<DIV>I would interpret that as by zone demand, since you will have both internal and external gains figured in to the "minimum cooling load conditions".&nbsp; There could be instances where the outdoor air temperature is relatively low, but your solar load in conjunction with the internal heat gains may be high, so a straight outdoor air reset wouldn't work.</DIV>
<DIV>&nbsp;</DIV>
<DIV>My thoughts.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Stirling<BR><BR>&gt;&gt;&gt; Julia Beabout &lt;juliabeabout@yahoo.com&gt; 4/5/2008 4:55 PM &gt;&gt;&gt;<BR></DIV>
<DIV style="FONT-SIZE: 10pt; FONT-FAMILY: arial, helvetica, sans-serif">
<DIV>All,</DIV>
<DIV>RE: ASHRAE 90.1, App G, Article G.4.2.3.1.2, Supply Air Reset</DIV>
<DIV>&nbsp;</DIV>
<DIV>Addendum A revised this article to say: "The air temperature for cooling shall be rest higher by 5F under the minimum cooling load conditions".</DIV>
<DIV>This sounds to me like they are saying the supply air temperature should be reset based on outdoor air temperature.&nbsp; This would be quite a change in concept from the original version of this article which&nbsp;required the supply air temperature to be reset based zone demand.</DIV>
<DIV>&nbsp;</DIV>
<DIV>Are others out there interpretting the revised addendum A version of this article the same way I am....i.e. that the SAT should now be reset based on outdoor air temperature?&nbsp; Or, are people still interpretting it&nbsp;as the SAT should be reset based on zone demand?</DIV>
<DIV>&nbsp;</DIV>
<DIV>Would appreciate any feedback anyone has on this, especially with respect to doing a LEED energy model.</DIV>
<DIV>Thanks.</DIV>
<DIV>Julia</DIV>