Hi,<br>
<br>
I am currently modeling a library building with large open book stack
spaces. The baseline system is System 5 Packaged VAV w/ reheat.
systems According to ASHRAE 90.1 Appendix G3.1.3.13, I have to model
the minimum VAV flow setpoint as 0.4 cfm/sq.ft. The problem is that
since these interior stack areas have almost no internal loads other
than lighting, the design cfm/sq.ft is less than 0.3 cfm/sq.ft. When I
run the simulation using Carrier HAP, the system CFM is much larger
than is should be as it is now based on the 0.4 cfm/sq.ft rather than
the calculated loads. <br>
<br>
For example, 6300 sq. ft. Stacks Rm. 300 calculated cfm based on load
is 1245 cfm (0.2 cfm/sq.ft). Since this is less than 0.4 cfm/sq.ft, the
simulation results in a much higher 2520 cfm<br>
<br>
I realize that this can only help my LEED energy savings calculation,
but am I doing this correctly?<br>
<br>
Thanks,<br>
<div class="moz-signature">-- <br>
<meta http-equiv="Content-Type" content="text/html; ">
<meta name="GENERATOR" content="Microsoft FrontPage 4.0">
<meta name="ProgId" content="FrontPage.Editor.Document">
<title>New Page 1</title>
<b><font color="#002d56" face="ArialMT">
</font></b>
<p align="left"><b><font color="#002d56" face="ArialMT">———————————————————————————<br>
</font><font color="#002d56" face="ArialMT" size="2">Allan Fox, P.E.
CBCP, LEED AP</font></b><font color="#002d56" face="ArialMT" size="2"><br>
Senior Mechanical Engineer
<br>
<a href="mailto:afox@osborn-eng.com">afox@osborn-eng.com</a></font></p>
<p align="left"><font color="#002d56" face="ArialMT"><font size="2"><b>OSBORN
ENGINEERING<br>
</b>1300 East 9th Street Suite 1500 | Cleveland, OH 44114<b><br>
t </b>216 861 2020 <b>x</b>3040 | <b>f </b>216 861 3329 |
</font><b><font size="2">osborn-eng.com</font><br>
———————————————————————————<br>
</b></font><b><font color="#002d56" face="ArialMT" size="1"><br>
</font></b><font color="#002d56" face="ArialMT" size="1">The
information in this e-mail message, including any
attachments, is for the sole use of the intended recipient(s)
as addressed,
and may contain confidential information. Any unauthorized review,
use,
copying, disclosure, or distribution is prohibited. If you are not
the intended recipient, please contact the sender by reply e-mail and
destroy
all copies of the original message. To view the complete email
disclosure
statement, please visit our website at: <a
href="http://www.osborn-eng.com/disclosure.html">http://www.osborn-eng.com/disclosure.html<br>
</a>© Copyright 2008 The Osborn Engineering Company. All rights
reserved.</font></p>
</div>
</body>
</html>