color=#0000ff size=2>The issue is slightly more complicated for unitary 
equipment over 5 tons because the ARI 340/360 testing standard for determining 
the EER of larger unitary equipment has pre-defined limits on the allowed 
fan ESP during test conditions.  If you are simulating packaged equipment 
that is designed with higher external fan static pressures than required by ARI 
340/360 and you use the as-designed fan power or fan power allowed by 
ASHRAE90.1 for calculating "Cooling-Only" EER,  you will 
over-estimate cooling energy savings.  This issues applies to Appendix G 
baseline systems 3,4,5 and 7 and any as-designed equipment whose 
performance is covered by ARI 340/360 (see minimum efficiency tables 
in Chapter 6 of ASHRAE 90).  </FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=750324419-18042008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=750324419-18042008><FONT face=Arial 
color=#0000ff size=2>For packaged equipment over 5 tons you should estimate 
fan power at the ARI 340/360 test conditions when separating EER into fan 
and cooling energy components rather than using rated fan power or the ASHRAE 
fan power allowance.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=750324419-18042008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=750324419-18042008> </SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=750324419-18042008><FONT face=Arial 
color=#0000ff size=2>Mike</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=750324419-18042008><FONT face=Arial 
color=#0000ff size=2></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=750324419-18042008>
<DIV align=left><FONT face="Arial Black" size=2>Michael Tillou, PE, 
LEED</FONT></DIV>
<DIV align=left>
<DIV align=left><FONT face="Arial Black" size=1></FONT></DIV><FONT 
face="Arial Black" size=1>P: 413-458-9870</FONT> <FONT face="Arial Black" 
size=1>C: 413-652-1087</FONT></DIV></SPAN></DIV><FONT face=Arial color=#0000ff 
size=2></FONT><BR>
<DIV class=OutlookMessageHeader lang=en-us dir=ltr align=left>
<HR tabIndex=-1>
<FONT face=Tahoma size=2><B>From:</B> bldg-sim-bounces@lists.onebuilding.org 
[mailto:bldg-sim-bounces@lists.onebuilding.org] <B>On Behalf Of </B>Loren 
Appin<BR><B>Sent:</B> Friday, April 18, 2008 2:30 AM<BR><B>To:</B> Michael 
Rosenberg<BR><B>Cc:</B> bldg-sim@lists.onebuilding.org<BR><B>Subject:</B> Re: 
[Bldg-sim] PTAC and PTHP EER, fan energy<BR></FONT><BR></DIV>
<DIV></DIV>Could anyone else comment on this?  I had asked this question a 
couple of months ago, and through some research and guidance received the answer 
that:<BR><BR>The EER does include the fan power, which you would calculate from 
Table 6.8.1.D and you would calculate this for each system based upon it's 
auto-sized capacity; thus, you will use a different EER for each 
system.<BR><BR>An important clause to then look at is G3.1.2.1 which states that 
equipment efficiencies must be broken down into their component parts, such as 
the EER into EIR and fan power.  One way of doing this is to parse it out 
using equest, capturing the correct EIR and then plugging that back in with a 
separate fan power.<BR><BR>To get the fan power you would use Table G3.1.2.9 to 
get BHP and calculate the fan power from this.<BR><BR>All of this, though, is 
according to ASHRAE 2004, I have not been using the 2007 Addendum.  I just 
wanted to see if this is what everyone else has been 
doing?<BR><BR>Thanks<BR><BR><B>Loren Appin</B><BR><BR>Energy 
Engineer<BR><BR><B>Silpa Inc.</B><BR><FONT size=1><B>s</B> i m p l e  . 
 <B>s</B> c i e n t i f i c  .  <B>s</B> u s t a i n a b l 
e<BR></FONT><FONT size=1>AMERICAS | ASIA<BR><A href="http://www.silpainc.com/" 
target=_blank>www.silpainc.com</A></FONT><BR><BR><BR><BR>
<DIV class=gmail_quote>On Thu, Apr 17, 2008 at 7:26 PM, Michael Rosenberg <<A 
href="mailto:Michael.Rosenberg@state.or.us" 
target=_blank>Michael.Rosenberg@state.or.us</A>> wrote:<BR>
<BLOCKQUOTE class=gmail_quote 
style="PADDING-LEFT: 1ex; MARGIN: 0pt 0pt 0pt 0.8ex; BORDER-LEFT: rgb(204,204,204) 1px solid">The 
  EER does include the fan power. The baseline fan power allowance in Appendix G 
  from 90.1 2004 was recognized as being much too high for PTACs and PTHPs. An 
  addendum was issued lowering the value to 0.3 W/cfm. This is captured in the 
  new 2007 version of 90.1 Appendix G.<BR><BR>Michael Rosenberg<BR>Oregon 
  Department of Energy<BR>625 Marion St. N.E.<BR>Salem, OR 97301-3742<BR>Phone : 
  (503) 373-7809<BR>Fax: (503) 373-7806<BR><BR>>>> "Xu, Xiaowei" <<A 
  href="mailto:xiaowei.xu@ny.fk.com" target=_blank>xiaowei.xu@ny.fk.com</A>> 
  4/17/2008 8:10:25 AM >>><BR>
  <DIV>Hi,<BR><BR>I have a quick question about the EER requirement for the PTAC 
  and PTHP<BR>system. In Standard 2004, Table 6.8.1D gives out the minimum 
  requirement<BR>for the PTAC and PTHP system. My question is does this EER 
  include the<BR>fan power or not?<BR><BR><BR><BR>Also for the PTAC and PTHP 
  system, following the Appendix G fan power<BR>energy calculation, the fan 
  power would be about 0.7~0.8W/cfm. However<BR>the manufacture's catalog data 
  usually gives out the value around<BR>0.2~0.3W/cfm, which means the proposed 
  case would get a lot of fan<BR>energy savings. Does this make sense? Thanks a 
  lot.<BR><BR><BR><BR><BR><BR>Xiaowei Xu<BR><BR>Engineer<BR><BR> FLACK + 
  KURTZ<BR><BR>475 Fifth Avenue<BR><BR>New York, NY 
  10017<BR><BR><BR><BR></DIV><A href="http://www.flackandkurtz.com" 
  target=_blank>http://www.flackandkurtz.com</A> <<A 
  href="http://www.flackandkurtz.com/" 
  target=_blank>http://www.flackandkurtz.com/</A>><BR>
  <DIV><BR>212.532.9600 Main<BR><BR>212.951.2662 Direct<BR><BR>212.689.7489 
  Fax<BR><A href="mailto:xiaowei.xu@ny.fk.com" 
  target=_blank>xiaowei.xu@ny.fk.com</A><BR><BR>Ensuring that today's built 
  environment preserves the natural<BR>environment in which we live.<BR><BR>This 
  e-mail may contain confidential and/or privileged information. If<BR>you are 
  not the intended recipient (or have received this e-mail in<BR>error) please 
  notify the sender immediately and destroy this e-mail.<BR>Any unauthorized 
  copying, disclosure or distribution of the material in<BR>this email is 
  strictly 
  forbidden.<BR><BR><BR><BR><BR></DIV>_______________________________________________<BR>Bldg-sim 
  mailing list<BR><A 
  href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" 
  target=_blank>http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</A><BR>To 
  unsubscribe from this mailing list send  a blank message to <A 
  href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" 
  target=_blank>BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR></BLOCKQUOTE></DIV><BR><BR 
clear=all><BR>-- <BR>Loren Appin | <A href="mailto:loren.appin@gmail.com" 
target=_blank>loren.appin@gmail.com</A> </BODY></HTML>