<div>A quasi
DOE2 approach would be to calculate the hourly system loads using DOE2
and calculate VRV energy consumption using spreadsheet calculations.
You will have to create a regression based model to calculate the
energy consumption as a function of the capacity and outdoor air
temperature (The data is available on Mr. Slim website). Once you are
sure the model is working correctly (be sure to put limits on your
equations for out of range data) you can use the hourly weather
boundary conditions to calculate the annual energy consumption. </div>
<div> </div>
<div>If you are doing code compliance using eQUEST you can calculate
the average calibrated EER using the above methodology and use it as a
DOE2 input. </div>
<div> </div>
Best Regards,<br>Haider M. Khan, MSME <br> <br>ICF International<br>9300 Lee Highway,<br>Fairfax, VA 22031<br>Ph: 703 934-3868<br>Fax: 703 934-3530<br><br><div class="gmail_quote">On Tue, Apr 1, 2008 at 6:59 AM, Howe, Timothy <<a href="mailto:Timothy.Howe@stantec.com">Timothy.Howe@stantec.com</a>> wrote:<br>
<blockquote class="gmail_quote" style="border-left: 1px solid rgb(204, 204, 204); margin: 0pt 0pt 0pt 0.8ex; padding-left: 1ex;">
<div>
<p><font size="2">As I am sure you are aware, this system type is not yet supported by DOE/eQuest. I personally have been trying to develop an exceptional calc method, using the bin output of eQuest.<br>
<br>
Anyone else successfully produced a side calc for this system?<br>
<br>
Tim.<div class="Ih2E3d"><br>
<br>
<br>
-----Original Message-----<br>
From: <a href="mailto:bldg-sim-bounces@lists.onebuilding.org" target="_blank">bldg-sim-bounces@lists.onebuilding.org</a> on behalf of Chatfield, Gary<br>
Sent: Mon 3/31/2008 5:56 PM<br>
To: <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a><br>
Subject: [Bldg-sim] VRV systems<br>
<br>
Does anyone have an idea of the percentage improvement of a VRV system<br>
over ASHRAE 90.1 Appendix G system 7?<br>
<br>
<br>
<br>
I have currently modeled one and I am not sure whether the results I am<br>
getting are accurate or I have done something wrong.<br>
<br>
<br>
<br>
Any information would be much appreciated.<br>
<br>
<br>
<br>
Gary Chatfield<br>
<br></div>
LEED(r) AP <div class="Ih2E3d"><br>
<br>
FLACK + KURTZ<br>
<br>
385 Pilot Road<br>
<br>
Suite D<br>
<br>
Las Vegas, NV 89119<br>
<br>
</div><a href="http://www.flackandkurtz.com" target="_blank">http://www.flackandkurtz.com</a> <<a href="http://www.flackandkurtz.com/" target="_blank">http://www.flackandkurtz.com/</a>> <div class="Ih2E3d"><br>
<br>
702.897.8181 Main<br>
<br>
702.352.9562 Direct<br>
<br>
702.914.6966 Fax<br>
<a href="mailto:gary.chatfield@lv.fk.com" target="_blank">gary.chatfield@lv.fk.com</a><br>
<br>
Ensuring that today's built environment preserves the natural<br>
environment in which we live.<br>
<br>
This e-mail may contain confidential and/or privileged information. If<br>
you are not the intended recipient (or have received this e-mail in<br>
error) please notify the sender immediately and destroy this e-mail.<br>
Any unauthorized copying, disclosure or distribution of the material in<br>
this email is strictly forbidden.<br>
<br>
<br>
<br>
<br>
<br>
<br>
</div></font>
</p>
</div>
<br>_______________________________________________<br>
Bldg-sim mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG">BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>