If this is a south-western facing room, this makes sense.&nbsp; For spaces with alot of glass, peak cooling loads typically occur in the fall when the sun sits lower in the sky.&nbsp; For a western or south-western facing room, at 5pm in October, the sun is shining directly into the windows.&nbsp; With a 62 degree outdoor air temperature, conductive losses are low, so the heat gained by the space does not have a chance to leave (as it would in December, with temperatures in the 30&#39;s).&nbsp; Solar gain trumps all other cooling loads in spaces with large window areas.&nbsp; You could try modeling an alternative with a really low SHGC glass, or exterior vertical shades and see how this affects the peak.<br>
<br>While this is the peak space load, this may not be the peak coil load as ventilation is not taken into account in the LS-B report (drives me crazy).&nbsp; It all depends on whether ventilation air is conditioned before it arrives at the terminal coils or not...<br>
<br>--<br>Karen<br><br><br><br><div class="gmail_quote">On Tue, Jul 8, 2008 at 9:30 AM, Tobias, Mike &lt;<a href="mailto:mtobias@loringengineers.com">mtobias@loringengineers.com</a>&gt; wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
The LS-B Space Peak Load Components Report shows my peak cooling load<br>
for a perimeter hotel room with windows occurring on Oct 2 at 5pm when<br>
its 62F outside in new york city. &nbsp;I believe this is an error. &nbsp;My peak<br>
heating load for this space appears correct occurring on jan 23 at 8am.<br>
Solar radiation dominates the total space load at 75% of the total<br>
cooling load. &nbsp;The overall building peak cooling load occurs on July 1<br>
at 8pm when its 92F outside which appears correct. &nbsp;What do you think?<br>
<font color="#888888"><br>
Mike Tobias PE<br>
<a href="mailto:mtobias@loringengineers.com">mtobias@loringengineers.com</a><br>