<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML><HEAD>
<META HTTP-EQUIV="Content-Type" CONTENT="text/html; charset=iso-8859-1">
<TITLE>Space Cooling Energy Consumption with GSHP</TITLE>

<META content="MSHTML 6.00.2900.3314" name=GENERATOR></HEAD>
<BODY>
<DIV><SPAN class=186375621-13052008><FONT face=Arial color=#0000ff 
size=2>Thomas:</FONT></SPAN></DIV>
<DIV><SPAN class=186375621-13052008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN>&nbsp;</DIV>
<DIV><SPAN class=186375621-13052008><FONT face=Arial color=#0000ff size=2>Does 
the simulated dorm operate 24 hours? What efficiency you specified for GSHP? 
What is the loop temperature in heating and cooling? Have you checked the pump 
related input and defaults?</FONT></SPAN></DIV>
<DIV><SPAN class=186375621-13052008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN>&nbsp;</DIV>
<DIV><SPAN class=186375621-13052008><FONT face=Arial color=#0000ff size=2>There 
are lots of thing can affect the results.</FONT></SPAN></DIV>
<DIV><SPAN class=186375621-13052008><FONT face=Arial color=#0000ff 
size=2></FONT></SPAN>&nbsp;</DIV>
<DIV><SPAN class=186375621-13052008><FONT face=Arial color=#0000ff 
size=2>Xiaobing</FONT></SPAN></DIV>
<BLOCKQUOTE>
  <DIV class=OutlookMessageHeader dir=ltr align=left><FONT face=Tahoma 
  size=2>-----Original Message-----<BR><B>From:</B> 
  bldg-sim-bounces@lists.onebuilding.org 
  [mailto:bldg-sim-bounces@lists.onebuilding.org]<B>On Behalf Of </B>Tom 
  Butler<BR><B>Sent:</B> Tuesday, May 13, 2008 4:53 PM<BR><B>To:</B> 
  bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> [Bldg-sim] Space Cooling 
  Energy Consumption with GSHP<BR><BR></FONT></DIV><!-- Converted from text/rtf format -->
  <P><FONT face=Arial size=2>I am modeling an apartment style dormitory for a 
  project in Atlanta, GA. Each of the 45 units is served by its own heat pump, 
  along with a few zones for public areas. For an energy efficiency grant 
  application I have compared the designed system, a ground source heat pump, 
  with an air source heat pump prescribed by 90.1. Other than the systems, the 
  models are identical. </FONT></P>
  <P><FONT face=Arial size=2>The energy use for space cooling is significantly 
  higher for the GSHP system (24,000 kWh vs. 17,000 kWh). Because the power 
  required to run pumps offsets the savings in heating energy, this destroys the 
  rationale for spending the extra money on the Ground Source Heat Pump, as well 
  as our chances of receiving the grant.</FONT></P>
  <P><FONT face=Arial size=2>Has any one encountered this issue? </FONT></P><BR>
  <P><FONT face=Arial size=2>Thanks</FONT> </P>
  <P><FONT face=Arial size=2>tb </FONT></P>
  <P><B><FONT face=Garamond color=#000000>Thomas Butler,</FONT></B> <FONT 
  face=Garamond color=#000000>LEED AP</FONT><B> </B><BR><FONT face=Garamond 
  color=#000000>Direct Phone 404-253-1435 | Direct Fax 404-253-1335</FONT> </P>
  <P><B><FONT face=Garamond color=#800000>L</FONT><FONT face=Garamond 
  color=#800000 size=2>ORD</FONT><FONT face=Garamond color=#800000>, 
  A</FONT><FONT face=Garamond color=#800000 size=2>ECK</FONT><FONT face=Garamond 
  color=#800000> &amp; S</FONT><FONT face=Garamond color=#800000 
  size=2>ARGENT</FONT><FONT face=Garamond color=#800000> A</FONT><FONT 
  face=Garamond color=#800000 size=2>RCHITECTURE</FONT><BR></B><FONT 
  face=Garamond size=2>Responsive Design</FONT> <FONT face=Symbol size=1>·<FONT 
  face="Courier New"></FONT></FONT> <FONT face=Garamond size=2>Technological 
  Expertise</FONT> <FONT face=Symbol size=1>·<FONT 
  face="Courier New"></FONT></FONT> <FONT face=Garamond size=2>Exceptional 
  Service</FONT> <BR><A href="file://www.lordaecksargent.com"><U></U><U><FONT 
  face=Garamond color=#0000ff>www.lordaecksargent.com</FONT></U></A> 
</P><BR></BLOCKQUOTE></BODY></HTML>