<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:arial, helvetica, sans-serif;font-size:10pt"><DIV>I don't think Trace has a specific way or pre-programmed feature that could be used to model this.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Your best bet is to figure out an equivalent shading factor or over hang.&nbsp; Maybe the mftr could give you an equivalent shading coefficient.&nbsp; </DIV>
<DIV>&nbsp;</DIV>
<DIV>Other options would be:</DIV>
<DIV>1. Divide the window into two windows from an input standpoint based on what percentage of the window is shaded from the louver.&nbsp; Input the portion that is shaded into trace with an overhang or with a north exposure or as spandrel glass.</DIV>
<DIV>2. Input the window as&nbsp;many smaller windows each with their own individual overhang.&nbsp; Although, this would probably take a long time from an input standpoint and may slow down running the program.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Maybe you could do a separate trace run looking at one window with louvers on each exposure using Option 2 above.&nbsp; Then&nbsp;use the results to figure out an effective shading coefficient or equivalent overhang to use in your main Trace file.</DIV>
<DIV>&nbsp;</DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif"><BR>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif">----- Original Message ----<BR>From: Myrene Giuliani &lt;mygiuliani@yahoo.com&gt;<BR>To: Energy Modeling &lt;bldg-sim@lists.onebuilding.org&gt;<BR>Sent: Wednesday, July 30, 2008 5:30:04 PM<BR>Subject: [Bldg-sim] modeling horizontal louvers in Trane Trace<BR><BR>I need to model some horizontal louvers that are part of a window and I am not sure if it can be done in Trane Trace.&nbsp; The louvers cover the full height of the window.&nbsp; They are about 2" deep and are spaced evenly at 2".&nbsp; Please let me know.<BR><BR>Thank you,<BR><BR>Myrene Giuliani <BR><BR><BR>&nbsp; &nbsp; &nbsp; <BR>_______________________________________________<BR>Bldg-sim mailing list<BR><A href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To unsubscribe from this mailing list send&nbsp; a blank