class=852420619-11082008>For those interested, I think I figured out how to do 
this (with some direction from Linda).  I set up a "dummy" water-cooled 
chiller with an associated drycooler for heat rejection.  The chiller EIR 
was set to 0, the condenser water circulating pump horsepower was set to 0, and 
the EIR of the drycooler was set to the power that I think the air-cooled 
chiller condenser fans will use during free-cooling 
operation.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008>I then set up two Equipment Control components called 
"Greater than 38" and "Less than 38".  "Less than 38" has my dummy chiller 
set up to handle the load, and "Greater than 38" has my normal air-cooled 
chillers set to handle the load.  I then set up a Load Management 
component.  Management Seq 1 references the "Less than 38" Eqpm Ctrl with 
the Max OSA Temp set to 38 degrees.  Management Seq 2 references the 
"Greater than 38" Eqpm Ctrl with the Max OSA Temp set to 110 degrees.  (You 
could set the switchover point to whatever you prefer).</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008>I didn't spend that much time fiddling with this, but 
it looks like it may have worked.  My dummy chiller operates 6 hrs in 
October, 19 in November, 106 in December, 149 in January, 133 in February, 47 in 
March and 4 in April (Washington, DC area).  That looks about 
right.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008>For reference, the utility bills dropped from $247,931 
to $246,744 (for a 140,000 sq ft office building in DC).  This worked out 
to a 6% reduction in total space cooling energy for the year, but only about a 
0.5% decrease in total utility bills.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008>And this doesn't take into account the added pressure 
drop across the air-cooled chiller condenser fans for the rest of the 
year.  This relatively minor increase in savings is probably why 
free-cooling coils in air-cooled chillers in this climate are not particularly 
favorable.  And also why the took the economizer requirement out of 
90.1-2004 and the 2006 IECC (for our climate zone).</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=852420619-11082008>I welcome any comments if I did something 
incorrectly....</SPAN></FONT></DIV>
<DIV> </DIV>
<DIV align=left>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><B><SPAN style="COLOR: teal; FONT-FAMILY: Arial">GHT 
Limited<BR></SPAN></B><st1:PersonName><B><SPAN 
style="FONT-SIZE: 11pt; FONT-FAMILY: Arial">James 
Hansen</SPAN></B></st1:PersonName><B><SPAN 
style="FONT-SIZE: 11pt; FONT-FAMILY: Arial">, <FONT size=2>PE, LEED 
AP</FONT></SPAN></B></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><B><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=2>Senior Associate</FONT></SPAN></B></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT size=1>1010 
N. Glebe Rd, Suite 200</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=1>Arlington, VA  22201-4749</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=1>703-338-5754 (Direct)</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=1>703-243-1200 (Office)</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=1>703-276-1376 (Fax)</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><A 
href="http://www.ghtltd.com/"><FONT 
size=2>www.ghtltd.com</FONT></A></SPAN></P></DIV>
<DIV> </DIV><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>James 
Hansen<BR><B>Sent:</B> Monday, August 11, 2008 1:51 PM<BR><B>To:</B> 
bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] Air-cooled chiller 
economizer<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV><SPAN class=399204817-11082008><FONT face=Arial size=2>Does anyone have 
insight on a relatively easy way to model free-cooling coils on air-cooled 
chillers?  I thought adding a drycooler might help simulate this, but I 
don't even think you can attach a heat-rejection device directly to a chilled 
water loop.  Is this one of those things that you have to "estimate" 
by approximating the total # of available free-cooling hours and 
subtracting compressor energy?</FONT></SPAN></DIV>
<DIV><SPAN class=399204817-11082008><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><SPAN class=399204817-11082008><FONT face=Arial 
size=2>Thanks</FONT></SPAN></DIV>
<DIV><SPAN class=399204817-11082008><FONT face=Arial 
size=2></FONT></SPAN> </DIV>
<DIV><B><SPAN style="COLOR: teal; FONT-FAMILY: Arial">GHT 
Limited<BR></SPAN></B><B><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial">James 
Hansen</SPAN></B><B><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial">, <FONT 
size=2>PE, LEED AP</FONT></SPAN></B></DIV>
<DIV align=left>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><B><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=2>Senior Associate</FONT></SPAN></B></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT size=1>1010 
N. Glebe Rd, Suite 200</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=1>Arlington, VA  22201-4749</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=1>703-338-5754 (Direct)</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=1>703-243-1200 (Office)</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><FONT 
size=1>703-276-1376 (Fax)</FONT></SPAN></P>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt; mso-layout-grid-align: none" 
align=left><SPAN style="FONT-SIZE: 11pt; FONT-FAMILY: Arial"><A 
href="http://www.ghtltd.com/"><FONT 
size=2>www.ghtltd.com</FONT></A></SPAN></P></DIV>
<DIV> </DIV><!--[object_id=#ghtltd.com#]-->
<P align=left><FONT size=2><FONT face=Tahoma><FONT color=#0000ff>
<HR>
</FONT></FONT><FONT color=#0000ff><FONT color=#000000><FONT face=Arial>The 
information contained in this communication is confidential, may be privileged, 
and is intended only for the use of the addressee.  It is the property of 
GHT Limited.  Unauthorized use, disclosure or copying of this communication 
or any part thereof is strictly prohibited and may be unlawful.  If you 
have received this communication in error, please notify me immediately by 
return e-mail or by e-mail to </FONT><A href="mailto:ght@ghtltd.com"><FONT 
face=Arial>ght@ghtltd.com</FONT></A><FONT face=Arial>, and destroy this 
communication and all copies thereof, including all attachments.  Thank 
you.</FONT></FONT><FONT face=Tahoma color=#000000></FONT>
<P></P></FONT></FONT></BODY></HTML>