<DIV>Dear colleague:</DIV>
<DIV> </DIV>
<DIV><FONT face=宋体 size=2>      <FONT 
face="Times New Roman" size=3>I have met a serious problem during LEED a 
factory.</FONT></FONT></DIV>
<DIV><FONT><FONT><FONT face=宋体 size=2>        
</FONT>
<DIV><FONT face=宋体 size=2>      <FONT 
face="Times New Roman" size=3>For this project, There equipped some 
HL-600G&HL-600 Gravity type skylight ventilator on the factory roof and some 
operable window at the surrounding walls. But the height of the ventilator is 
from 10.5m to 13m over the ground surface.</FONT></FONT></DIV>
<DIV><FONT face=宋体 size=2></FONT> </DIV>
<DIV>           
 LEED/ASHRAE 62 requirment: Natural ventilation spaces shall be 
permanently open to and within 8m of operable wall or roof opening to the 
outdoors.   </DIV>
<DIV><FONT face=宋体 size=2></FONT> </DIV>
<DIV>           Assume the 
breathing zone is 1.6m high, So LEED accept height of the ventilator 
should be lower than 9.6(1.6+8)m. So the interior area(more than 8 m away from 
surrounding walls) does not have valid natural ventalition system as described 
by LEED/ASHRAE.</DIV>
<DIV><FONT face=宋体 size=2></FONT> </DIV>
<DIV><FONT face=宋体 
size=2>     </FONT></DIV></FONT></FONT></DIV>
<DIV>           The 
designer does not agree our opinion, their reason:</DIV>
<DIV> </DIV>
<DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=827563803-10042008>1.    the design is to give comfort to 
the operators on the floor since the process equipment is very hot and the space 
within the 8-m high will get unbearably hot.  Nanjing is known for its hot 
summers</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=827563803-10042008>2.    the specification is for 22 air 
changes per hour (ACPH) and the need for 8-m floor to roof eave height is to aid 
natural draught ventilation so it is easier to reach 22 ACPH</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=827563803-10042008>3.    The supplier is to warrant 22 ACPH 
and provide ASHRAE calculations to reach this figure.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=827563803-10042008>4.    It is less acceptable to fill the 
roof area with mechanical roof ventilators since it is energy dependent (an 
increase in the carbon footprint) and as such agaist the LEED 
concept</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT face=Arial color=#0000ff size=2><SPAN 
class=827563803-10042008>5.    The approach is within the 
philosophy of LEED in that the operators comfort and well being is at the heart 
of this design, the use on natural ventilation address sustainable design in 
that no energy is required to get 22 ACPH.</SPAN></FONT></DIV></DIV>
<DIV><FONT face=宋体 size=2></FONT> </DIV>
<DIV><FONT face=宋体 size=2>    <FONT face="Times New Roman" 
size=3>QUESTION:  1. Are the designers reason will be agreed by 
LEED?</FONT></FONT></DIV>
<DIV> </DIV>
<DIV><FONT face=宋体 
size=2>               <FONT 
face="Times New Roman" size=3> 2.  If we installed some exhaust fan on 
the roof, makeup air will go in through operable windows on the surrounding 
walls. whether the ventalition system changed to mechanical ventalition system 
as defined by ASHRAE/LEED?</FONT></FONT></DIV>
<DIV> </DIV>
<DIV> Any further suggestion is highly appreciated. </DIV>
<DIV><FONT face=宋体 size=2></FONT> </DIV>
<DIV><FONT face=宋体 size=2></FONT> </DIV>
<DIV>Ziqiang Chen<BR> <BR>Project 
Engineer<BR> <BR>EMSI<BR> <BR>86-21-54962727 
TEL<BR> <BR>86-21-64435767 FAX<BR> <BR><A 