV>
  <DIV></DIV>
  <DIV><FONT face=Arial color=#000000 size=2>Hi all-</FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>A quick, but kind of hazy question for me at 
  least, regarding LEED projects.  Let's just say, that a building is 
  composed of multiple wall types, spanning a range of the ASHRAE 90.1 
  definitions...some portions of the building is steel framed, another portion 
  is mass wall, and yet another portion is wood framed, for example.  In 
  this case, what would the baseline be defined as?  Does each wall remain 
  categorically intact, and you simply choose the baseline U-factor that 
  corresponds to that wall type, or do you have to determine the wall type that 
  makes up the majority of the proposed building, and choose this wall type as 
  the baseline wall type?  </FONT></DIV>
  <DIV><FONT face=Arial size=2></FONT> </DIV>
  <DIV><FONT face=Arial size=2>Thanks in advance,</FONT></DIV>
  <DIV><FONT face=Arial size=2>Chien</FONT></DIV></BLOCKQUOTE></BODY></HTML>