Could anyone else comment on this?&nbsp; I had asked this question a couple of months ago, and through some research and guidance received the answer that:<br><br>The EER does include the fan power, which you would calculate from Table 6.8.1.D and you would calculate this for each system based upon it&#39;s auto-sized capacity; thus, you will use a different EER for each system.<br>

<br>An important clause to then look at is G3.1.2.1 which states that equipment efficiencies must be broken down into their component parts, such as the EER into EIR and fan power.&nbsp; One way of doing this is to parse it out using equest, capturing the correct EIR and then plugging that back in with a separate fan power.<br>

<br>To get the fan power you would use Table G3.1.2.9 to get BHP and calculate the fan power from this.<br><br>All of this, though, is according to ASHRAE 2004, I have not been using the 2007 Addendum.&nbsp; I just wanted to see if this is what everyone else has been doing?<br>

<br>Thanks<br><br><b>
Loren Appin</b><br>
<br>
Energy Engineer<br>
<br><b>
Silpa Inc.</b><br><font size="1"><b>
s</b> i m p l e &nbsp;. &nbsp;<b>s</b> c i e n t i f i c&nbsp; .&nbsp; <b>s</b> u s t a i n a b l e<br></font><font size="1">AMERICAS | ASIA<br><a href="http://www.silpainc.com/" target="_blank">www.silpainc.com</a></font><br><br><br><br><div class="gmail_quote">
On Thu, Apr 17, 2008 at 7:26 PM, Michael Rosenberg &lt;<a href="mailto:Michael.Rosenberg@state.or.us" target="_blank">Michael.Rosenberg@state.or.us</a>&gt; wrote:<br><blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">

The EER does include the fan power. The baseline fan power allowance in Appendix G from 90.1 2004 was recognized as being much too high for PTACs and PTHPs. An addendum was issued lowering the value to 0.3 W/cfm. This is captured in the new 2007 version of 90.1 Appendix G.<br>


<br>
Michael Rosenberg<br>
Oregon Department of Energy<br>
625 Marion St. N.E.<br>
Salem, OR 97301-3742<br>
Phone : (503) 373-7809<br>
Fax: (503) 373-7806<br>
<br>
&gt;&gt;&gt; &quot;Xu, Xiaowei&quot; &lt;<a href="mailto:xiaowei.xu@ny.fk.com" target="_blank">xiaowei.xu@ny.fk.com</a>&gt; 4/17/2008 8:10:25 AM &gt;&gt;&gt;<br>
<div>Hi,<br>
<br>
I have a quick question about the EER requirement for the PTAC and PTHP<br>
system. In Standard 2004, Table 6.8.1D gives out the minimum requirement<br>
for the PTAC and PTHP system. My question is does this EER include the<br>
fan power or not?<br>
<br>
<br>
<br>
Also for the PTAC and PTHP system, following the Appendix G fan power<br>
energy calculation, the fan power would be about 0.7~0.8W/cfm. However<br>
the manufacture&#39;s catalog data usually gives out the value around<br>
0.2~0.3W/cfm, which means the proposed case would get a lot of fan<br>
energy savings. Does this make sense? Thanks a lot.<br>
<br>
<br>
<br>
<br>
<br>
Xiaowei Xu<br>
<br>
Engineer<br>
<br>
 &nbsp;FLACK + KURTZ<br>
<br>
475 Fifth Avenue<br>
<br>
New York, NY 10017<br>
<br>
<br>
<br>
</div><a href="http://www.flackandkurtz.com" target="_blank">http://www.flackandkurtz.com</a> &lt;<a href="http://www.flackandkurtz.com/" target="_blank">http://www.flackandkurtz.com/</a>&gt;<br>
<div><br>
212.532.9600 Main<br>
<br>
212.951.2662 Direct<br>
<br>
212.689.7489 Fax<br>
<a href="mailto:xiaowei.xu@ny.fk.com" target="_blank">xiaowei.xu@ny.fk.com</a><br>
<br>
Ensuring that today&#39;s built environment preserves the natural<br>
environment in which we live.<br>
<br>
This e-mail may contain confidential and/or privileged information. If<br>
you are not the intended recipient (or have received this e-mail in<br>
error) please notify the sender immediately and destroy this e-mail.<br>
Any unauthorized copying, disclosure or distribution of the material in<br>
this email is strictly forbidden.<br>
<br>
<br>
<br>
<br>
</div>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send &nbsp;a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><br>-- <br>Loren Appin | <a href="mailto:loren.appin@gmail.com" target="_blank">loren.appin@gmail.com</a>