<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:arial, helvetica, sans-serif;font-size:10pt"><DIV>Regarding your first question when you're modeling a building connected to a city chilled water loop: </DIV>
<DIV>&nbsp;</DIV>
<DIV>First -&nbsp;be aware that LEED recently issues new modeling rules for this exact situation.&nbsp; The document is called "Required Treatment of District Thermal Energy"&nbsp; and is located at usgbc.org/LEED/LEED Resources/LEED Reference Documents.&nbsp; If your project was registered BEFORE&nbsp;May 28, 2008, then you can elect to follow these rules.&nbsp; If you're project was registered AFTER that date, then you MUST&nbsp;follow the new rules.&nbsp; The rules&nbsp;basically effect the baseline building systems that are modeled....i.e. so what you're comparing yourself to.&nbsp; </DIV>
<DIV>&nbsp;</DIV>
<DIV>In terms of modeling the situation, (I'm not an Equest user....but, if it's similar to Trace at the plant simulation&nbsp;level) you'd choose "purchased chilled water" as the equipment/system type.&nbsp; Then you'd input the cost of your chilled water (per therm or other similar unit that your software uses)&nbsp;in the economics portion of the software.</DIV>
<DIV>&nbsp;</DIV>
<DIV>J&nbsp;<BR></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif"><BR>
<DIV style="FONT-SIZE: 12pt; FONT-FAMILY: times new roman, new york, times, serif">----- Original Message ----<BR>From: Keith Swartz &lt;kswartz@ecw.org&gt;<BR>To: bldg-sim@lists.onebuilding.org<BR>Sent: Thursday, July 17, 2008 4:29:03 PM<BR>Subject: [Bldg-sim] FW: eQUEST - City Chilled Water Loop and ASHRAE Appendix G<BR><BR>
<STYLE>
<!-- 
 _filtered {font-family:Tahoma;panose-1:2 11 6 4 3 5 4 4 2 4;}
 
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin-right:0in;margin-left:0in;font-size:12.0pt;font-family:"Times New Roman";}
a:link, span.MsoHyperlink
        {color:blue;text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {color:purple;text-decoration:underline;}
span.EmailStyle17
        {font-family:Arial;color:navy;}
 _filtered {margin:1.0in 1.25in 1.0in 1.25in;}
div.Section1
        {}
-->
</STYLE>

<STYLE>
p.MsoNormal
        {margin-left:3.0pt;}
</STYLE>

<DIV class=Section1>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">Michael,</SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">Regarding modeling “extra” systems for conditioned spaces, the key is “<B><I><SPAN style="FONT-WEIGHT: bold; FONT-STYLE: italic">conditioned</SPAN></I></B>” spaces. See the definition of “conditioned space” in the standard. If a space has no heating or cooling, it is not a conditioned space. The User’s Manual for ASHRAE 90.1-2004 clarifies that “This requirement only applies to conditioned spaces in the building. Semiheated spaces would only have a heating system; unconditioned spaces would have neither heating nor cooling systems.” (p. G-21) See the definition for “semiheated space” too. I believe the intent here is to add a cooling system to spaces that only have a heating system and add a heating system to spaces that only have a cooling system.</SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">If the model is for LEED, the LEED-NC v2.2 Reference Guide clarifies it. “For areas of the project without heating or cooling systems (such as parking garages), there is no need to model heating or cooling systems in either the Proposed or Baseline Designs.” (p. 181)</SPAN></FONT></P>
<P class=MsoNormal><FONT face=Arial color=navy size=2><SPAN style="FONT-SIZE: 10pt; COLOR: navy; FONT-FAMILY: Arial">I don’t know of any restrictions on the thermostat settings, so you might be able to just make the thermostat setting of the fictitious system pretty extreme so that the system rarely (or never) comes on. This would satisfy the requirement to have a system, but keep your energy consumption numbers more realistic.</SPAN></FONT></P>
<DIV>
<P class=MsoNormal><FONT face="Times New Roman" color=navy size=3><SPAN style="FONT-SIZE: 12pt; COLOR: navy">Sincerely,<BR><BR>Keith Swartz, PE, LEED® AP<BR>Energy Engineer / Senior Project Manager<BR></SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">Energy</SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy"> </SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">Center</SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy"> of </SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">Wisconsin</SPAN></FONT><BR><FONT color=navy><SPAN style="COLOR: navy">455 Science Drive, </SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">Suite</SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy"> 200<BR></SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">Madison</SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">, </SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">WI</SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">
 </SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">53711<BR><BR></SPAN></FONT><FONT color=navy><SPAN style="COLOR: navy">Phone: 608-238-8276 ext. 123, Fax: 608-238-0523<BR><A href="http://www.ecw.org/" target=_blank rel=nofollow></A><A href="http://www.ecw.org/" target=_blank rel=nofollow>www.ecw.org</A>&nbsp; The Energy Center of Wisconsin is a nonprofit organization that seeks solutions to energy challenges.</SPAN></FONT></P></DIV>
<DIV>
<DIV class=MsoNormal style="MARGIN: 0in 0in 0pt; TEXT-ALIGN: center" align=center><FONT face="Times New Roman" size=3><SPAN style="FONT-SIZE: 12pt">
<HR tabIndex=-1 align=center width="100%" SIZE=2>
</SPAN></FONT></DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><B><FONT face=Tahoma size=2><SPAN style="FONT-WEIGHT: bold; FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">From:</SPAN></FONT></B><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma"> Michael Bejrowski [mailto:MichaelB@auseea.com] <BR><B><SPAN style="FONT-WEIGHT: bold">Sent:</SPAN></B> Wednesday, July 16, 2008 2:40 PM<BR><B><SPAN style="FONT-WEIGHT: bold">To:</SPAN></B> Bldg-sim@lists.onebuilding.org<BR><B><SPAN style="FONT-WEIGHT: bold">Subject:</SPAN></B> [Bldg-sim] eQUEST - City Chilled Water Loop and ASHRAE Appendix G</SPAN></FONT></P></DIV>
<P class=MsoNormal><FONT face="Times New Roman" size=3><SPAN style="FONT-SIZE: 12pt">&nbsp;</SPAN></FONT></P>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">How do you model a building that is attached to a city chilled water loop?</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">&nbsp;</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">and</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">&nbsp;</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">Have any of you had experience with ASHRAE 90.1 Append. G, Table G3.1, 1c where it&nbsp;says "All conditioned spaces in the proposed design shall be simulated as being both heated and cooled even if no heating or cooling system is to be installed,..."?</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">&nbsp;</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">We modeled a building that had heated vehicle maintenance bays, so by the ASHRAE standard it would seem that we could not model it that way, but would have to model it as being heated AND cooled.</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">&nbsp;</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">Any ideas or experience would be greatly appreciated.</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">&nbsp;</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">&nbsp;</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">Thanks,</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">&nbsp;</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">Michael Bejrowski</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">Mechanical EIT</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">Austin, TX</SPAN></FONT></P></DIV>
<DIV>
<P class=MsoNormal style="MARGIN: 0in 0in 0pt"><FONT face=Tahoma size=2><SPAN style="FONT-SIZE: 10pt; FONT-FAMILY: Tahoma">&nbsp;</SPAN></FONT></P></DIV></DIV></DIV></DIV></div></body></html>