<div>Usually when you specify a heat pump system, the cooling compressor type is specified as single speed (under airside HVAC, Cooling, Unitary Power). I believe that the part load ratio is based on how often the compressor cycles over the hour simulated.</div>
<div> </div>
<div>Also, even though the system is PVVT, default minimum airflows are given at a ratio of 1.</div>
<div> </div>
<div>--</div>
<div>Karen<br><br> </div>
<div class="gmail_quote">On Tue, May 20, 2008 at 9:45 AM, Tony Kriel <<a onclick="return top.js.OpenExtLink(window,event,this)" href="mailto:tkriel@sustaineng.com" target="_blank">tkriel@sustaineng.com</a>> wrote:<br>
<blockquote class="gmail_quote" style="PADDING-LEFT: 1ex; MARGIN: 0pt 0pt 0pt 0.8ex; BORDER-LEFT: rgb(204,204,204) 1px solid">
<div lang="EN-US" vlink="purple" link="blue">
<div>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">SIM List,</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">We are modeling a GSHP system in eQuest. After selecting the options in the wizard and running the model we noticed that the space heating was quite a bit lower when compared to a VAV system for the same project. </span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">We then went into detailed mode and started to look into what performance curves the heat pumps had defaulted. It seemed that the default part load curve (HEAT-EIR-FPLR) that eQuest selected, seemed very aggressive. It is my understanding that the heat pumps cycle on and off when needed, and when they cycle on and off they operate at 100%. So, should the part load curve be changed to be 100%, (ie it shouldn't have a part load curve)? Or should we be looking at something else.</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Thanks,</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial"> </span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Tony Kriel</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Mechanical Engineer</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Sustainable Engineering Group, LLC.</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">431 Charmany Drive, Suite 102</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Madison</span></font><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">, WI 53719</span></font></p>
<p><font face="Times New Roman" size="3"><span style="FONT-SIZE: 12pt"> </span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Phone: (608) 231-9664 ext. 16</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Fax: (608) 231-9665</span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">E-mail: <a onclick="return top.js.OpenExtLink(window,event,this)" href="mailto:tkriel@sustaineng.com" target="_blank">tkriel@sustaineng.com</a></span></font></p>
<p><font face="Arial" size="2"><span style="FONT-SIZE: 10pt; FONT-FAMILY: Arial">Web: <a onclick="return top.js.OpenExtLink(window,event,this)" href="http://www.sustaineng.com/" target="_blank">www.sustaineng.com</a> </span></font></p>
<p><font face="Times New Roman" size="3"><span style="FONT-SIZE: 12pt"> </span></font></p></div></div><br>_______________________________________________<br>Bldg-sim mailing list<br><a onclick="return top.js.OpenExtLink(window,event,this)" href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a onclick="return top.js.OpenExtLink(window,event,this)" href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>